Bob,

The reason is quite simple.  If a fault (say, a short to the case) occurs in
a piece of equipment that is grounded per the NEC, the fault current- which
may be 100 amperes or more- flows from the service through the circuit
protection device (fuse or circuit breaker) to the fault, and returns via
the equipment grounding conductor (green wire) to the service.  When the
green wire is in close proximity to the hot wire (in the same conduit or
cable jacket), the impedance to the fault is as low as it can possibly be-
ensuring the immediate functioning of the circuit protection device.  If the
fault return path were to follow a circular route- as it would if through a
path not in close proximity to the supply conductor- the impedance will
ALWAYS be much greater, and can possibly be high enough to limit the fault
current to a value near the rating of the circuit protective device.  For
example, if the impedance of the ground return path limited the fault
current to 25 amperes on a 20 ampere branch circuit, the circuit may "cook"
for several minutes before tripping.  Keep in mind that a fancy copper strip
running around the shack may have a DC resistance that is a fraction of one
ohm, but its AC impedance may be many ohms.

When the electrical installation is within steel conduit, the problem
becomes much worse if the grounding conductor follows a different path from
the hot and neutral conductors.  When a fault occurs, the presence of the
steel conduit creates a solenoid and the impedance increases significantly.
Case in point:  About 20 years ago, I was rewiring a very old theater that
was then almost 50 years old.  When I got around to working on the house
lights, I found that an audible hum could be heard when the dimming
rheostats were in a certain position.  The hum seemed to come from
everywhere, making it difficult to pinpoint the source.  On a hunch, I used
my trusty Simpson clamp ammeter to test the conduits up in the rafters.
Surprise!  One of the conduits had almost 15 amperes flowing through it,
meaning that there was a fault in the house light circuit, but the impedance
of the grounding circuit limited the current to less than the circuit
breaker rating.  While pulling out the ancient TW wires, I found one that
was skinned bare by being pulled through an unreamed conduit, and had
shorted to the conduit.  Had this circuit been properly grounded, the
circuit breaker would have tripped instantly; instead, a dangerous
electrical fault persisted, and in a place of assembly, that is
unacceptable.

The NEC includes many references to minimizing the impedance of a fault
current path, but the NEC Handbook includes detailed explanations of the
rationale.  For example, Article 250.24(C)(1) states, "This [grounding]
conductor shall be routed with the phase conductors..."  Article
250.32(B)(1) states, "An equipment grounding conductor as described in
250.118 shall be run with the supply conductors..."  It takes a leap to
assume that it's okay to depart from this consistent mantra.

An electrical inspector's primary concern is ensuring the safety of the
public and of structures occupied by the public.  I will admit that few
inspectors will perform a thorough inspection of a mountaintop radio or
cellular site, because the public's safety is not much of an issue there.  I
also understand why an electrician- regardless of how experienced he or she
may be- will probably never object to performing an installation that is not
fully compliant with the NEC.  The owner will probably perceive that
electrician as a troublemaker, leading to lost business.  The electrician
can always say that he followed the plans exactly, and is therefore not
likely to be held accountable.  I have worked with many electrical
inspectors who don't sweat the small stuff, but also with many who are very
thorough and would never allow "creative grounding" methods.  As an
IAEI/ICBO Certified Electrical Inspector myself, I have been in the business
long enough to know that a telecommunications site wired and grounded in
accordance with the NEC will work properly and be safe.

As for the currency of R56, I do not know how often it is updated.  I do
know that its authors are aware of the NEC conflicts and are planning to
reconcile those issues in a future edition.

73, Eric Lemmon WB6FLY
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bob M.
Sent: Thursday, April 09, 2009 1:29 AM
To: [email protected]
Subject: RE: [Repeater-Builder] Re: Motorola R56 grounding




I question the validity of your statement that separating the grounding
conductor "would greatly increase the impedance of the grounding system" 

It might do this depending on the route the ground wire takes, but if the
installation had a 4 inch ground foil running around the perimeter of the
building and every grounding conductor ran from an outlet to this ground
foil, wouldn't that REDUCE the impedance and possibly offer better ground
conduction? Seems to me that a long #12 ground wire, from the outlet all the
way back to the service panel, would have a higher impedance.

I agree with the rest of the paragraph below however.

How often is R56 updated? Does R56 mention somewhere that local regs take
precedence, or that NFPA codes supercede R56? Is R56 just a thorough
collection of installation guidelines and recommended practices? I've never
seen a copy so I'm asking merely for my own education.

Bob M.
======
--- On Wed, 4/8/09, Eric Lemmon <[email protected]
<mailto:wb6fly%40verizon.net> > wrote:

> From: Eric Lemmon <[email protected] <mailto:wb6fly%40verizon.net> >
> Subject: RE: [Repeater-Builder] Re: Motorola R56 grounding
> To: [email protected]
<mailto:Repeater-Builder%40yahoogroups.com> 
> Date: Wednesday, April 8, 2009, 10:04 PM
> Martin,
> 
> Sure!  The National Electrical Code (NEC) requires
> that the equipment
> grounding conductor (green or bare wire) must always follow
> the same route
> and wireway used by the supply and return conductors. 
> There must never be
> any deviation from this basic requirement.  The three
> wires (hot, neutral,
> and ground) feeding every receptacle must always run
> together, but the R56
> manual proposes that the grounding conductors of some
> "technical"
> receptacles shall follow a path separate from the hot and
> neutral
> conductors.  That is not allowed by the NEC, since
> that would greatly
> increase the impedance of the grounding system and thereby
> reduce the
> protection of the circuit against faults.  Also, the
> NEC requires that the
> system grounding conductors, equipment grounding
> conductors, and lightning
> protection grounding conductors must ultimately be bonded
> together to create
> ONE grounding system.  The R56 manual proposes a
> scheme that creates
> separate grounding circuits that can create dangerous
> voltages on some
> circuits if a fault occurs on another circuit. 
> Despite some really creative
> schemes to create separate grounding paths, such schemes
> are not allowed by
> the NEC or by state electrical codes based upon the NEC.
> 
> Readers following this thread should be aware that the NEC
> is updated every
> three years, and becomes law as each state or commonwealth
> ratifies it
> through legislative action.  The current edition of
> the National Electrical
> Code, NFPA 70, is the 2008 edition.
> 
> 73, Eric Lemmon WB6FLY





Reply via email to