For all of our free standing arrays we now use a Ufer clamp to the rebar either 
cage or just anti spin rebar that is welded to the pole in the concrete, with 
#4 braided copper up to the pole combiner box, inverter, etc. for our ground.
With a pole mount & a concrete base it is way easier & less expensive than a 
ground rod, & the inspector seems happier with this approach. 



Dana Orzel                              Great Solar Works, Inc. 
C - 208.721.7003                       [email protected]
Idaho Contractor - # 028765         Idaho PV # 028374
NABCEP # 051112-136                       www.greatsolarworks.com
"Responsible Technologies for Responsible People since 1988"  
 Please consider the environment before printing this email.


-----Original Message-----
From: RE-wrenches <[email protected]> On Behalf Of 
[email protected]
Sent: Wednesday, June 23, 2021 9:33 PM
To: RE-wrenches <[email protected]>
Subject: Re: [RE-wrenches] Top of Pole Mount Array on Ledge

Ben, 
There is a way if the ledge is solid and true. Twice I have done the following 
with ledge at 18” to 24” below grade. Excavate down to ledge, drill down into 
the ledge and you will determine the suitability of the following method. Drill 
for a pattern of many rebar penetrations in to the ledge. Drill to a reasonable 
depth (as deep into the ledge as you are able) in my case it was based on our 
drilling tool and bit length capabilities. We used a large sono tube. 42” as a 
recall, both of these jobs were over 12 years ago and my recall on the exact 
size may be off. 
Determine the best adhesive product to use in your drilled holes for the rebar, 
again my memory fails as to what we used based on recommendation from a local 
civil engineer. The sono tube height above grade was determined to be 2’ for 
one TPM12 and 3.5’ above grade for a TPM16. Depth down to the ledge determines 
how high above grade you need the concrete footing/base. Use rebar lengths that 
will end a few inches below the finished surface. For grounding you can coil up 
ground wire and lay it on the surface of the ledge before your concrete pour. I 
ran the ground wire through a short length of 1/2” or 3/4” PVC conduit, to 
protect the copper ground wire where it comes out of the concrete. Place the 
conduit coming out of the concrete with the ground wire just to the side of 
where the mounting plate base for the TPM will be and fill the PVC conduit with 
a good caulk sealer to keep air and water out of this hole as a nexus of 
concrete, and air will corrode the copper. The TPM’s for those two jobs were 
made of 8” SCHD 80 steel, we had a large plate welded to the bottom with 4 
vertical side supports on the pipe up about a foot. Place the appropriate sized 
anchor bolts in the concrete pour to match your TPM base. Both of these TPM’s 
have worked out well over the years. Local conditions will determine the 
suitability of this method.


Sent from my iPhone

> On Jun 23, 2021, at 6:39 PM, Ben's Solar and Battery <[email protected]> 
> wrote:
> 
> Hi Wrenches,
> 
> We typically use SunModo ground mounts with ground screws which we can put 
> just about anywhere as our screw guy has a rock drill.  
> We have one customer who is dead set on a top of pole mount array and will 
> not settle for a typical ground mount with multiple posts.  
> There is shallow ledge all over her property and we feel that digging 
> multiple large holes to find one spot where we might be able to get deep 
> enough would be a waste of time and resources.  We have called an underground 
> locator who uses ground penetrating radar and he scanned a few spots, but was 
> unable to give us a good location based on soil types.   
> What are you guys doing in this situation?  Are there any alternatives, such 
> as a pole mount with large base and ground screws?
> I hate saying it can't be done! 
> 
> Thanks! 
> Ben 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to