I spent decades talking folks through recovering HUPs that had been
chronically under charged. The fact that the batteries are just
hovering around 52 v and not breaking out above that is another sign
that there is capacity left. Its when they charge right up to 58 v and
go into float before 10 AM that you have no capacity left. That hovering
at partial SOC is because there is not a high enough charge rate.
They need to start the generator in the morning, so that both the
generator and the solar can work together to have a high enough charge rate.
Equalize, Equalize, Equalize, they will come back to full charge, but
yes they will have lost some capacity from when they were new. These
batteries could easily last another 5 years if recovered.
We're not talking 2 to 4 hours of generator charging either, we're
talking like 12 hours a day possibly, for 3 to 4 days. You just keep
going until the SG comes up. Period. Then bring them to full charge
every week to 10 days, and don't let them sit chronically under charged
again.
More solar or a drastic weight loss program is the only way to make this
system work long term.
Ray Walters
Remote Solar
On 12/13/2025 12:13 PM, pieter offgridenterprises.org via RE-wrenches wrote:
I couldn't agree more with Ray. Those batteries are tough. Assuming
there is adequate charging capacity the batteries have a very good
chance of recovering. That being said the renter has to be trained!
Simply spending more money to replace the Hup batteries wit a set of
new LIPO batteries will most likely trade one problem for another. As
others have already pointed out: If energy in is less than energy out
the batteries will not be able to make up the difference. Even LIPO
batteries.
Pieter Huebner
Project Manager
Off Grid Enerprises
------------------------------------------------------------------------
*From:* RE-wrenches <[email protected]> on
behalf of Nick Lucchese via RE-wrenches
<[email protected]>
*Sent:* Friday, December 12, 2025 11:41 PM
*To:* RE-wrenches <[email protected]>
*Cc:* Nick Lucchese <[email protected]>
*Subject:* Re: [RE-wrenches] FLA battery problelm
Are you able to get near the 75 amp charge rate with the SW's charger
and that 7.5 KW generator with a step down transformer maybe? Neither
charging combos can push the voltage above 52? All the bus bars and
hardware have been cleaned and reassembled recently or not since 2022?
Have you made any other observations looking over that 128 day logging
menu?
Battery banks prematurely heading to the smelter is the unfortunate
reality of our systems of the past. Chasing that mostly unrealistic
goal that the bank will do some dramatic turn around to redeem
everyone's efforts may likely result in more wasted time and money.
Replacing with a lithium pack that offer's it's own onboard SOC
capacity meter is almost a necessity with renters. Removing the
unknown cloud around understanding what the battery needs results in a
much more enjoyable homestead experience and engages the renter to be
accountable for recharging. Offerings from both Midnite and Rubix can
be had for less than $.28 a watt hour retail these days. Impressive
times for folks storing sunshine. The sooner it goes in the sooner the
fuel savings and lack of service calls can start paying it off.
I always default to Midnite first for quite a few reasons and
especially for `UL9540 but Rubix might be a better solution in this
case since that volatile memory Steve mentions might become a concern
if a trained individual isn't frequently checking up on the system to
make sure all the settings are still in tune with the battery. Besides
for LBCO, SW default settings are quite ideal for all of the Rubix
series. You also gain the bonus of a digital net power meter on the
battery to validate the SW's meter screens along with the Outback
logging menu.
Nick
On Fri, Dec 12, 2025 at 10:21 AM David Coale via RE-wrenches
<[email protected]> wrote:
Hi Wrenchers,
I have a client with an old off-grid Trace system and he is having
trouble with the batteries. He has HUP Solar One FLA batteries
that are about 4 years old, so they should be in good shape. The
last set lasted almost 20 years with a fair amount of abuse.
Here is he history and what I think is going on. 7/21 they got new
batteries after about 19 years of use.
7/22 I get a call saying the batteries are not charging up all the
way. When I check out the system, the batteries needed cleaning,
and I found three low cells, and the charger settings were back to
default, not set high enough to charge the batteries all the way
(it’s always multiple problems). The client (now a new renter,
new to the system) said he was filing the batteries once a month
and experienced some overflowing when the batteries were charged up.
I cleaned things up, reset the charging parameters and set up an
equalizing charge to even out the cells. Hopefully this will fix
things.
11/25. The client calls and said the batteries don’t charge up all
the way and he is running the generator a lot and worried about
getting though the wintertime.
When I check things out, there are three bad cells and there is
soda on the batteries. It is hard to get a good voltage readings
because of the soda. Most of the cells are reading 2.1 volts under
about a 40 amp load.
Yesterday I check things out, and all the cells are reading
between 1.93 to 1.98 under a 40 amp load in the morning, and I
don’t find any bad cells. The charging voltage is never going
over about 52 volts so the system is never getting fully charged
up. The charge setting look OK, so not sure what is going on.
This is acting like an old battery pack but these batteries are
relatively new.
My guess at this point is that maybe the batteries lost acid with
the overflowing event and lost capacity. Maybe adding acid back
in would bring them back up to working order. The SG measured at
1.150 or less.
At this point the client (renter) has had enough of these battery
problems and is wondering every morning if the batteries will last
long enough to until the sun comes up. The renter is pushing for a
replacement LFP battery, but there should be lots of life left in
this battery pack.
Let me know what you all think.
Thanks,
David
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work,
try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here:http://re-wrenches.org
List Address:[email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org