It might be worth checking the brushes if it is an older unit. Chris Worcester 
[email protected] from my Samsung Galaxy s9.
-------- Original message --------From: William Miller 
<[email protected]> Date: 12/19/20  6:30 PM  (GMT-08:00) To: RE-wrenches 
<[email protected]> Subject: Re: [RE-wrenches] generator 
tripping GFCI Friends:I have seen THD on the voltage waveform trip GFIs and 
AFCIs. The case where this happened was during gen run periods. AC to DC 
converters can be brutal in regards to generating distortion and sending it to 
loads. I am out in the shop away from the manuals, but check if these FX 
inverters can be programmed for Support mode on the gen input. This may knock 
THD back to acceptable levels, if indeed this is the cause. Best of luck. 
William Millerwww.millersolar.comOn Dec 19, 2020, at 5:33 PM, Darryl Thayer 
<[email protected]> wrote:The way a GFCI operates is by comparing the line 
current and the neutral current inside the device.  If some of the neutral 
current is returning through a ground circuit instead of the neutral the 
imbalance will trip the device.  The generator neutral and the inverter neutral 
must have a common neutral-ground bond and only one!  Your presentation 
indicates operational differences, multiple bonding points (two or more) can 
cause a neutral ground imbalance when load, source changes occur.  The 
load-source changes can affect the tripping result.    On Sat, Dec 19, 2020 at 
5:23 PM jay <[email protected]> wrote:HI All,

I have a client with a older Kohler 8-10kw generator, VFX 3648 stacked 
inverters, newer rolls batteries. its been installed and operating normally for 
10+ years.

Customer had to upgrade the house for code, which involved installing GFCI 
outlets and GFCI breakers.  

Since then the  GFI outlets trip every time the generator starts but only after 
3-30 minutes.   They work normally on the inverters. And if you do a 
bypass/generator direct the GFI outlets don’t trip.

The GFI breakers trip when the generator is about to turn off, not during warm 
down but say 30 minutes before it will turn off.  So charging current is at the 
lowest. And again they all work normally on the inverters and all the rest of 
the charge cycle.


Voltage is a bit high, around 254v-259v from the generator but it is the whole 
time and seems to stable voltage. But if the voltage was the issue the outlets 
would keep tripping.  If it was too high for the breakers, why at the end and 
not the beginning?

I’m thinking its possibly a control board in the generator that’s not working 
well.  Can’t keep up with the PF for the inverters, etc.  

Buts its a new issue I’ve not run across.

Any ideas?

thanks

jay

peltz power




_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


_______________________________________________List sponsored by Redwood 
AllianceList Address: [email protected] listserver email 
address & 
settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgThere
 are two list archives for searching. When one doesn't work, try the 
other:https://www.mail-archive.com/[email protected]/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orgList
 rules & etiquette:http://www.re-wrenches.org/etiquette.htmCheck out or update 
participant bios:http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to