We use the FM 100, but not Outback inverters.  We have one Mate 3 meter on the truck, we use it to program the controller, and then pull the meter. It holds all its programming, and this saves the customer $600.00.  They can monitor with the amp hr meter (Magnum or Trimetric)

Its not the best solution, and I find it annoying that Outback's most expensive controller does not have an onboard screen like the much lower cost little FMs.

Ray Walters
Remote Solar
303 505-8760

On 10/19/20 12:55 PM, Jay wrote:
On page 71 there is a small note about hooking up a FNDC without an inverter.

It might be what Brad was mentioning.

Jay


On Oct 19, 2020, at 12:48 PM, Dan Fink <[email protected]> wrote:


Maybe Brad is referring to the GFDI jumper or the RSS jumper? I don't know of a jumper to activate comms with the Mate 3S.

The former is for bonding and you remove it if you use an external GFDI, like a Midnite GFCI in a Midnite MNDC enclosure. It's the little black wire with 2 red spade connectors under the terminal block.

The RSS jumper you have to make out of a scrap of wire to DIS-able the Flexmax 100 internal RSS trigger. It goes between the yellow and purple terminal blocks. If you don't install it, the CC assumes the RSS has been activated. I love this one for my students, when their homework before lab class is to *thoroughly* read the instructions and make notes! I can easily tell if they actually did LOL.

Dan Fink
Owner, Buckville Energy Consulting
NABCEP Certified PV System Inspector
IREC Certified Instructor™ for:
~ PV Installation Professional
~ Small Wind Installer
NABCEP Registered Continuing Education Providers
d <mailto:[email protected]>[email protected] <mailto:[email protected]>
970-672-4342

On Sat, Oct 17, 2020 at 8:11 AM Bradley Bassett <[email protected] <mailto:[email protected]>> wrote:

    I think there is a jumper in the FM100 that will allow the Mate3s
    to communicate with it. I don't remember off hand where it is and
    am not at a computer with that info, but maybe this will prompt a
    look at the manual to see if they mention it.

    Brad


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to