Ray,

            I couldn't agree more, its been my experience over the years that using 20 feet of #4 rebar in a building's footing was kosher and accepted NEC 250.52(3).  There's a heck of a lot more surface area in 8" pipe 5-6 feet into the earth than rebar in a foundation footing.  The ground at the bottom of the pole footing is also more likely to be damper.  Our AHJ has always accepted the steel pole as a ground rod....common sense prevails sometimes.

Bill

Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.
Taylorsville, CA 95983
530.284.7849
CA Lic 874049
www.frenergy.net

On 6/24/2021 7:31 AM, Ray wrote:
Usually a steel pole in concrete has enough surface area to qualify as a plate electrode under 250.52(A)(7).  It needs to be at least 2 sq ft and 1/4" thick, and have an electrically conductive surface. So we just drill and tap our ground connection into the pole, near the combiner box.

Ray Walters
Remote Solar
303 505-8760

On 6/24/21 8:16 AM, Dana Orzel wrote:
For all of our free standing arrays we now use a Ufer clamp to the rebar either cage or just anti spin rebar that is welded to the pole in the concrete, with #4 braided copper up to the pole combiner box, inverter, etc. for our ground. With a pole mount & a concrete base it is way easier & less expensive than a ground rod, & the inspector seems happier with this approach.



Dana Orzel                              Great Solar Works, Inc.
C - 208.721.7003                       [email protected]
Idaho Contractor - # 028765         Idaho PV # 028374
NABCEP # 051112-136 www.greatsolarworks.com
"Responsible Technologies for Responsible People since 1988"
 Please consider the environment before printing this email.


-----Original Message-----
From: RE-wrenches <[email protected]> On Behalf Of [email protected]
Sent: Wednesday, June 23, 2021 9:33 PM
To: RE-wrenches <[email protected]>
Subject: Re: [RE-wrenches] Top of Pole Mount Array on Ledge

Ben,
There is a way if the ledge is solid and true. Twice I have done the following with ledge at 18” to 24” below grade. Excavate down to ledge, drill down into the ledge and you will determine the suitability of the following method. Drill for a pattern of many rebar penetrations in to the ledge. Drill to a reasonable depth (as deep into the ledge as you are able) in my case it was based on our drilling tool and bit length capabilities. We used a large sono tube. 42” as a recall, both of these jobs were over 12 years ago and my recall on the exact size may be off. Determine the best adhesive product to use in your drilled holes for the rebar, again my memory fails as to what we used based on recommendation from a local civil engineer. The sono tube height above grade was determined to be 2’ for one TPM12 and 3.5’ above grade for a TPM16. Depth down to the ledge determines how high above grade you need the concrete footing/base. Use rebar lengths that will end a few inches below the finished surface. For grounding you can coil up ground wire and lay it on the surface of the ledge before your concrete pour. I ran the ground wire through a short length of 1/2” or 3/4” PVC conduit, to protect the copper ground wire where it comes out of the concrete. Place the conduit coming out of the concrete with the ground wire just to the side of where the mounting plate base for the TPM will be and fill the PVC conduit with a good caulk sealer to keep air and water out of this hole as a nexus of concrete, and air will corrode the copper. The TPM’s for those two jobs were made of 8” SCHD 80 steel, we had a large plate welded to the bottom with 4 vertical side supports on the pipe up about a foot. Place the appropriate sized anchor bolts in the concrete pour to match your TPM base. Both of these TPM’s have worked out well over the years. Local conditions will determine the suitability of this method.


Sent from my iPhone


--
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to