HI William,

Yes the FM-100 has no problem with keeping the volts pretty tight and i’ve not 
heard of any lithium related issues, and someone is bound to chime in if there 
are.

jay



> On May 8, 2024, at 9:39 AM, William Miller <will...@millersolar.com> wrote:
> 
> Jay:
> 
> I am considering ditching the Sunny Boys and installing 2 Outback FM100s.  It 
> seems to me this might solve a few problems:
> 
> 1. The cc should voltage clamp and prevent over voltage when the batteries go 
> higher Z. 
> 2. The CCs should start up at lower voltages as soon as the sun comes out.  
> 3. One of the FM 100s could be configured to drive an AGS relay. 
> 4. The operation would be voltage dependent, not SOC dependent. 
> 
> My concern is the shallow voltage/charge curve. Can I set this system fine 
> enough to work reliably?
> 
> Has anyone used Outback charge controllers with lithium batteries?  Any 
> advice?
> 
> 
> William Miller
> Miller Solar.com
> 805-438-5600
> www.millersolar.com <http://www.millersolar.com/>
> 
> 
> On Wed, May 8, 2024 at 8:30 AM jay <jay.pe...@gmail.com 
> <mailto:jay.pe...@gmail.com>> wrote:
> Hi William,
> 
> Since the SOC isn’t being reliable maybe due to not charging correctly?
> 
> I would recommend going to volts for the relay driver.  Thats why I suggested 
> the tristar with RD-1.
> Because really volts at full is the most accurate.
> Not knowing how many PV inputs you could do a cascade.
> 
> 
> jay
> 
>> On May 8, 2024, at 9:00 AM, William Miller <will...@millersolar.com 
>> <mailto:will...@millersolar.com>> wrote:
>> 
>> Jay:
>> 
>> Thank you for taking the time. 
>> 
>> We are doing just what you suggest as an interim solution. 
>> 
>> The shortcoming of this work-around is that the highest setting for this 
>> relay function is 90% SOC. This may not be high enough to recalibrate the 
>> BMS units. And again, relying on SOC to drive operational decisions becomes 
>> problematic when one can’t rely on the accuracy of the SOC value. 
>> 
>> 
>> William Miller
>> Miller Solar.com <http://solar.com/>
>> 805-438-5600
>> www.millersolar.com <http://www.millersolar.com/>
>> 
>> 
>> On Wed, May 8, 2024 at 7:16 AM jay <jay.pe...@gmail.com 
>> <mailto:jay.pe...@gmail.com>> wrote:
>> A possible fix.
>> 
>> You could run a DC relay on the SB PV input that would be voltage triggered 
>> to prevent the battery volts from getting higher than you want.
>> 
>> The SI has 2 aux relays I think?  Or could do a tristar with RD-1 relay that 
>> has 4 channels.
>> 
>> Just a thought
>> 
>> jay
>> 
>>> On May 7, 2024, at 11:11 PM, William Miller via RE-wrenches 
>>> <re-wrenches@lists.re-wrenches.org 
>>> <mailto:re-wrenches@lists.re-wrenches.org>> wrote:
>>> 
>>> Friends:
>>>  
>>> I am still wrestling with problems integrating a Sunny Island / Sunny Boy 
>>> AC coupled system to a set of 5 E-vault Max battery cabinets.  
>>>  
>>> As a refresher, with closed loop comms, the Frequency Shift Power Control 
>>> system is not working, or not working quickly enough, and when nearing full 
>>> charge, the voltage can spike up to 66 volts and the SI system shuts down.  
>>> Fortress has told me in a roundabout way that they agree this is a real 
>>> problem and they are working on a solution.
>>>  
>>> Another problem has reared its head:  If the E-Vaults do not get charged 
>>> fully every 5 to 7 days, the BMS units SOC value becomes radically out of 
>>> calibration.  The E-vault will report a higher SOC than is realistic.  The 
>>> SI system starts the generator based on SOC and if the SOC is reported as 
>>> high the generator don’t start.  Sooner rather than later the battery 
>>> voltage gets too low and the system shuts down.
>>>  
>>> I have been tweaking on the settings like days-since-full-charge to attempt 
>>> to get this cycle to stop.  No definitive answer yet.
>>>  
>>> Here is the reason I am writing:  Yesterday I could not get the Sunny 
>>> Islands to start.  The battery voltage was 46 which should have been enough 
>>> but for some reason they just would not start.  Because of this I could not 
>>> charge the batteries from generator or from AC coupled solar.  I called SMA 
>>> but they told me they could not advise because of the non-compatible 
>>> batteries.  I asked about the emergency charging procedure in the manual 
>>> but I was told this does not work with lithium batteries.  The process is 
>>> pretty scary anyway so I was not inclined to try.
>>>  
>>> SMA told me I may need an external 48 volt charging system.  I have heard 
>>> of this being required in certain scenarios by wrenches.  This would be a 
>>> huge pain in the ass: ordering one, waiting for it, hooking it up, etc.
>>>  
>>> Here is what I did:  I initiated the Quick Start Configuration mode and 
>>> told the SI system there was a new battery bank.  I told it the bank was a 
>>> very small VRLA battery.   The SI system accepted the 46 volts, started up 
>>> and allowed a generator charge.  After an hour or so we reprogrammed the 
>>> system for lithium and problem resolved, at least for now.
>>>  
>>> Hopefully this trick may help one of you some day.  If it does, it was 
>>> worth my time typing it out.
>>>  
>>> William
>>>  
>>> Miller Solar
>>> 17395 Oak Road, Atascadero, CA 93422
>>> 805-438-5600
>>> www.millersolar.com <http://www.millersolar.com/>
>>> CA Lic. 773985
>>>  
>>>  
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> Pay optional member dues here: http://re-wrenches.org 
>>> <http://re-wrenches.org/>
>>> 
>>> List Address: RE-wrenches@lists.re-wrenches.org 
>>> <mailto:RE-wrenches@lists.re-wrenches.org>
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>> 
>>> There are two list archives for searching. When one doesn't work, try the 
>>> other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ 
>>> <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/>
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>>> 
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm 
>>> <http://www.re-wrenches.org/etiquette.htm>
>>> 
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
> 

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to