What happens if the study shows yes, that their no was wrong. Or does that never happen?😕

On 12/26/2022 12:48 PM, Jay via RE-wrenches wrote:
If the utility is PG&E in my experience here is what happens

They say yes or no to the interconnection.
If no you have the option to request an engineering study to determine how much solar. That study is at your expense, paid in advance and the exact cost isn’t known until the study is done. Could be $500 to $15,000 or more.

I’ll be curious to know what happens

Jay





On Dec 26, 2022, at 9:07 AM, Drake Chamberlin via RE-wrenches <[email protected]> wrote:




William,

I ran into this once on an old transformer, which fortunately they changed at no cost. It was a 10 kW transformer on a 200 A (48 kW) service. They had some dimming of lights on heavy loads, and the transformer was changed out on that basis, at no charge.

My questions for the utility would be?

  * Are there any other PV systems feeding the transformer?
      o If so, what is their maximum production.
  * What size is the transformer?
  * What percentage of transformer capacity is allowed to be back-fed.

If the math comes out in your favor, you will have a good case to escalate to the next level.


Good Luck,

Drake


Drake Chamberlin

Athens Electric LLC

Ohio Electrical Contractor’s License 44810

CO Master Electrician’s License 4526

NABCEP Certified PV Installation Professional

-------------------------------------------------------------------------------

On 2022-12-25 13:58, William Miller via RE-wrenches wrote:

Wrenched:

Merry Christmas to those of you that observe such traditions, or substitute the winter festivity of your choice.

I helped a previous employee install an Enphase IQ8 system on his home.  He applied for the utility approval concurrently with his building permit  The day he got his final inspection the utility contacted him and claimed "The aggregate generation exceeds the identified transformer rating" and refused him a Permission to Operate letter.

Adding up the service ratings of the homes on his secondary we get about 336 kW of potential consumption. Adding the grid-tied systems on his secondary we get about 16.5 kW.  How is it that the back-feed exceeds the transformer rating?

I would appreciate any insight on how to consider this situation and how to fight it.

Sincerely,

William Miller

Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com <http://www.millersolar.com/>

CA Lic. 773985


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here:http://re-wrenches.org

List Address:[email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

--
            Christopher Warfel
                     ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
                                401-466-8978
<http://entech-engineering.com>

BEGIN:VCARD
VERSION:4.0
N:Warfel;Christopher;;;
TEL;VALUE=TEXT:401-447-5773 (c)
NOTE:Use the cell phone number for all communications.  Thank you.
URL:https://www.entech-engineering.com
END:VCARD
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to