2200' EL should not influence the generator, seems the first 4500-5000' are
covered like sealevel. How old is gen?

Have you been into the settings menu as well as the Wizard?

I have found settings in one and not the other that definitely effect the
overall parameters.

 

A call to OB might shortcut your Q.

 

___________________________________________________

Dana Orzel  c- 2087217003   e - [email protected]

 

--- Begin Message ---
Hello wrenches,

We just installed an GS8048a Radian build with Mate 3SL controller (no Optics). 
 We are having some with charging from the generator, as the generator charging 
seems to be limited to about 4500Watts +/- (20amps AC) when charging through 
the Radian.  It is a Kohler 8.5RES generator and we have the AC input limit set 
to 30amps and the Gen input set to 30amps.  The house load is only about 
200Watts when we are charging.  The system is at 2200ft of elevation, but I 
don’t know if that makes enough of a difference.
The Gen output voltage seems pretty good and holds around 234V-236V while 
charging.

Any thoughts as to why it may be limiting would be appreciated.

Thanks,
Amos



       Amos Post
   Integrity Energy
  W 802.763.7023
   C 802.291.2188
     <http://www.ienergyvt.com> ienergyVT.com
        Facebook <https://www.facebook.com/integrityenergyllp?ref=hl> 

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


--- End Message ---
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to