Wrenches, Will
This is a hack trick but it can work as long as you don't have failed
cells, bring the static voltage up to 26 by adding just one battery, this
might be easier on the logistics issue. By doing this you will in the end
sacrifice the additional Battery but increasing the static voltage will
also increase it under load and reduce the run time of the genny, you will
also want to increase the charge voltage settings to accommodate the higher
voltage. Yes it's a hack but can help get you through the winter.
Fun times

On Fri, Oct 27, 2023, 8:03 AM White, Will via RE-wrenches <
[email protected]> wrote:

> Hello Wrenches,
>
>
>
> I installed my off-grid system in 2008. It’s 24 V using 2 V industrial FLA
> batteries. As you can imagine after 15 years the capacity of my battery
> bank is significantly less than it used to be.
>
>
>
> For logistic reasons, I won’t be able to replace them till around June of
> next year, but it’s not even into winter yet and my generator is already
> running every day.
>
>
>
> Does anyone have any tips on how to get through the winter on these
> batteries while minimizing generator run time? I’ve got two FM80’s with 3.8
> kW of PV, two VFX3524 inverters, and a Kohler RES12 generator. I haven’t
> changed any settings since I installed the system.
>
>
> Thanks,
>
> Will
> ------------------------------
>
> Please be advised that this email may contain confidential information. If
> you are not the intended recipient, please notify us by email by replying
> to the sender and delete this message.
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to