Friends:


I am still wrestling with problems integrating a Sunny Island / Sunny Boy
AC coupled system to a set of 5 E-vault Max battery cabinets.



As a refresher, with closed loop comms, the Frequency Shift Power Control
system is not working, or not working quickly enough, and when nearing full
charge, the voltage can spike up to 66 volts and the SI system shuts down.
Fortress has told me in a roundabout way that they agree this is a real
problem and they are working on a solution.



Another problem has reared its head:  If the E-Vaults do not get charged
fully every 5 to 7 days, the BMS units SOC value becomes radically out of
calibration.  The E-vault will report a higher SOC than is realistic.  The
SI system starts the generator based on SOC and if the SOC is reported as
high the generator don’t start.  Sooner rather than later the battery
voltage gets too low and the system shuts down.



I have been tweaking on the settings like days-since-full-charge to attempt
to get this cycle to stop.  No definitive answer yet.



Here is the reason I am writing:  Yesterday I could not get the Sunny
Islands to start.  The battery voltage was 46 which should have been enough
but for some reason they just would not start.  Because of this I could not
charge the batteries from generator or from AC coupled solar.  I called SMA
but they told me they could not advise because of the non-compatible
batteries.  I asked about the emergency charging procedure in the manual
but I was told this does not work with lithium batteries.  The process is
pretty scary anyway so I was not inclined to try.



SMA told me I may need an external 48 volt charging system.  I have heard
of this being required in certain scenarios by wrenches.  This would be a
huge pain in the ass: ordering one, waiting for it, hooking it up, etc.



Here is what I did:  I initiated the Quick Start Configuration mode and
told the SI system there was a new battery bank.  I told it the bank was a
very small VRLA battery.   The SI system accepted the 46 volts, started up
and allowed a generator charge.  After an hour or so we reprogrammed the
system for lithium and problem resolved, at least for now.



Hopefully this trick may help one of you some day.  If it does, it was
worth my time typing it out.



William



Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com

CA Lic. 773985
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to