Hello Tump
You may want to go into the aux setpoints on the inverter being used to signal 
a gen run condition and check to see
how it is programmed. It could be that the aux is being instructed to turn on
by the aux setpoints as set in the inverter.
If AGS tells it to turn on great but if inside the inverters aux programming 
some parameters are being met that tell the 12 volt aux to active then 
seemingly random gen runs can occur.
Depending on age and the firmware of the inverter there are 9 or more 
programmable conditions that can trigger the 12 volt aux. At one point there 
was a setpoint called Remote which told the inverter some other device other 
than  you is in control of your auxiliary output.
  If you do not see a Remote setting you might try setting the inverters aux to 
Vent Fan then set the trigger point (Battery Voltage) to a condition that is 
impossible to achieve. I have a 48 volt system and I can set the Vent Fan 
trigger point up to 72VDC this will ensure the AGS is the only way the 12 volt 
Aux can be activated.
I left a message on your phone if you continue to have issues please call me.
Take Care Sir


From: RE-wrenches <[email protected]> On Behalf Of Tump
Sent: Friday, October 2, 2020 7:24 AM
To: RE-wrenches <[email protected]>
Subject: [RE-wrenches] Mate3 verses Mate3S

I have a client w/ 8 stack of older VFX3648s, Off Grid. Presently connected to 
a Mate 3 & older hub 10.  The generator run time/shut down time is never the 
same, sometimes 10+ hours of running while the inverters in “silent” mode.  Gen 
stays running despite full batteries, confirmed by battery voltage & using my 
refractometer.
The only "gen trigger" is battery voltage. I have cleared the history 
repeatedly & updated the Mate3 FW.
 Is there any conflict replacing the Mate 3 with the Mate 3S in an older system?
I will be also changing out the Hub as well. Thoughts/suggestions
[email protected]<blocked::mailto:[email protected]%22%20%5Co%20%22blocked::mailto:[email protected]>
               
www.SWNL.net<blocked::http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/>
                Solarwinds Northernlights
       Serving Mid Coast Maine & Northern California
                         207-832-7574   Cl. 610-517-8401
                              Blair "TUMP" May
               ********  MAINE'S CHARTER ********
                      NABCEP    "Certified PV Installer"

              ********  MAINE'S CHARTER ********
                  Trace Xantrex "Certified" Dealer / Installer"





This email and any attachments may contain confidential information that is 
intended only for the recipient(s). If you have received this email in error, 
please notify the sender and delete it from your system. Any views or opinions 
presented in this email are solely those of the author and do not necessarily 
represent those of the company or its affiliates. This email does not 
constitute an agreement to conduct transactions by electronic means and does 
not create any legally binding contract or enforceable obligation in the 
absence of a fully signed written contract. The recipient should check this 
email and any attachments for viruses. The company accepts no liability for any 
loss or damage caused by software viruses. If you are the intended recipient 
and you do not wish to receive similar email(s) from us in the future then 
please notify the sender. Please consider the environment before printing.
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to