I would reset to factory settings and start again.
Jay
On Oct 25, 2023, at 5:59 PM, integrityenergy101 via RE-wrenches <[email protected]> wrote:
Charger Limit is also set to 30 amps. We tried raising the total AC input limit to max and that may have helped increase the chargeby 200-300watts up to 4.8kw but thats it. By my math we should be able to see about 6KW+/- of charging power.
We are using Generator input mode I believe. We will try switching to Support mode and see if that helps.
By the way batteries are 8- Simpliphi 3.8.
-------- Original message -------- Date: 10/25/23 4:43 PM (GMT-05:00) Subject: Re: [RE-wrenches] Outback Radian Generator Charging
What is the charger ac limit set to?
Jay Hi Amos,
What input mode are you using?
Try switching to "support" mode and see if the charging current increases.
<IE LOGO 150x78.jpg> _______________________________________________List sponsored by Redwood AlliancePay optional member dues here: http://re-wrenches.orgList Address: [email protected]Change listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgThere are two list archives for searching. When one doesn't work, try the other:https://www.mail-archive.com/[email protected]/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orgList rules & etiquette:http://www.re-wrenches.org/etiquette.htmCheck out or update participant bios:http://www.members.re-wrenches.org _______________________________________________List sponsored by Redwood AlliancePay optional member dues here: http://re-wrenches.orgList Address: [email protected]Change listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgThere are two list archives for searching. When one doesn't work, try the other:https://www.mail-archive.com/[email protected]/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orgList rules & etiquette:http://www.re-wrenches.org/etiquette.htmCheck out or update participant bios:http://www.members.re-wrenches.org
|
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org