When lightning strikes a structure, it causes a current pulse to flow, and
that pulse has an extremely fast rise time- making it appear to be a
high-frequency signal in the MHz range.  A pulse of 200,000 amperes flowing
through a steel tower's impedance may allow a voltage gradient of several
thousand volts to appear along its length.  That is why all conductive metal
objects (ladders, window frames, HVAC ductwork, etc.) within six feet of a
down conductor must be cross-bonded to the lightning protection down
conductor to prevent side-flashes.

Extensive research on lightning conducted years ago by Dr. Phillip Krider at
Kennedy Space Center, FL and at Tucson, AZ, proved that magnetic forces
generated by the lightning current caused the current to flow mostly along
the outside corners of a square or triangular tower.  Relatively little
current flows through the bulk steel of a tower.  That is why you will find
the heavy copper down conductors placed along the outside corners of such
towers.  The details of this design can be found in NFPA 780, Standard for
the Installation of Lightning Protection Systems.

While it is true that the lightning protection system must have its own
grounding rods and interconnecting system, it is also true that the
lightning protection grounding system and the building electrical and
communication grounding system MUST be bonded together to create one
grounding system.  The NEC makes this requirement very clear in Article
250.106:  "The lightning protection system ground terminals shall be bonded
to the building or structure grounding electrode system."  Failure to follow
this requirement to the letter can have disastrous and possibly tragic
consequences.

Readers of this thread may be surprised to learn that Article 810 of the NEC
applies to Radio and Television antenna systems, and to Amateur Radio
equipment.  It should be mandatory reading for any Ham who seeks to erect an
outdoor antenna system.  This Article covers grounding systems, surge
protection, building penetrations, and similar topics.  Definitely good
information.

73, Eric Lemmon WB6FLY
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of wd8chl
Sent: Friday, April 10, 2009 8:22 AM
To: [email protected]
Subject: Re: [Repeater-Builder] Re: Motorola R56 grounding



Eric Lemmon wrote:
> Bob,
> 
> The reason is quite simple. If a fault (say, a short to the case) occurs
in
> a piece of equipment that is grounded per the NEC, the fault current-
which
> may be 100 amperes or more- flows from the service through the circuit
> protection device (fuse or circuit breaker) to the fault, and returns via
> the equipment grounding conductor (green wire) to the service. 
<snip for brevity>

The problem with all this is that, for lightning protection at a tower 
site, the ground for the arrestor should not run along the same path as 
the AC conduit, because it will be a much HIGHER impedance.
So while you need a proper ground within the service wiring, there also 
needs to be a good separate ground for lightning protection. Ideally, a 
bulkhead plate where the cable enters the building, but that's not 
always possible, especially at older sites. Next best is to mount the 
arrestor on the cabinet where the feedline enters, and run a large 
ground wire to the site ground in as short a run as possible, minimum 
bends, etc.
And I think lightning grounds is what R56 is more concerned with, more 