It's a simple visit to ohms law.
OR
Just grab a "kill a watt" tester and look at your current draw.
With a quick "in the head math" the 15 amp breaker will be fine.

Remember the 30amp supply is at 13.8v not 117v ac the panel breaker is at.

Again

Ohms law.
BTW : glad you asked the question rather than change breaker size.
73
Dean


On Wed, Jun 13, 2018, 23:03 Michael Gillen via Elecraft <
elecraft@mailman.qth.net> wrote:

> Kind of a dumb question however here goes:
>
> I got my K3S a short while ago and now I want to add the KPA500 and KAT500
> to it however it just now occurred to me that I should check how much juice
> I need to power that thing!
>
> I’m currently using an Alinco DM-330MV which I believe puts out 30A
> continuous however its probably plugged into one the house 15A lines.
>
> So my questions are:
>
> 1) Will 15A house line supply enough juice for the K3S, KPA500, KAT500,
> and in the future a P3 Panadaper?
>
> 2) If not can I get away with replacing the breaker with a 20A breaker?
> 30A?
>
> 3) Will the Alinco be big enough or should I upgrade that as well?
>
>
> Thanks guys,
> Michael
>
> __
> Elecraft mailing list
> Home: http://mailman.qth.net/mailman/listinfo/elecraft
> Help: http://mailman.qth.net/mmfaq.htm
> Post: mailto:Elecraft@mailman.qth.net
>
> This list hosted by: http://www.qsl.net
> Please help support this email list: http://www.qsl.net/donate.html
> Message delivered to dean.k...@gmail.com
__
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:Elecraft@mailman.qth.net

This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html
Message delivered to arch...@mail-archive.com

Re: [Elecraft] power requirements for a K3S, KPA500, KAT500, P3?

2018-06-14 Thread Jim Brown

On 6/14/2018 10:18 AM, ANDY DURBIN wrote:

When I added my KPA500 to my TS-590S station I found the drop in mains voltage 
unacceptable.


I'd bet that was because of the IR drop in the long #14 wires feeding 
the outlet (and maybe other stuff running off that circuit).


Yes, 240VAC is better, simply because it requires half the current, and 
thus half the IR drop.



  With this power distribution arrangement I run my KPA500 at 500 W output and 
PA voltage does not usually drop below 60 V.


Remember that there's a three-position jumper that selects a transformer 
tap inside the amp to adjust for line voltage. Access it by removing the 
top cover, and RTFM to learn how to set it. Unplug from power, of 
course. The KPA will go into protect mode if the HV is too high when NOT 
transmitting (greater than about 82V) and too low when transmitting 
(less than about 55V), so the key is to watch that voltage after 
changing the jumper.


We run two K3/KPA500 for 7QP and CQP county expeditions from two Yamaha 
2000i generators, which are providing 120V. We're running about 40 ft of 
#10-3 from the generator to the outlet where the amps are plugged in, 
and typically get 500W from the amp. Team leader W6GJB bought a 
"strapping kit" to run the generators in parallel, and changed the 
breaker on the one feeding the station to 30A. We do this for the 
generators -- they're happier in parallel with keyed CW.


73, Jim K9YC

__
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:Elecraft@mailman.qth.net

This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html
Message delivered to arch...@mail-archive.com


Re: [Elecraft] power requirements for a K3S, KPA500, KAT500, P3?

2018-06-14 Thread Harlan Sherriff via Elecraft
John, I didn’t think you were suggesting changing breakers. The original post 
asked if he could change out breakers to a 20A or 30A breaker. 

Sent from my iPhone

> On Jun 14, 2018, at 1:39 PM, Jim Brown  wrote:
> 
>> On 6/14/2018 4:14 AM, j...@kk9a.com wrote:
>> It should be fine to run the KPA500 at reduced power using your existing
>> 15 amp outlet, unless you have a lot of other stuff plugged in.
> 
> No power reduction is required -- let's do the simple math. The KPA draws 
> about 10A at 120v keydown. That 12v (probably 13.8V) supply shouldn't draw 
> much more than about 2A when the K3 is driving the KPA500, because the KPA 
> needs less than 30W to get to full power. The 13.8V supply should draw no 
> more than about 2A with the K3 barefoot at full power keydown.
> 
> 73, Jim K9YC
> 
> __
> Elecraft mailing list
> Home: http://mailman.qth.net/mailman/listinfo/elecraft
> Help: http://mailman.qth.net/mmfaq.htm
> Post: mailto:Elecraft@mailman.qth.net
> 
> This list hosted by: http://www.qsl.net
> Please help support this email list: http://www.qsl.net/donate.html
> Message delivered to hsherr...@reagan.com

__
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:Elecraft@mailman.qth.net

This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html
Message delivered to arch...@mail-archive.com

Re: [Elecraft] power requirements for a K3S, KPA500, KAT500, P3?

2018-06-14 Thread Jim Brown

On 6/14/2018 4:14 AM, j...@kk9a.com wrote:

It should be fine to run the KPA500 at reduced power using your existing
15 amp outlet, unless you have a lot of other stuff plugged in.


No power reduction is required -- let's do the simple math. The KPA 
draws about 10A at 120v keydown. That 12v (probably 13.8V) supply 
shouldn't draw much more than about 2A when the K3 is driving the 
KPA500, because the KPA needs less than 30W to get to full power. The 
13.8V supply should draw no more than about 2A with the K3 barefoot at 
full power keydown.


73, Jim K9YC

__
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:Elecraft@mailman.qth.net

This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html
Message delivered to arch...@mail-archive.com


[Elecraft] power requirements for a K3S, KPA500, KAT500, P3?

2018-06-14 Thread ANDY DURBIN
"Will 15A house line supply enough juice for the K3S, KPA500, KAT500, and in 
the future a P3 Panadaper?"

When I added my KPA500 to my TS-590S station I found the drop in mains voltage 
unacceptable.  I made some changes in power distribution and now have a web 
power switch connected directly to the 120 V outlet.  That web power switch 
feeds the KPA500 directly and feeds the other station equipment via breakout 
strips.   One port of the web switch has a permanently installed "kill-a-watt" 
monitor.

The outlet I'm plugged into is just the other side of the house wall from the 
breaker panel.   With this power distribution arrangement I run my KPA500 at 
500 W output and PA voltage does not usually drop below 60 V.

In a spot check on 20 m (the band at which my KPA500 efficiency seems to be 
worst)  I saw 119.0 V with KPA500 standby and 113.4 V with key down 500 W RF 
output.   The situation is a bit worse when the heat pump is running but 
doesn't seem to cause any operational problems.

If I ever build a real station I'll include 240 V outlets.

73,
Andy k3wyc







__
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:Elecraft@mailman.qth.net

This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html
Message delivered to arch...@mail-archive.com


Re: [Elecraft] power requirements for a K3S, KPA500, KAT500, P3?

2018-06-14 Thread Lynn W. Taylor, WB6UUT
NO!  The wire will get very hot, and you may burn down your house as a 
result.


On 6/13/2018 8:02 PM, Michael Gillen via Elecraft wrote:

2) If not can I get away with replacing the breaker with a 20A breaker? 30A?

__
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:Elecraft@mailman.qth.net

This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html
Message delivered to arch...@mail-archive.com


Re: [Elecraft] power requirements for a K3S, KPA500, KAT500, P3?

2018-06-14 Thread j...@kk9a.com
I did not suggest changing the breaker.  I wrote either use what he has at
reduced output or install at least one new dedicated circuit.

John KK9A

Sent via the Samsung Galaxy 7 edge, an AT 4G LTE smartphone.

On Thu, Jun 14, 2018 at 8:26 AM, Harlan Sherriff 
wrote:

> Michael,
> Do NOT replace the breaker with a larger current breaker UNLESS the wiring
> is rated for the extra current.
> 15A = 14 gage wire
> 20A = 12 gage wire
> 30A = 10 gage wire
>
> Harlan
> K4HES
>
> Sent from my iPhone
>
> > On Jun 14, 2018, at 7:14 AM, "j...@kk9a.com"  wrote:
> >
> > It should be fine to run the KPA500 at reduced power using your existing
> > 15 amp outlet, unless you have a lot of other stuff plugged in. You can
> > always add a 240v outlet later.  I ran a separate 20 amp 120v outlet
> along
> > with a new 240v outlet into the shack. Your 30 amp power supply is
> > adequate for the K3S and P3.
> >
> > GL
> > John KK9A
> >
> >
> > Michael Gillen KK6RWK wrote:
> >
> > Kind of a dumb question however here goes:
> >
> > I got my K3S a short while ago and now I want to add the KPA500 and
> KAT500
> > to it however it just now occurred to me that I should check how much
> > juice I need to power that thing!
> >
> > I’m currently using an Alinco DM-330MV which I believe puts out 30A
> > continuous however its probably plugged into one the house 15A lines.
> >
> > So my questions are:
> >
> > 1) Will 15A house line supply enough juice for the K3S, KPA500, KAT500,
> > and in the future a P3 Panadaper?
> >
> > 2) If not can I get away with replacing the breaker with a 20A breaker?
> 30A?
> >
> > 3) Will the Alinco be big enough or should I upgrade that as well?
> >
> >
> > Thanks guys,
> > Michael
> >
> > __
> > Elecraft mailing list
> > Home: http://mailman.qth.net/mailman/listinfo/elecraft
> > Help: http://mailman.qth.net/mmfaq.htm
> > Post: mailto:Elecraft@mailman.qth.net
> >
> > This list hosted by: http://www.qsl.net
> > Please help support this email list: http://www.qsl.net/donate.html
> > Message delivered to hsherr...@reagan.com
>
>
__
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:Elecraft@mailman.qth.net

This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html
Message delivered to arch...@mail-archive.com

Re: [Elecraft] power requirements for a K3S, KPA500, KAT500, P3?

2018-06-14 Thread Harlan Sherriff via Elecraft
Michael,
Do NOT replace the breaker with a larger current breaker UNLESS the wiring is 
rated for the extra current. 
15A = 14 gage wire
20A = 12 gage wire
30A = 10 gage wire

Harlan
K4HES 

Sent from my iPhone

> On Jun 14, 2018, at 7:14 AM, "j...@kk9a.com"  wrote:
> 
> It should be fine to run the KPA500 at reduced power using your existing
> 15 amp outlet, unless you have a lot of other stuff plugged in. You can
> always add a 240v outlet later.  I ran a separate 20 amp 120v outlet along
> with a new 240v outlet into the shack. Your 30 amp power supply is
> adequate for the K3S and P3.
> 
> GL
> John KK9A
> 
> 
> Michael Gillen KK6RWK wrote:
> 
> Kind of a dumb question however here goes:
> 
> I got my K3S a short while ago and now I want to add the KPA500 and KAT500
> to it however it just now occurred to me that I should check how much
> juice I need to power that thing!
> 
> I’m currently using an Alinco DM-330MV which I believe puts out 30A
> continuous however its probably plugged into one the house 15A lines.
> 
> So my questions are:
> 
> 1) Will 15A house line supply enough juice for the K3S, KPA500, KAT500,
> and in the future a P3 Panadaper?
> 
> 2) If not can I get away with replacing the breaker with a 20A breaker? 30A?
> 
> 3) Will the Alinco be big enough or should I upgrade that as well?
> 
> 
> Thanks guys,
> Michael
> 
> __
> Elecraft mailing list
> Home: http://mailman.qth.net/mailman/listinfo/elecraft
> Help: http://mailman.qth.net/mmfaq.htm
> Post: mailto:Elecraft@mailman.qth.net
> 
> This list hosted by: http://www.qsl.net
> Please help support this email list: http://www.qsl.net/donate.html
> Message delivered to hsherr...@reagan.com

__
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:Elecraft@mailman.qth.net

This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html
Message delivered to arch...@mail-archive.com

[Elecraft] power requirements for a K3S, KPA500, KAT500, P3?

2018-06-14 Thread j...@kk9a.com
It should be fine to run the KPA500 at reduced power using your existing
15 amp outlet, unless you have a lot of other stuff plugged in. You can
always add a 240v outlet later.  I ran a separate 20 amp 120v outlet along
with a new 240v outlet into the shack. Your 30 amp power supply is
adequate for the K3S and P3.

GL
John KK9A


Michael Gillen KK6RWK wrote:

Kind of a dumb question however here goes:

I got my K3S a short while ago and now I want to add the KPA500 and KAT500
to it however it just now occurred to me that I should check how much
juice I need to power that thing!

I’m currently using an Alinco DM-330MV which I believe puts out 30A
continuous however its probably plugged into one the house 15A lines.

So my questions are:

1) Will 15A house line supply enough juice for the K3S, KPA500, KAT500,
and in the future a P3 Panadaper?

2) If not can I get away with replacing the breaker with a 20A breaker? 30A?

3) Will the Alinco be big enough or should I upgrade that as well?


Thanks guys,
Michael

__
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:Elecraft@mailman.qth.net

This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html
Message delivered to arch...@mail-archive.com

Re: [Elecraft] power requirements for a K3S, KPA500, KAT500, P3?

2018-06-13 Thread Charlie T
AND, if there's any sort of electrical fire and it is discovered a 20 A breaker 
was installed with 14Ga wire, you fire insurance becomes instantly 
"non-functus".
That's Latin for "You're screwed".

Charlie k3ICH




-Original Message-
From: elecraft-boun...@mailman.qth.net  On 
Behalf Of Jim Brown
Sent: Wednesday, June 13, 2018 11:16 PM
To: elecraft@mailman.qth.net
Subject: Re: [Elecraft] power requirements for a K3S, KPA500, KAT500, P3?

On 6/13/2018 8:02 PM, Michael Gillen via Elecraft wrote:
>   Will 15A house line supply enough juice for the K3S, KPA500, KAT500, and in 
> the future a P3 Panadaper?

Yes.

> 2) If not can I get away with replacing the breaker with a 20A breaker?

Only if all the wiring on that breaker is #12 or larger.

>   30A?

Only if all the wiring on that breaker is #10.  These are electrical safety 
code requirements, which carry the force of law.

> 3) Will the Alinco be big enough

Yes

> or should I upgrade that as well?

  No.

73, Jim K9YC


__
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:Elecraft@mailman.qth.net

This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html Message 
delivered to pin...@erols.com

__
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:Elecraft@mailman.qth.net

This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html
Message delivered to arch...@mail-archive.com


Re: [Elecraft] power requirements for a K3S, KPA500, KAT500, P3?

2018-06-13 Thread Michael Gillen via Elecraft
Thanks for the thorough answer Jim!

Michael 
KK6RWK 

> On Jun 13, 2018, at 8:15 PM, Jim Brown  wrote:
> 
>> On 6/13/2018 8:02 PM, Michael Gillen via Elecraft wrote:
>>  Will 15A house line supply enough juice for the K3S, KPA500, KAT500, and in 
>> the future a P3 Panadaper?
> 
> Yes.
> 
>> 2) If not can I get away with replacing the breaker with a 20A breaker?
> 
> Only if all the wiring on that breaker is #12 or larger.
> 
>>  30A?
> 
> Only if all the wiring on that breaker is #10.  These are electrical safety 
> code requirements, which carry the force of law.
> 
>> 3) Will the Alinco be big enough
> 
> Yes
> 
>> or should I upgrade that as well?
> 
>  No.
> 
> 73, Jim K9YC
> 
> 
> __
> Elecraft mailing list
> Home: http://mailman.qth.net/mailman/listinfo/elecraft
> Help: http://mailman.qth.net/mmfaq.htm
> Post: mailto:Elecraft@mailman.qth.net
> 
> This list hosted by: http://www.qsl.net
> Please help support this email list: http://www.qsl.net/donate.html
> Message delivered to mjgil...@yahoo.com

__
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:Elecraft@mailman.qth.net

This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html
Message delivered to arch...@mail-archive.com


Re: [Elecraft] power requirements for a K3S, KPA500, KAT500, P3?

2018-06-13 Thread Michael Gillen via Elecraft
I understand not to change any breakers. Roger that.

Thank you for the quick replies!

Michael
KK6RWK 

> On Jun 13, 2018, at 8:25 PM, David Christ  wrote:
> 
> DO NOT change the breaker
> 
> 
> I am concerned about your so blithely talking about just changing the 
> breaker.  The breaker is there to protect the wire and is sized according to 
> the wire.  Do not increase the size of the breaker without verifying what the 
> wire gauge is.  Quite likely if the breaker is now 15 amp the wire is 
> probably #14.  This is common in residential situations.  Increasing the 
> breaker will create a fire hazard.  Whether that circuit is sufficient 
> depends on the length of the run as well as the size of the wire. Smaller 
> wire and longer runs will have more voltage drop which is not good.  Others 
> on this reflector can give you more detail on this.
> 
> 
> The Alinco should do OK for the K3S, KAT500, and P3. It doesn’t power 
> anything in the KPA500.
> 
> David K0LUM
> 
>> On Jun 13, 2018, at 10:02 PM, Michael Gillen via Elecraft 
>>  wrote:
>> 
>> Kind of a dumb question however here goes:
>> 
>> I got my K3S a short while ago and now I want to add the KPA500 and KAT500 
>> to it however it just now occurred to me that I should check how much juice 
>> I need to power that thing!
>> 
>> I’m currently using an Alinco DM-330MV which I believe puts out 30A 
>> continuous however its probably plugged into one the house 15A lines.
>> 
>> So my questions are:
>> 
>> 1) Will 15A house line supply enough juice for the K3S, KPA500, KAT500, and 
>> in the future a P3 Panadaper?
>> 
>> 2) If not can I get away with replacing the breaker with a 20A breaker? 30A?
>> 
>> 3) Will the Alinco be big enough or should I upgrade that as well?
>> 
>> 
>> Thanks guys,
>> Michael
>> 
>> __
>> Elecraft mailing list
>> Home: http://mailman.qth.net/mailman/listinfo/elecraft
>> Help: http://mailman.qth.net/mmfaq.htm
>> Post: mailto:Elecraft@mailman.qth.net
>> 
>> This list hosted by: http://www.qsl.net
>> Please help support this email list: http://www.qsl.net/donate.html
>> Message delivered to radio...@mchsi.com
> 

__
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:Elecraft@mailman.qth.net

This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html
Message delivered to arch...@mail-archive.com

Re: [Elecraft] power requirements for a K3S, KPA500, KAT500, P3?

2018-06-13 Thread David Christ
DO NOT change the breaker


I am concerned about your so blithely talking about just changing the breaker.  
The breaker is there to protect the wire and is sized according to the wire.  
Do not increase the size of the breaker without verifying what the wire gauge 
is.  Quite likely if the breaker is now 15 amp the wire is probably #14.  This 
is common in residential situations.  Increasing the breaker will create a fire 
hazard.  Whether that circuit is sufficient depends on the length of the run as 
well as the size of the wire. Smaller wire and longer runs will have more 
voltage drop which is not good.  Others on this reflector can give you more 
detail on this.


The Alinco should do OK for the K3S, KAT500, and P3. It doesn’t power anything 
in the KPA500.

David K0LUM

> On Jun 13, 2018, at 10:02 PM, Michael Gillen via Elecraft 
>  wrote:
> 
> Kind of a dumb question however here goes:
> 
> I got my K3S a short while ago and now I want to add the KPA500 and KAT500 to 
> it however it just now occurred to me that I should check how much juice I 
> need to power that thing!
> 
> I’m currently using an Alinco DM-330MV which I believe puts out 30A 
> continuous however its probably plugged into one the house 15A lines.
> 
> So my questions are:
> 
> 1) Will 15A house line supply enough juice for the K3S, KPA500, KAT500, and 
> in the future a P3 Panadaper?
> 
> 2) If not can I get away with replacing the breaker with a 20A breaker? 30A?
> 
> 3) Will the Alinco be big enough or should I upgrade that as well?
> 
> 
> Thanks guys,
> Michael
> 
> __
> Elecraft mailing list
> Home: http://mailman.qth.net/mailman/listinfo/elecraft
> Help: http://mailman.qth.net/mmfaq.htm
> Post: mailto:Elecraft@mailman.qth.net
> 
> This list hosted by: http://www.qsl.net
> Please help support this email list: http://www.qsl.net/donate.html
> Message delivered to radio...@mchsi.com

__
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:Elecraft@mailman.qth.net

This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html
Message delivered to arch...@mail-archive.com

Re: [Elecraft] power requirements for a K3S, KPA500, KAT500, P3?

2018-06-13 Thread Jim Brown

On 6/13/2018 8:02 PM, Michael Gillen via Elecraft wrote:

  Will 15A house line supply enough juice for the K3S, KPA500, KAT500, and in 
the future a P3 Panadaper?


Yes.


2) If not can I get away with replacing the breaker with a 20A breaker?


Only if all the wiring on that breaker is #12 or larger.


  30A?


Only if all the wiring on that breaker is #10.  These are electrical 
safety code requirements, which carry the force of law.



3) Will the Alinco be big enough


Yes


or should I upgrade that as well?


 No.

73, Jim K9YC


__
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:Elecraft@mailman.qth.net

This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html
Message delivered to arch...@mail-archive.com

[Elecraft] power requirements for a K3S, KPA500, KAT500, P3?

2018-06-13 Thread Michael Gillen via Elecraft
Kind of a dumb question however here goes:

I got my K3S a short while ago and now I want to add the KPA500 and KAT500 to 
it however it just now occurred to me that I should check how much juice I need 
to power that thing!

I’m currently using an Alinco DM-330MV which I believe puts out 30A continuous 
however its probably plugged into one the house 15A lines.

So my questions are:

1) Will 15A house line supply enough juice for the K3S, KPA500, KAT500, and in 
the future a P3 Panadaper?

2) If not can I get away with replacing the breaker with a 20A breaker? 30A?

3) Will the Alinco be big enough or should I upgrade that as well?


Thanks guys,
Michael

__
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:Elecraft@mailman.qth.net

This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html
Message delivered to arch...@mail-archive.com