Ground kits at top and bottom of vertical feedline run (before any bends),
and another ground kit at the entrance port to the buildling/shelter.
Polyphasers inside the shelter mounted to the the common-point ground bus
bar for all of the indoor equipment, with the indoor common-point ground
tied into the site ground system using low L/C conductors (3" Cu strap
preferred, #2 AWG for short runs, avoiding right-angle bends).
--- Jeff
> -----Original Message-----
> From: [email protected]
> [mailto:[EMAIL PROTECTED] On Behalf Of Mike
> Besemer (WM4B)
> Sent: Thursday, June 21, 2007 10:13 AM
> To: [email protected]
> Subject: RE: [Repeater-Builder] RE: VSWR Issues - Repairs Complete
>
> No. but that was recommended and we're considering. What are
> your thoughts?
>
>
>
> ________________________________
>
> From: [email protected]
> [mailto:[EMAIL PROTECTED] On Behalf Of Jeff DePolo
> Sent: Thursday, June 21, 2007 10:03 AM
> To: [email protected]
> Subject: RE: [Repeater-Builder] RE: VSWR Issues - Repairs Complete
>
>
>
> > Someone decided to pull the hardline out of the shack - I
> > think the idea was to remove the bottom 35 feet, which had
> > been spliced on using a hardline splice) to test the two
> > sections individually. As we uncoiled it from where it
> > passed behind the shack, next to the chainlink fence, the
> > problem became quite apparent. Staring me directly in the
> > face, was a spot on the hardline which was blown out by a
> > lightning strike. I cut out about an 8 inch section around
> > the blow-out and measured it with an ohmmeter - 100k! The
> > two remaining halves from either side of the cut measured
> > completely open.
>
> Out of curiosity, did you have ground kits on the feedline at
> top and bottom
> of the run?
>
> --- Jeff
>
>
>
>
> No virus found in this incoming message.
> Checked by AVG Free Edition.
> Version: 7.5.472 / Virus Database: 269.9.1/857 - Release
> Date: 6/20/2007 2:18 PM
>
>
>