William. We have used FM100's, 80's and 60's to charge numerous brands of lithium batteries with no troubles. I don't think you will have any issues in this regard.
Sunny Regards, Kirpal Khalsa Oregon LRT#25 Oregon Solarworks LLC www.oregonsolarworks.com 541-299-0402 On Wed, May 8, 2024 at 8:49 AM jay via RE-wrenches < [email protected]> wrote: > HI William, > > Yes the FM-100 has no problem with keeping the volts pretty tight and i’ve > not heard of any lithium related issues, and someone is bound to chime in > if there are. > > jay > > > > On May 8, 2024, at 9:39 AM, William Miller <[email protected]> > wrote: > > Jay: > > I am considering ditching the Sunny Boys and installing 2 Outback FM100s. > It seems to me this might solve a few problems: > > 1. The cc should voltage clamp and prevent over voltage when the batteries > go higher Z. > 2. The CCs should start up at lower voltages as soon as the sun comes > out. > 3. One of the FM 100s could be configured to drive an AGS relay. > 4. The operation would be voltage dependent, not SOC dependent. > > My concern is the shallow voltage/charge curve. Can I set this system fine > enough to work reliably? > > Has anyone used Outback charge controllers with lithium batteries? Any > advice? > > > William Miller > Miller Solar.com > 805-438-5600 > www.millersolar.com > > > On Wed, May 8, 2024 at 8:30 AM jay <[email protected]> wrote: > >> Hi William, >> >> Since the SOC isn’t being reliable maybe due to not charging correctly? >> >> I would recommend going to volts for the relay driver. Thats why I >> suggested the tristar with RD-1. >> Because really volts at full is the most accurate. >> Not knowing how many PV inputs you could do a cascade. >> >> >> jay >> >> On May 8, 2024, at 9:00 AM, William Miller <[email protected]> >> wrote: >> >> Jay: >> >> Thank you for taking the time. >> >> We are doing just what you suggest as an interim solution. >> >> The shortcoming of this work-around is that the highest setting for this >> relay function is 90% SOC. This may not be high enough to recalibrate the >> BMS units. And again, relying on SOC to drive operational decisions becomes >> problematic when one can’t rely on the accuracy of the SOC value. >> >> >> William Miller >> Miller Solar.com <http://solar.com/> >> 805-438-5600 >> www.millersolar.com >> >> >> On Wed, May 8, 2024 at 7:16 AM jay <[email protected]> wrote: >> >>> A possible fix. >>> >>> You could run a DC relay on the SB PV input that would be voltage >>> triggered to prevent the battery volts from getting higher than you want. >>> >>> The SI has 2 aux relays I think? Or could do a tristar with RD-1 relay >>> that has 4 channels. >>> >>> Just a thought >>> >>> jay >>> >>> On May 7, 2024, at 11:11 PM, William Miller via RE-wrenches < >>> [email protected]> wrote: >>> >>> Friends: >>> >>> >>> I am still wrestling with problems integrating a Sunny Island / Sunny >>> Boy AC coupled system to a set of 5 E-vault Max battery cabinets. >>> >>> >>> As a refresher, with closed loop comms, the Frequency Shift Power >>> Control system is not working, or not working quickly enough, and when >>> nearing full charge, the voltage can spike up to 66 volts and the SI system >>> shuts down. Fortress has told me in a roundabout way that they agree this >>> is a real problem and they are working on a solution. >>> >>> >>> Another problem has reared its head: If the E-Vaults do not get charged >>> fully every 5 to 7 days, the BMS units SOC value becomes radically out of >>> calibration. The E-vault will report a higher SOC than is realistic. The >>> SI system starts the generator based on SOC and if the SOC is reported as >>> high the generator don’t start. Sooner rather than later the battery >>> voltage gets too low and the system shuts down. >>> >>> >>> I have been tweaking on the settings like days-since-full-charge to >>> attempt to get this cycle to stop. No definitive answer yet. >>> >>> >>> Here is the reason I am writing: Yesterday I could not get the Sunny >>> Islands to start. The battery voltage was 46 which should have been enough >>> but for some reason they just would not start. Because of this I could not >>> charge the batteries from generator or from AC coupled solar. I called SMA >>> but they told me they could not advise because of the non-compatible >>> batteries. I asked about the emergency charging procedure in the manual >>> but I was told this does not work with lithium batteries. The process is >>> pretty scary anyway so I was not inclined to try. >>> >>> >>> SMA told me I may need an external 48 volt charging system. I have >>> heard of this being required in certain scenarios by wrenches. This would >>> be a huge pain in the ass: ordering one, waiting for it, hooking it up, etc. >>> >>> >>> Here is what I did: I initiated the Quick Start Configuration mode and >>> told the SI system there was a new battery bank. I told it the bank was a >>> very small VRLA battery. The SI system accepted the 46 volts, started up >>> and allowed a generator charge. After an hour or so we reprogrammed the >>> system for lithium and problem resolved, at least for now. >>> >>> >>> Hopefully this trick may help one of you some day. If it does, it was >>> worth my time typing it out. >>> >>> >>> William >>> >>> >>> Miller Solar >>> 17395 Oak Road, Atascadero, CA 93422 >>> 805-438-5600 >>> www.millersolar.com >>> CA Lic. 773985 >>> >>> >>> >>> >>> _______________________________________________ >>> List sponsored by Redwood Alliance >>> >>> Pay optional member dues here: http://re-wrenches.org >>> >>> List Address: [email protected] >>> >>> Change listserver email address & settings: >>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >>> >>> There are two list archives for searching. When one doesn't work, try >>> the other: >>> https://www.mail-archive.com/[email protected]/ >>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org >>> >>> List rules & etiquette: >>> http://www.re-wrenches.org/etiquette.htm >>> >>> Check out or update participant bios: >>> http://www.members.re-wrenches.org >>> >>> >>> >> > _______________________________________________ > List sponsored by Redwood Alliance > > Pay optional member dues here: http://re-wrenches.org > > List Address: [email protected] > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > There are two list archives for searching. When one doesn't work, try the > other: > https://www.mail-archive.com/[email protected]/ > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > http://www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > http://www.members.re-wrenches.org > >
_______________________________________________ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/[email protected]/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org