Words of wisdom Ray! One has to occasionally measure the impedance
especially if you are in lightning country! 

I wish the midnite spd's had
another blue led that told you impedance was in a good range. Probably not
easy, but a nice dream!  

Dave Angelini Offgrid Solar
"we go where
powerlines don't"
http://members.sti.net/offgridsolar/ [1]
e-mail
[email protected] [2]
text 209 813 0060

On Fri, 25 Jun 2021 12:16:18
-0400, Ray  wrote:    

Copper can get a pretty good oxide layer on it as
well, but I'm not versed in the science enough to know how any of that
effects the conductivity. Instead, I assume that the NEC has investigated
corrosion, and so we just follow the code. For plate electrodes
(250.52(A)(7)), it just specifies dimensions and thickness, and
specifically mentions bare iron or steel. 250.52(A)(3)(_1_) for Concrete
encased electrodes (UFER) also allows bare steel reinforcing rod, while
section (_2_) allows your #4 copper UFER.  

Lacking further information, I
just go with the code, and my own ground impedance measurements over the
years. My small sampling of measurements has found steel rebar grounds and
large steel pipe (4"D and larger) to be under 25 ohms, while I have
measured copper coated rods as high as 700 ohms in dry soil. I haven't
measure copper UFER or compared it to steel, so again, I don't know. It
might be better than steel, but all are allowed by code.  

Ultimately it
might come down to soil and weather conditions for different areas? 
Ray
Walters
Remote Solar
303 505-8760
 On 6/25/21 10:35 AM, Dana Orzel wrote: 

That's why we use the Ufer, our AHJ assumes that once a layer of rust
develops this is not valid...........

Dana Orzel Great Solar Works, Inc.

C - 208.721.7003 [email protected] [3]
Idaho Contractor - # 028765 Idaho
PV # 028374
NABCEP # 051112-136 www.greatsolarworks.com [4]
"Responsible
Technologies for Responsible People since 1988" 
 Please consider the
environment before printing this email.

-----Original Message-----
From:
RE-wrenches  [5] On Behalf Of Ray
Sent: Thursday, June 24, 2021 4:51 PM
To:
[email protected] [6]
Subject: Re: [RE-wrenches] Grounding
Top of Pole Mount Array with a Ufer

We always put our assumption in our
plan notes, based on our interpretation of 250.52(A)(7). AHJs have never
questioned it, and we also tie the pole to any rebar, so its all one big
happy grounding electrode.

Ray Walters
Remote Solar
303 505-8760

On
6/24/21 6:49 PM, frenergy wrote:

Ray,

 I couldn't agree more, its been my
experience over the 
years that using 20 feet of #4 rebar in a building's
footing was 
kosher and accepted NEC 250.52(3). There's a heck of a lot
more 
surface area in 8" pipe 5-6 feet into the earth than rebar in a

foundation footing. The ground at the bottom of the pole footing is 
also
more likely to be damper. Our AHJ has always accepted the steel 
pole as a
ground rod....common sense prevails sometimes.

Bill

Feather River Solar
Electric
Bill Battagin, Owner
4291 Nelson St.
Taylorsville, CA
95983
530.284.7849
CA Lic 874049
www.frenergy.net [7]

On 6/24/2021 7:31
AM, Ray wrote:

Usually a steel pole in concrete has enough surface area to
qualify 
as a plate electrode under 250.52(A)(7). It needs to be at least 2

sq ft and 1/4" thick, and have an electrically conductive surface. So 
we
just drill and tap our ground connection into the pole, near the 
combiner
box.

Ray Walters
Remote Solar
303 505-8760

On 6/24/21 8:16 AM, Dana Orzel
wrote:

For all of our free standing arrays we now use a Ufer clamp to the

rebar either cage or just anti spin rebar that is welded to the pole 
in
the concrete, with #4 braided copper up to the pole combiner box,

inverter, etc. for our ground.
With a pole mount & a concrete base it is
way easier & less 
expensive than a ground rod, & the inspector seems
happier with this 
approach.

Dana Orzel Great Solar Works, Inc.
C -
208.721.7003 [email protected] [8] Idaho 
Contractor - # 028765 Idaho PV #
028374 NABCEP # 051112-136 
www.greatsolarworks.com [9] "Responsible
Technologies for Responsible 
People since 1988"
 Please consider the
environment before printing this email.

-----Original Message-----
From:
RE-wrenches  [10] On 
Behalf Of [email protected] [11]
Sent: Wednesday,
June 23, 2021 9:33 PM
To: RE-wrenches  [12]
Subject: Re: [RE-wrenches] Top
of Pole Mount Array on Ledge

Ben,
There is a way if the ledge is solid and
true. Twice I have done the 
following with ledge at 18" to 24" below
grade. Excavate down to 
ledge, drill down into the ledge and you will
determine the 
suitability of the following method. Drill for a pattern of
many 
rebar penetrations in to the ledge. Drill to a reasonable depth (as

deep into the ledge as you are able) in my case it was based on our

drilling tool and bit length capabilities. We used a large sono 
tube. 42"
as a recall, both of these jobs were over 12 years ago and 
my recall on
the exact size may be off.
Determine the best adhesive product to use in
your drilled holes for 
the rebar, again my memory fails as to what we used
based on 
recommendation from a local civil engineer. The sono tube height

above grade was determined to be 2' for one TPM12 and 3.5' above 
grade
for a TPM16. Depth down to the ledge determines how high above 
grade you
need the concrete footing/base. Use rebar lengths that 
will end a few
inches below the finished surface. For grounding you 
can coil up ground
wire and lay it on the surface of the ledge 
before your concrete pour. I
ran the ground wire through a short 
length of 1/2" or 3/4" PVC conduit, to
protect the copper ground 
wire where it comes out of the concrete. Place
the conduit coming 
out of the concrete with the ground wire just to the
side of where 
the mounting plate base for the TPM will be and fill the PVC
conduit 
with a good caulk sealer to keep air and water out of this hole as
a 
nexus of concrete, and air will corrode the copper. The TPM's for 
those
two jobs were made of 8" SCHD 80 steel, we had a large plate 
welded to the
bottom with 4 vertical side supports on the pipe up 
about a foot. Place
the appropriate sized anchor bolts in the 
concrete pour to match your TPM
base. Both of these TPM's have 
worked out well over the years. Local
conditions will determine the 
suitability of this method.

Sent from my
iPhone

_______________________________________________
List sponsored by
Redwood Alliance

Pay optional member dues here: http://re-wrenches.org
[13]

List Address: [email protected] [14]

Change
listserver email address &
settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[15]

There are two list archives for searching. When one doesn't work,
try the
other:
https://www.mail-archive.com/[email protected]/
[16]
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
[17]

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
[18]

Check out or update participant
bios:
http://www.members.re-wrenches.org
[19]

_______________________________________________
List sponsored by
Redwood Alliance

Pay optional member dues here: http://re-wrenches.org
[20]

List Address: [email protected] [21]

Change
listserver email address &
settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[22]

There are two list archives for searching. When one doesn't work,
try the
other:
https://www.mail-archive.com/[email protected]/
[23]
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
[24]

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
[25]

Check out or update participant
bios:
http://www.members.re-wrenches.org [26]

  

Links:
------
[1]
http://members.sti.net/offgridsolar/
[2] mailto:[email protected]
[3]
mailto:[email protected]
[4] http://www.greatsolarworks.com
[5]
mailto:[email protected]
[6]
mailto:[email protected]
[7] http://www.frenergy.net
[8]
mailto:[email protected]
[9] http://www.greatsolarworks.com
[10]
mailto:[email protected]
[11]
mailto:[email protected]
[12]
mailto:[email protected]
[13] http://re-wrenches.org
[14]
mailto:[email protected]
[15]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[16]
https://www.mail-archive.com/[email protected]/
[17]
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
[18]
http://www.re-wrenches.org/etiquette.htm
[19]
http://www.members.re-wrenches.org
[20] http://re-wrenches.org
[21]
mailto:[email protected]
[22]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[23]
https://www.mail-archive.com/[email protected]/
[24]
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
[25]
http://www.re-wrenches.org/etiquette.htm
[26]
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to