William,

Years ago we tried using the relay in the FNDC with a system of sealed Outback FX inverters.  After a few times call backs about the generator being left running long after it should have stopped, I discovered that the problem was indeed caused by the relay in the FNDC. That relay is a latching type and Outback sends the signal for it to change state only once; they don't check to see if it actually changed state (apparently the hardware wasn't set up to allow that); and they don't send a second signal to improve the chance of a successful operation. You know the screen in the Mate where they keep a tally of communication errors, not sure that is comm errors at unfortunate times are the cause or not, but I suspect it is. Maybe the relay in this FNDC was sluggish because in the garage temperatures could occasionally got lower than 0°C - the lower limit of the FNDC. Whatever the cause, we decided that the FNDC relay was not suitable for starting and stopping a generator. I ended up re-purposing the FX's external vent fan to control the generator (and fan) and never had any more trouble. The fan is rarely needed except while charging batteries with the generator, and the inverter has the ability to reduce its output if it is too hot.

Kent Osterberg

Blue Mountain Solar


On 9/14/2021 5:56 PM, William Miller wrote:

Friends:

A couple of years ago we installed an all sealed Outback FX system.  All of the FX inverters were equipped with Turbo fans which connect to the relay in the inverters so those were not available for generator starting.  A senior Outback tech support person (one who has been with Outback for a long time) told me the relay in the FNDC was not reliable. Instead it was suggested that I use the relay in an Outback Extreme charge controller that was part of the system.  I never tried the relay in the FNDC so I don’t have first-hand knowledge if the relay is reliable or not.  Can anyone confirm or debunk this assertion?

Remember the Extreme <https://outbackpower.com/products/discontinued-products/discontinued-product-documentation/item/flexmax-extreme-technical-documentation>?  It was the precursor to the FlexMax 100.  It is discontinued.

William

Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com <http://www.millersolar.com/>

CA Lic. 773985

*From:*RE-wrenches [mailto:[email protected] <mailto:[email protected]>] *On Behalf Of *Michael Morningstar
*Sent:* Tuesday, September 14, 2021 11:16 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Radian Generator Relay

Actually I’m using the 12V relay to activate a battery vent fan. For generator starting, I’m using the dry contact relay for two-wire start. I have the circuit protected by a 2amp fast acting fuse. Fuse is good.



On Sep 14, 2021, at 11:10 AM, Tuss, Lones <[email protected] <mailto:[email protected]>> wrote:

Hi Michael

It sound like you are using the 12 volt aux out on the radian to activate a separate relay.

If so disconnect the relay then check and see if the 12 aux attempts to go high (12v dc).

If it does it may be a relay issue.

The Radian does have an on board relay you could use that instead of a discrete relay.

In AGS on the Mate3(s) just select Relay.

I hope this helps sir.

Take Care

*From:*RE-wrenches <[email protected] <mailto:[email protected]>>*On Behalf Of*Michael Morningstar
*Sent:*Tuesday, September 14, 2021 10:55 AM
*To:*RE-wrenches <[email protected] <mailto:[email protected]>>
*Subject:*[RE-wrenches] Radian Generator Relay


        

*CAUTION:*This email originated from outside of the Company. Do not click links or open attachments unless you recognize the sender and know the content is safe.

Wrenches,

I’ve got a Radian 8048/Mate 3S that no longer is activating the relay responsible for generator starting. I’ve power cycled everything and updated firmware. When I attempt to start the generator via the Mate 3S, the relay does not close.

Any suggestions before I look into replacing the relay/board?

Which board do I order and what is the best source?

Many thanks,

Michael

*Michael Morningstar*

**

/Morningstar Electric/

PO Box 1494

Mount Shasta, California 96067

530-921-0560

CSLB 949635

  <image001.gif>



This email and any attachments may contain confidential information that is intended only for the recipient(s). If you have received this email in error, please notify the sender and delete it from your system. Any views or opinions presented in this email are solely those of the author and do not necessarily represent those of the company or its affiliates. This email does not constitute an agreement to conduct transactions by electronic means and does not create any legally binding contract or enforceable obligation in the absence of a fully signed written contract. The recipient should check this email and any attachments for viruses. The company accepts no liability for any loss or damage caused by software viruses. If you are the intended recipient and you do not wish to receive similar email(s) from us in the future then please notify the sender. Please consider the environment before printing. _______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here:http://re-wrenches.org <http://re-wrenches.org/>

List Address:[email protected] <mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>

There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/[email protected]/ <https://www.mail-archive.com/[email protected]/> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>

*Michael Morningstar*

**/Morningstar Electric/

PO Box 1494

Mount Shasta, California 96067

530-921-0560

CSLB 949635


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to