Jason 
What’s the possibllity it was a lighting strike?

Jay

> On Oct 10, 2024, at 2:57 PM, Jason Szumlanski via RE-wrenches 
> <[email protected]> wrote:
> 
> 
> We have been talking a lot recently about all-in-ones. I just had a massive 
> fail during Hurricane Milton with a quad Sol-Ark 15K off-grid system that 
> deserves some discussion about whether AIO is a good idea if it can't build 
> in some resilience to errors. I'm not sure if the new Midnite unit is better 
> in this respect, but this is what happened to the Sol-Ark system...
> 
> Four inverters, each with 4 strings of PV paralleled to 2 MPPT per inverter. 
> One of the slave units developed some sort of PV DC fault during the storm. 
> This caused the slave inverter to shut down and throw an error, which in turn 
> caused a parallel fault across all four inverters. Power output ceases at 
> that point. Apparently the system keeps resetting because I have a cell modem 
> that uploads data to Sol-Ark, but that cell modem is powered by the inverter 
> outputs, so it must be getting power at least intermittently. The rest of the 
> loads are basically flatlined according to the Sol-Ark data. It's mostly air 
> conditioners, so they probably can't turn on fast enough before the PV fault 
> causes another shutdown.
> 
> So, in essence, one of 16 strings of PV develops a fault, and that causes all 
> four inverters to malfunction? What is the point of redundancy if a fault of 
> one results in a fault of all?! If there is a true PV input fault, shouldn't 
> that just shut down that MPPT, or perhaps all of the PV DC input to that 
> inverter? And why can't this inverter continue to invert power from the 
> batteries and charge from a generator when there is a DC input fault that 
> could be programmatically isolated and ignored?
> 
> This is a bad design in my opinion, and something I hadn't considered. If the 
> faulted inverter can't function with a DC input fault, it should just take 
> itself out of the game. (This is 120/240 split phase, BTW). Is this how all 
> AIO inverters work? One inverter fault on the DC side kills all paralleled 
> units' AC output? Not good.
> 
> This is a completely off-grid system on a remote island with no vehicle 
> access, so it's not exactly easy to do a "truck roll" on this one, especially 
> post-hurricane. To make matters worse, the generator was running at the time 
> of the fault, as it was being signaled to run because the battery had reached 
> the assigned charge voltage. The fault also killed the 2-wire start signal 
> from the master, so the system also stopped passing through generator power 
> to the loads. The house is dark.
> 
> 
> Jason Szumlanski
> Florida Solar Design Group
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to