I’ve installed Hundreds upon hundreds of diesel generators at elevation here in the mountains of NorCal. Temps down to -15F. None have needed block heaters. For under 40KW, Wrico International. Growers were getting 20-40K hours out of them. They are open frame. MQ Power for an off the shelf enclosed gen-set. Ray is correct in that there aren’t any decent (low rpm, liquid cooled) propane generators. We won’t touch the disposable propane generators like the Kohler RES and Genercrap equivalents. Oh, Wrico does build legit <15kw propane generators…..they cost 14K
> On Jan 18, 2022, at 10:15 AM, Ray <[email protected]> wrote: > > I won't go less than double the inverter rating anymore with gensets. So the > Kohler 12 kW is probably the lowest cost, decent match for the XW. Otherwise > you're just over working the genset, which usually aren't designed for > continuous duty. It keeps the voltage stable enough to not disconnect when a > surge (like that sewage pump) comes on. > > As far as 1800 rpm, I don't know anything under 20 kw in propane. The fuel > consumption of a 20kw at 25% is very comparable to the 12kW at 50%. I've > been considering diesel, but just always have been worried about cold > starting in the mountains. > > Ray Walters > Remote Solar > 303 505-8760 > On 1/18/22 9:17 AM, Tump wrote: >> Ray I would love to know which larger propane gen set you are suggesting. >> 1800 or 3600 rpm. Air cooled or water cooled. To my knowledge there are >> very few L cooled 1800 rpm gen sets in the 12-15kW range. T >>> On Jan 17, 2022, at 11:11 PM, Ray <[email protected] >>> <mailto:[email protected]>> wrote: >>> >>> I have a question: why so small a generator? I've always regretted under >>> sizing the genny for battery charging. Larger gensets are not as fuel >>> hungry as you might think. I was surprised recently when I did some calcs, >>> and found that a larger genset would actually get slightly better fuel >>> consumption at the proposed load. >>> >>> Plus the larger gensets are usually built to last longer than the portable >>> stuff. >>> >>> Ray Walters >>> Remote Solar >>> 303 505-8760 >>> On 1/17/22 5:33 PM, Jeff Clearwater wrote: >>>> Hello Again All, >>>> >>>> Or I'd consider suggesting propane to the customer as well. Any >>>> experience with know compatibles in propane? >>>> >>>> txnks >>>> >>>> jc >>>> >>>>> Jeff Clearwater <mailto:[email protected]> January 17, 2022 at >>>>> 1:29 PM >>>>> Thanks All, >>>>> >>>>> Aren't there any 5-8 KW gas gennys out there already set up for 2-wire >>>>> start? We do that all the time with bigger units. >>>>> >>>>> Thanks again! >>>>> >>>>> Best, >>>>> >>>>> jc >>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/> >>>> >>> _______________________________________________ >>> List sponsored by Redwood Alliance >>> >>> Pay optional member dues here: http://re-wrenches.org >>> <http://re-wrenches.org/> >>> >>> List Address: [email protected] >>> <mailto:[email protected]> >>> >>> Change listserver email address & settings: >>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org> >>> >>> There are two list archives for searching. When one doesn't work, try the >>> other: >>> https://www.mail-archive.com/[email protected]/ >>> <https://www.mail-archive.com/[email protected]/> >>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org >>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org> >>> >>> List rules & etiquette: >>> http://www.re-wrenches.org/etiquette.htm >>> <http://www.re-wrenches.org/etiquette.htm> >>> >>> Check out or update participant bios: >>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/> >>> >> >>> Tump >>> <blocked::mailto:[email protected]%22%20%5Co%20%22blocked::mailto:[email protected]>[email protected] >>> <mailto:[email protected]> www.SWNL.net >>> <blocked::http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/> >>> Solarwinds Northernlights >>> Serving Mid Coast Maine & Northern California >>> 207-832-7574 Cl. 610-517-8401 >>> >>> Blair "TUMP" May >>> ******** MAINE'S CHARTER ******** >>> NABCEP "Certified PV Installer" >>> >>> ******** MAINE'S CHARTER ******** >>> Trace Xantrex "Certified" Dealer / Installer" >>> >> >> >> >> >> >> _______________________________________________ >> List sponsored by Redwood Alliance >> >> Pay optional member dues here: http://re-wrenches.org >> <http://re-wrenches.org/> >> >> List Address: [email protected] >> <mailto:[email protected]> >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org> >> >> There are two list archives for searching. When one doesn't work, try the >> other: >> https://www.mail-archive.com/[email protected]/ >> <https://www.mail-archive.com/[email protected]/> >> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org >> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org> >> >> List rules & etiquette: >> http://www.re-wrenches.org/etiquette.htm >> <http://www.re-wrenches.org/etiquette.htm> >> >> Check out or update participant bios: >> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/> >> > _______________________________________________ > List sponsored by Redwood Alliance > > Pay optional member dues here: http://re-wrenches.org > > List Address: [email protected] > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > There are two list archives for searching. When one doesn't work, try the > other: > https://www.mail-archive.com/[email protected]/ > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > http://www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > http://www.members.re-wrenches.org > Michael Morningstar Morningstar Electric PO Box 1494 Mount Shasta, California 96067 530-921-0560 CSLB 949635
_______________________________________________ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/[email protected]/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org

