Re: [AFMUG] Is there such a thing as a AC Capacitor?

2017-07-29 Thread Josh Reynolds
We used these with as many batteries as we needed, figured out a good
charge rate with temp controlled charging (monitors battery temp), and
walked away.

No 24v or 48v or -48v or 12v or 56v to worry about. Drop the batteries in
and inverter and walk away. If you need a gen start they have those too.

Good for very high power if you wanted your plant to have like a 150A
charge rate :P

On Sat, Jul 29, 2017 at 12:35 AM, Jason McKemie <
j.mcke...@veloxinetbroadband.com> wrote:

> So what's the advantage of something like this vs an Eltek system. The
> price is up there.
>
> On Friday, July 28, 2017, Josh Reynolds  wrote:
>
>> Damnit, wrong link on the monitor... here's the ethernet one:
>> http://www.magnum-dimensions.com/magweb-monitoring-kit-ethernet
>>
>> They also have a wireless one
>>
>> Sorry for threadspam.
>>
>> On Fri, Jul 28, 2017 at 5:48 PM, Josh Reynolds 
>> wrote:
>>
>>> Almost forgot... for bigger sites
>>> http://www.magnum-dimensions.com/renewable-energy-products/i
>>> nterconnection-system-equipment
>>>
>>>
>>> ​
>>>
>>> On Fri, Jul 28, 2017 at 5:43 PM, Josh Reynolds 
>>> wrote:
>>>
 https://www.amazon.com/s/ref=nb_sb_noss_2?url=search-alias%3
 Daps=magnum+inverter

 http://www.magnum-dimensions.com/mobile-power-products/inver
 ter-chargers?field_output_waveform_value_selective%5B%5D=1
 ield_output_power_watts_value%5Bmin%5D=200_output_powe
 r_watts_value%5Bmax%5D=15000_output_frequency_value_
 selective%5B%5D=2_output_voltage_value_selective%5B%5D=1


 On Fri, Jul 28, 2017 at 2:42 PM, Jason McKemie <
 j.mcke...@veloxinetbroadband.com> wrote:

> Where do you source these?
>
> On Friday, July 28, 2017, Josh Reynolds  wrote:
>
>> We use Magnum Power pure sine wave on-line UPSs with AGM batts. Yeah
>> we lose in the conversion, but we also don't have to fumble around with a
>> couple of various DC voltages.
>>
>> Love them. Made in the US too.
>>
>> On Jul 28, 2017 4:20 AM, "Gino A. Villarini" 
>> wrote:
>>
>>> Our issues is exclusively with AF24’s and APC SU750’s.  On a
>>> Switching event the AF24 lock up about 50% of the time.  We have been
>>> changing the APC750 with the newer APC SUA750 and the problem vanishes…
>>>  believe me we have trie everything, grounding, changing UBNT POE, Surge
>>> Suppressors, you name it.
>>>
>>> 2 things have only worked:
>>>
>>> Newer APC models with any POE
>>> Powering the the AF24 with a dc-dc converter connected to the site
>>> batteries and into a McCown DC injector
>>>
>>> From: Af  on behalf of Colin Stanners <
>>> cstann...@gmail.com>
>>> Reply-To: "af@afmug.com" 
>>> Date: Thursday, July 27, 2017 at 9:53 PM
>>> To: "af@afmug.com" 
>>> Subject: Re: [AFMUG] Is there such a thing as a AC Capacitor?
>>>
>>> I forgot to mention:
>>> -if it's a non-sinewave UPS, it could be that the powersupply is
>>> designed to expect sinewave AC.
>>> -are you certain that it's not a grounding issue or other stray
>>> voltage between the circuits?
>>>
>>>
>>>
>>> *Gino A. Villarini*
>>> President
>>> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968
>>>
>>> On Thu, Jul 27, 2017 at 8:50 PM, Colin Stanners >> > wrote:
>>>
 Gino, can you say which gear? Most UPSes switch pretty much
 "instantly" (less than one AC cycle, which lasts 16ms) so a PSU that
 wouldn't last one AC cycle must have very questionable engineering. Or
 assuming that you use APC UPSes, you can change the sensitivity 
 setting to
 switch quicker:  http://www.apc.com/us/en/faqs/FA156514/

 On Thu, Jul 27, 2017 at 2:57 PM, Gino A. Villarini <
 g...@aeronetpr.com> wrote:

> Got some  gear that hangs when UPS switches from AC power to
> Batts… needs something to power AC for microseconds
>
>
>
> *Gino A. Villarini*
> President
> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968
>
>

>>>

>>>
>>


Re: [AFMUG] Is there such a thing as a AC Capacitor?

2017-07-28 Thread Jason McKemie
So what's the advantage of something like this vs an Eltek system. The
price is up there.

On Friday, July 28, 2017, Josh Reynolds  wrote:

> Damnit, wrong link on the monitor... here's the ethernet one:
> http://www.magnum-dimensions.com/magweb-monitoring-kit-ethernet
>
> They also have a wireless one
>
> Sorry for threadspam.
>
> On Fri, Jul 28, 2017 at 5:48 PM, Josh Reynolds  > wrote:
>
>> Almost forgot... for bigger sites
>> http://www.magnum-dimensions.com/renewable-energy-products/i
>> nterconnection-system-equipment
>>
>>
>> ​
>>
>> On Fri, Jul 28, 2017 at 5:43 PM, Josh Reynolds > > wrote:
>>
>>> https://www.amazon.com/s/ref=nb_sb_noss_2?url=search-alias%3
>>> Daps=magnum+inverter
>>>
>>> http://www.magnum-dimensions.com/mobile-power-products/inver
>>> ter-chargers?field_output_waveform_value_selective%5B%5D=1&
>>> field_output_power_watts_value%5Bmin%5D=200_output_
>>> power_watts_value%5Bmax%5D=15000_output_frequency_
>>> value_selective%5B%5D=2_output_voltage_value_selective%5B%5D=1
>>>
>>>
>>> On Fri, Jul 28, 2017 at 2:42 PM, Jason McKemie <
>>> j.mcke...@veloxinetbroadband.com
>>> >
>>> wrote:
>>>
 Where do you source these?

 On Friday, July 28, 2017, Josh Reynolds > wrote:

> We use Magnum Power pure sine wave on-line UPSs with AGM batts. Yeah
> we lose in the conversion, but we also don't have to fumble around with a
> couple of various DC voltages.
>
> Love them. Made in the US too.
>
> On Jul 28, 2017 4:20 AM, "Gino A. Villarini" 
> wrote:
>
>> Our issues is exclusively with AF24’s and APC SU750’s.  On a
>> Switching event the AF24 lock up about 50% of the time.  We have been
>> changing the APC750 with the newer APC SUA750 and the problem vanishes…
>>  believe me we have trie everything, grounding, changing UBNT POE, Surge
>> Suppressors, you name it.
>>
>> 2 things have only worked:
>>
>> Newer APC models with any POE
>> Powering the the AF24 with a dc-dc converter connected to the site
>> batteries and into a McCown DC injector
>>
>> From: Af  on behalf of Colin Stanners <
>> cstann...@gmail.com>
>> Reply-To: "af@afmug.com" 
>> Date: Thursday, July 27, 2017 at 9:53 PM
>> To: "af@afmug.com" 
>> Subject: Re: [AFMUG] Is there such a thing as a AC Capacitor?
>>
>> I forgot to mention:
>> -if it's a non-sinewave UPS, it could be that the powersupply is
>> designed to expect sinewave AC.
>> -are you certain that it's not a grounding issue or other stray
>> voltage between the circuits?
>>
>>
>>
>> *Gino A. Villarini*
>> President
>> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968
>>
>> On Thu, Jul 27, 2017 at 8:50 PM, Colin Stanners 
>> wrote:
>>
>>> Gino, can you say which gear? Most UPSes switch pretty much
>>> "instantly" (less than one AC cycle, which lasts 16ms) so a PSU that
>>> wouldn't last one AC cycle must have very questionable engineering. Or
>>> assuming that you use APC UPSes, you can change the sensitivity setting 
>>> to
>>> switch quicker:  http://www.apc.com/us/en/faqs/FA156514/
>>>
>>> On Thu, Jul 27, 2017 at 2:57 PM, Gino A. Villarini <
>>> g...@aeronetpr.com> wrote:
>>>
 Got some  gear that hangs when UPS switches from AC power to Batts…
 needs something to power AC for microseconds



 *Gino A. Villarini*
 President
 Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968


>>>
>>
>>>
>>
>


Re: [AFMUG] Is there such a thing as a AC Capacitor?

2017-07-28 Thread Josh Reynolds
Damnit, wrong link on the monitor... here's the ethernet one:
http://www.magnum-dimensions.com/magweb-monitoring-kit-ethernet

They also have a wireless one

Sorry for threadspam.

On Fri, Jul 28, 2017 at 5:48 PM, Josh Reynolds  wrote:

> Almost forgot... for bigger sites
> http://www.magnum-dimensions.com/renewable-energy-products/
> interconnection-system-equipment
>
>
> ​
>
> On Fri, Jul 28, 2017 at 5:43 PM, Josh Reynolds 
> wrote:
>
>> https://www.amazon.com/s/ref=nb_sb_noss_2?url=search-alias%3
>> Daps=magnum+inverter
>>
>> http://www.magnum-dimensions.com/mobile-power-products/inver
>> ter-chargers?field_output_waveform_value_selective%5B%
>> 5D=1_output_power_watts_value%5Bmin%5D=200_
>> output_power_watts_value%5Bmax%5D=15000_output_
>> frequency_value_selective%5B%5D=2_output_voltage_
>> value_selective%5B%5D=1
>>
>>
>> On Fri, Jul 28, 2017 at 2:42 PM, Jason McKemie <
>> j.mcke...@veloxinetbroadband.com> wrote:
>>
>>> Where do you source these?
>>>
>>> On Friday, July 28, 2017, Josh Reynolds  wrote:
>>>
 We use Magnum Power pure sine wave on-line UPSs with AGM batts. Yeah we
 lose in the conversion, but we also don't have to fumble around with a
 couple of various DC voltages.

 Love them. Made in the US too.

 On Jul 28, 2017 4:20 AM, "Gino A. Villarini"  wrote:

> Our issues is exclusively with AF24’s and APC SU750’s.  On a Switching
> event the AF24 lock up about 50% of the time.  We have been changing the
> APC750 with the newer APC SUA750 and the problem vanishes…  believe me we
> have trie everything, grounding, changing UBNT POE, Surge Suppressors, you
> name it.
>
> 2 things have only worked:
>
> Newer APC models with any POE
> Powering the the AF24 with a dc-dc converter connected to the site
> batteries and into a McCown DC injector
>
> From: Af  on behalf of Colin Stanners <
> cstann...@gmail.com>
> Reply-To: "af@afmug.com" 
> Date: Thursday, July 27, 2017 at 9:53 PM
> To: "af@afmug.com" 
> Subject: Re: [AFMUG] Is there such a thing as a AC Capacitor?
>
> I forgot to mention:
> -if it's a non-sinewave UPS, it could be that the powersupply is
> designed to expect sinewave AC.
> -are you certain that it's not a grounding issue or other stray
> voltage between the circuits?
>
>
>
> *Gino A. Villarini*
> President
> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968
>
> On Thu, Jul 27, 2017 at 8:50 PM, Colin Stanners 
> wrote:
>
>> Gino, can you say which gear? Most UPSes switch pretty much
>> "instantly" (less than one AC cycle, which lasts 16ms) so a PSU that
>> wouldn't last one AC cycle must have very questionable engineering. Or
>> assuming that you use APC UPSes, you can change the sensitivity setting 
>> to
>> switch quicker:  http://www.apc.com/us/en/faqs/FA156514/
>>
>> On Thu, Jul 27, 2017 at 2:57 PM, Gino A. Villarini > > wrote:
>>
>>> Got some  gear that hangs when UPS switches from AC power to Batts…
>>> needs something to power AC for microseconds
>>>
>>>
>>>
>>> *Gino A. Villarini*
>>> President
>>> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968
>>>
>>>
>>
>
>>
>


Re: [AFMUG] Is there such a thing as a AC Capacitor?

2017-07-28 Thread Josh Reynolds
Almost forgot... for bigger sites
http://www.magnum-dimensions.com/renewable-energy-products/interconnection-system-equipment


​

On Fri, Jul 28, 2017 at 5:43 PM, Josh Reynolds  wrote:

> https://www.amazon.com/s/ref=nb_sb_noss_2?url=search-alias%
> 3Daps=magnum+inverter
>
> http://www.magnum-dimensions.com/mobile-power-products/
> inverter-chargers?field_output_waveform_value_selective%5B%5D=1_
> output_power_watts_value%5Bmin%5D=200_output_
> power_watts_value%5Bmax%5D=15000_output_frequency_
> value_selective%5B%5D=2_output_voltage_value_selective%5B%5D=1
>
>
> On Fri, Jul 28, 2017 at 2:42 PM, Jason McKemie <
> j.mcke...@veloxinetbroadband.com> wrote:
>
>> Where do you source these?
>>
>> On Friday, July 28, 2017, Josh Reynolds  wrote:
>>
>>> We use Magnum Power pure sine wave on-line UPSs with AGM batts. Yeah we
>>> lose in the conversion, but we also don't have to fumble around with a
>>> couple of various DC voltages.
>>>
>>> Love them. Made in the US too.
>>>
>>> On Jul 28, 2017 4:20 AM, "Gino A. Villarini"  wrote:
>>>
 Our issues is exclusively with AF24’s and APC SU750’s.  On a Switching
 event the AF24 lock up about 50% of the time.  We have been changing the
 APC750 with the newer APC SUA750 and the problem vanishes…  believe me we
 have trie everything, grounding, changing UBNT POE, Surge Suppressors, you
 name it.

 2 things have only worked:

 Newer APC models with any POE
 Powering the the AF24 with a dc-dc converter connected to the site
 batteries and into a McCown DC injector

 From: Af  on behalf of Colin Stanners <
 cstann...@gmail.com>
 Reply-To: "af@afmug.com" 
 Date: Thursday, July 27, 2017 at 9:53 PM
 To: "af@afmug.com" 
 Subject: Re: [AFMUG] Is there such a thing as a AC Capacitor?

 I forgot to mention:
 -if it's a non-sinewave UPS, it could be that the powersupply is
 designed to expect sinewave AC.
 -are you certain that it's not a grounding issue or other stray voltage
 between the circuits?



 *Gino A. Villarini*
 President
 Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968

 On Thu, Jul 27, 2017 at 8:50 PM, Colin Stanners 
 wrote:

> Gino, can you say which gear? Most UPSes switch pretty much
> "instantly" (less than one AC cycle, which lasts 16ms) so a PSU that
> wouldn't last one AC cycle must have very questionable engineering. Or
> assuming that you use APC UPSes, you can change the sensitivity setting to
> switch quicker:  http://www.apc.com/us/en/faqs/FA156514/
>
> On Thu, Jul 27, 2017 at 2:57 PM, Gino A. Villarini 
> wrote:
>
>> Got some  gear that hangs when UPS switches from AC power to Batts…
>> needs something to power AC for microseconds
>>
>>
>>
>> *Gino A. Villarini*
>> President
>> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968
>>
>>
>

>


Re: [AFMUG] Is there such a thing as a AC Capacitor?

2017-07-28 Thread Josh Reynolds
Make sure you get the controller kit for them as well, otherwise you won't
be able to program them.

If you need a way to monitor them the battery monitor kit is here:
https://www.amazon.com/Magnum-Energy-Battery-Monitor-ME-BMK/dp/B00DG5SSH8/ref=pd_bxgy_263_img_3?_encoding=UTF8=1=1CX6462ZHMW8QXQQYWQ1

Just make sure it supports the model you are looking at.

On Fri, Jul 28, 2017 at 2:42 PM, Jason McKemie <
j.mcke...@veloxinetbroadband.com> wrote:

> Where do you source these?
>
> On Friday, July 28, 2017, Josh Reynolds  wrote:
>
>> We use Magnum Power pure sine wave on-line UPSs with AGM batts. Yeah we
>> lose in the conversion, but we also don't have to fumble around with a
>> couple of various DC voltages.
>>
>> Love them. Made in the US too.
>>
>> On Jul 28, 2017 4:20 AM, "Gino A. Villarini"  wrote:
>>
>>> Our issues is exclusively with AF24’s and APC SU750’s.  On a Switching
>>> event the AF24 lock up about 50% of the time.  We have been changing the
>>> APC750 with the newer APC SUA750 and the problem vanishes…  believe me we
>>> have trie everything, grounding, changing UBNT POE, Surge Suppressors, you
>>> name it.
>>>
>>> 2 things have only worked:
>>>
>>> Newer APC models with any POE
>>> Powering the the AF24 with a dc-dc converter connected to the site
>>> batteries and into a McCown DC injector
>>>
>>> From: Af  on behalf of Colin Stanners <
>>> cstann...@gmail.com>
>>> Reply-To: "af@afmug.com" 
>>> Date: Thursday, July 27, 2017 at 9:53 PM
>>> To: "af@afmug.com" 
>>> Subject: Re: [AFMUG] Is there such a thing as a AC Capacitor?
>>>
>>> I forgot to mention:
>>> -if it's a non-sinewave UPS, it could be that the powersupply is
>>> designed to expect sinewave AC.
>>> -are you certain that it's not a grounding issue or other stray voltage
>>> between the circuits?
>>>
>>>
>>>
>>> *Gino A. Villarini*
>>> President
>>> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968
>>>
>>> On Thu, Jul 27, 2017 at 8:50 PM, Colin Stanners 
>>> wrote:
>>>
 Gino, can you say which gear? Most UPSes switch pretty much "instantly"
 (less than one AC cycle, which lasts 16ms) so a PSU that wouldn't last one
 AC cycle must have very questionable engineering. Or assuming that you use
 APC UPSes, you can change the sensitivity setting to switch quicker:
 http://www.apc.com/us/en/faqs/FA156514/

 On Thu, Jul 27, 2017 at 2:57 PM, Gino A. Villarini 
 wrote:

> Got some  gear that hangs when UPS switches from AC power to Batts…
> needs something to power AC for microseconds
>
>
>
> *Gino A. Villarini*
> President
> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968
>
>

>>>


Re: [AFMUG] Is there such a thing as a AC Capacitor?

2017-07-28 Thread Josh Reynolds
https://www.amazon.com/s/ref=nb_sb_noss_2?url=search-alias%3Daps=magnum+inverter

http://www.magnum-dimensions.com/mobile-power-products/inverter-chargers?field_output_waveform_value_selective%5B%5D=1_output_power_watts_value%5Bmin%5D=200_output_power_watts_value%5Bmax%5D=15000_output_frequency_value_selective%5B%5D=2_output_voltage_value_selective%5B%5D=1


On Fri, Jul 28, 2017 at 2:42 PM, Jason McKemie <
j.mcke...@veloxinetbroadband.com> wrote:

> Where do you source these?
>
> On Friday, July 28, 2017, Josh Reynolds  wrote:
>
>> We use Magnum Power pure sine wave on-line UPSs with AGM batts. Yeah we
>> lose in the conversion, but we also don't have to fumble around with a
>> couple of various DC voltages.
>>
>> Love them. Made in the US too.
>>
>> On Jul 28, 2017 4:20 AM, "Gino A. Villarini"  wrote:
>>
>>> Our issues is exclusively with AF24’s and APC SU750’s.  On a Switching
>>> event the AF24 lock up about 50% of the time.  We have been changing the
>>> APC750 with the newer APC SUA750 and the problem vanishes…  believe me we
>>> have trie everything, grounding, changing UBNT POE, Surge Suppressors, you
>>> name it.
>>>
>>> 2 things have only worked:
>>>
>>> Newer APC models with any POE
>>> Powering the the AF24 with a dc-dc converter connected to the site
>>> batteries and into a McCown DC injector
>>>
>>> From: Af  on behalf of Colin Stanners <
>>> cstann...@gmail.com>
>>> Reply-To: "af@afmug.com" 
>>> Date: Thursday, July 27, 2017 at 9:53 PM
>>> To: "af@afmug.com" 
>>> Subject: Re: [AFMUG] Is there such a thing as a AC Capacitor?
>>>
>>> I forgot to mention:
>>> -if it's a non-sinewave UPS, it could be that the powersupply is
>>> designed to expect sinewave AC.
>>> -are you certain that it's not a grounding issue or other stray voltage
>>> between the circuits?
>>>
>>>
>>>
>>> *Gino A. Villarini*
>>> President
>>> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968
>>>
>>> On Thu, Jul 27, 2017 at 8:50 PM, Colin Stanners 
>>> wrote:
>>>
 Gino, can you say which gear? Most UPSes switch pretty much "instantly"
 (less than one AC cycle, which lasts 16ms) so a PSU that wouldn't last one
 AC cycle must have very questionable engineering. Or assuming that you use
 APC UPSes, you can change the sensitivity setting to switch quicker:
 http://www.apc.com/us/en/faqs/FA156514/

 On Thu, Jul 27, 2017 at 2:57 PM, Gino A. Villarini 
 wrote:

> Got some  gear that hangs when UPS switches from AC power to Batts…
> needs something to power AC for microseconds
>
>
>
> *Gino A. Villarini*
> President
> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968
>
>

>>>


Re: [AFMUG] Is there such a thing as a AC Capacitor?

2017-07-28 Thread Jason McKemie
Where do you source these?

On Friday, July 28, 2017, Josh Reynolds  wrote:

> We use Magnum Power pure sine wave on-line UPSs with AGM batts. Yeah we
> lose in the conversion, but we also don't have to fumble around with a
> couple of various DC voltages.
>
> Love them. Made in the US too.
>
> On Jul 28, 2017 4:20 AM, "Gino A. Villarini"  > wrote:
>
>> Our issues is exclusively with AF24’s and APC SU750’s.  On a Switching
>> event the AF24 lock up about 50% of the time.  We have been changing the
>> APC750 with the newer APC SUA750 and the problem vanishes…  believe me we
>> have trie everything, grounding, changing UBNT POE, Surge Suppressors, you
>> name it.
>>
>> 2 things have only worked:
>>
>> Newer APC models with any POE
>> Powering the the AF24 with a dc-dc converter connected to the site
>> batteries and into a McCown DC injector
>>
>> From: Af > > on behalf of
>> Colin Stanners > >
>> Reply-To: "af@afmug.com " <
>> af@afmug.com >
>> Date: Thursday, July 27, 2017 at 9:53 PM
>> To: "af@afmug.com " <
>> af@afmug.com >
>> Subject: Re: [AFMUG] Is there such a thing as a AC Capacitor?
>>
>> I forgot to mention:
>> -if it's a non-sinewave UPS, it could be that the powersupply is designed
>> to expect sinewave AC.
>> -are you certain that it's not a grounding issue or other stray voltage
>> between the circuits?
>>
>>
>>
>> *Gino A. Villarini*
>> President
>> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968
>>
>> On Thu, Jul 27, 2017 at 8:50 PM, Colin Stanners > > wrote:
>>
>>> Gino, can you say which gear? Most UPSes switch pretty much "instantly"
>>> (less than one AC cycle, which lasts 16ms) so a PSU that wouldn't last one
>>> AC cycle must have very questionable engineering. Or assuming that you use
>>> APC UPSes, you can change the sensitivity setting to switch quicker:
>>> http://www.apc.com/us/en/faqs/FA156514/
>>>
>>> On Thu, Jul 27, 2017 at 2:57 PM, Gino A. Villarini >> > wrote:
>>>
 Got some  gear that hangs when UPS switches from AC power to Batts…
 needs something to power AC for microseconds



 *Gino A. Villarini*
 President
 Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968


>>>
>>


Re: [AFMUG] Is there such a thing as a AC Capacitor?

2017-07-28 Thread Lewis Bergman
I agree. When I had one we did that as well and our power related issues
sank to nearly zero.

On Fri, Jul 28, 2017 at 10:06 AM George Skorup 
wrote:

> I have about half of our sites converted to DC UPS's. Well, maybe about
> 60%. The number one issue I have is putting everything together for it is
> time consuming, but in the end, it's better in every way.
>
>
> On 7/28/2017 8:29 AM, Eric Muehleisen wrote:
>
> This is great info. We too have experienced this same issue with AF24's.
> Like Gino, we always set it to Low Sensitivity. This setting allows us to
> easily run the site off portable generator in a pinch. High Sensitivity
> won't allow for a portable genset.
>
> On Fri, Jul 28, 2017 at 4:24 AM, Gino A. Villarini 
> wrote:
>
> Wow, might try this… we usually put them on low sensitivity for a more
>> robust experience.  Didn’t know this affected the switching time!
>>
>> Thanks Collin!!!
>>
>> From: Af  on behalf of Colin Stanners <
>> cstann...@gmail.com>
>> Reply-To: "af@afmug.com" 
>>
> Date: Thursday, July 27, 2017 at 9:51 PM
>>
>
>> To: "af@afmug.com" 
>> Subject: Re: [AFMUG] Is there such a thing as a AC Capacitor?
>>
> Gino, can you say which gear? Most UPSes switch pretty much "instantly"
>> (less than one AC cycle, which lasts 16ms) so a PSU that wouldn't last one
>> AC cycle must have very questionable engineering. Or assuming that you use
>> APC UPSes, you can change the sensitivity setting to switch quicker:
>> http://www.apc.com/us/en/faqs/FA156514/
>>
>
>>
>>
>> *Gino A. Villarini*
>> President
>> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968
>>
>> [image: aeronet-logo_310cfc3e-6691-4f69-bd49-b37b834b9238.png]
>>
>> On Thu, Jul 27, 2017 at 2:57 PM, Gino A. Villarini 
>> wrote:
>>
>
>> Got some  gear that hangs when UPS switches from AC power to Batts… needs
>>> something to power AC for microseconds
>>>
>>>
>>>
>>> *Gino A. Villarini*
>>> President
>>> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968
>>>
>>> [image: aeronet-logo_310cfc3e-6691-4f69-bd49-b37b834b9238.png]
>>>
>>>


Re: [AFMUG] Is there such a thing as a AC Capacitor?

2017-07-28 Thread Colin Stanners
High sensitivity often works with generators in my experience as long as
they're the inverter type.

On Fri, Jul 28, 2017 at 8:29 AM, Eric Muehleisen  wrote:

> This is great info. We too have experienced this same issue with AF24's.
> Like Gino, we always set it to Low Sensitivity. This setting allows us to
> easily run the site off portable generator in a pinch. High Sensitivity
> won't allow for a portable genset.
>
> On Fri, Jul 28, 2017 at 4:24 AM, Gino A. Villarini 
> wrote:
>
>> Wow, might try this… we usually put them on low sensitivity for a more
>> robust experience.  Didn’t know this affected the switching time!
>>
>> Thanks Collin!!!
>>
>> From: Af  on behalf of Colin Stanners <
>> cstann...@gmail.com>
>> Reply-To: "af@afmug.com" 
>> Date: Thursday, July 27, 2017 at 9:51 PM
>> To: "af@afmug.com" 
>> Subject: Re: [AFMUG] Is there such a thing as a AC Capacitor?
>>
>> Gino, can you say which gear? Most UPSes switch pretty much "instantly"
>> (less than one AC cycle, which lasts 16ms) so a PSU that wouldn't last one
>> AC cycle must have very questionable engineering. Or assuming that you use
>> APC UPSes, you can change the sensitivity setting to switch quicker:
>> http://www.apc.com/us/en/faqs/FA156514/
>>
>>
>>
>> *Gino A. Villarini*
>> President
>> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968
>>
>> On Thu, Jul 27, 2017 at 2:57 PM, Gino A. Villarini 
>> wrote:
>>
>>> Got some  gear that hangs when UPS switches from AC power to Batts…
>>> needs something to power AC for microseconds
>>>
>>>
>>>
>>> *Gino A. Villarini*
>>> President
>>> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968
>>>
>>>
>>
>


Re: [AFMUG] Is there such a thing as a AC Capacitor?

2017-07-28 Thread George Skorup
I have about half of our sites converted to DC UPS's. Well, maybe about 
60%. The number one issue I have is putting everything together for it 
is time consuming, but in the end, it's better in every way.


On 7/28/2017 8:29 AM, Eric Muehleisen wrote:
This is great info. We too have experienced this same issue with 
AF24's. Like Gino, we always set it to Low Sensitivity. This setting 
allows us to easily run the site off portable generator in a pinch. 
High Sensitivity won't allow for a portable genset.


On Fri, Jul 28, 2017 at 4:24 AM, Gino A. Villarini > wrote:


Wow, might try this… we usually put them on low sensitivity for a
more robust experience.  Didn’t know this affected the switching
time!

Thanks Collin!!!

From: Af > on
behalf of Colin Stanners >
Reply-To: "af@afmug.com " >
Date: Thursday, July 27, 2017 at 9:51 PM
To: "af@afmug.com " >
Subject: Re: [AFMUG] Is there such a thing as a AC Capacitor?

Gino, can you say which gear? Most UPSes switch pretty much
"instantly" (less than one AC cycle, which lasts 16ms) so a PSU
that wouldn't last one AC cycle must have very questionable
engineering. Or assuming that you use APC UPSes, you can change
the sensitivity setting to switch quicker:
http://www.apc.com/us/en/faqs/FA156514/


*//*

*/Gino A. Villarini/*

President
Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968

On Thu, Jul 27, 2017 at 2:57 PM, Gino A. Villarini
> wrote:

Got some  gear that hangs when UPS switches from AC power to
Batts… needs something to power AC for microseconds

*//*

*/Gino A. Villarini/*

President
Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968







Re: [AFMUG] Is there such a thing as a AC Capacitor?

2017-07-28 Thread Josh Reynolds
We use Magnum Power pure sine wave on-line UPSs with AGM batts. Yeah we
lose in the conversion, but we also don't have to fumble around with a
couple of various DC voltages.

Love them. Made in the US too.

On Jul 28, 2017 4:20 AM, "Gino A. Villarini"  wrote:

> Our issues is exclusively with AF24’s and APC SU750’s.  On a Switching
> event the AF24 lock up about 50% of the time.  We have been changing the
> APC750 with the newer APC SUA750 and the problem vanishes…  believe me we
> have trie everything, grounding, changing UBNT POE, Surge Suppressors, you
> name it.
>
> 2 things have only worked:
>
> Newer APC models with any POE
> Powering the the AF24 with a dc-dc converter connected to the site
> batteries and into a McCown DC injector
>
> From: Af  on behalf of Colin Stanners <
> cstann...@gmail.com>
> Reply-To: "af@afmug.com" 
> Date: Thursday, July 27, 2017 at 9:53 PM
> To: "af@afmug.com" 
> Subject: Re: [AFMUG] Is there such a thing as a AC Capacitor?
>
> I forgot to mention:
> -if it's a non-sinewave UPS, it could be that the powersupply is designed
> to expect sinewave AC.
> -are you certain that it's not a grounding issue or other stray voltage
> between the circuits?
>
>
>
> *Gino A. Villarini*
> President
> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968
>
> On Thu, Jul 27, 2017 at 8:50 PM, Colin Stanners 
> wrote:
>
>> Gino, can you say which gear? Most UPSes switch pretty much "instantly"
>> (less than one AC cycle, which lasts 16ms) so a PSU that wouldn't last one
>> AC cycle must have very questionable engineering. Or assuming that you use
>> APC UPSes, you can change the sensitivity setting to switch quicker:
>> http://www.apc.com/us/en/faqs/FA156514/
>>
>> On Thu, Jul 27, 2017 at 2:57 PM, Gino A. Villarini 
>> wrote:
>>
>>> Got some  gear that hangs when UPS switches from AC power to Batts…
>>> needs something to power AC for microseconds
>>>
>>>
>>>
>>> *Gino A. Villarini*
>>> President
>>> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968
>>>
>>>
>>
>


Re: [AFMUG] Is there such a thing as a AC Capacitor?

2017-07-28 Thread Eric Muehleisen
This is great info. We too have experienced this same issue with AF24's.
Like Gino, we always set it to Low Sensitivity. This setting allows us to
easily run the site off portable generator in a pinch. High Sensitivity
won't allow for a portable genset.

On Fri, Jul 28, 2017 at 4:24 AM, Gino A. Villarini 
wrote:

> Wow, might try this… we usually put them on low sensitivity for a more
> robust experience.  Didn’t know this affected the switching time!
>
> Thanks Collin!!!
>
> From: Af  on behalf of Colin Stanners <
> cstann...@gmail.com>
> Reply-To: "af@afmug.com" 
> Date: Thursday, July 27, 2017 at 9:51 PM
> To: "af@afmug.com" 
> Subject: Re: [AFMUG] Is there such a thing as a AC Capacitor?
>
> Gino, can you say which gear? Most UPSes switch pretty much "instantly"
> (less than one AC cycle, which lasts 16ms) so a PSU that wouldn't last one
> AC cycle must have very questionable engineering. Or assuming that you use
> APC UPSes, you can change the sensitivity setting to switch quicker:
> http://www.apc.com/us/en/faqs/FA156514/
>
>
>
> *Gino A. Villarini*
> President
> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968
>
> On Thu, Jul 27, 2017 at 2:57 PM, Gino A. Villarini 
> wrote:
>
>> Got some  gear that hangs when UPS switches from AC power to Batts… needs
>> something to power AC for microseconds
>>
>>
>>
>> *Gino A. Villarini*
>> President
>> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968
>>
>>
>


Re: [AFMUG] Is there such a thing as a AC Capacitor?

2017-07-28 Thread Gino A. Villarini
Wow, might try this… we usually put them on low sensitivity for a more robust 
experience.  Didn’t know this affected the switching time!

Thanks Collin!!!

From: Af > on behalf of Colin 
Stanners >
Reply-To: "af@afmug.com" 
>
Date: Thursday, July 27, 2017 at 9:51 PM
To: "af@afmug.com" >
Subject: Re: [AFMUG] Is there such a thing as a AC Capacitor?

Gino, can you say which gear? Most UPSes switch pretty much "instantly" (less 
than one AC cycle, which lasts 16ms) so a PSU that wouldn't last one AC cycle 
must have very questionable engineering. Or assuming that you use APC UPSes, 
you can change the sensitivity setting to switch quicker:  
http://www.apc.com/us/en/faqs/FA156514/




Gino A. Villarini


President
Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968

[cid:aeronet-logo_310cfc3e-6691-4f69-bd49-b37b834b9238.png]

On Thu, Jul 27, 2017 at 2:57 PM, Gino A. Villarini 
> wrote:
Got some  gear that hangs when UPS switches from AC power to Batts… needs 
something to power AC for microseconds



Gino A. Villarini


President
Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968

[cid:aeronet-logo_310cfc3e-6691-4f69-bd49-b37b834b9238.png]



Re: [AFMUG] Is there such a thing as a AC Capacitor?

2017-07-28 Thread Gino A. Villarini
Our issues is exclusively with AF24’s and APC SU750’s.  On a Switching event 
the AF24 lock up about 50% of the time.  We have been changing the APC750 with 
the newer APC SUA750 and the problem vanishes…  believe me we have trie 
everything, grounding, changing UBNT POE, Surge Suppressors, you name it.

2 things have only worked:

Newer APC models with any POE
Powering the the AF24 with a dc-dc converter connected to the site batteries 
and into a McCown DC injector

From: Af > on behalf of Colin 
Stanners >
Reply-To: "af@afmug.com" 
>
Date: Thursday, July 27, 2017 at 9:53 PM
To: "af@afmug.com" >
Subject: Re: [AFMUG] Is there such a thing as a AC Capacitor?

I forgot to mention:
-if it's a non-sinewave UPS, it could be that the powersupply is designed to 
expect sinewave AC.
-are you certain that it's not a grounding issue or other stray voltage between 
the circuits?




Gino A. Villarini


President
Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968

[cid:aeronet-logo_310cfc3e-6691-4f69-bd49-b37b834b9238.png]

On Thu, Jul 27, 2017 at 8:50 PM, Colin Stanners 
> wrote:
Gino, can you say which gear? Most UPSes switch pretty much "instantly" (less 
than one AC cycle, which lasts 16ms) so a PSU that wouldn't last one AC cycle 
must have very questionable engineering. Or assuming that you use APC UPSes, 
you can change the sensitivity setting to switch quicker:  
http://www.apc.com/us/en/faqs/FA156514/

On Thu, Jul 27, 2017 at 2:57 PM, Gino A. Villarini 
> wrote:
Got some  gear that hangs when UPS switches from AC power to Batts… needs 
something to power AC for microseconds



Gino A. Villarini


President
Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968

[cid:aeronet-logo_310cfc3e-6691-4f69-bd49-b37b834b9238.png]




Re: [AFMUG] Is there such a thing as a AC Capacitor?

2017-07-28 Thread Lewis Bergman
I don't think it really applies to the intent, but now that I thunk about
it, a friend of mine owns a few gins. A single gin has a bunches of 3 phase
large motors. As a result, he had some kind of load shunting system. He
didn't know enough about it to explain it but it sounded like huge caps
designed to even or the huge start demand  the motors. I never actually saw
the piece of equipment.  His electric bill usually runs in the $40k range
in cotton season for each gin.

On Thu, Jul 27, 2017, 9:07 PM Seth Mattinen  wrote:

> On 7/27/17 6:51 PM, Colin Stanners wrote:
> > Gino, can you say which gear? Most UPSes switch pretty much "instantly"
> > (less than one AC cycle, which lasts 16ms) so a PSU that wouldn't last
> > one AC cycle must have very questionable engineering. Or assuming that
> > you use APC UPSes, you can change the sensitivity setting to switch
> > quicker: http://www.apc.com/us/en/faqs/FA156514/
> >
>
>
> Even on the cheapest BackUPS, anything with a decent power supply is
> going to have capacitors with its own holdup time that's greater than
> any line interactive UPS. I've got some old late 90's vintage BackUPS
> units back when they were made out of metal still going strong.
>
> If the power supply is a linear wall wart though, that could be a problem.
>
> ~Seth
>


Re: [AFMUG] Is there such a thing as a AC Capacitor?

2017-07-27 Thread Seth Mattinen

On 7/27/17 6:51 PM, Colin Stanners wrote:
Gino, can you say which gear? Most UPSes switch pretty much "instantly" 
(less than one AC cycle, which lasts 16ms) so a PSU that wouldn't last 
one AC cycle must have very questionable engineering. Or assuming that 
you use APC UPSes, you can change the sensitivity setting to switch 
quicker: http://www.apc.com/us/en/faqs/FA156514/





Even on the cheapest BackUPS, anything with a decent power supply is 
going to have capacitors with its own holdup time that's greater than 
any line interactive UPS. I've got some old late 90's vintage BackUPS 
units back when they were made out of metal still going strong.


If the power supply is a linear wall wart though, that could be a problem.

~Seth


Re: [AFMUG] Is there such a thing as a AC Capacitor?

2017-07-27 Thread Seth Mattinen

On 7/27/17 6:45 PM, Eric Kuhnke wrote:
With a big flywheel setup, it might take up less space and cost less 
than a huge AGM battery plant, but you had better be *really* 
*confident* in the maintenance, load testing and quality of your 
generator...  The ones I have seen are good for 30 to 60 seconds of load 
buffer, maximum, just enough time for a big diesel generator to start up 
and get slightly warmed up before the load transfers onto it.





The incident I'm recalling was the type where the flywheel, generator, 
and engine are linear on the same shaft. While the power is on it's a 
motor that maintains the flywheel. If the power goes out it becomes a 
generator just barely long enough for the engine to start. The fatal 
flaw IMO is that type can't cold start on the diesel engine. It needed 
batteries to "jumpstart" the flywheel, so you end up having the 
expensive flywheel system *and* a battery plant to cover all your bases.


~Seth


Re: [AFMUG] Is there such a thing as a AC Capacitor?

2017-07-27 Thread Colin Stanners
I forgot to mention:
-if it's a non-sinewave UPS, it could be that the powersupply is designed
to expect sinewave AC.
-are you certain that it's not a grounding issue or other stray voltage
between the circuits?

On Thu, Jul 27, 2017 at 8:50 PM, Colin Stanners  wrote:

> Gino, can you say which gear? Most UPSes switch pretty much "instantly"
> (less than one AC cycle, which lasts 16ms) so a PSU that wouldn't last one
> AC cycle must have very questionable engineering. Or assuming that you use
> APC UPSes, you can change the sensitivity setting to switch quicker:
> http://www.apc.com/us/en/faqs/FA156514/
>
> On Thu, Jul 27, 2017 at 2:57 PM, Gino A. Villarini 
> wrote:
>
>> Got some  gear that hangs when UPS switches from AC power to Batts… needs
>> something to power AC for microseconds
>>
>>
>>
>> *Gino A. Villarini*
>> President
>> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968
>>
>>
>


Re: [AFMUG] Is there such a thing as a AC Capacitor?

2017-07-27 Thread Colin Stanners
Gino, can you say which gear? Most UPSes switch pretty much "instantly"
(less than one AC cycle, which lasts 16ms) so a PSU that wouldn't last one
AC cycle must have very questionable engineering. Or assuming that you use
APC UPSes, you can change the sensitivity setting to switch quicker:
http://www.apc.com/us/en/faqs/FA156514/

On Thu, Jul 27, 2017 at 2:57 PM, Gino A. Villarini 
wrote:

> Got some  gear that hangs when UPS switches from AC power to Batts… needs
> something to power AC for microseconds
>
>
>
> *Gino A. Villarini*
> President
> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968
>
>


Re: [AFMUG] Is there such a thing as a AC Capacitor?

2017-07-27 Thread Eric Kuhnke
With a big flywheel setup, it might take up less space and cost less than a
huge AGM battery plant, but you had better be *really* *confident* in the
maintenance, load testing and quality of your generator...  The ones I have
seen are good for 30 to 60 seconds of load buffer, maximum, just enough
time for a big diesel generator to start up and get slightly warmed up
before the load transfers onto it.



On Thu, Jul 27, 2017 at 6:43 PM, Seth Mattinen  wrote:

> On 7/27/17 4:16 PM, Robert Andrews wrote:
>
>> http://www.pscpower.com/what-we-do/products/uninterruptible-
>> power-supply/batteryless-ups/
>>
>
> Was it 365 Main that had their flywheels lose too much inertia during a
> power outage and ended up dumping the load? I forget the brand of
> motor-generator system it was. Ironically the only way to get theirs back
> up to speed without utility power was batteries, which they didn't option
> because flywheel.
>
> ~Seth
>


Re: [AFMUG] Is there such a thing as a AC Capacitor?

2017-07-27 Thread Seth Mattinen

On 7/27/17 4:16 PM, Robert Andrews wrote:
http://www.pscpower.com/what-we-do/products/uninterruptible-power-supply/batteryless-ups/ 



Was it 365 Main that had their flywheels lose too much inertia during a 
power outage and ended up dumping the load? I forget the brand of 
motor-generator system it was. Ironically the only way to get theirs 
back up to speed without utility power was batteries, which they didn't 
option because flywheel.


~Seth


Re: [AFMUG] Is there such a thing as a AC Capacitor?

2017-07-27 Thread Robert Andrews

http://www.pscpower.com/what-we-do/products/uninterruptible-power-supply/batteryless-ups/

On 07/27/2017 04:06 PM, Jaime Solorza wrote:

These big enough?

Jaime Solorza

On Jul 27, 2017 5:00 PM, "Chuck McCown" > wrote:

I imagine a motor-generator set with lots of inertia would be good
at this.

*From:* Jaime Solorza
*Sent:* Thursday, July 27, 2017 4:45 PM
*To:* Animal Farm
*Subject:* Re: [AFMUG] Is there such a thing as a AC Capacitor?

We were working at a storm well site today with engineer,
electricians and us.  The motors that run pumps and Gates are high
voltage systems with a train car size diesel Cummins generator that
also supplies 120 vac to instrumentation and SCADA
systems..(converted to 24vdc)...they have a refrigerator size APC
UPS for panel and radio...when generator kicks in...UPS continues to
supply power for a bit then alarms with fault wire message.  The
electricians tested lines, added and bonded more grounds but nothing
changes with either auto or manual switch.  Our panel does detect
issue and cuts off UPS feed, and sends message to water company
operators over radio feed.   After several tests and measurements,
engineer suspects the Cummins generator is not grounded properly.
We are going back Tuesday with Cummins tech.  Never saw so many
Fluke high end meters and testers in one place.

Jaime Solorza

On Jul 27, 2017 4:25 PM, "Lewis Bergman" 
wrote:

Yea, an online UPS is designed to do what you want. AS a side
note, you should always use an online UPS when backed by a genset.

On Thu, Jul 27, 2017 at 3:28 PM Jaime Solorza
 wrote:

Gino...PULS Power has solutions for this...


Jaime Solorza

On Jul 27, 2017 1:57 PM, "Gino A. Villarini"
 wrote:

Got some  gear that hangs when UPS switches from AC
power to Batts… needs something to power AC for
microseconds

*//*

*/Gino A. Villarini/*

President
Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968



Re: [AFMUG] Is there such a thing as a AC Capacitor?

2017-07-27 Thread Chuck McCown
I imagine a motor-generator set with lots of inertia would be good at this.  

From: Jaime Solorza 
Sent: Thursday, July 27, 2017 4:45 PM
To: Animal Farm 
Subject: Re: [AFMUG] Is there such a thing as a AC Capacitor?

We were working at a storm well site today with engineer, electricians and us.  
The motors that run pumps and Gates are high voltage systems with a train car 
size diesel Cummins generator that also supplies 120 vac to instrumentation and 
SCADA systems..(converted to 24vdc)...they have a refrigerator size APC UPS for 
panel and radio...when generator kicks in...UPS continues to supply power for a 
bit then alarms with fault wire message.  The electricians tested lines, added 
and bonded more grounds but nothing changes with either auto or manual switch.  
Our panel does detect issue and cuts off UPS feed, and sends message to water 
company operators over radio feed.   After several tests and measurements, 
engineer suspects the Cummins generator is not grounded properly.  We are going 
back Tuesday with Cummins tech.  Never saw so many Fluke high end meters and 
testers in one place.  


Jaime Solorza

On Jul 27, 2017 4:25 PM, "Lewis Bergman"  wrote:

  Yea, an online UPS is designed to do what you want. AS a side note, you 
should always use an online UPS when backed by a genset.

  On Thu, Jul 27, 2017 at 3:28 PM Jaime Solorza  
wrote:

Gino...PULS Power has solutions for this...



Jaime Solorza

On Jul 27, 2017 1:57 PM, "Gino A. Villarini"  wrote:

  Got some  gear that hangs when UPS switches from AC power to Batts… needs 
something to power AC for microseconds 


Gino A. Villarini
   
President 
Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968 





Re: [AFMUG] Is there such a thing as a AC Capacitor?

2017-07-27 Thread Jaime Solorza
We were working at a storm well site today with engineer, electricians and
us.  The motors that run pumps and Gates are high voltage systems with a
train car size diesel Cummins generator that also supplies 120 vac to
instrumentation and SCADA systems..(converted to 24vdc)...they have a
refrigerator size APC UPS for panel and radio...when generator kicks
in...UPS continues to supply power for a bit then alarms with fault wire
message.  The electricians tested lines, added and bonded more grounds but
nothing changes with either auto or manual switch.  Our panel does detect
issue and cuts off UPS feed, and sends message to water company operators
over radio feed.   After several tests and measurements, engineer suspects
the Cummins generator is not grounded properly.  We are going back Tuesday
with Cummins tech.  Never saw so many Fluke high end meters and testers in
one place.

Jaime Solorza

On Jul 27, 2017 4:25 PM, "Lewis Bergman"  wrote:

> Yea, an online UPS is designed to do what you want. AS a side note, you
> should always use an online UPS when backed by a genset.
>
> On Thu, Jul 27, 2017 at 3:28 PM Jaime Solorza 
> wrote:
>
>> Gino...PULS Power has solutions for this...
>>
>>
>> Jaime Solorza
>>
>> On Jul 27, 2017 1:57 PM, "Gino A. Villarini"  wrote:
>>
>>> Got some  gear that hangs when UPS switches from AC power to Batts…
>>> needs something to power AC for microseconds
>>>
>>>
>>>
>>> *Gino A. Villarini*
>>> President
>>> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968
>>>
>>>


Re: [AFMUG] Is there such a thing as a AC Capacitor?

2017-07-27 Thread Lewis Bergman
Yea, an online UPS is designed to do what you want. AS a side note, you
should always use an online UPS when backed by a genset.

On Thu, Jul 27, 2017 at 3:28 PM Jaime Solorza 
wrote:

> Gino...PULS Power has solutions for this...
>
>
> Jaime Solorza
>
> On Jul 27, 2017 1:57 PM, "Gino A. Villarini"  wrote:
>
>> Got some  gear that hangs when UPS switches from AC power to Batts… needs
>> something to power AC for microseconds
>>
>>
>>
>> *Gino A. Villarini*
>> President
>> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968
>>
>>


Re: [AFMUG] Is there such a thing as a AC Capacitor?

2017-07-27 Thread Jaime Solorza
Gino...PULS Power has solutions for this...

Jaime Solorza

On Jul 27, 2017 1:57 PM, "Gino A. Villarini"  wrote:

> Got some  gear that hangs when UPS switches from AC power to Batts… needs
> something to power AC for microseconds
>
>
>
> *Gino A. Villarini*
> President
> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968
>
>


Re: [AFMUG] Is there such a thing as a AC Capacitor?

2017-07-27 Thread Chris Fabien
You need a faster UPS or if you are feeling hacky, open the device up and
see if you could add capacitor to a DC bus inside.

On Thu, Jul 27, 2017 at 3:57 PM, Gino A. Villarini 
wrote:

> Got some  gear that hangs when UPS switches from AC power to Batts… needs
> something to power AC for microseconds
>
>
>
> *Gino A. Villarini*
> President
> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968
>
>


Re: [AFMUG] Is there such a thing as a AC Capacitor?

2017-07-27 Thread Gino A. Villarini
Well duh! :-/

Trying to save some $$ and time…

From: Af > on behalf of 
"eric.kuh...@gmail.com" 
>
Reply-To: "af@afmug.com" 
>
Date: Thursday, July 27, 2017 at 4:03 PM
To: "af@afmug.com" >
Subject: Re: [AFMUG] Is there such a thing as a AC Capacitor?

no, but there is this amazing thing called a double conversion/true online UPS 
:-)

or build a rectifier + battery setup and use equipment with DC power supplies...





Gino A. Villarini


President
Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968

[cid:aeronet-logo_310cfc3e-6691-4f69-bd49-b37b834b9238.png]

On Thu, Jul 27, 2017 at 12:57 PM, Gino A. Villarini 
> wrote:
Got some  gear that hangs when UPS switches from AC power to Batts… needs 
something to power AC for microseconds



Gino A. Villarini


President
Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968

[cid:aeronet-logo_310cfc3e-6691-4f69-bd49-b37b834b9238.png]



Re: [AFMUG] Is there such a thing as a AC Capacitor?

2017-07-27 Thread Eric Kuhnke
no, but there is this amazing thing called a double conversion/true online
UPS :-)

or build a rectifier + battery setup and use equipment with DC power
supplies...


On Thu, Jul 27, 2017 at 12:57 PM, Gino A. Villarini 
wrote:

> Got some  gear that hangs when UPS switches from AC power to Batts… needs
> something to power AC for microseconds
>
>
>
> *Gino A. Villarini*
> President
> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968
>
>