Trying to troubleshoot an outback FNDC that's giving completely wacky SOC
readings.  Yet the current readings all appear to be reasonable. We just
replaced the FNDC because of a lightning strike -- came in through the
ethernet to the mate it seems (took out a router too), and took out the
mate3s, hub10, and possibly the old FNDC.  So all of those are new.  Rest
of the system is maybe 5 to 6 years old -- four radians, four FM100's,
1200AH of 16 cell LFP batteries (open loop).  Has been operating pretty
well for the past few years other than some battery BMS failures.  About 6
weeks ago, it looks like the SOC started being completely wrong on the old
FNDC as well... which makes me question something about wiring... a wire
coming loose from the shunt or or ??

Whenever I do a spot check for amperage from it, it looks right.  But then
it bounces from 100% SOC to 2% SOC in one hour... physically impossible.
And then, I drain 23kWh out of the batteries, and it stays at 100% SOC for
the next 6 hours.  Recorded voltages also look good during spot checks, and
for the recorded min-max on the graph (not sure if those are from the FNDC
or the inverter though).  System is operating fine, as long as I do all
controls based on voltage, not SOC.

Of course the system is 2500 miles from me, so I'm also trying to
troubleshoot remotely.

I did ask outback tech support, and was surprised to get an answer back...
which turned out to be completely useless.  They said the FNDC only works
with lead acid batteries, and lithium batteries are used in closed loop.
Nevermind that I have well over a dozen radian systems with lithium
batteries and FNDC's working correctly, and this exact system was working
correctly that way for 5 years.

Zeke

-- 
Zeke Yewdall
PV Engineer
NABCEP #031508-89
[email protected]
303-523-3592
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to