I'm loving my first install of Sol Arks - One downside of Sol-Ark (and I can't find many!) is that the GEN terminal can only handle 1 of the following 3: Generator, AC Coupling, or Smart Load.  So if you want both a generator and AC coupling you have to either do a separate transfer switch for the GEN and not run it through the inverters - or you have to go with their internal DC MPPTif you do want the GEN to charge the batteries (unless you are off-grid totally and have no Grid in which case you might be able to run the Generator into Grid?  not sure about that - don't quote me!).

Anyone else with any downsides?

Best,

Jeff



Jason Szumlanski wrote on 9/10/20 4:44 AM:
There is a huge distinction in a hybrid inverter that integrates MPPT charge control. Eliminating all of the extraneous hardware and circuit protection associated with charge controllers is very appealing. The 500V input limit is also a game-changer in terms of wire size. I'm very interested in this approach.

On the flip size, an AC Coupled approach is also appealing in a lot of circumstances. Since Sol-Ark supports that, too, it's hard to find downsides other than their infancy in the industry.

And for what it's worth, my experience with SMA tech support recently has been abysmal. Long hold times and getting bounced around departments.

Jason Szumlanski

*

*


On Wed, Sep 9, 2020 at 9:50 PM Mark Frye <[email protected] <mailto:[email protected]>> wrote:

    The most important thing here is that no one is standing up to
    sing the praises of either SMA or Outback.

    I myself have sent about 2 hours on hold over 2 days trying to get
    an issue addressed by SMA.

    Re: Sol-Arc I would pay a lot extra or take some not so good
    aspect in exchange for good technical support.

    On 9/9/2020 1:12 PM, Jason Szumlanski wrote:
    Any tips on combining AC output from these units when stacking
    several of them? What bus/OCPD system are you using? Same
    question for generator/grid input.

    The solar MPPT inputs appear to be dead simple.

    Jason Szumlanski


        

        
        

    *

    *


    On Tue, Sep 8, 2020 at 10:45 PM MiJo Nels
    <[email protected] <mailto:[email protected]>>
    wrote:

        we've found SolArk to be SOLID!! .. And yes 8 inv yield about
        96kW, with a TON of surge capabilities..

        Joe Nelson

        Project Manager C-46/C-10
        Sustainable Energy Group Inc., A California Corporation

        CSL# 868816
        www.SustainableEnergyGroup.com
        
<https://mailtrack.io/trace/link/8f0e320b52948f22a9ae9682bd3b5e9dc8d6c68f?url=http%3A%2F%2Fwww.SustainableEnergyGroup.com&userId=1613865&signature=e7d246f94af9a065>
        530-273-4422 (Office)

        530-217-8385 (Cell)

        

           


        ------------------------------------------------------------------------
        *From:* RE-wrenches
        <[email protected]
        <mailto:[email protected]>> on behalf
        of [email protected] <mailto:[email protected]>
        <[email protected] <mailto:[email protected]>>
        *Sent:* Tuesday, September 8, 2020 1:24:03 PM
        *To:* 'RE-wrenches' <[email protected]
        <mailto:[email protected]>>
        *Subject:* Re: [RE-wrenches] Microgrid... Outback or SMA or
        other?

        I also suggest the Sol-Ark 12’s. Extremely efficient, simple
        to program, does a wonderful job in either ac coupling, stand
        alone or pure off grid and terrific customer support.

        Peter Giroux

        ASAE

        *From:*RE-wrenches <[email protected]
        <mailto:[email protected]>> *On
        Behalf Of *Bryan Norkunas
        *Sent:* Tuesday, September 8, 2020 1:50 PM
        *To:* 'RE-wrenches' <[email protected]
        <mailto:[email protected]>>
        *Subject:* Re: [RE-wrenches] Microgrid... Outback or SMA or
        other?

        Sol-Arks would be possible, you can link 8 inverters.

        *Bryan *

        *PV-Cables*

        *From:*RE-wrenches
        [mailto:[email protected]] *On Behalf
        Of *Chris Schaefer
        *Sent:* Tuesday, September 8, 2020 10:40 AM
        *To:* RE-wrenches
        *Subject:* Re: [RE-wrenches] Microgrid... Outback or SMA or
        other?

        I'd suggest giving the crew at Sol-Ark a quick call @
        972-575-8875 with their 12kw unit. Not sure what their max
        number of inverters are.

        Christopher

        On Tue, Sep 8, 2020 at 1:14 PM Kienan Maxfield
        <[email protected]
        <mailto:[email protected]>> wrote:

            Hey all, I'm designing a microgrid sized off-grid system
            for somebody, and I'm just wondering if anyone knows of
            any issues with the following designs...

            The client says he needs 70 kW. His load data looks
            pretty solid, so I'm sticking to using that number as a
            minimum, at least during the initial proposal stage. I
            only know of two possible equipment options for this size
            range...

             1. I think I can use up to 10 Outback Radians, for up to
                an 80 kW system. Are there any bugs or problems with
                using this many inverters on one hub? I know I've
                read about issues with selling to the grid, but
                that's not an issue, this is off-grid.
             2. I know that the SMA cluster box with sunny islands
                can allow for up to a 72 kW system. Do you know of
                any bugs or problems with this system?

            Are there any other options that anyone would suggest?
            Schneider's website says they can only do up to 61 kW,
            and Victron can only do up to 60 kW.

            I know that the Outback system would yield a 240/120
            Split-Phase system and that the SMA would yield a 208/120
            3Ø system, but this doesn't really matter either way for
            this job.

            Thanks so much,

            Kienan

            *Maxfield Solar*

            *[email protected]*
            <mailto:[email protected]>

            *(801) 631-5584 (Cell)***

            _______________________________________________
            List sponsored by Redwood Alliance

            List Address: [email protected]
            <mailto:[email protected]>

            Change listserver email address & settings:
            http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
            
<https://mailtrack.io/trace/link/7118772550f67326bf449e9f3105d94b2a7b74b4?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=e1b83eb5e4f926e7>

            List-Archive:
            http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
            
<https://mailtrack.io/trace/link/c5457950749993eaf94dc7f72a33825e6e66fb1b?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=0031eb630b917fa3>

            List rules & etiquette:
            www.re-wrenches.org/etiquette.htm
            
<https://mailtrack.io/trace/link/863e7b45d70c42504299d435c477fd7ce070a999?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=201d4fc86e181859>

            Check out or update participant bios:
            www.members.re-wrenches.org
            
<https://mailtrack.io/trace/link/b5c596979aba68fb00e5e571f62bcbaeaadd3618?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=b27563b3083d3ceb>


--
        Chris Schaefer’s
        Image removed by sender.
        
<https://mailtrack.io/trace/link/6b69a480ea4449f57c42f803d4a726d5ddf0ccc4?url=http%3A%2F%2Fwww.solarandwindfx.com%2F&userId=1613865&signature=6bb84a96dad38d97>
        /Tel/Fax 585-229-2083 or Cell 585-748-1870
        //5115 South Hill Road ~ Canandaigua New York 14424
        www.solarandwindfx.com
        
<https://mailtrack.io/trace/link/864e18304c1425fb0f58d6ed8ea0e16c3e9402d7?url=http%3A%2F%2Fwww.solarandwindfx.com&userId=1613865&signature=87fa9d489354e433>
        ~ E-mail: //[email protected]
        <mailto:[email protected]>/

        /Image removed by sender./

        Thomas Jefferson, the author of our great Constitution, once
        said, "democracy" will cease to exist when you take away from
        those who are willing to work and give to those who would not."


        
<https://mailtrack.io/trace/link/f4964f47f3632046571a644ebfc74dd37fc349ab?url=http%3A%2F%2Fwww.avg.com%2Femail-signature%3Futm_medium%3Demail%26utm_source%3Dlink%26utm_campaign%3Dsig-email%26utm_content%3Demailclient&userId=1613865&signature=7ef512bd066bbd50>
                Virus-free. www.avg.com
        
<https://mailtrack.io/trace/link/48a44a842703a6744e4bd9b4bdadc457b6f4638e?url=http%3A%2F%2Fwww.avg.com%2Femail-signature%3Futm_medium%3Demail%26utm_source%3Dlink%26utm_campaign%3Dsig-email%26utm_content%3Demailclient&userId=1613865&signature=3e478a2a375a7bc5>


        _______________________________________________
        List sponsored by Redwood Alliance

        List Address: [email protected]
        <mailto:[email protected]>

        Change listserver email address & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
        
<https://mailtrack.io/trace/link/fc1b2521beb6ed5044854d33d56b95e71ca61590?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=b85aa44e99dc5faf>

        List-Archive:
        http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
        
<https://mailtrack.io/trace/link/1b09831c60927375ede751a7f47a27309b4c858c?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=6712962d0ceaf701>

        List rules & etiquette:
        www.re-wrenches.org/etiquette.htm
        
<https://mailtrack.io/trace/link/de9674746eedb972903621c016fadae65329a20d?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=164d7b7638da0383>

        Check out or update participant bios:
        www.members.re-wrenches.org
        
<https://mailtrack.io/trace/link/9b916e5e7e182544268c032b7ad89b5bb3ec64ad?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=bee7ba1ac877929f>


    _______________________________________________
    List sponsored by Redwood Alliance

    List Address:[email protected]
    <mailto:[email protected]>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
    
<https://mailtrack.io/trace/link/bc1dfc88c7999f47f10d4f75be24b0b1a9107e47?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=3af4cd2f9e95c66c>

    
List-Archive:http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
    
<https://mailtrack.io/trace/link/8a35d4ef560780fc7340088e0b755a516ee757d8?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=14abd03ed82088c4>

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    
<https://mailtrack.io/trace/link/1223e546d7c2d1872fa70dc8605af274ff2665de?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=ad527ae315c76471>

    Check out or update participant bios:
    www.members.re-wrenches.org
    
<https://mailtrack.io/trace/link/0f9efb827e162f2d58e74b3f0f046a32945e2edb?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=87bd1495e740447a>

    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: [email protected]
    <mailto:[email protected]>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
    
<https://mailtrack.io/trace/link/d0deefc4e6a8debd5b8abdde3afc44c86994f28c?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=56c8ac84b4211516>

    List-Archive:
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
    
<https://mailtrack.io/trace/link/4de70129f1d6519ae4887f672f558b51a6285743?url=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=177d5b1c95cbef2c>

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    
<https://mailtrack.io/trace/link/9cb9a72d33ec8e47fe536b23930788f42715d6a5?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=2f4d3d48fc28f962>

    Check out or update participant bios:
    www.members.re-wrenches.org
    
<https://mailtrack.io/trace/link/241a1c2847564fc6df61a1f14b2d66ea535594fe?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=9020190af4c79c8f>



_______________________________________________
List sponsored by Redwood Alliance

List Address:[email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



--
~~~~~~~~~~~
Jeff Clearwater
Village Power Design
linkedin <https://www.linkedin.com/in/jeff-clearwater-0622a312/>
www.villagepowerdesign.com <http://www.villagepowerdesign.com>
cell - 413-559-9763
~~~~~~~~~~~~~~~~~~~~~~~
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to