Thanks for the explanation. I was certainly thinking lower resistance with the 
4-inch copper ground but didn't think the impedance at 60 Hz would be that much 
different. I can definitely see the coupling problem with conduit and I believe 
conduit is required in commercial installations.

I bet a lot more people would follow R56 if it was more freely available and 
not shrouded in secrecy and cost.

Bob M.
======
--- On Thu, 4/9/09, Eric Lemmon <[email protected]> wrote:

> From: Eric Lemmon <[email protected]>
> Subject: RE: [Repeater-Builder] Re: Motorola R56 grounding
> To: [email protected]
> Date: Thursday, April 9, 2009, 10:51 PM
> Bob,
> 
> The reason is quite simple.  If a fault (say, a short
> to the case) occurs in
> a piece of equipment that is grounded per the NEC, the
> fault current- which
> may be 100 amperes or more- flows from the service through
> the circuit
> protection device (fuse or circuit breaker) to the fault,
> and returns via
> the equipment grounding conductor (green wire) to the
> service.  When the
> green wire is in close proximity to the hot wire (in the
> same conduit or
> cable jacket), the impedance to the fault is as low as it
> can possibly be-
> ensuring the immediate functioning of the circuit
> protection device.  If the
> fault return path were to follow a circular route- as it
> would if through a
> path not in close proximity to the supply conductor- the
> impedance will
> ALWAYS be much greater, and can possibly be high enough to
> limit the fault
> current to a value near the rating of the circuit
> protective device.  For
> example, if the impedance of the ground return path limited
> the fault
> current to 25 amperes on a 20 ampere branch circuit, the
> circuit may "cook"
> for several minutes before tripping.  Keep in mind
> that a fancy copper strip
> running around the shack may have a DC resistance that is a
> fraction of one
> ohm, but its AC impedance may be many ohms.
> 
> When the electrical installation is within steel conduit,
> the problem
> becomes much worse if the grounding conductor follows a
> different path from
> the hot and neutral conductors.  When a fault occurs,
> the presence of the
> steel conduit creates a solenoid and the impedance
> increases significantly.
> Case in point:  About 20 years ago, I was rewiring a
> very old theater that
> was then almost 50 years old.  When I got around to
> working on the house
> lights, I found that an audible hum could be heard when the
> dimming
> rheostats were in a certain position.  The hum seemed
> to come from
> everywhere, making it difficult to pinpoint the
> source.  On a hunch, I used
> my trusty Simpson clamp ammeter to test the conduits up in
> the rafters.
> Surprise!  One of the conduits had almost 15 amperes
> flowing through it,
> meaning that there was a fault in the house light circuit,
> but the impedance
> of the grounding circuit limited the current to less than
> the circuit
> breaker rating.  While pulling out the ancient TW
> wires, I found one that
> was skinned bare by being pulled through an unreamed
> conduit, and had
> shorted to the conduit.  Had this circuit been
> properly grounded, the
> circuit breaker would have tripped instantly; instead, a
> dangerous
> electrical fault persisted, and in a place of assembly,
> that is
> unacceptable.
> 
> The NEC includes many references to minimizing the
> impedance of a fault
> current path, but the NEC Handbook includes detailed
> explanations of the
> rationale.  For example, Article 250.24(C)(1) states,
> "This [grounding]
> conductor shall be routed with the phase
> conductors..."  Article
> 250.32(B)(1) states, "An equipment grounding conductor as
> described in
> 250.118 shall be run with the supply conductors..." 
> It takes a leap to
> assume that it's okay to depart from this consistent
> mantra.
> 
> An electrical inspector's primary concern is ensuring the
> safety of the
> public and of structures occupied by the public.  I
> will admit that few
> inspectors will perform a thorough inspection of a
> mountaintop radio or
> cellular site, because the public's safety is not much of
> an issue there.  I
> also understand why an electrician- regardless of how
> experienced he or she
> may be- will probably never object to performing an
> installation that is not
> fully compliant with the NEC.  The owner will probably
> perceive that
> electrician as a troublemaker, leading to lost
> business.  The electrician
> can always say that he followed the plans exactly, and is
> therefore not
> likely to be held accountable.  I have worked with
> many electrical
> inspectors who don't sweat the small stuff, but also with
> many who are very
> thorough and would never allow "creative grounding"
> methods.  As an
> IAEI/ICBO Certified Electrical Inspector myself, I have
> been in the business
> long enough to know that a telecommunications site wired
> and grounded in
> accordance with the NEC will work properly and be safe.
> 
> As for the currency of R56, I do not know how often it is
> updated.  I do
> know that its authors are aware of the NEC conflicts and
> are planning to
> reconcile those issues in a future edition.
> 
> 73, Eric Lemmon WB6FLY
>  
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]]
> On Behalf Of Bob M.
> Sent: Thursday, April 09, 2009 1:29 AM
> To: [email protected]
> Subject: RE: [Repeater-Builder] Re: Motorola R56 grounding
> 
> 
> 
> 
> I question the validity of your statement that separating
> the grounding
> conductor "would greatly increase the impedance of the
> grounding system" 
> 
> It might do this depending on the route the ground wire
> takes, but if the
> installation had a 4 inch ground foil running around the
> perimeter of the
> building and every grounding conductor ran from an outlet
> to this ground
> foil, wouldn't that REDUCE the impedance and possibly offer
> better ground
> conduction? Seems to me that a long #12 ground wire, from
> the outlet all the
> way back to the service panel, would have a higher
> impedance.
> 
> I agree with the rest of the paragraph below however.
> 
> How often is R56 updated? Does R56 mention somewhere that
> local regs take
> precedence, or that NFPA codes supercede R56? Is R56 just a
> thorough
> collection of installation guidelines and recommended
> practices? I've never
> seen a copy so I'm asking merely for my own education.
> 
> Bob M.
> ======
> --- On Wed, 4/8/09, Eric Lemmon <[email protected]
> <mailto:wb6fly%40verizon.net> > wrote:
> 
> > From: Eric Lemmon <[email protected]
> <mailto:wb6fly%40verizon.net> >
> > Subject: RE: [Repeater-Builder] Re: Motorola R56
> grounding
> > To: [email protected]
> <mailto:Repeater-Builder%40yahoogroups.com> 
> > Date: Wednesday, April 8, 2009, 10:04 PM
> > Martin,
> > 
> > Sure!  The National Electrical Code (NEC)
> requires
> > that the equipment
> > grounding conductor (green or bare wire) must always
> follow
> > the same route
> > and wireway used by the supply and return conductors.
> 
> > There must never be
> > any deviation from this basic requirement.  The
> three
> > wires (hot, neutral,
> > and ground) feeding every receptacle must always run
> > together, but the R56
> > manual proposes that the grounding conductors of some
> > "technical"
> > receptacles shall follow a path separate from the hot
> and
> > neutral
> > conductors.  That is not allowed by the NEC,
> since
> > that would greatly
> > increase the impedance of the grounding system and
> thereby
> > reduce the
> > protection of the circuit against faults.  Also,
> the
> > NEC requires that the
> > system grounding conductors, equipment grounding
> > conductors, and lightning
> > protection grounding conductors must ultimately be
> bonded
> > together to create
> > ONE grounding system.  The R56 manual proposes a
> > scheme that creates
> > separate grounding circuits that can create dangerous
> > voltages on some
> > circuits if a fault occurs on another circuit. 
> > Despite some really creative
> > schemes to create separate grounding paths, such
> schemes
> > are not allowed by
> > the NEC or by state electrical codes based upon the
> NEC.
> > 
> > Readers following this thread should be aware that the
> NEC
> > is updated every
> > three years, and becomes law as each state or
> commonwealth
> > ratifies it
> > through legislative action.  The current edition
> of
> > the National Electrical
> > Code, NFPA 70, is the 2008 edition.
> > 
> > 73, Eric Lemmon WB6FLY


      

Reply via email to