Another reason to do separate charge controllers is Low battery. If the AIO inverter hits its LBCO, then it takes out the PV input as well. Then the draw of the BCM takes what's left in the battery, and you're into a dark start.  Generator won't even help.  AIOs are easy to install, but not as full proof as DC coupled PV systems.  Also, the inter communication is a major issue.  I've seen inter connected charge controllers take each other out, which really defeats the redundancy of having multiple units.  I'm sure many on the list will question my wisdom; but I usually don't interconnect any of the equipment from a comms stand point.  I use open loop charging based on voltage.

I once had a pinched temp sensor, that thought the batteries were at 5000 deg Kelvin.  It shut all 4 inverters down.  My most reliable multiple inverter setup is a four SW4048 system that is now 24 years old.  Each inverter feeds one leg of two load centers.  No comms, No 240 vac loads.  No shut downs.  That is the gold standard, and none of the AIO stuff, nor the module level rapid shutdown etc, can even get close to the level of reliability we had in the past.  In the off grid world, shut downs can be life threatening, and all the additional "safety" stuff added to the code since, has actually made my off grid customers less safe.

You have to think what happens if the battery gets low, and no one is home?  Can it recover on its own, like a traditional DC coupled Lead acid system?  Basically, If the system can't hit LBCO, recharge the next day, and automatically turn loads back on, we've gone backwards in our designs, and equipment selection. AIOs are inferior if they can't achieve this basic functionality.  If UL standards are causing this, then those standards are incorrect for critical off grid and backup applications.

Ray Walters
Remote Solar

On 10/10/2024 4:02 PM, Eric Smiley via RE-wrenches wrote:
Install stand-alone charge controllers. That is the only way to get redundancy.

Eric Smiley (he/him) - Design Manager
 250.703.6004
[email protected]
 888.386.0116
3-4997 Polkey Rd, Duncan BC, V9L 6W3
viridiansolar.ca <https://www.google.com/url?q=https://viridiansolar.ca&source=gmail-html&ust=1702155901939000&usg=AOvVaw3SHpXB-WRSlzWmjpz4htqG>


                

Viridian Solar honours the ancestral grounds on which we live and provide services, recognising that these lands are unceded Indigenous territory. We are steadfast in our commitment to reconciliation and acknowledge the rich history and traditions that characterise this land that we all consider home.



On Thu, 10 Oct 2024 at 14:59, Lou Russo via RE-wrenches <[email protected]> wrote:

    Aloha All,

    Thank you Jason. This is a huge and surprising issue. So much so
    that I dropped what I was doing and called Sol-Ark to confirm.
    Mind you this was level 1 support, but I was told this is what the
    Sol-Arks are supposed to do and it is a feature not a bug.
    Their take is if there is any fault on any one string, the Sol-Ark
    assumes the worst and shuts everything down.

    I wonder what solutions could be implemented on future installs to
    prevent this from happening?

    Aloha,

    Lou Russo
    Owner
    [email protected]
    Office - 808 345 6762
    Spree Solar Systems LLC
    CT-34322



    On Thu, Oct 10, 2024 at 11:45 AM Jason Szumlanski via RE-wrenches
    <[email protected]> wrote:

        I think it's more likely water in a J-box or possibly physical
        damage, but someone passed by the property and did not observe
        any physical damage to the array.

        Jason Szumlanski
        Principal Solar Designer | Florida Solar Design Group
        NABCEP Certified Solar Professional (PVIP)
        Florida State Certified Solar Contractor CVC56956
        Florida Certified Electrical Contractor EC13013208


        On Thu, Oct 10, 2024 at 5:41 PM Jay <[email protected]> wrote:

            Jason
            What’s the possibllity it was a lighting strike?

            Jay

            On Oct 10, 2024, at 2:57 PM, Jason Szumlanski via
            RE-wrenches <[email protected]> wrote:

            
            We have been talking a lot recently about all-in-ones. I
            just had a massive fail during Hurricane Milton with a
            quad Sol-Ark 15K off-grid system that deserves some
            discussion about whether AIO is a good idea if it can't
            build in some resilience to errors. I'm not sure if the
            new Midnite unit is better in this respect, but this is
            what happened to the Sol-Ark system...

            Four inverters, each with 4 strings of PV paralleled to 2
            MPPT per inverter. One of the slave units developed some
            sort of PV DC fault during the storm. This caused the
            slave inverter to shut down and throw an error, which in
            turn caused a parallel fault across all four inverters.
            Power output ceases at that point. Apparently the system
            keeps resetting because I have a cell modem that uploads
            data to Sol-Ark, but that cell modem is powered by the
            inverter outputs, so it must be getting power at least
            intermittently. The rest of the loads are basically
            flatlined according to the Sol-Ark data. It's mostly air
            conditioners, so they probably can't turn on fast enough
            before the PV fault causes another shutdown.

            So, in essence, one of 16 strings of PV develops a fault,
            and that causes all four inverters to malfunction? What
            is the point of redundancy if a fault of one results in a
            fault of all?! If there is a true PV input fault,
            shouldn't that just shut down that MPPT, or perhaps all
            of the PV DC input to that inverter? And why can't this
            inverter continue to invert power from the batteries and
            charge from a generator when there is a DC input fault
            that could be programmatically isolated and ignored?

            This is a bad design in my opinion, and something I
            hadn't considered. If the faulted inverter can't function
            with a DC input fault, it should just take itself out of
            the game. (This is 120/240 split phase, BTW). Is this how
            all AIO inverters work? One inverter fault on the DC side
            kills all paralleled units' AC output? Not good.

            This is a completely off-grid system on a remote island
            with no vehicle access, so it's not exactly easy to do a
            "truck roll" on this one, especially post-hurricane. To
            make matters worse, the generator was running at the time
            of the fault, as it was being signaled to run because the
            battery had reached the assigned charge voltage. The
            fault also killed the 2-wire start signal from the
            master, so the system also stopped passing through
            generator power to the loads. The house is dark.


            Jason Szumlanski
            Florida Solar Design Group

            _______________________________________________
            List sponsored by Redwood Alliance

            Pay optional member dues here: http://re-wrenches.org

            List Address: [email protected]

            Change listserver email address & settings:
            http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

            There are two list archives for searching. When one
            doesn't work, try the other:
            https://www.mail-archive.com/[email protected]/
            http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

            List rules & etiquette:
            http://www.re-wrenches.org/etiquette.htm

            Check out or update participant bios:
            http://www.members.re-wrenches.org

        _______________________________________________
        List sponsored by Redwood Alliance

        Pay optional member dues here: http://re-wrenches.org

        List Address: [email protected]

        Change listserver email address & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

        There are two list archives for searching. When one doesn't
        work, try the other:
        https://www.mail-archive.com/[email protected]/
        http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

        List rules & etiquette:
        http://www.re-wrenches.org/etiquette.htm

        Check out or update participant bios:
        http://www.members.re-wrenches.org

    _______________________________________________
    List sponsored by Redwood Alliance

    Pay optional member dues here: http://re-wrenches.org

    List Address: [email protected]

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    There are two list archives for searching. When one doesn't work,
    try the other:
    https://www.mail-archive.com/[email protected]/
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    http://www.re-wrenches.org/etiquette.htm

    Check out or update participant bios:
    http://www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here:http://re-wrenches.org

List Address:[email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to