& from what I was told this week split you only get 1/2 the power per leg? 
Please clarify if different

_________________________________________________________
Dana Orzel                GREAT SOLAR WORKS!
C - 208.721.7003      E - [email protected]<mailto:[email protected]>
W - www. greatsolarworks.com     www.solarwork.com<http://www.solarwork.com/>
"Responsible Technologies for Responsible People since 1988!"

--- Begin Message ---
David is correct.  We have some experience with Sol-Ark’s inverter, and it’s a 
good product.  However, be aware that you can configure it either as a 120V 
inverter with a max. output of about 5 kW or as a 240V inverter with a max. 
output of about 8 kW.  However, it does NOT do split-phase, meaning if you 
configure it for 240V, it cannot run loads that require a neutral.

Tom McCalmont
Paired Power


On May 3, 2024, at 4:12 PM, david quattro via RE-wrenches 
<[email protected]> wrote:

I think SolArk makes an 8K 120V-only version
David




On Fri, May 3, 2024 at 3:13 PM Jason Szumlanski via RE-wrenches 
<[email protected]<mailto:[email protected]>> 
wrote:
For this application I was originally thinking about a 48V inverter with 120V 
output, but there are not many options in the size range I was considering. It 
hit me that I could potentially get a 120/240V split-phase inverter and run the 
DC converter from one leg and the 120V loads from the other leg. The Sol-Ark 8K 
would probably be the right size for this application. Despite there being no 
240V loads, they "could" add them in the future if needed. I know about 
imbalance issues with the 12k, but have not heard this same feedback about the 
8k, so please let me know if you know otherwise.

I really doubt there will be enough imbalance here to cause issues. The biggest 
load on the DC side is a tiny 12V DC pump and the largest load on the AC side 
will be the new refrigerator, or maybe a big ceiling fan starting up. The 
inductive loads are almost negligible. Really the only reason I want an 
inverter this large is for the charger capacity. The owner wants a 9.6kWh LiPo 
battery minimum, so I want a sizable charger.

BUT, the client would need to replace their 120V portable generator with a 
split-phase unit. That could be a sticking point taking me back to a 120V 
inverter.

I was hoping for an all-in-one for this particular job, but the only one I can 
find that is 48Vdc and 120Vac is the EG4 6500EX-48. At the price point they 
offer it, I guess it can't hurt to try! I can even have a spare on the shelf 
for less in total than the cost of a Victron inverter charger and separate 
charge controller, and still have money to spare. I have been dabbling into the 
EG4 brand, mostly with clients that went ahead and bought EG4 batteries before 
they ever met me, and I haven't had any real issues other than battery to 
inverter closed loop comms. It's too early to say I'm impressed, but the prices 
are in the too-good-to-be-true category. I don't want to get off topic here 
with batteries and manufacturer reliability, but I wanted to mention the EG4 
6500EX-48, which seems like perfect specs for this job.


And... I know... someone is probably thinking that we're up to a 9.6kWh battery 
with a small 120V generator, and that's probably not a good match. I get that, 
but the client expects the PV to handle all of their needs with the generator 
only serving as an emergency backup. I have alerted them to the potential 
mismatch. I still want a sizeable charger in case they upgrade their generator 
for faster battery recharges.

Jason Szumlanski
Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956
Florida Certified Electrical Contractor EC13013208



On Wed, Apr 24, 2024 at 1:52 PM John Blittersdorf via RE-wrenches 
<[email protected]<mailto:[email protected]>> 
wrote:
Jason,
  Just using the converter works fine. They are considered a battery charger or 
a regulated power supply. I am currently running that way now with the battery 
cables going nowhere.  I was thinking of putting the battery back in the system 
just for triple redundancy when my inverter hits low battery cutoff voltage on 
a cold winter night and no fuel for the generator (or it won't start).
My Iota DLS puts out a regulated 13.4 volts up to 30 amps.

John

On Wed, Apr 24, 2024 at 8:25 AM Jason Szumlanski via RE-wrenches 
<[email protected]<mailto:[email protected]>> 
wrote:
Ah ha! I didn't consider using a small 12V battery with a charger. I was 
thinking of just using a 120V -> 12V converter to handle the DC loads. Is the 
12V battery really necessary, or can I just power the DC loads directly with a 
converter? If I just have lights and fans on the DC system, the load should be 
pretty minimal.

I could use a separate 12V battery, but I would like to eliminate that cost and 
complexity if possible.


And yeah, I am not considering this a money making opportunity. It's really 
just a challenge to ward off boredom from the daily grind.

Jason Szumlanski
Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956
Florida Certified Electrical Contractor EC13013208


On Wed, Apr 24, 2024 at 8:01 AM John Blittersdorf via RE-wrenches 
<[email protected]<mailto:[email protected]>> 
wrote:
Jason,
  I have a customer with the same situation except he already has a 12 V VFX 
inverter,  He has a sunfrost fridge and other small loads with a very fancy 
custom control board
originally set up to handle AC and DC systems.  We are adding a lot more solar 
and I was considering a dual battery system but the owner didn't like that 
idea.  We are going with and Iota 12v power supply (i use one at my house for 
my sunfrost) to power up all his DC loads and will be adding a large 48 V 
battery bank and over 4Kw of solar using a VFXR3648 directly in place of the 
12V inverter.  He complained that the existing inverter would not handle all 
his current AC loads very well.  My own house is fully wired for 12VDC as well 
as AC (lots of #10 copper not being used) and I have been considering getting a 
small LFP 12V battery to put back on by DC System. Then use the Iota as a 
secondary charging method with some of my large stash of older modules hooked 
up for 12V direct with C40 charge controller to recreate my original system 
just for kicks. I'm only using DC for my Sunfrost and one "emergency light" in 
the livingroom right now.  For your customer, a small LFP 12v battery 
(approximately $500 or less) to replace his old battery bankm and more larger 
ones for the new AC side with 48V inverter fed by his generator or through an 
Iota 48 V charger ifusing a smaller non charging inverter. Unlike Dave, I like 
these challenges. Maybe thats why I never seem to make money.!!

John Blittersdorf
offgridvermont.com<http://offgridvermont.com/>


On Wed, Apr 24, 2024 at 7:22 AM Jason Szumlanski via RE-wrenches 
<[email protected]<mailto:[email protected]>> 
wrote:
Fortunately, the owner is pretty handy and is willing to live with any negative 
consequences. That said, I want to offer him something as simple and 
bulletproof as possible. I am walking into this with eyes wide open, for sure.

Jason Szumlanski
Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956
Florida Certified Electrical Contractor EC13013208


On Tue, Apr 23, 2024 at 5:47 PM Dave Angelini Offgrid Solar via RE-wrenches 
<[email protected]<mailto:[email protected]>> 
wrote:

Not being helpful but I  walk away from these.  It will come back to you.

Dave Angelini Offgrid Solar
"we go where powerlines don't"
  <http://members.sti.net/offgridsolar/> https://offgridsolar1.com/ 
<http://members.sti.net/offgridsolar/>
e-mail  [email protected]<mailto:[email protected]>
text 209 813 0060


On 2024-04-23 2:40 pm, Jason Szumlanski via RE-wrenches wrote:

I have an off-grid client who is working on replacing old equipment at a cabin. 
He has a lot of 12 volt distribution in the house for lighting, fans, and a 12 
volt refrigerator. He also has 120 volt AC loads that run through a separate 
distribution panel where the only source is a 2000 Watt Honda generator. There 
is no inverter present. The batteries are charged through a Trace C40.

He currently has a few ancient solar panels and a struggling Bank of AGM 
batteries. It's time for an upgrade. I can easily supply enough PV power for 
what he needs. He currently has a 9 kilowatt hour battery capacity that he was 
happy with when the batteries operated optimally. Nonetheless, I would probably 
future-proof him with a 10 to 15 kilowatt hour LiPo to double or triple his 
usable capacity.

For convenience, obviously it would be nice to have an inverter to eliminate or 
reduce the generator requirement. But he seems committed to keeping his 12 volt 
distribution because it would be costly to replace fixtures. I think he would 
consider replacing the 12 volt refrigerator if he has an inverter.

He definitely wants LiPo batteries.

I don't like the idea of 12 volt direct from a battery plus connecting an 
inverter to that same battery. It is going to be hard to measure and monitor 
things.

I am thinking about using a 48 volt battery with a single phase 120 volt 
inverter, getting him to change to a 120 volt refrigerator, and using a DC 
converter to give him somewhere in the range of 100 amps at 12 volts for his 
existing DC lighting and fan loads. Is this a bad idea? Should I stick with a 
12 volt battery system? He does have a tiny 12 volt pressure pump which might 
be an issue for the converter. I'm not sure. I am a bit worried about the 
efficiency loss and capacity of DC converters and not sure how to size it.

Jason Szumlanski
Florida Solar Design Group






_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org<http://re-wrenches.org/>

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org<http://www.members.re-wrenches.org/>

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org<http://re-wrenches.org/>

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org<http://www.members.re-wrenches.org/>

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org<http://re-wrenches.org/>

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org<http://www.members.re-wrenches.org/>

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org<http://re-wrenches.org/>

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org<http://www.members.re-wrenches.org/>

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org<http://re-wrenches.org/>

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org<http://www.members.re-wrenches.org/>

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org<http://re-wrenches.org/>

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org<http://www.members.re-wrenches.org/>

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org<http://re-wrenches.org/>

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org<http://www.members.re-wrenches.org/>

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


--- End Message ---
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to