And can't you just wire up the new inverter as a "dumb" battery charger
only? If you don't need to double KW to loads, don't try to stack it, or
connect it to the hub. Just cable it to the batteries, and wire the genny
to it's AC in. NO AC out wiring. When genny is running, it should charge
fine. A last resort.

On Sun, Mar 20, 2022 at 10:14 AM John Blittersdorf <
[email protected]> wrote:

> Wrenches, I just added a 2nd VFX3648 stacked as SLAVE L1 to increase
> charging of his new eVault 18.5 from 12kw Kohler gen. It connects to the
> generator but doesn’t charge.  I read in the manual that both inverters
> must be the same firmware revision.  Once hooked up I found that the added
> inverter was rev #68 and the original one rev 61.  Would it be possible to
> switch which inverter is the master and have the newer one recognize the
> older one.? Otherwise is my only option to put a new control board in the
> original inverter? And possibly also in the new one.  Anyone know what the
> latest rev or last one was?
>
> John Blittersdorf
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>

-- 

*Kirk Herander / **[email protected] <[email protected]>*

*Owner|Principal, VT Solar, LLC*

*Celebrating our 31st Anniversary 1991-2022!!*

*www.vermont.solar*
<https://nam02.safelinks.protection.outlook.com/?url=www.vermontsolarnow.com&data=02%7C01%7C%7C9f0330d75a244870112408d685311841%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C636842843233477645&sdata=0NjyuKeQbEK6245SNnk8X4XnP9Q%2B%2BqtvcALkdDghvk4%3D&reserved=0>

dba Vermont Solar Engineering

802.863.1202
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to