I am trying to devise a way to monitor my Rack PDUs without getting 10 pages 
everytime City power is lost.  Heres the scenario.  Any suggestion would be 
helpful.  I really would like a single page is all of City power drops, not one 
per PDU. 

 

Each Rack            1 PDU(with SNMP Monitoring)208  - Three Phase Power 

Each PDU             2 Towers – 1 for City Power, 1 for UPS Power( Can be 
checked independent) 

Each Tower         3 Phases(Can each be checked individually) 

 

Right now I have each phase set to send an email and each tower, and if a ping 
against the PDU fails.  The phases are dependent upon their tower and the tower 
upon their PDU but that still leaves a page for each PDU if I lose City or UPS 
power for some reason. 

 

Thanks 

 

 

Michael Letschin 

Network Administrator 

First Advantage-SafeRent 

(301) 881-3400 