Yes often the study says, yes it’s ok to do the original design and you still have to pay. Remember it’s pay in advance of getting the report.
If no then usually they give a cost estimate to upgrade what ever needs to be replaced or a downgraded solar design that will work with existing equipment.
Jay
On Dec 26, 2022, at 10:12 AM, Christopher Warfel via RE-wrenches <[email protected]> wrote:
What happens if the study shows yes, that their no
was wrong. Or does that never happen?😕
On 12/26/2022 12:48 PM, Jay via
RE-wrenches wrote:
If the utility is PG&E in my experience here is
what happens
They say yes or no to the interconnection.
If no you have the option to request an engineering
study to determine how much solar. That study is at your
expense, paid in advance and the exact cost isn’t known until
the study is done. Could be $500 to $15,000 or more.
I’ll be curious to know what happens
Jay
William,
I ran into this once on an
old transformer, which fortunately they changed at no
cost. It was a 10 kW transformer on a 200 A (48 kW)
service. They had some dimming of lights on heavy loads,
and the transformer was changed out on that basis, at no
charge.
My questions for the utility
would be?
- Are there any other PV
systems feeding the transformer?
- If so, what is their
maximum production.
- What size is the
transformer?
- What percentage of
transformer capacity is allowed to be back-fed.
If the math comes out in
your favor, you will have a good case to escalate to the
next level.
Good Luck,
Drake
Drake Chamberlin
Athens Electric LLC
Ohio Electrical Contractor’s License 44810
CO Master Electrician’s License 4526
NABCEP Certified PV Installation Professional
-------------------------------------------------------------------------------
On 2022-12-25 13:58, William Miller via
RE-wrenches wrote:
Wrenched:
Merry
Christmas to those of you that observe such
traditions, or substitute the winter festivity of
your choice.
I helped a
previous employee install an Enphase IQ8 system on
his home. He applied for the utility approval
concurrently with his building permit The day he
got his final inspection the utility contacted him
and claimed "The aggregate generation exceeds the
identified transformer rating" and refused him a
Permission to Operate letter.
Adding up
the service ratings of the homes on his secondary
we get about 336 kW of potential consumption.
Adding the grid-tied systems on his secondary we
get about 16.5 kW. How is it that the back-feed
exceeds the transformer rating?
I would
appreciate any insight on how to consider this
situation and how to fight it.
Sincerely,
William
Miller
Miller Solar
17395 Oak
Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com
CA Lic. 773985
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one
doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
--
Christopher Warfel
ENTECH
Engineering, Inc.
PO Box 871, Block Island, RI
02807
401-466-8978
<EEIlogolong.jpg>
<cwarfel.vcf> _______________________________________________List sponsored by Redwood AlliancePay optional member dues here: http://re-wrenches.orgList Address: [email protected]Change listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgThere are two list archives for searching. When one doesn't work, try the other:https://www.mail-archive.com/[email protected]/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orgList rules & etiquette:http://www.re-wrenches.org/etiquette.htmCheck out or update participant bios:http://www.members.re-wrenches.org
|