Wrenches. I am hesitant to post here, since I am not really a Wrench. I feel 
like maybe I can get by with it since I'm so involved with running the list. So 
...

After many years, my VFX 2812 stopped charging my batteries, but continues 
powering my home.

The VFX 2812 is mounted to a Midnite e-panel, with two PV inputs (MX-60 and an 
old Heliotrope CC-60), a FlexNet DC, HUB, and a Mate2. A battery temp sensor is 
between two of my Surrette 2-KS-33P batteries.

Some time ago, the red error light behind the clear cover on the inverter 
started blinking, but it continued charging from our 7 kW generator -- so I 
suspect it had nothing to do with my current charging problem. Discussing with 
Bill Battagin, the light was possibly a fan error, apparently a bit common. 

I tried switching generators, as the first one showed 64 CPS, but that did not 
help.
When I start the generator, the AC In light on the Mate2 on (and stays on), and 
I hear an inverter relay clicking as if the generator warm-up delay feature 
keeps going through its cycle. The house lights flicker at the same time as the 
click, but charging never happens.

I've re-seated all the Cat-5 cables with Outback contact goop on all ends, and 
I replaced the Mate2 cable with a new Outback one. I've checked and tightened 
all the connections in the e-Panel and batteries.

Question 1: 
So what can I do to further diagnose or even fix this? Buying a new or even 
used VFX inverter is out of the question, financially.

Question 2:
I still have my old Trace U2512 inverter. I'd like to hook its charger into the 
 e-Panel, as a temporary situation -- for times like last week when we were 
fogged in for a few days, letting my batteries get a lot lower than I want. 

I would not use the AC output on the Trace, but would continue powering my home 
with the VFX. I figured I would put the Trace battery cables in parallel with 
the VFX so that the Trace charging will also go through the shunt so I can see 
the charge rates and levels on the Mate2. 

The generator's wires would be changed from the e-Panel  AC In to the Trace AC  
In.  

The last thing I want to do is further harm my equipment. What say ye to this 
temporary idea?

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to