HI All,
Does anyone have a person at Magnum in engineering or higher up than tech
Seems to me that the best practice for TL inverters is to use
double-insulated conductors from the array string(s) to the combiner (if
used) to the inverter.
That said, there doesn't appear to be any written requirement in the NEC to
use double-jacketed conductors. So as long at the conductor
The Inverters are operating 180° out of phase with each other for 120/240vac with a balancing transformer. dbDan BrownFoxfire Energy Corp.Renewable Energy Systems(802)-483-2564www.Foxfire-Energy.comNABCEP #092907-44
Original Message
Subject: Re: [RE-wrenches] Mitsubishi Mini
Wrenches,
...its the little things. Recently someone here brought up the issue
of combining AC outputs prior to backfeeding the solar CB in the mains panel.
In the past I've run AC outs from inverters into a small AC dist panel,
backfeeding CBs and then ran my combined AC out from a
Does anyone have any recommendations for outdoor equipment enclosures that are
reasonably affordable? I need to house a classic charge controller, Midnite
Din rail with breakers, relay driver, shunt and a few relays. This enclosure
will be mounted to a pole. Any leads on some brands or
Marco:
Once your conductor enters conduit you are no longer required to use PV
wire. 690.35D (2011).
William
Gradient Cap_mini
Lic 773985
http://www.millersolar.com/ millersolar.com
805-438-5600
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
Behalf Of
Bill:
There was an extensive discussion here on this exact subject recently. If I
may be so bold, I believe we reached consensus that it is best practice that
each inverter have a dedicated disconnecting means for allowing servicing, if
for no other reason.
William
Gradient
Jay,
Perhaps asking the question here. I have hundreds of Magnum inverter
installations, perhaps I or others can help.
Larry
On Oct 23, 2014, at 5:44 PM, jay peltz j...@asis.com wrote:
HI All,
Does anyone have a person at Magnum in engineering or higher up than tech
support.
I've got a
Even at night? This is hardly believable, as the inverter is supposedly shut down at night. Maybe he meant late evening, when the inverter has not shut down yet?If the utility tech claims he can see meter interference that disappears when he opens the AC disconnect, ask him to try the same test
Bill, typically inverters have a max OCPD that can be installed on their
output, and these sizes are generally not large enough to accommodate
two same-model inverters. And manuals often note that you need to have a
dedicated OCPD anyway. At least if I were ever to double-up two
inverters on a
It seems that 690.64(B)1 (2008) prohibits anything but landing the outputs on
dedicated breakers or disable disconnecting means.
Glenn
-Original Message-
From: frenergy frene...@psln.com
Sent: 10/24/2014 11:05
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches]
Friends;
Looking for the older Outback (Green) DC Distribution Panel that was commonly
used with either 4 Outback Inverters or 2 of the Trace SW Inverters.
With or without breakers. Please contact off list.
Thank you in advance
Bill Haase
Haase Energy Systems, Inc.
12561 Wilder Road
Red Bluff,
Bill:
Good luck with that. I think I bought the last set from a fellow wrench
years ago. I really miss that gear.
You can retrofit the Flexware gear to accommodate SW inverters but it
requires cutting metal. We have some photos on our web site, if that is
what you are doing.
William
I have a new in the box DC disconnect box that is used for dual SW's
Jerry
On Oct 24, 2014 8:49 PM, William Miller will...@millersolar.com wrote:
Bill:
Good luck with that. I think I bought the last set from a fellow wrench
years ago. I really miss that gear.
You can retrofit the