Is it possible that neutral is bonded to ground in the generator?  I've found lots of multi-bonded neutrals over the years, and had it cause all sorts of weirdness.

Ray Walters
Remote Solar
303 505-8760

On 12/19/20 5:33 PM, jay wrote:
HI All,

I have a client with a older Kohler 8-10kw generator, VFX 3648 stacked 
inverters, newer rolls batteries. its been installed and operating normally for 
10+ years.

Customer had to upgrade the house for code, which involved installing GFCI 
outlets and GFCI breakers.

Since then the  GFI outlets trip every time the generator starts but only after 
3-30 minutes.   They work normally on the inverters. And if you do a 
bypass/generator direct the GFI outlets don’t trip.

The GFI breakers trip when the generator is about to turn off, not during warm 
down but say 30 minutes before it will turn off.  So charging current is at the 
lowest. And again they all work normally on the inverters and all the rest of 
the charge cycle.


Voltage is a bit high, around 254v-259v from the generator but it is the whole 
time and seems to stable voltage. But if the voltage was the issue the outlets 
would keep tripping.  If it was too high for the breakers, why at the end and 
not the beginning?

I’m thinking its possibly a control board in the generator that’s not working 
well.  Can’t keep up with the PF for the inverters, etc.

Buts its a new issue I’ve not run across.

Any ideas?

thanks

jay

peltz power




_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to