Minor update, I got word from Snapnrack that: "The new protocol established
with UL eliminates the need to include the wattage ranges for each module
type"
Still a pain and the manufacturer/model should be on the rack manufacturer
list - but not down to the precise wattage -  so slightly less of a pain.

Rebekah
Tel: 336.266.8800



On Tue, Jul 20, 2021 at 4:37 PM Rebekah Hren <[email protected]> wrote:

> Hi William
>
> Groan, I don't see that precise model in the series 100 installation
> manual
> <https://snapnrack.com/wp-content/uploads/2019/05/S100-UL-Install-Manual_v2.0_web.pdf>
>  on
> pg 74 which is the bonding evaluation list of modules
> I hope for your sake Snapnrack will send an email the AHJ will accept that
> includes that module.
> I wish there was a reasonable workaround for AHJs here, like onsite
> resistance measurements.
>
> Good luck,
> Rebekah
> Tel: 336.266.8800
>
>
>
> On Tue, Jul 20, 2021 at 2:36 PM Sam Haraldson <[email protected]>
> wrote:
>
>> The SnapNrack UL 2703 document highlights it's UL listing when used with
>> Type 1 and Type 2 modules.
>>
>>
>> https://snapnrack.com/wp-content/uploads/2019/05/SnapNrack_Fire_Classification_Tech_Bulletin_v.2-1.pdf
>>
>> *SnapNrack Series 100, Ultra Rail and RL systems have been Certified for
>> a Class A fire rating with Type 1 and Type 2 modules, in accordance with
>> the standards set forth in UL1703/2703 and IBC 2012.*
>>
>>
>> The Mission Spec sheet references that it is UL listed under 1703.
>>
>>
>> https://s3.amazonaws.com/ecodirect_docs/Mission-Solar/Mission-Solar-MSE320SR8T-datasheet.pdf
>>
>>
>> For further reference this 1703 document talks a little about the
>> different module "types" that are tested.
>>
>> https://www.intertek.com/building/standards/ul-1703/
>>
>> *The “Type” of module dictates the number of fire tests that will be
>> required during the test process, there are 3 common types (15 total) that
>> are determined by their superstrate, encapsulant, substrate materials, and
>> size of module.*
>>
>>
>>
>>
>>
>>
>> Sam Haraldson <[email protected]>
>> Installation & Service Manager
>> <http://www.onsiteenergyinc.com/>
>>
>> | o. (406) 551-6135
>> <https://www.facebook.com/onsiteenergysolar/>
>> <https://www.instagram.com/onsiteenergyinc/>
>> <https://twitter.com/onsiteenergyinc>
>> <https://www.linkedin.com/company/onsite-energy-inc/>
>>
>> <https://onsiteenergyinc.com/bcorp>
>>
>>
>> On Tue, Jul 20, 2021 at 3:25 PM William Miller <[email protected]>
>> wrote:
>>
>>> Friends:
>>>
>>>
>>>
>>> I received the following correction noticed from a hired plan-checker:
>>>
>>>
>>>
>>> *Please provide the technical listing for the support rail system
>>> documenting that the supports have been tested with the PERC 60 panels. The
>>> UL 2703 listing requires the two to be tested/listed together for the rack
>>> to functionally ground the solar panels. [CEC 690.43(A)] Alternately, bond
>>> the metal parts of PV equipment to grounded metal supports per CEC
>>> 690.43(B).*
>>>
>>>
>>>
>>> Is it true that UL2703 requires testing with each and every type of
>>> module? I am using 100 Series rail from my stock with Mission MSE325SR8K
>>> panels.  Does anyone have any documentation on file that would satisfy this
>>> request?
>>>
>>>
>>>
>>> I have sent an inquiry to Snap-n-rack about this but they often take a
>>> week or more to respond.
>>>
>>>
>>>
>>> Thanks in advance.
>>>
>>>
>>>
>>> William Miller
>>>
>>>
>>>
>>> Miller Solar
>>>
>>> 17395 Oak Road, Atascadero, CA 93422
>>>
>>> 805-438-5600
>>>
>>> www.millersolar.com
>>>
>>> CA Lic. 773985
>>>
>>>
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: [email protected]
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/[email protected]/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: [email protected]
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to