New AC board [if available) is around $250  +/- and relatively straightforward 
to replace.
FET board is twice as much $

Sent from my iPad

> On Aug 14, 2024, at 6:19 PM, jay via RE-wrenches 
> <[email protected]> wrote:
> 
> HI Michael,
> 
> I’d say the AC board on the VFX is suspect. Bad relay. 
> 
> 
> Yes to #2.  That will work just fine.  
> Good luck
> 
> jay
> 
>> On Aug 14, 2024, at 4:13 PM, Michael Welch via RE-wrenches 
>> <[email protected]> wrote:
>> 
>> Wrenches. I am hesitant to post here, since I am not really a Wrench. I feel 
>> like maybe I can get by with it since I'm so involved with running the list. 
>> So ...
>> 
>> After many years, my VFX 2812 stopped charging my batteries, but continues 
>> powering my home.
>> 
>> The VFX 2812 is mounted to a Midnite e-panel, with two PV inputs (MX-60 and 
>> an old Heliotrope CC-60), a FlexNet DC, HUB, and a Mate2. A battery temp 
>> sensor is between two of my Surrette 2-KS-33P batteries.
>> 
>> Some time ago, the red error light behind the clear cover on the inverter 
>> started blinking, but it continued charging from our 7 kW generator -- so I 
>> suspect it had nothing to do with my current charging problem. Discussing 
>> with Bill Battagin, the light was possibly a fan error, apparently a bit 
>> common. 
>> 
>> I tried switching generators, as the first one showed 64 CPS, but that did 
>> not help.
>> When I start the generator, the AC In light on the Mate2 on (and stays on), 
>> and I hear an inverter relay clicking as if the generator warm-up delay 
>> feature keeps going through its cycle. The house lights flicker at the same 
>> time as the click, but charging never happens.
>> 
>> I've re-seated all the Cat-5 cables with Outback contact goop on all ends, 
>> and I replaced the Mate2 cable with a new Outback one. I've checked and 
>> tightened all the connections in the e-Panel and batteries.
>> 
>> Question 1: 
>> So what can I do to further diagnose or even fix this? Buying a new or even 
>> used VFX inverter is out of the question, financially.
>> 
>> Question 2:
>> I still have my old Trace U2512 inverter. I'd like to hook its charger into 
>> the  e-Panel, as a temporary situation -- for times like last week when we 
>> were fogged in for a few days, letting my batteries get a lot lower than I 
>> want. 
>> 
>> I would not use the AC output on the Trace, but would continue powering my 
>> home with the VFX. I figured I would put the Trace battery cables in 
>> parallel with the VFX so that the Trace charging will also go through the 
>> shunt so I can see the charge rates and levels on the Mate2. 
>> 
>> The generator's wires would be changed from the e-Panel  AC In to the Trace 
>> AC  In.  
>> 
>> The last thing I want to do is further harm my equipment. What say ye to 
>> this temporary idea?
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org
>> 
>> List Address: [email protected]
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to