I couldn't agree more with Ray. Those batteries are tough. Assuming there is 
adequate charging capacity the batteries have a very good chance of recovering. 
That being said the renter has to be trained! Simply spending more money to 
replace the Hup batteries wit a set of new LIPO batteries will most likely 
trade one problem for another. As others have already pointed out: If energy in 
is less than energy out the batteries will not be able to make up the 
difference. Even LIPO batteries.
Pieter Huebner
Project Manager
Off Grid Enerprises
________________________________
From: RE-wrenches <[email protected]> on behalf of Nick 
Lucchese via RE-wrenches <[email protected]>
Sent: Friday, December 12, 2025 11:41 PM
To: RE-wrenches <[email protected]>
Cc: Nick Lucchese <[email protected]>
Subject: Re: [RE-wrenches] FLA battery problelm

Are you able to get near the 75 amp charge rate with the SW's charger and that 
7.5 KW generator with a step down transformer maybe? Neither charging combos 
can push the voltage above 52? All the bus bars and hardware have been cleaned 
and reassembled recently or not since 2022? Have you made any other 
observations looking over that 128 day logging menu?

Battery banks prematurely heading to the smelter is the unfortunate reality of 
our systems of the past. Chasing that mostly unrealistic goal that the bank 
will do some dramatic turn around to redeem everyone's efforts may likely 
result in more wasted time and money. Replacing with a lithium pack that 
offer's it's own onboard SOC capacity meter is almost a necessity with renters. 
Removing the unknown cloud around understanding what the battery needs results 
in a much more enjoyable homestead experience and engages the renter to be 
accountable for recharging. Offerings from both Midnite and Rubix can be had 
for less than $.28 a watt hour retail these days. Impressive times for folks 
storing sunshine. The sooner it goes in the sooner the fuel savings and lack of 
service calls can start paying it off.

I always default to Midnite first for quite a few reasons and especially for 
`UL9540 but Rubix might be a better solution in this case since that volatile 
memory Steve mentions might become a concern if a trained individual isn't 
frequently checking up on the system to make sure all the settings are still in 
tune with the battery. Besides for LBCO, SW default settings are quite ideal 
for all of the Rubix series. You also gain the bonus of a digital net power 
meter on the battery to validate the SW's meter screens along with the Outback 
logging menu.

Nick



On Fri, Dec 12, 2025 at 10:21 AM David Coale via RE-wrenches 
<[email protected]<mailto:[email protected]>> 
wrote:
Hi Wrenchers,

I have a client with an old off-grid Trace system and he is having trouble with 
the batteries.  He has HUP Solar One FLA batteries that are about 4 years old, 
so they should be in good shape.  The last set lasted almost 20 years with a 
fair amount of abuse.

Here is he history and what I think is going on. 7/21 they got new batteries 
after about 19 years of use.

7/22 I get a call saying the batteries are not charging up all the way.  When I 
check out the system, the batteries needed cleaning, and I found three low 
cells, and the charger settings were back to default, not set high enough to 
charge the batteries all the way (it’s always multiple problems).  The client 
(now a new renter, new to the system) said he was filing the batteries once a 
month and experienced some overflowing when the batteries were charged up.

I cleaned things up, reset the charging parameters and set up an equalizing 
charge to even out the cells. Hopefully this will fix things.

11/25. The client calls and said the batteries don’t charge up all the way and 
he is running the generator a lot and worried about getting though the 
wintertime.
When I check things out, there are three bad cells and there is soda on the 
batteries. It is hard to get a good voltage readings because of the soda. Most 
of the cells are reading 2.1 volts under about a 40 amp load.

Yesterday I check things out, and all the cells are reading between 1.93 to 
1.98 under a 40 amp load in the morning, and I don’t find any bad cells.  The 
charging voltage is never going over about 52 volts so the system is never 
getting fully charged up.  The charge setting look OK, so not sure what is 
going on. This is acting like an old battery pack but these batteries are 
relatively new.

My guess at this point is that maybe the batteries lost acid with the 
overflowing event and lost capacity.  Maybe adding acid back in would bring 
them back up to working order.  The SG measured at 1.150 or less.

At this point the client (renter) has had enough of these battery problems and 
is wondering every morning if the batteries will last long enough to until the 
sun comes up.  The renter is pushing for a replacement LFP battery, but there 
should be lots of life left in this battery pack.

Let me know what you all think.

Thanks,

David


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to