I just can't believe that Midnite would not have solar stay on after LBCO !
Schneider and Outback always did this from a long way back to Trace.

Hear the water sound as it circles the drain?

Dave Angelini Offgrid Solar
"we go where powerlines don't"
   [1]https://offgridsolar1.com/ [2]  [1]
e-mail  offgridso...@sti.net
text 209 813 0060

On 2025-05-12 10:33 am, MDElectricSolar via RE-wrenches wrote:

We have been using the Solark inverter for GTBB and off grid clients. In the case of low battery cut out the solar does stay alive in the background and will recharge the batteries when the sun comes out the next day and turn itself back on and provide AC power output.

Michael D Nelson
MD Electric & Solar, Inc.
707-684-0064 mobile
707-884-1862 office
www.mdelectricsolar.com
www.facebook.com/mdelectricandsolar

On May 12, 2025, at 10:13 AM, Ray Walters via RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:

So the bypass switch gets the house power on, and I too always recommend a hard bypass switch. However, you still need a 48 v power supply to get the battery system back up, and that's becoming a serious pain in my aging backside. Until AIOs with Li+ batteries, lead acid would have enough voltage to get the charge controller to come back on, and eventually the customer could get the inverter back on too. No special trip out.

We need an independent circuit that would sense array voltage, and wake up the battery, so it could take a charge: a backup battery for the offgrid battery. Without that, AIOs and Li+ batteries are not self healing like Lead Acid. We are going backwards fast, but with an amazing amount of new Chinese technology driving the jalopy in reverse. (Danger Will Robinson)

Ray Walters
Remote Solar

On 5/12/2025 10:54 AM, Jason Szumlanski via RE-wrenches wrote:

We always recommend a transfer switch to bypass the inverter and send generator power to the loads. Most clients take us up on it. For retrofits, sometimes there can be space limitations, however.

As for the function of the AIO, there is no integrated mechanical bypass, and since there is an internal relay controlling the generator input (or smart load output on that breaker), I think the default function is for the relay to open when the inverter turns off. AC voltage on the load side of the breaker does not close the relay and turn the inverter back on automatically.

Jason Szumlanski
Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956
Florida Certified Electrical Contractor EC13013208

On Mon, May 12, 2025 at 9:49 AM Dave Angelini Offgrid Solar via RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:

All sounds wrong to me. Call Midnite.

Typically there is a AC bypass mechanical switch that allows the gen to bypass the inverter and power loads.

Dave Angelini Offgrid Solar
"we go where powerlines don't"
[1]https://offgridsolar1.com/ [2]  [1]
e-mail  offgridso...@sti.net
text 209 813 0060

On 2025-05-12 9:29 am, Jason Szumlanski via RE-wrenches wrote:

Maybe I'm missing something, but it seems like there is a flaw in the logic for how generator integration works with this product. Unlike some of the other AIOs, you can't put the generator on the Grid input in an off-grid scenario. You have to use the Generator smart load breaker, which isn't a dedicated generator input, but a programmable circuit. This is problematic because it seemingly has a normally open internal relay that closes only when the inverter is ON. At least, that's how it seems to work in my limited experience.

Why is this a problem? If the battery capacity drops below the low voltage cutoff, the inverter turns off. You have to turn the inverter ON for the generator relay to close so you can charge the battery, but since the battery is too low, the inverter won't turn on. You would have to reprogram the inverter to drop the cutoff voltage/SOC below the current battery state. For people who do not want to use AGS, or if AGS fails to start the generator for any reason, getting the generator to charge the battery manually is no easy task.

Moreover, turning the generator on manually when the inverter is in an OFF state will not pass power to the loads, and will not turn the inverter ON automatically. You have to get the inverter turned ON somehow so that the generator power can pass through to the loads. And since the startup sequence for this inverter is very quirky, non-intuitive, and unreliable, that makes the problem even worse. I'm not sure if you can even turn the inverter ON when there is generator input and the battery is too low. I don't think you can because the relay is open and the inverter doesn't even see generator voltage when it is in an OFF state.

This seems like a serious oversight and a reason to go with one of the other AIOs on the market. I believe the Sol-Ark 15K and EG4 18kPV will both immediately power loads and start charging when the generator is on, regardless of whether the generator is connected to the Grid or Generator input. Any AC input immediately passes through to the loads. This is because those inverters stay "on" when a low battery condition is met, and they simply stop using the battery to invert power if the battery conditions do not allow it, based on the settings.

The logic of the Midnite AIOs turning "off" when battery cutoff is met and opening the generator relay doesn't make sense to me. Am I wrong about how this works?

Jason Szumlanski
Principal Solar Designer
Florida Solar Design Group

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

 _______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Links:
------
[1] http://members.sti.net/offgridsolar/
[2] https://offgridsolar1.com/
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to