Hey Jay,
Yes the Sunny island Master of this Quad SI AC-coupled off-grid system
has been giving automatic Eq and Full charge charges perodically as
appropriate to this 48 V EnergyCell RE2700 pack.
We are getting whole pack volt drops way before we should at 600 well-
maintained cycles. When we do whole pack testing - when the voltage
drops off there are 5 of the 24 cells lagging - their voltage drops
faster than the rest - but they operate well between 50%-100% - all
busbars have been triple checked for corrosion and tourque.
So it looks like they just aged prematurely - so I'm in the process of
collating data from EnnexOS to get exact numbers on how they've been
treated. But even with a few hard cycles they should held up better
than they have. So perhaps a warranty claim - I've gone through charge
settings with SMA etc. I did have the AHrs programmed slightly below
rated AHrs due to confusion of whether the SI uses the 20 hr or 10 hr
rate (in Europe they use 10 but apparently - unbeknowst to me - the US
SI uses the 20 Hr - I swear SMA tech support years ago told me 10
hours) but now they are claiming that might be the culprit - I have a
hard time believing that setting the Ahour rating in the SI to 2100
instead of 2288 as rated would lead to pack failure - but they are
claiming that could have contributed.
Thoughts?
Best,
Jeff
Jay <mailto:[email protected]>
July 14, 2021 at 1:15 PM
Hi Jeff
If it’s the energy cell xlc from Outback then it shows an eq requirement.
If not that battery, most industrial quality VRLA I’ve seen have a eq
requirement, conditioning charge or something similar.
And the lowering of capacity is common from experience.
Question
What equipment/brand is charging it?
Jay
Peltz power
Jeff Clearwater <mailto:[email protected]>
July 14, 2021 at 11:32 AM
Thanks Dave - yes I've done whole pack load testing. The deal with
this pack though is that it is so remote and the expense of "just
replace the pack" in terms of shipping and labor is extreme - (tiny
Bahaman island with only regular small boat access}
And if it was toward the end of the pack's life anyway I'd not mess
around - but with only 600 well documented cylces on a $25K pack - and
with probably half that again in shipping and labor to replace - I'm
needing to carefully document the lagging cells for either a warranty
claim or at least to make good decisions going forward.
It's easy to access the cells as this is an EnergyCell AGM stack with
easily accessible terminals and removable terminal bars.
If we replace we'd go LFP - on the order of 100 KWHrs. So no small
decision for the customer - so worth the testing.
Thanks!
Jeff Clearwater
Village Power Design
www.villagepowerdesign.com <http://www.villagepowerdesign.com>
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try
the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org