I do have a Megatron  battery tester that does test internal resistance whit 
voltage present.  The battery Manu usually has that information. When I get my 
Unigy II battery banks they supply the sheet w/ those #. Did you say what the 
battery charge settings were? Not much use at this point as it is tough to 
clean up AGM cells.
> On Jul 14, 2021, at 5:43 PM, Jeff Clearwater <[email protected] 
> <mailto:[email protected]>> wrote:
> 
> Yes good thought Chris -I doubt if there is an IR tester anywhere on the 
> island - but when I go I will for sure look at that - thanks for that.
> 
> How would one measure battery resistance with voltage present? I guess with a 
> known voltage applied and current held constant one could calculate?  but 
> then how do you know you are measuring resistance vs storing energy?   I 
> don't think that's possible - others?
> 
> jc
> 
>> Chris Worcester <mailto:[email protected]> July 14, 2021 at 2:14 PM
>> Has an infra-red thermometer been used on every battery's terminals to check 
>> for resistance? I recall, although this might be my own thoughts, that 
>> internal resistance of each cell can be measured with an ohm meter...
>> 
>> 
>> 
>> Chris Worcester 
>> [email protected] <mailto:[email protected]>
>> 530-448-9692
>> 
>> Sent from my Samsung Galaxy s9.
>> 
>> 
>> -------- Original message --------
>> From: Jeff Clearwater <[email protected]> 
>> <mailto:[email protected]>
>> Date: 7/14/21 1:42 PM (GMT-08:00)
>> To: RE-wrenches <[email protected]> 
>> <mailto:[email protected]>
>> Subject: Re: [RE-wrenches] How Best to Load Test 2 V Cells
>> 
>> Hey Jay,
>> 
>> Yes the Sunny island Master of this Quad SI AC-coupled off-grid system has 
>> been giving automatic Eq and Full charge charges perodically as appropriate 
>> to this 48 V EnergyCell RE2700 pack.
>> 
>> We are getting whole pack volt drops way before we should at 600 well- 
>> maintained cycles.  When we do whole pack testing - when the voltage drops 
>> off there are 5 of the 24 cells lagging - their voltage drops faster than 
>> the rest - but they operate well between 50%-100% - all busbars have been 
>> triple checked for corrosion and tourque.   
>> 
>> So it looks like they just aged prematurely - so I'm in the process of 
>> collating data from EnnexOS to get exact numbers on how they've been 
>> treated.  But even with a few hard cycles they should held up better than 
>> they have.  So perhaps a warranty claim - I've gone through charge settings 
>> with SMA etc.  I did have the AHrs programmed slightly below rated AHrs due 
>> to confusion of whether the SI uses the 20 hr or 10 hr rate (in Europe they 
>> use 10 but apparently - unbeknowst to me - the US SI uses the 20 Hr - I 
>> swear SMA tech support years ago told me 10 hours)  but now they are 
>> claiming that might be the culprit - I have a hard time believing that 
>> setting the Ahour rating in the SI to 2100 instead of 2288 as rated would 
>> lead to pack failure - but they are claiming that could have contributed.
>> 
>> Thoughts?
>> 
>> Best,
>> 
>> Jeff
>> 
>> 
>> 
>> 
>> Jeff Clearwater <mailto:[email protected]> July 14, 2021 at 1:42 
>> PM
>> Hey Jay,
>> 
>> Yes the Sunny island Master of this Quad SI AC-coupled off-grid system has 
>> been giving automatic Eq and Full charge charges perodically as appropriate 
>> to this 48 V EnergyCell RE2700 pack.
>> 
>> We are getting whole pack volt drops way before we should at 600 well- 
>> maintained cycles.  When we do whole pack testing - when the voltage drops 
>> off there are 5 of the 24 cells lagging - their voltage drops faster than 
>> the rest - but they operate well between 50%-100% - all busbars have been 
>> triple checked for corrosion and tourque.   
>> 
>> So it looks like they just aged prematurely - so I'm in the process of 
>> collating data from EnnexOS to get exact numbers on how they've been 
>> treated.  But even with a few hard cycles they should held up better than 
>> they have.  So perhaps a warranty claim - I've gone through charge settings 
>> with SMA etc.  I did have the AHrs programmed slightly below rated AHrs due 
>> to confusion of whether the SI uses the 20 hr or 10 hr rate (in Europe they 
>> use 10 but apparently - unbeknowst to me - the US SI uses the 20 Hr - I 
>> swear SMA tech support years ago told me 10 hours)  but now they are 
>> claiming that might be the culprit - I have a hard time believing that 
>> setting the Ahour rating in the SI to 2100 instead of 2288 as rated would 
>> lead to pack failure - but they are claiming that could have contributed.
>> 
>> Thoughts?
>> 
>> Best,
>> 
>> Jeff
>> 
>> 
>> 
>> 
>> 
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org 
>> <http://re-wrenches.org/>
>> 
>> List Address: [email protected] 
>> <mailto:[email protected]>
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/ 
>> <https://www.mail-archive.com/[email protected]/>
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm 
>> <http://www.re-wrenches.org/etiquette.htm>
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org 
> <http://re-wrenches.org/>
> 
> List Address: [email protected] 
> <mailto:[email protected]>
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 



> Tump 
> <blocked::mailto:[email protected]%22%20%5Co%20%22blocked::mailto:[email protected]>[email protected]
>        www.SWNL.net 
> <blocked::http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/>
>                 Solarwinds Northernlights       
>        Serving Mid Coast Maine & Northern California
>                          207-832-7574   Cl. 610-517-8401                      
>         
>                               Blair "TUMP" May
>                ********  MAINE'S CHARTER ********
>                       NABCEP    "Certified PV Installer" 
>    
>               ********  MAINE'S CHARTER ********
>                   Trace Xantrex "Certified" Dealer / Installer"
> 



_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to