You must be quoting the 6 hr forklift discharge rate.  That's actually the HUP SO-6-85-17 which is rated at 845 amp-hrs at the 20 hr discharge rate.  The 20 hr rate is what we should be using most of the time for off grid solar.   The minimum charge rate for that battery is 68 amps.  That array could only do 50 amps on a perfect day, so immediately, your array is undersized.  Plus from the sound of it, they are just chronically under charging/ over discharging the battery.  I would suggest doing a complete load profile of their daily loads, and designing an array that can meet that load year round.

Renting an off grid home is always a mess.  I started charging anytime I was going to be brought into that situation, since I didn't design the system for the new user.  Just because it worked great fro the original user, does NOT mean its going to be adequate at all for the average American consumer.   I'm guessing the array needs to be doubled in size.

Ray Walters
Remote Solar

On 12/12/2025 3:51 PM, David Coale via RE-wrenches wrote:
Thanks for the comments so far.  The system consist of two Trace SW5548 inverter couple into a 240 volt system.  Batteries are 680 amp/h 48 volts, with 2.4kw solar and an Outback charge controller.  The generator is a 7.5kW generator.  When the inverters shut down, the charge parameter are reset to default, which is too low for these batteries.  That said, this does not happen with the charge controller which does most of the charging, though this might not be enough in the wintertime.

The voltage used to go up to 58 on bulk charge but now never goes higher then about 52 and the capacity is down.

It’s always hard to tell from a distance what is actually happening at the site, so I am sue I don’t have the complete picture.

Thanks,

David


On Dec 12, 2025, at 1:38 PM, Jay via RE-wrenches <[email protected]> wrote:

A few questions

What’s the charge capacity?  Like how big is the generator and solar

How many amp hrs is the battery?

How are they determining they are not getting full?

What controller?

Is there a trimetric to keep tabs.

Given what you’ve said, I lean towards constant undercharging. Are they salvageable? Possibly

I’d do a eq as high as possible from the oem. Take SG readings. Let them cool a few days and do it again. If you are seeing an increase in SG and leveling out of the differences then keep going.

Depending on the size of the generator and loads and size of the bank it could take a lot of hours of charging. So people run out of gasoline or hate hearing the generator or figure 2 hours is enough.







On Dec 12, 2025, at 11:34 AM, Jason Szumlanski via RE-wrenches <[email protected]> wrote:


I second the chronic undercharging suggestion. We have a client with a 64 kWh FLA battery bank that only has 2.4 kW of PV. When they bought these batteries two years ago, they thought they could solve all of their energy woes by just buying a bigger battery. It is astonishing how many people don't understand that batteries themselves do not generate electricity - they just store it. They must think it's magic!

Anyway, with that kind of PV to storage ratio, they were probably barely getting past the internal resistance. The batteries are completely toast now, and the client is moving to LFP (with more solar per my demand).


Jason Szumlanski
Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956
Florida Certified Electrical Contractor EC13013208


On Fri, Dec 12, 2025 at 1:32 PM Michael Morningstar via RE-wrenches <[email protected]> wrote:

    Chronic undercharging, electrolyte dilution, lack of informed
    equalization, and adding water without knowledge of the how’s,
    whys, and when’s will kill those batteries in no time. I’ve
    pulled out to many of those heavy bastards to count, most of
    them at a fresh young  age because the installer didn’t educate
    the clients properly.


    On Fri, Dec 12, 2025 at 10:21 AM David Coale via RE-wrenches
    <[email protected]> wrote:

        Hi Wrenchers,

        I have a client with an old off-grid Trace system and he is
        having trouble with the batteries.  He has HUP Solar One FLA
        batteries that are about 4 years old, so they should be in
        good shape. The last set lasted almost 20 years with a fair
        amount of abuse.

        Here is he history and what I think is going on. 7/21 they
        got new batteries after about 19 years of use.

        7/22 I get a call saying the batteries are not charging up
        all the way.  When I check out the system, the batteries
        needed cleaning, and I found three low cells, and the
        charger settings were back to default, not set high enough
        to charge the batteries all the way (it’s always multiple
        problems).  The client (now a new renter, new to the system)
        said he was filing the batteries once a month and
        experienced some overflowing when the batteries were charged up.

        I cleaned things up, reset the charging parameters and set
        up an equalizing charge to even out the cells. Hopefully
        this will fix things.

        11/25. The client calls and said the batteries don’t charge
        up all the way and he is running the generator a lot and
        worried about getting though the wintertime.
        When I check things out, there are three bad cells and there
        is soda on the batteries. It is hard to get a good voltage
        readings because of the soda. Most of the cells are reading
        2.1 volts under about a 40 amp load.

        Yesterday I check things out, and all the cells are reading
        between 1.93 to 1.98 under a 40 amp load in the morning, and
        I don’t find any bad cells.  The charging voltage is never
        going over about 52 volts so the system is never getting
        fully charged up.  The charge setting look OK, so not sure
        what is going on. This is acting like an old battery pack
        but these batteries are relatively new.

        My guess at this point is that maybe the batteries lost acid
        with the overflowing event and lost capacity.  Maybe adding
        acid back in would bring them back up to working order.  The
        SG measured at 1.150 or less.

        At this point the client (renter) has had enough of these
        battery problems and is wondering every morning if the
        batteries will last long enough to until the sun comes up. 
        The renter is pushing for a replacement LFP battery, but
        there should be lots of life left in this battery pack.

        Let me know what you all think.

        Thanks,

        David


        _______________________________________________
        List sponsored by Redwood Alliance

        Pay optional member dues here: http://re-wrenches.org

        List Address: [email protected]

        Change listserver email address & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

        There are two list archives for searching. When one doesn't
        work, try the other:
        https://www.mail-archive.com/[email protected]/
        http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

        List rules & etiquette:
        http://www.re-wrenches.org/etiquette.htm

        Check out or update participant bios:
        http://www.members.re-wrenches.org

--

    Michael Morningstar

    Morningstar Electric Inc
    PO Box 1494
    Mount Shasta, CA 96067
    530-921-0560
    CSLB 1116835
    [email protected]

    _______________________________________________
    List sponsored by Redwood Alliance

    Pay optional member dues here: http://re-wrenches.org

    List Address: [email protected]

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    There are two list archives for searching. When one doesn't
    work, try the other:
    https://www.mail-archive.com/[email protected]/
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    http://www.re-wrenches.org/etiquette.htm

    Check out or update participant bios:
    http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here:http://re-wrenches.org

List Address:[email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to