Re: [AFMUG] solar question

2016-07-05 Thread Eric Kuhnke
First figure out how many kWh all that consumes in 31 days...  Then
calculate what pvwatts says an off grid solar system of N size (example:
3kW) can produce in December and January.


On Tue, Jul 5, 2016 at 7:42 AM, Tim Reichhart <
timreichh...@hometowncable.net> wrote:

> Hey Guys
> I need to know what kind of size of solar setup I need to be able power 4
> rockets,2 powerbeam m5 500, 1 rb2011ils-in, 1 nanostation m2
> this site have no option for power from power company and this location in
> northwest ohio.
>
> Tim
>
>
>
>
>


Re: [AFMUG] solar question

2016-07-05 Thread Mathew Howard
My load estimate is also based on 6 watts per radio (which is the number I
usually see thrown around), but I suspect the actual average would be
closer to 4 watts, which is going to put it right in line with your 1.3-1.4
amp @24v estimate, which would put 20X the load at something more like 650
watts. A lot really depends on how easy the site is to access and how tight
your budget is.

On Tue, Jul 5, 2016 at 1:35 PM, Jesse DuPont <jesse.dup...@celeritycorp.net>
wrote:

> Agreed! My sizing was based on my willingness to take generator to the
> site if there was no charging for 4.5 days (which I never had to do last
> winter, but last winter seemed nicer than ones prior - I'm in Western SD).
> Chucks battery sizing will at least double that run time and probably more
> (depending on battery temp) and the additional panels will charge them more
> quickly after extended run down.
>
> *Jesse DuPont*
>
> Network Architect
> email: jesse.dup...@celeritycorp.net
> Celerity Networks LLC
>
> Celerity Broadband LLC
> Like us! facebook.com/celeritynetworksllc
>
> Like us! facebook.com/celeritybroadband
> On 7/5/16 12:14 PM, Mathew Howard wrote:
>
> Chuck is saying 1000 watts, which would be 4 x 250 watt panels, but keep
> in mind I'm figuring load on the high side to be safe.
>
> You could probably get away with 500 watts of panels, like Jesse said, but
> if you want to be sure it's never going to have problems, go with Chuck's
> numbers.
> Mathew
>
> Ok what size solar panels are we talking about jesse is saying 2 x 250
> watt panels is that correct?
>
> Tim
>
> --
> -Original Message-
> From: "Mathew Howard" <mhoward...@gmail.com>
> To: af <af@afmug.com>
> Date: 07/05/16 11:43 AM
> Subject: Re: [AFMUG] solar question
>
> Most people will tell you to figure about 6 watts each for Ubiquiti
> radios... I typically see close to for 4 watts average on ours, but it's
> better to err on the high side, so I'd plan for about 50 watts on that
> setup.
>
>
> On Tue, Jul 5, 2016 at 9:47 AM, Chuck McCown < <ch...@wbmfg.com>
> ch...@wbmfg.com> wrote:
>
>> How many watts of load does that total?
>>
>> -Original Message- From: Tim Reichhart
>> Sent: Tuesday, July 05, 2016 8:42 AM
>> To: af@afmug.com
>> Subject: [AFMUG] solar question
>>
>>
>> Hey Guys
>> I need to know what kind of size of solar setup I need to be able power 4
>> rockets,2 powerbeam m5 500, 1 rb2011ils-in, 1 nanostation m2
>> this site have no option for power from power company and this location
>> in northwest ohio.
>>
>> Tim
>>
>>
>>
>>
>>
>>
>
>
>
>
>
>
>
>


Re: [AFMUG] solar question

2016-07-05 Thread Chuck McCown
http://www.wisptech.com/index.php?title=Solar_Powered_Site_App_Notes

From: Jesse DuPont 
Sent: Tuesday, July 05, 2016 12:35 PM
To: af@afmug.com 
Subject: Re: [AFMUG] solar question

Agreed! My sizing was based on my willingness to take generator to the site if 
there was no charging for 4.5 days (which I never had to do last winter, but 
last winter seemed nicer than ones prior - I'm in Western SD). Chucks battery 
sizing will at least double that run time and probably more (depending on 
battery temp) and the additional panels will charge them more quickly after 
extended run down.


Jesse DuPont

Network Architect
email: jesse.dup...@celeritycorp.net
Celerity Networks LLC

Celerity Broadband LLC
Like us! facebook.com/celeritynetworksllc

Like us! facebook.com/celeritybroadband


On 7/5/16 12:14 PM, Mathew Howard wrote:

  Chuck is saying 1000 watts, which would be 4 x 250 watt panels, but keep in 
mind I'm figuring load on the high side to be safe. 

  You could probably get away with 500 watts of panels, like Jesse said, but if 
you want to be sure it's never going to have problems, go with Chuck's numbers. 

  Mathew
  Ok what size solar panels are we talking about jesse is saying 2 x 250 watt 
panels is that correct?

  Tim




-Original Message-
From: "Mathew Howard" <mhoward...@gmail.com>
To: af <af@afmug.com>
Date: 07/05/16 11:43 AM
    Subject: Re: [AFMUG] solar question


Most people will tell you to figure about 6 watts each for Ubiquiti 
radios... I typically see close to for 4 watts average on ours, but it's better 
to err on the high side, so I'd plan for about 50 watts on that setup.
 

On Tue, Jul 5, 2016 at 9:47 AM, Chuck McCown <ch...@wbmfg.com> wrote:

  How many watts of load does that total?

  -Original Message- From: Tim Reichhart
  Sent: Tuesday, July 05, 2016 8:42 AM
  To: af@afmug.com
  Subject: [AFMUG] solar question 


  Hey Guys
  I need to know what kind of size of solar setup I need to be able power 4 
rockets,2 powerbeam m5 500, 1 rb2011ils-in, 1 nanostation m2
  this site have no option for power from power company and this location 
in northwest ohio.

  Tim




   
 

 
   



Re: [AFMUG] solar question

2016-07-05 Thread Jesse DuPont

  
  
Agreed! My sizing was based on my willingness to take generator to
the site if there was no charging for 4.5 days (which I never had to
do last winter, but last winter seemed nicer than ones prior - I'm
in Western SD). Chucks battery sizing will at least double that run
time and probably more (depending on battery temp) and the
additional panels will charge them more quickly after extended run
down.


  
  
  
  
  
  
  
  
  
  
  
  
  
Jesse DuPont

  Network
  Architect
  email: jesse.dup...@celeritycorp.net
  Celerity Networks LLC
  Celerity
  Broadband LLC
Like us! facebook.com/celeritynetworksllc
  Like us! facebook.com/celeritybroadband
  

  

On 7/5/16 12:14 PM, Mathew Howard
  wrote:


  Chuck is saying 1000 watts, which would be 4 x 250
watt panels, but keep in mind I'm figuring load on the high side
to be safe. 
  You could probably get away with 500 watts of panels,
like Jesse said, but if you want to be sure it's never going to
have problems, go with Chuck's numbers. 
  

  Mathew
Ok what size solar panels are we talking about jesse is
saying 2 x 250 watt panels is that correct?

Tim


  -Original Message-
  From: "Mathew Howard" <mhoward...@gmail.com>
  To: af <af@afmug.com>
  Date: 07/05/16 11:43 AM
      Subject: Re: [AFMUG] solar question
  
  Most people will tell you to figure about 6
watts each for Ubiquiti radios... I typically see close
to for 4 watts average on ours, but it's better to err
on the high side, so I'd plan for about 50 watts on that
setup.
 
   
On Tue, Jul 5, 2016 at 9:47 AM,
  Chuck McCown <ch...@wbmfg.com>
  wrote:
  How
many watts of load does that total?

-Original Message- From: Tim Reichhart
Sent: Tuesday, July 05, 2016 8:42 AM
To: af@afmug.com
        Subject: [AFMUG] solar question

   

Hey Guys
I need to know what kind of size of solar setup
I need to be able power 4 rockets,2 powerbeam m5
500, 1 rb2011ils-in, 1 nanostation m2
this site have no option for power from power
company and this location in northwest ohio.

Tim




 

  
   

 

 

  


  



Re: [AFMUG] solar question

2016-07-05 Thread Chuck McCown
If you live in an area with no snow, no ice, lotsa sun, then 10X the load and a 
week of batts will barely suffice.
If you have snow, ice, locations that are hard to get to, etc then 20X the load 
and two weeks of batts will take care of you.

I have done this many times over on many mountain tops.  I have also hired 
helicopters at 2000/hour to get to sites that did not have enough panel or 
battery.  

If you can drive to the site year around to top off a battery during periods of 
inclement weather, then you can cut back on the size of the battery.  Telemetry 
is very important no matter what you do.  You can keep an eye on things and 
know they are going to fail before they do.  You can also remote start a small 
propane generator with telemetry too if you want to scrimp on panel.

If money is tight, go with the larger battery and smaller panel.  If money is 
squeaky tight, remote start generator and batts can be the whole system.  Just 
start it once every 3 days and let it run for an hour.  

From: Mathew Howard 
Sent: Tuesday, July 05, 2016 12:14 PM
To: af 
Subject: Re: [AFMUG] solar question

Chuck is saying 1000 watts, which would be 4 x 250 watt panels, but keep in 
mind I'm figuring load on the high side to be safe. 

You could probably get away with 500 watts of panels, like Jesse said, but if 
you want to be sure it's never going to have problems, go with Chuck's numbers. 

Mathew
Ok what size solar panels are we talking about jesse is saying 2 x 250 watt 
panels is that correct?

Tim




--
  -Original Message-
  From: "Mathew Howard" <mhoward...@gmail.com>
  To: af <af@afmug.com>
  Date: 07/05/16 11:43 AM
  Subject: Re: [AFMUG] solar question


  Most people will tell you to figure about 6 watts each for Ubiquiti radios... 
I typically see close to for 4 watts average on ours, but it's better to err on 
the high side, so I'd plan for about 50 watts on that setup.
   

  On Tue, Jul 5, 2016 at 9:47 AM, Chuck McCown <ch...@wbmfg.com> wrote:

How many watts of load does that total?

-Original Message- From: Tim Reichhart
Sent: Tuesday, July 05, 2016 8:42 AM
To: af@afmug.com
Subject: [AFMUG] solar question 


Hey Guys
I need to know what kind of size of solar setup I need to be able power 4 
rockets,2 powerbeam m5 500, 1 rb2011ils-in, 1 nanostation m2
this site have no option for power from power company and this location in 
northwest ohio.

Tim




 
   

   
 

Re: [AFMUG] solar question

2016-07-05 Thread Mathew Howard
Chuck is saying 1000 watts, which would be 4 x 250 watt panels, but keep in
mind I'm figuring load on the high side to be safe.

You could probably get away with 500 watts of panels, like Jesse said, but
if you want to be sure it's never going to have problems, go with Chuck's
numbers.
Mathew
Ok what size solar panels are we talking about jesse is saying 2 x 250 watt
panels is that correct?

Tim

--
-Original Message-
From: "Mathew Howard" <mhoward...@gmail.com>
To: af <af@afmug.com>
Date: 07/05/16 11:43 AM
Subject: Re: [AFMUG] solar question

Most people will tell you to figure about 6 watts each for Ubiquiti
radios... I typically see close to for 4 watts average on ours, but it's
better to err on the high side, so I'd plan for about 50 watts on that
setup.


On Tue, Jul 5, 2016 at 9:47 AM, Chuck McCown <ch...@wbmfg.com> wrote:

> How many watts of load does that total?
>
> -Original Message- From: Tim Reichhart
> Sent: Tuesday, July 05, 2016 8:42 AM
> To: af@afmug.com
> Subject: [AFMUG] solar question
>
>
> Hey Guys
> I need to know what kind of size of solar setup I need to be able power 4
> rockets,2 powerbeam m5 500, 1 rb2011ils-in, 1 nanostation m2
> this site have no option for power from power company and this location in
> northwest ohio.
>
> Tim
>
>
>
>
>
>


Re: [AFMUG] solar question

2016-07-05 Thread Tim Reichhart
Mathew
Ok what size solar panels are we talking about jesse is saying 2 x 250 watt 
panels is that correct?

Tim


-Original Message-
From: "Mathew Howard" <mhoward...@gmail.com>
To: af <af@afmug.com>
Date: 07/05/16 11:43 AM
Subject: Re: [AFMUG] solar question

Most people will tell you to figure about 6 watts each for Ubiquiti radios... I 
typically see close to for 4 watts average on ours, but it's better to err on 
the high side, so I'd plan for about 50 watts on that setup.
 
 
On Tue, Jul 5, 2016 at 9:47 AM, Chuck McCown <ch...@wbmfg.com> wrote:
How many watts of load does that total?

-Original Message- From: Tim Reichhart
Sent: Tuesday, July 05, 2016 8:42 AM
To: af@afmug.com
Subject: [AFMUG] solar question 

Hey Guys
I need to know what kind of size of solar setup I need to be able power 4 
rockets,2 powerbeam m5 500, 1 rb2011ils-in, 1 nanostation m2
this site have no option for power from power company and this location in 
northwest ohio.

Tim




 
 
 




Re: [AFMUG] solar question

2016-07-05 Thread Chuck McCown
50 watts=1000 watts of panel.  $650
16.8 kWh of battery.  $2500
+ controller.  $300

Two weeks of autonomous use, enough solar panel to not use batteries when 
overcast.  
Guaranteed to work.  

From: Mathew Howard 
Sent: Tuesday, July 05, 2016 9:43 AM
To: af 
Subject: Re: [AFMUG] solar question

Most people will tell you to figure about 6 watts each for Ubiquiti radios... I 
typically see close to for 4 watts average on ours, but it's better to err on 
the high side, so I'd plan for about 50 watts on that setup.


On Tue, Jul 5, 2016 at 9:47 AM, Chuck McCown <ch...@wbmfg.com> wrote:

  How many watts of load does that total?

  -Original Message- From: Tim Reichhart
  Sent: Tuesday, July 05, 2016 8:42 AM
  To: af@afmug.com
  Subject: [AFMUG] solar question 


  Hey Guys
  I need to know what kind of size of solar setup I need to be able power 4 
rockets,2 powerbeam m5 500, 1 rb2011ils-in, 1 nanostation m2
  this site have no option for power from power company and this location in 
northwest ohio.

  Tim







Re: [AFMUG] solar question

2016-07-05 Thread Mathew Howard
Most people will tell you to figure about 6 watts each for Ubiquiti
radios... I typically see close to for 4 watts average on ours, but it's
better to err on the high side, so I'd plan for about 50 watts on that
setup.

On Tue, Jul 5, 2016 at 9:47 AM, Chuck McCown <ch...@wbmfg.com> wrote:

> How many watts of load does that total?
>
> -Original Message- From: Tim Reichhart
> Sent: Tuesday, July 05, 2016 8:42 AM
> To: af@afmug.com
> Subject: [AFMUG] solar question
>
>
> Hey Guys
> I need to know what kind of size of solar setup I need to be able power 4
> rockets,2 powerbeam m5 500, 1 rb2011ils-in, 1 nanostation m2
> this site have no option for power from power company and this location in
> northwest ohio.
>
> Tim
>
>
>
>
>


Re: [AFMUG] solar question

2016-07-05 Thread Jesse DuPont

  
  
With that equipment, you probably have about 1.3-1.4A of load at
24VDC. Using 2x250W, 24VDC panels and 4x100Ah batteries should get
you through 4-4.5 days of heavy overcast. If you need more runtime,
add another pair of 100Ah batteries. An MPPT controller will charge
better as the panels reach full voltage during the day (PWM
controllers are less expensive, but will limit charge efficiency).

Where you are, I'd consider putting the batteries in the ground in
some kind of an enclosure. This will keep them at least 35-40F in
the dead of winter, giving you predictable run time when it's cold.
I just make a 4' x 4' x 4' box with hinged lid made from treated
lumber, dig a hole, put gravel on the bottom of it, throw in the box
and back fill. Insulate the top 12" and the lid and they'll stay
warmer. It's not elegant, but it works. There are much better
solutions out there, I'm sure.


  
  
  
  
  
  
  
  
  
  
  
  
  
Jesse DuPont

  Network
  Architect
  email: jesse.dup...@celeritycorp.net
  Celerity Networks LLC
  Celerity
  Broadband LLC
Like us! facebook.com/celeritynetworksllc
  Like us! facebook.com/celeritybroadband
  

  

On 7/5/16 8:42 AM, Tim Reichhart wrote:


  Hey Guys
I need to know what kind of size of solar setup I need to be able power 4 rockets,2 powerbeam m5 500, 1 rb2011ils-in, 1 nanostation m2
this site have no option for power from power company and this location in northwest ohio.

Tim







  



Re: [AFMUG] solar question

2016-07-05 Thread Chuck McCown

How many watts of load does that total?

-Original Message- 
From: Tim Reichhart

Sent: Tuesday, July 05, 2016 8:42 AM
To: af@afmug.com
Subject: [AFMUG] solar question

Hey Guys
I need to know what kind of size of solar setup I need to be able power 4 
rockets,2 powerbeam m5 500, 1 rb2011ils-in, 1 nanostation m2
this site have no option for power from power company and this location in 
northwest ohio.


Tim






[AFMUG] solar question

2016-07-05 Thread Tim Reichhart
Hey Guys
I need to know what kind of size of solar setup I need to be able power 4 
rockets,2 powerbeam m5 500, 1 rb2011ils-in, 1 nanostation m2
this site have no option for power from power company and this location in 
northwest ohio.

Tim