RE: HiPot testing of DC mains powered products

2001-11-13 Thread Peter Tarver

Rich -

While I can't speak for Chris, there are a few reasons to
perform production line ESTs on 48V dc mains powered
equipment.

1) in 48Vdc SMPSs, the voltages present on transformer
insulation are typically in excess of ELV limits.  If the
power supply has had fault testing performed that clearly
indicates hazardous voltages are not presented at the
outputs, there may be reason to waive an input-to-output
production line EST.

2) unless the design and documentation explicitly address
electrical bonding of the chassis to the battery return
terminal in the equipment (refer to CSA/UL60950, Annex NAB
and related information in Annex NAA), demonstration of
electrical separation of battery return and chassis
(protective earthing) is necessary.

3) quality control issues

4) customer requirements



Regards,

Peter L. Tarver, PE
Product Safety Manager
Sanmina Homologation Services
peter.tar...@sanmina.com


 From: Rich Nute

 Hi Chris:


 I wonder why you need to hi-pot test a SELV-powered
 product?  (I presume your external 48-volt dc source
 is SELV.)

 We make products intended for connection to an external
 dc source (SELV).  We have never been required to
 perform a hi-pot test on such products.

 The production-line hi-pot is a test that tests the
 insulation between the two input leads (in parallel)
 and the chassis (or accessible metal).  The insulation
 provides protection against electric shock.  Since no
 electric shock is possible from 48 V dc (according to
 the standards), then there is no requirement for the
 insulation to withstand the transient overvoltages (if
 any) on the dc mains.  Indeed, if the insulation were
 to fail, there would be no electric shock.


 Best regards,
 Rich



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


RE: HiPot testing of DC mains powered products

2001-11-13 Thread Gary McInturff

I agree with Rich. Appendix D of your UL report or procedure has
Exceptions to the standard dielectric and ground continuity tests done by
the manufacturer. In my case I have 4 products which do not require either
of these tests. I'd take a quick glance in your procedure.
Gary

-Original Message-
From: Rich Nute [mailto:ri...@sdd.hp.com]
Sent: Monday, November 12, 2001 4:34 PM
To: chris.maxw...@nettest.com
Cc: emc-p...@majordomo.ieee.org
Subject: Re: HiPot testing of DC mains powered products






Hi Chris:


I wonder why you need to hi-pot test a SELV-powered
product?  (I presume your external 48-volt dc source
is SELV.)

We make products intended for connection to an external
dc source (SELV).  We have never been required to 
perform a hi-pot test on such products.

The production-line hi-pot is a test that tests the 
insulation between the two input leads (in parallel) 
and the chassis (or accessible metal).  The insulation 
provides protection against electric shock.  Since no 
electric shock is possible from 48 V dc (according to 
the standards), then there is no requirement for the 
insulation to withstand the transient overvoltages (if 
any) on the dc mains.  Indeed, if the insulation were 
to fail, there would be no electric shock.


Best regards,
Rich




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old
messages are imported into the new server.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


RE: Define Continuous DC Voltage

2001-11-13 Thread Gregg Kervill

There was also a very good (but short) article by Tektronix in the 70's
called The Lethal Current.

It concluded that currents between 100 mA and 3 Amps were more lethal that
currents of more than 3 Amps because those high currents tended to 'restart'
the heart.


I think I will try not the check that out.


Gregg

PLEASE NOTE NEW NUMBERS
P.O. Box 310, Reedville,
Virginia 22539  USA

Phone: (804) 453-3141
Fax: (804) 453-9039
Web: www.test4safety.com



-Original Message-
From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of
jrbar...@lexmark.com
Sent: Monday, November 12, 2001 8:16 AM
To: 'EMC-PSTC Discussion Group'
Subject: RE: Define Continuous DC Voltage





From my reading on the subject, EN 60950 has different Safety Extra-Low
Voltage
(SELV) limits for alternating current (AC) and direct current (DC) because
the
human body reacts to them differently.  AC makes your muscles contract, so
you
tend to hang onto the source of the electric shock.  DC makes you push away,
removing contact, but you may fall or otherwise hurt yourself as you jerk
away
from the source of the shock.  I have heard hams (amateur radio operators)
tell
of picking themselves off the floor, clear across the room, after accidently
touching the plate supply of a tube radio.

I found an article in Electronics magazine, published between 1940 and 1945
(I
can't find the article right now), on a study that was done on let-go
current.
In this study the subjects (something like 100 young males) would grab a
1/4
wire with one hand, and put their other hand on a copper or brass plate.
The
experimenter would apply a voltage between the wire and the plate, giving
the
subject a shock.  Then the subject would try to let go of the wire.  If they
couldn't, they could open the circuit just by lifting their hand from the
plate.
If the subject could let go of the wire, the experimenter would increase the
voltage and they would try the experiment again.  As I recall the
experiments
were done mainly at 50 and 60Hz, with some done at DC and low frequencies,
and
others up to 10kHz.

The results of the study were that let-go current was lowest in the 40-100Hz
range, and ranged from 15mA up to about 100mA.   (I got the impression that
some
of the young men were trying to show how macho they were...)  The
let-go current increased as the frequency increased above 100Hz, or
decreased
below 40Hz.  For DC the subjects had trouble trying to hold onto the wire,
and
instead of a shock they felt a heating effect.

I have not seen any studies on how much AC superimposed on DC changes the
let-go
effect to a hang-on effect, and I don't plan to find out for myself if I
don't
have to...

  John Barnes  Advisory Engineer
  Lexmark International




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old
messages are imported into the new server.


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


RE: 80/80 rule for euro compliance?

2001-11-13 Thread Chris Maxwell

I have seen this in

Section 6 of EN 55011:1990

Section 8 of EN 55022:1995

I'm not sure if there are any plans to remove these references from
newer versions of these standards.

Best regards,

Chris

 -Original Message-
 From: David Heald [SMTP:davehe...@mediaone.net]
 Sent: Monday, November 12, 2001 3:59 PM
 To:   emc-p...@majordomo.ieee.org
 Subject:  80/80 rule for euro compliance?
 
 
 Greetings all,
   I remember hearing somewhere ( it seems that I found the answer
 somewhere but I can't remember) that there is a stipulation for
 European
 compliance that one should have 80% certainty that 80% of one's
 products
 are compliant.  I have no idea where this idea originally came from or
 what standards it may apply to. 
 
 Can anyone out there help me out?
 
 Dave
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
 
 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc
 
 For help, send mail to the list administrators:
  Michael Garretson:pstc_ad...@garretson.org
  Dave Healddavehe...@mediaone.net
 
 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org
 
 All emc-pstc postings are archived and searchable on the web at:
 No longer online until our new server is brought online and the
 old messages are imported into the new server.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


CISPR 11 and CISPR 22

2001-11-13 Thread Kim Boll Jensen
Hi all

Could somebody please send me the basic requirements for CISPR 11
emission limits I need to compare with CISPR 22 for a non radio product
under EN60601-2.

Best regards,

Kim Boll Jensen
Bolls Raadgivning
Consultancy in world wide approvals
attachment: kimboll.vcf

Re: 80/80 rule for euro compliance?

2001-11-13 Thread John Woodgate

I read in !emc-pstc that Dan Irish - Sun BOS Hardware
dan.ir...@sun.com wrote (in 2000.RAA05232@st-
ides.East.Sun.COM) about '80/80 rule for euro compliance?', on Mon, 12
Nov 2001:
As I recall, this used to be in CISPR16 ...Radio Interference Measuring
Apparatus and Methods, section 9.
In later versions of CISPR16, this requirement was mysteriously

Not mysteriously, but not everyone in the world was told about it; that
didn't seem necessary. (;-)

deleted from CISPR16, and section 9 became Reserved for future use.
I have the old version of CISPR16 buried in my paper files
somewhere. 

CISPR 16 is a Basic Standard, covering methods of measurement and other
product-independent matters. It is now in three Parts, CISPR16-1, -2 and
-3. The subject is now dealt with in much greater detail in CISPR16-3.

For ITE, CISPR16 was obsoleted by CISPR22.

Not at all. CISPR 22 is a Product Family Standard, that refers to
CISPR16 Parts where necessary.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Eat mink and be dreary!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: 80/80 rule for euro compliance?

2001-11-13 Thread John Woodgate

I read in !emc-pstc that David Heald davehe...@mediaone.net wrote (in
3bf037f8.c93b8...@mediaone.net) about '80/80 rule for euro
compliance?', on Mon, 12 Nov 2001:
 I remember hearing somewhere ( it seems that I found the answer
somewhere but I can't remember) that there is a stipulation for European
compliance that one should have 80% certainty that 80% of one's products
are compliant.  I have no idea where this idea originally came from or
what standards it may apply to. 

Can anyone out there help me out?

It's not peculiar to Europe, it's in many CISPR *international*
standards, and thus appears in the corresponding (but not necessarily
identical) EN 550xx series of European standards. 
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Eat mink and be dreary!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: [Fwd: User Warning Signal Words]

2001-11-13 Thread John Woodgate

I read in !emc-pstc that Rich Nute ri...@sdd.hp.com wrote (in
20030122.raa03...@epgc196.sdd.hp.com) about '[Fwd: User Warning
Signal Words]', on Mon, 12 Nov 2001:

I feel the authors of these definitions neither consulted
a dictionary nor the users of warnings.  

I'm sure that you are right, but what is the alternative to using
existing words but with special definitions that make their meanings
more precise? If you solve this one, you clear up a significant problem
in standards-writing.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Eat mink and be dreary!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: CLASS 11(DOUBLE INSULATED) 2/3-CORE CABLE

2001-11-13 Thread John Woodgate

I read in !emc-pstc that Rich Nute ri...@sdd.hp.com wrote (in
20022357.paa03...@epgc196.sdd.hp.com) about 'CLASS 11(DOUBLE
INSULATED)  2/3-CORE CABLE', on Mon, 12 Nov 2001:



Hi John:


   No; France and Norway have 'IT' systems, in which grounding is only to
   prevent static charge build-up; the neutral is grounded through an
   impedance at the sub-station. AIUI, this is used in mountainous
   districts where ground paths are long and of low conductivity. There are
   significant differences between the French and Norwegian systems.

Can you please explain what those differences are?


I don't know at present, but I may be able to find out next week. The
explanation I have seen was said by some people in EDF to be wrong, and
they should know!
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Eat mink and be dreary!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: Safety Critical etc - the future

2001-11-13 Thread John Woodgate

I read in !emc-pstc that Rich Nute ri...@sdd.hp.com wrote (in
20022339.paa03...@epgc196.sdd.hp.com) about 'Safety Critical etc
- the future', on Mon, 12 Nov 2001:
   A supply transformer of a not grounded SELV is a safety critical component.
   A supply transformer of a grounded SELV is a safety related component.

For me, whether or not the SELV output of a safety-isolating
transformer is grounded is irrelevant.  Two safeguards must
be interposed between the mains and the SELV.  In some 
situations, the grounding of the SELV output winding can
serve as the required grounded barrier (a supplemental 
safeguard to the Basic insulation, the principal safeguard).

This could be confusing. SELV is usually NOT permitted to be grounded.
The term 'Protected Extra-Low Voltage' (PELV) is now used for a source
which is grounded but meets all the other requirements of SELV. 

In many fault conditions, PELV is much safer than SELV! A fault on an
SELV system can persist undetected for a very long time, until a second
fault, or intervention with the system, *quite unrelated*, occurs, and a
very hazardous situation then arises. The earthing of PELV ensures, in
almost all cases, that the first fault is not undetected and does not
persist.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Eat mink and be dreary!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: [Fwd: User Warning Signal Words]

2001-11-13 Thread Rich Nute




   According to ANSI Z35.4 the following definitions are provided:
   
   
   
   DANGER - Indicates an imminently hazardous situation which, if not
   avoided will result in death or serious injury. This signal word is to
   be limited to the most extreme situations.
   
   WARNING - Indicates a potentially hazardous situation which, if not
   avoided may result in minor or moderate injury. It may also be used to
   alert against unsafe practices.

   CAUTION - Indicates a potentially hazardous situation which, if not
   avoided may result in minor or moderate injury. It may also be used to
   alert against unsafe practices. 
   
   Note: DANGER or WARNING should not be considered for property damage
   accidents unless personal injury risk appropriate to these levels is
   also involved. CAUTION is permitted for property-damage-only accidents.

I feel the authors of these definitions neither consulted
a dictionary nor the users of warnings.  According to my 
Webster's Collegiate Dictionary:

warn (verb):  1a: to give notice to beforehand, especially
of danger or evil; 1b: to give admonishing advice to; 1c:
to call to one's attention; 2: to order to go or stay away:
to give a warning.

So, all of the ANSI definitions serve to warn.

warning (noun):  1: the act of warning: the state of being 
warned; 2: something that warns or serves to warn, especially
a notice or bulletin that alerts the public that a tornado
has been reported in the immediate vicinity or that the 
approach of a severe storm is imminent.

So, all of the ANSI definitions are warnings.

danger (noun):  1:  (archaic);  2:  (obsolete); 3:  exposure
or liability to injury, pain, harm, or loss a place where
children could play without danger;  4:  a case or cause of 
danger the dangers of mining.

So, the word danger refers to a thing.  

caution (noun):  1: warning, admonishment; 2: precaution; 3:
prudent forethought to minimize risk; 4: one that astonishes
or commands attention some shoes you see these days are a 
caution.

So, the word caution is defined as a warning.

The so-called signal words are fabrications unrelated to the
definitions of the words.  This is a shame because it dilutes the
power of the words.

In my experience, users do not understand the subtle differences
intended by the signal words.


Best regards,
Rich


Richard Nute
Hewlett-Packard Company
San Diego





---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


RE: RF Immunity Testing to 50V

2001-11-13 Thread Price, Ed




-Original Message-
From: Kevin Harris [mailto:harr...@dscltd.com]
Sent: Monday, November 12, 2001 9:18 AM
To: EMC-PSTC (E-mail)
Subject: RF Immunity Testing to 50V



Hello Group,

Does anybody know of a test lab being able to test small 
objects (less than
15cm in any axis) up to 50V (with 80% AM 1KHz tone) from 80MHz to 1GHz

Best Regards,


Kevin Harris
Manager, Approval Services
Digital Security Controls
3301 Langstaff Road
Concord, Ontario
CANADA
L4K 4L2

Tel: +1 905 760 3000 Ext. 2378
Fax +1 905 760 3020

Email: harr...@dscltd.com mailto:harr...@dscltd.com 


Kevin:

CDS can easily test to your needs (we can do +200 V/M, any modulation, 10
kHz to 18 GHz). Email me with details  I'll get you a quote. I'm desperate
to not have to get a part-time job this year as a mall Santa.

Ed


Ed Price
ed.pr...@cubic.com
Electromagnetic Compatibility Lab
Cubic Defense Systems
San Diego, CA  USA
858-505-2780  (Voice)
858-505-1583  (Fax)
Military  Avionics EMC Services Is Our Specialty
Shake-Bake-Shock - Metrology - Reliability Analysis

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: HiPot testing of DC mains powered products

2001-11-13 Thread Rich Nute




Hi Chris:


I wonder why you need to hi-pot test a SELV-powered
product?  (I presume your external 48-volt dc source
is SELV.)

We make products intended for connection to an external
dc source (SELV).  We have never been required to 
perform a hi-pot test on such products.

The production-line hi-pot is a test that tests the 
insulation between the two input leads (in parallel) 
and the chassis (or accessible metal).  The insulation 
provides protection against electric shock.  Since no 
electric shock is possible from 48 V dc (according to 
the standards), then there is no requirement for the 
insulation to withstand the transient overvoltages (if 
any) on the dc mains.  Indeed, if the insulation were 
to fail, there would be no electric shock.


Best regards,
Rich




---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


RE: 80/80 rule for euro compliance?

2001-11-13 Thread jestuckey

It is implied by the statistical analysis of a sample population during
formal conformity assessment.  Reference EN 55022:1998 Clause 7 (7.2.3)

Regards,

JOHN E. STUCKEY
EMC Engineer
NCT EMC 002047

Micron Technology, Inc.
Quality and Reliability Assurance
EMC Group
M/S 941
3176 S. Denver Way
Boise, Idaho 83705
PH: (208) 363.5313
FX: (208) 333.7302
jestuc...@micron.com



-Original Message-
From: Dan Irish - Sun BOS Hardware [mailto:dan.ir...@sun.com]
Sent: Monday, November 12, 2001 15:24
To: emc-p...@majordomo.ieee.org
Subject: Re: 80/80 rule for euro compliance?



Dave,

As I recall, this used to be in CISPR16 ...Radio Interference Measuring
Apparatus and Methods, section 9.
In later versions of CISPR16, this requirement was mysteriously
deleted from CISPR16, and section 9 became Reserved for future use.
I have the old version of CISPR16 buried in my paper files
somewhere. For ITE, CISPR16 was obsoleted by CISPR22.

The VCCI audit requirements per V-3/2000.04 were taken almost
verbatim from this.

Dan

 Date: Mon, 12 Nov 2001 15:58:32 -0500
 From: David Heald davehe...@mediaone.net
 X-Accept-Language: en
 MIME-Version: 1.0
 To: emc-p...@majordomo.ieee.org emc-p...@majordomo.ieee.org
 Subject: 80/80 rule for euro compliance?
 Content-Transfer-Encoding: 7bit
 X-Resent-To: Multiple Recipients emc-p...@majordomo.ieee.org
 X-Listname: emc-pstc
 X-Info: Help requests to  emc-pstc-requ...@majordomo.ieee.org
 X-Info: [Un]Subscribe requests to  majord...@majordomo.ieee.org
 X-Moderator-Address: emc-pstc-appro...@majordomo.ieee.org
 
 
 Greetings all,
   I remember hearing somewhere ( it seems that I found the answer
 somewhere but I can't remember) that there is a stipulation for European
 compliance that one should have 80% certainty that 80% of one's products
 are compliant.  I have no idea where this idea originally came from or
 what standards it may apply to. 
 
 Can anyone out there help me out?
 
 Dave
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
 
 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc
 
 For help, send mail to the list administrators:
  Michael Garretson:pstc_ad...@garretson.org
  Dave Healddavehe...@mediaone.net
 
 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org
 
 All emc-pstc postings are archived and searchable on the web at:
 No longer online until our new server is brought online and the old 
messages are imported into the new server.


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old
messages are imported into the new server.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: CLASS 11(DOUBLE INSULATED) 2/3-CORE CABLE

2001-11-13 Thread Rich Nute




Hi John:


   No; France and Norway have 'IT' systems, in which grounding is only to
   prevent static charge build-up; the neutral is grounded through an
   impedance at the sub-station. AIUI, this is used in mountainous
   districts where ground paths are long and of low conductivity. There are
   significant differences between the French and Norwegian systems.

Can you please explain what those differences are?


Thanks, and best regards,
Rich


Richard Nute
Hewlett-Packard Company
San Diego






---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: Group:

2001-11-13 Thread John Woodgate

I read in !emc-pstc that Donald McElheran don...@hq.rossvideo.com
wrote (in 808E4747B94FD511BDB0005004A1DE7F0521E3@HQ-EXCHANGE) about
'Group:', on Mon, 12 Nov 2001:
The product being supplied via an external low voltage ( 20V DC @ 6A )

Do you mean 'less than 20 V'? The symbols  and  are often confused.

appears to technically fall outside the scope of both the European LVD
directive and North American NRTL certification requirements for products
directly connected to the public mains. 

It is likely that the LVD will be revised within the foreseeable future
to have no lower limit of voltage, like the RTTE Directive. 

The product is similar to that of a laptop computer running from an wall
mounted adapter.

Questions have been raised regarding flammability of enclosure materials
which will have a significant impact of the products cost. 

Could any member of the forum who may have had to address similar situation
share there thoughts?

At this point it would appear that provided we ensure the external power
supply conforms to any applicable safety standards in which the equipment is
to be marketed that their is no legislated (hate to use this term)
requirements to safety certify the table top product.

The input power is up to 120 W, which is quite enough to cause a
significant fire hazard. Also, are any voltages higher than 20 V
generated inside the box?

You would be well-advised to apply the appropriate safety standard
(IEC/EN60950/UL1950?), even if according to the letter of the law you
may not need to.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Eat mink and be dreary!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: Radio Module, full product re-test?

2001-11-13 Thread Paolo Gemma

Hi Alex
If you integrate the new radio module without change anything on the radio 
module I suggest to make no test on the product.

Ciao
Paolo
At 13:36 11/12/01 +, Alex McNeil wrote:


Hi Group,

Situation
I have an alternate Small Radio Device (SRD) Module, previous one obsoleted,
in a product. This new alternate Radio Module has ETS 300 683 (EMC) and EN
300 220-1 (Radio) approvals and DoC supplied by the manufacturer. The
product was already approved to these standards with the obsoleted module,
plus EN55022 and EN55024.

To Show Due Dilligence (CE Mark)
What is the minimum I need to do for EMC re-verification, if any?


Kind Regards
Alex McNeil
Principal Engineer
Tel: +44 (0)131 479 8375
Fax: +44 (0)131 479 8321
email: alex.mcn...@ingenicofortronic.com

 -Original Message-
From:   jim.hulb...@pb.com [mailto:jim.hulb...@pb.com]
Sent:   Friday, November 09, 2001 7:19 PM
To: emc-p...@ieee.org
Subject:CISPR 22:1997


The European Union has postponed mandatory compliance with CISPR 22:1997
(EN 55022:1998) until 1 August 2003.  This version of the standard includes
the new requirement for conducted emissions on cables connected to
telecommunications ports.

Have other countries that require compliance with CISPR 22 (or some
variation thereof) also postponed implementation of the 1997 version?  My
immediate concern is Australia.

Any information members of this group can share is greatly appreciated.

Jim Hulbert
Senior Engineer - EMC
Pitney Bowes


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old
messages are imported into the new server.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.



--
Paolo Gemma
Siemens Information and Communication Network spa
Microwave Networks MW RD NSA EMC
SS Padana sup. KM 158 20060 Cassina de'Pecchi (MI) Italy
phone +39 02 9526 6587fax +39 02 9526 6203
mobile +39 348 3690185
e-mail paolo.ge...@icn.siemens.it

--



Re: Define Continuous DC Voltage

2001-11-13 Thread Rich Nute




Hi Dan:


   Does anyone know what voltage is used in electric chairs?  Just Curious.

I'm sorry you asked.  The electric chair is one of
the more barbarous methods of execution.

The voltage is a function of time, and varies with
the execution authority.  The voltage is in the range
of 1000-2000 volts, sometimes more, sometimes less.

For more than you would ever want to know, including
the voltage specs, see:

http://www.theelectricchair.com/

You will need to use search the site to find voltage
and other details.  Be sure to read biology of 
electrocution.  Also check out the botched 
electrocutions.

Here are other sites I found as the result of a web
search.  The descriptions and pictures are gruesome
and are not recommended.

http://www.geocities.com/CapitolHill/6142/chair.html
http://www.albany.edu/~brandon/sparky.html
http://hypertextbook.com/facts/NancyRyan.shtml
http://hypertextbook.com/facts/AprilDunetz.shtml
http://members.aol.com/karlkeys/chair.htm
http://www.pdimages.com/X0029.html-ssi
http://www.suburbanchicagonews.com/joliet/prisons/chair2.html
http://noop.rotten.com/chair/
http://library.thinkquest.org/23685/data/chair.html
http://www.capitalcentury.com/1907.html
http://www.fcc.state.fl.us/fcc/reports/methods/emappa.html
http://www.hatchoo.com/deathrow/
http://www.ariel.com/au/jokes/The_Electric_Chair.html
http://northstargallery.com/pages/Electric01.htm

This site has some body impedance data taken during 
several executions.  The descriptions and arguments
are explicit and gruesome.

http://www.dc.state.fl.us/oth/deathrow/drorder.html

Calculate the power (E x I) dissipated in the body.


Regards,
Rich












---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: Define Continuous DC Voltage

2001-11-13 Thread Ken Javor

Whoops!!!  I was thinking wheel chair and on second thought I realized what
you were thinking of was a means of intentional electrocution and execution.
My mistake!

--
From: Dan Kinney (A) dan.kin...@heapg.com
To: Rich Nute ri...@sdd.hp.com, gkerv...@eu-link.com
Cc: jrbar...@lexmark.com, emc-p...@majordomo.ieee.org
Subject: RE: Define Continuous DC Voltage
Date: Tue, Nov 13, 2001, 3:56 PM



 Does anyone know what voltage is used in electric chairs?  Just Curious.
 Dan Kinney
 Horner APG
 Indianapolis

 -Original Message-
 From: Rich Nute [SMTP:ri...@sdd.hp.com]
 Sent: Tuesday, November 13, 2001 2:08 PM
 To: gkerv...@eu-link.com
 Cc: jrbar...@lexmark.com; emc-p...@majordomo.ieee.org
 Subject: Re: Define Continuous DC Voltage





 Hi Gregg:


There was also a very good (but short) article by Tektronix in the
 70's
called The Lethal Current.
 
It concluded that currents between 100 mA and 3 Amps were more lethal
 that
currents of more than 3 Amps because those high currents tended to
 'restart'
the heart.

 Hmm.  Having been the manager of product safety at Tektronix in
 the '70's, I don't recall such an article.  At least not by that
 name.

 Electric energy causes various injuries to the body depending
 on the magnitude of the energy.  Only two of the injuries can
 lead to a fatality.

 The two injuries are fibrillation of the heart, and overheating
 of internal organs, especially the liver.

 Fibrillation is caused by ac current in the range of 50 mA to
 500 mA (external connections) where the current pathway through
 the body includes the chest (and the heart).  Above 500 mA,
 fibrillation is not a likely consequence.  (And, I believe I
 am correct in asserting that dc cannot cause fibrillation.)

 Overheating of internal organs is a function of power dissipated
 in the body, where the body impedance can be taken as 1000 ohms.
 The power required depends on the time of contact.  Electric
 utility linemen are subject to such injury.  Consider 1 ampere
 through 1000 ohms is 1000 watts!  (The electric chair kills by
 over-heating the internal organs, not by fibrillation.)

 So, Gregg's statement that there is both a lower and upper limit
 for fibrillation is correct (although I do not agree with Gregg's
 values).


 Best regards,
 Rich






 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Michael Garretson:pstc_ad...@garretson.org
  Dave Healddavehe...@mediaone.net

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

 All emc-pstc postings are archived and searchable on the web at:
 No longer online until our new server is brought online and the old
 messages are imported into the new server.

 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Michael Garretson:pstc_ad...@garretson.org
  Dave Healddavehe...@mediaone.net

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

 All emc-pstc postings are archived and searchable on the web at:
 No longer online until our new server is brought online and the old
 messages are imported into the new server.
 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: Define Continuous DC Voltage

2001-11-13 Thread Ken Javor

I know of at least one that runs off a 12 Volt battery.  I think it is a 
gel-cell but I KNOW it charges off an ordinary 12 Volt charger and it is
supposed to be trickled charged nightly, so it is like a lead-acid in that
it likes to be constantly charged and doesn't have memory.


--
From: Dan Kinney (A) dan.kin...@heapg.com
To: Rich Nute ri...@sdd.hp.com, gkerv...@eu-link.com
Cc: jrbar...@lexmark.com, emc-p...@majordomo.ieee.org
Subject: RE: Define Continuous DC Voltage
Date: Tue, Nov 13, 2001, 3:56 PM



 Does anyone know what voltage is used in electric chairs?  Just Curious.
 Dan Kinney
 Horner APG
 Indianapolis

 -Original Message-
 From: Rich Nute [SMTP:ri...@sdd.hp.com]
 Sent: Tuesday, November 13, 2001 2:08 PM
 To: gkerv...@eu-link.com
 Cc: jrbar...@lexmark.com; emc-p...@majordomo.ieee.org
 Subject: Re: Define Continuous DC Voltage





 Hi Gregg:


There was also a very good (but short) article by Tektronix in the
 70's
called The Lethal Current.
 
It concluded that currents between 100 mA and 3 Amps were more lethal
 that
currents of more than 3 Amps because those high currents tended to
 'restart'
the heart.

 Hmm.  Having been the manager of product safety at Tektronix in
 the '70's, I don't recall such an article.  At least not by that
 name.

 Electric energy causes various injuries to the body depending
 on the magnitude of the energy.  Only two of the injuries can
 lead to a fatality.

 The two injuries are fibrillation of the heart, and overheating
 of internal organs, especially the liver.

 Fibrillation is caused by ac current in the range of 50 mA to
 500 mA (external connections) where the current pathway through
 the body includes the chest (and the heart).  Above 500 mA,
 fibrillation is not a likely consequence.  (And, I believe I
 am correct in asserting that dc cannot cause fibrillation.)

 Overheating of internal organs is a function of power dissipated
 in the body, where the body impedance can be taken as 1000 ohms.
 The power required depends on the time of contact.  Electric
 utility linemen are subject to such injury.  Consider 1 ampere
 through 1000 ohms is 1000 watts!  (The electric chair kills by
 over-heating the internal organs, not by fibrillation.)

 So, Gregg's statement that there is both a lower and upper limit
 for fibrillation is correct (although I do not agree with Gregg's
 values).


 Best regards,
 Rich






 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Michael Garretson:pstc_ad...@garretson.org
  Dave Healddavehe...@mediaone.net

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

 All emc-pstc postings are archived and searchable on the web at:
 No longer online until our new server is brought online and the old
 messages are imported into the new server.

 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Michael Garretson:pstc_ad...@garretson.org
  Dave Healddavehe...@mediaone.net

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

 All emc-pstc postings are archived and searchable on the web at:
 No longer online until our new server is brought online and the old
 messages are imported into the new server.
 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Wiring - Single faults

2001-11-13 Thread k3row
As a military radar systems engineer I deal with various safety issues 
associated with aircraft radar systems.  However, I have recently been looking 
at the safety of some associated benign environment test equipment comprising 
(at least in the context of safety) various simple 230v standard mains power 
commercial components. The connection mechanism for these internal components 
are, in some cases, tight push fit spade terminal type connections. The free 
terminal at the end of the connection wire is insulated with a recessed inner. 
The wire connection to this free spade connector is also covered with a 
heatshrink sleeve which provides additional insulation and containment for the 
wire. Thus if the wire joint somehow breaks, the wire remains insulated and 
held in place. This then provides adequate single fault containment as far as, 
say, wire breakage at the wire joint is concerned.

Here is my very trivial question.

What I can't get clear in my mind is this: If I wish, I can, of course, just 
completely pull the free connector off the component terminal. Is the 
complete disconnection of the spade terminal pair, with the free end now 
hanging loose, regarded as a single fault to be dealt with, or is this regarded 
as too gross to be considered a single fault?

Any advice would be appreciated
 
Regards

Dave Palmer


RE: ULC vs. CUL

2001-11-13 Thread Jim Eichner

Perhaps they can reply if they are monitoring this forum, but I'll give it a
shot...

ULC is Underwriters Laboratories of Canada, and while they do product
approvals, they generally in the past have not done the sort of product
safety work that UL does.  ULC has focussed more on building products for
fire safety - things like fire doors, fire extinguishers, gas burning
appliances, etc.  Their approval mark looks much like the UL listing mark,
but it's ULC, with the C inside the circle.

The CUL mark has the C outside the circle, with the normal UL listing
mark inside the circle, and maybe a US outside the circle as well.  This
mark is used by UL for product safety approvals where it needs to be made
clear whether the requirements used were only US ones (read UL standards),
only Canadian ones (CSA standards), or both.  Normally where it is only the
UL standards, they will just use the normal UL mark without either the C or
the US.  When CSA requirements are included, the C(UL)US mark is used to
make it clear that both country's requirements were met.  If they truly are
approving only to the CSA requirements, the C(UL) mark would be used without
the US.

Regards, 
Jim Eichner, P.Eng. 
Manager, Engineering Services 
Xantrex Technology Inc. 
Mobile Power
web: www.xantrex.com http://www.xantrex.com 
Any opinions expressed are those of my invisible friend, who really
exists. Honest.



Jim Eichner, P.Eng.
Manager, Engineering Services
Xantrex Technology Inc.
Mobile Power
phone:  (604) 422-2546
fax:  (604) 420-1591
e-mail:  jim.eich...@xantrex.com
web: www.xantrex.com 


-Original Message-
From: geor...@lexmark.com [mailto:geor...@lexmark.com]
Sent: Tuesday, November 13, 2001 12:47 PM
To: emc-p...@ieee.org
Subject: Re: ULC vs. CUL





There is a UL mark acceptable for the U.S.
There was a c-UL mark, acceptable to both Canada and the U.S.
The more correct mark from UL for the c-UL mark is now the
c-UL-us mark, i.e. circled UL with small c outside lower left of
circle and small us outside lower right of circle.

I have never heard any of these referred to as a ULC mark.

George Alspaugh




burchj%andovercontrols@interlock.lexmark.com on 11/13/2001 03:18:12 PM

Please respond to burchj%andovercontrols@interlock.lexmark.com

To:   emc-pstc%majordomo.ieee@interlock.lexmark.com
cc:(bcc: George Alspaugh/Lex/Lexmark)
Subject:  ULC vs. CUL

Someone from our UK office is asking if ULC is the same as CUL.  Does anyone
know the difference between these two marks?
Your help is always appreciated.

Thanks,
Joe

Josiah P. Burch
Compliance Engineer II
Andover Controls Corporation
300 Brickstone Square
Andover,Ma 01810
(978)-470-0555  x335
(978)-470-3615  Fax





---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old
messages are imported into the new server.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: ULC vs. CUL

2001-11-13 Thread john . merrill


ULC is Underwriters Laboratories of Canada
CUL is a Listing or classification mark from Underwriters Laboratories Inc.

Note: I have only seen ULC come up in approvals of FIre Detection and
Suppression Equipment.
e.g. Fire Extinguishers etc.





bur...@andovercontrols.com on 11/13/2001 03:18:12 PM

Please respond to bur...@andovercontrols.com

To:   emc-p...@majordomo.ieee.org
cc:(bcc: John Merrill/Aut/Schneider)

Subject:  ULC vs. CUL



Someone from our UK office is asking if ULC is the same as CUL.  Does anyone
know the difference between these two marks?
Your help is always appreciated.

Thanks,
Joe

Josiah P. Burch
Compliance Engineer II
Andover Controls Corporation
300 Brickstone Square
Andover,Ma 01810
(978)-470-0555  x335
(978)-470-3615  Fax


Title: ULC vs. CUL





Someone from our UK office is asking if ULC is the same as CUL. Does anyone know the difference between these two marks?

Your help is always appreciated.


Thanks,
Joe


Josiah P. Burch
Compliance Engineer II
Andover Controls Corporation
300 Brickstone Square
Andover,Ma 01810
(978)-470-0555 x335
(978)-470-3615 Fax





AC, DC definitions and safety

2001-11-13 Thread Ted Rook

my two cents worth

About electric shock:

I'm finding it hard to reconcile some of what I'm reading here with real world 
experience of electric shock, not saying anyone's wrong, just that evidence is 
open to interpretation. 

In particular the statement Dc does not cause either tetanus or fibrillation 
seems to be contrary to common experience, I'm using the meaning of 'tetanus' 
to be paralysis and 'fibrillation' as uncontrolled motion. 


The electrician's rule of thumb when working on domestic wiring was to always 
check the wire is dead, even though you isolated it, in case of bridging or 
faulty connection. The technique used was to brush the exposed conductor 
lightly with the back of the fingers. Any AC present will be noticeable as a 
tingle. DC would cause contraction of hand muscles which would cause the hand 
to withdraw from the conductor. 

The same teacher explained that this precaution saved lives. 
Should the hand be allowed to grasp a live conductor the paralyzing effect of 
DC would be more likely to cause injury, shock or death because the effect of 
the current on the hand muscles when grasping would increase the grip and 
prevent the hand being opened to break the circuit. In this case it is 
precisely tetanus of the body which is dangerous because it interferes with the 
ability to move away from the hazard.

The effect of AC on the hand was not described at the time but the implication 
was that a similar amplitude AC shock would be less hazardous to health.

The basic studies of the nervous system made long ago used crude voltaic cells 
(DC) across muscle tissue to demonstrate muscle action by electrical 
stimulation. Try it yourself and then see if you agree that DC causes neither 
tetanus nor fibrillation!

Definition of DC for test purposes:

I wonder if I've missed the point or not? 
Maybe the rules and instructions were written in good faith with the 
expectation that safety evaluation would include recognition of the intent of 
the designer and the purpose of the circuit. 
When the purpose of the circuit is to handle power (not information) then it 
doesn't matter what the power signal format is, AC or DC, low or high 
frequency, any mark-space ratio. Power is hazardous to health in all its forms. 
It would seem to be in bad faith to ask what the definition of DC is for safety 
purposes if the intent of the evaluation is to promote safety. 




Best Regards

Ted Rook
Crest Audio
201 909 8700 ext 213


---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


RE: ULC vs. CUL

2001-11-13 Thread John Juhasz
Joe,
 
The ULC mark is describe at the following link.
http://www.ulc.ca/marks.asp http://www.ulc.ca/marks.asp 
 
John Juhasz
Fiber Options
Bohemia, NY

-Original Message-
From: bur...@andovercontrols.com [mailto:bur...@andovercontrols.com]
Sent: Tuesday, November 13, 2001 3:18 PM
To: emc-p...@majordomo.ieee.org
Subject: ULC vs. CUL



Someone from our UK office is asking if ULC is the same as CUL.  Does anyone
know the difference between these two marks?

Your help is always appreciated. 

Thanks, 
Joe 

Josiah P. Burch 
Compliance Engineer II 
Andover Controls Corporation 
300 Brickstone Square 
Andover,Ma 01810 
(978)-470-0555  x335 
(978)-470-3615  Fax 



Re: CISPR 11 and CISPR 22

2001-11-13 Thread John Woodgate

I read in !emc-pstc that Kim Boll Jensen kimb...@post7.tele.dk wrote
(in 3bf0ed95.d6886...@post7.tele.dk) about 'CISPR 11 and CISPR 22', on
Tue, 13 Nov 2001:
Could somebody please send me the basic requirements for CISPR 11
emission limits I need to compare with CISPR 22 for a non radio product
under EN60601-2.

This question is really ill-advised. You need to see the WHOLE of a
standard, not just a small part of it. There are notes and cross-
references etc. that can considerably alter the apparent meaning of any
text taken out of context.

You are also quite likely to be given information from an out-of-date
issue of the standard.

Pay up your USD75 or whatever, and have your very own copy to keep. 

NOTE ALSO that you need to look at EN55011 for Europe. While the EN550xx
series are BASED ON the CISPRxx series, they are NOT identical.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Eat mink and be dreary!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


RE: ULC vs. CUL

2001-11-13 Thread Kazimier_Gawrzyjal

Joe,

Some info on the various marks is available at:
http://www.ul.com/mark/index.html
http://www.ulc.ca/marks.asp



Regards,
Kaz Gawrzyjal
Dell Computer Corp.
-Original Message-
From: bur...@andovercontrols.com [mailto:bur...@andovercontrols.com]
Sent: Tuesday, November 13, 2001 2:18 PM
To: emc-p...@majordomo.ieee.org
Subject: ULC vs. CUL


Someone from our UK office is asking if ULC is the same as CUL.  Does anyone
know the difference between these two marks?
Your help is always appreciated. 
Thanks, 
Joe 
Josiah P. Burch 
Compliance Engineer II 
Andover Controls Corporation 
300 Brickstone Square 
Andover,Ma 01810 
(978)-470-0555  x335 
(978)-470-3615  Fax 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: AW: Define Continuous DC Voltage

2001-11-13 Thread John Woodgate

I read in !emc-pstc that Rich Nute ri...@sdd.hp.com wrote (in
20031830.kaa06...@epgc196.sdd.hp.com) about 'AW: Define Continuous
DC Voltage', on Tue, 13 Nov 2001:




Hi John:


   I have never been very keen on the concept of SELV, and I am glad to see
   that others are now recognizing the problems.

Interesting statement.  In contrast, I don't see how we
can get along without SELV.

My concept for SELV is that of ELV so protected from a 
higher voltage such that in the event of a fault, the
SELV does not exceed the ELV limits.

SELV can protect under single fault conditions. BUT, as I tried to
explain, under some conditions, it can allow a single fault *to persist
undetected*, until eventually a second, unrelated fault occurs which
then results in a serious hazard.

My concept for ELV is a voltage source that provides
protection against electric shock by limitation of
voltage.  (ELV is not protected against an increase in
voltage in the event of a fault.)

Well, there is FELV (Functional ELV), which is protected by basic
insulation only.

ELV/SELV are important and extremely useful concepts 
because they allow access to low voltages such as those 
that become accessible during the interconnection of 
various units.  

As one example, consider the camcorder.  SELV allows 
access to the battery charger terminals.  Making these 
terminals inaccessible would increase the complexity and 
cost of a camcorder.

For a single piece of equipment or a small collection very close
together, SELV may be sufficient. But notice that if the double or
reinforced insulation WERE to be faulty, the SELV would be S no longer.
This is simply regarded as an event of acceptably low probability. 

Now consider the case of a video camera and recorder, connected via a
cable carrying video on coax and power at SELV, some distance apart in a
building. Contact between live mains and the video cable shield, due to
an errant nail or screw, puts live mains on the shield, BUT  the fault
may remain undetected until someone tries to disconnect the cable or
open one of the enclosures.

With PELV, this does not happen: the grounding ensures that the
protective device operates. 

I cannot imagine that you truly are not keen on the
concept of SELV.  I can imagine that you are not keen
on the complexity of voltage limits for ELV/SELV.  To
this, I agree.

Well, perhaps I have made it clearer now. My beef with SELV is the ban
on grounding, whereas PELV which is grounded AND double/reinforced
insulated is clearly safer for systems extended in space.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Eat mink and be dreary!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: Define Continuous DC Voltage

2001-11-13 Thread John Woodgate

I read in !emc-pstc that Rich Nute ri...@sdd.hp.com wrote (in
20031730.jaa05...@epgc196.sdd.hp.com) about 'Define Continuous DC
Voltage', on Tue, 13 Nov 2001:
Dc does not cause either tetanus or fibrillation. 

Tetanus is a disease caused by a bacillus. Muscles spasm is tetany.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Eat mink and be dreary!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: [Fwd: User Warning Signal Words]

2001-11-13 Thread Rich Nute



Hi John:


   I feel the authors of these definitions neither consulted
   a dictionary nor the users of warnings.  
   
   I'm sure that you are right, but what is the alternative to using
   existing words but with special definitions that make their meanings
   more precise? If you solve this one, you clear up a significant problem
   in standards-writing.

Well... I guess I didn't make my point.

The ANSI standard defines three classes of signal 
words.  

My point is that the actual signal word is largely 
unimportant to warning (the verb) the user.  The 
signal word calls attention to the warning.  The 
classes of attention-getting simply are not 
recognized by users (and are not consistent with 
dictionary definitions of the words).  

One could just as well use any of the described 
signal words (and maybe some others as already 
suggested here) or various suitable symbols for 
any of the severity classes of warnings.

The degree of detail in specifying classes for
signal words is not warranted.  Delete these 
specific requirements for signal words from the 
standards.  (We are over-standardized in this
case.)  Instead, concentrate on effective content 
of the warning.


Best regards,
Rich





---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: ULC vs. CUL

2001-11-13 Thread georgea



There is a UL mark acceptable for the U.S.
There was a c-UL mark, acceptable to both Canada and the U.S.
The more correct mark from UL for the c-UL mark is now the
c-UL-us mark, i.e. circled UL with small c outside lower left of
circle and small us outside lower right of circle.

I have never heard any of these referred to as a ULC mark.

George Alspaugh




burchj%andovercontrols@interlock.lexmark.com on 11/13/2001 03:18:12 PM

Please respond to burchj%andovercontrols@interlock.lexmark.com

To:   emc-pstc%majordomo.ieee@interlock.lexmark.com
cc:(bcc: George Alspaugh/Lex/Lexmark)
Subject:  ULC vs. CUL

Someone from our UK office is asking if ULC is the same as CUL.  Does anyone
know the difference between these two marks?
Your help is always appreciated.

Thanks,
Joe

Josiah P. Burch
Compliance Engineer II
Andover Controls Corporation
300 Brickstone Square
Andover,Ma 01810
(978)-470-0555  x335
(978)-470-3615  Fax





---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


ULC vs. CUL

2001-11-13 Thread BurchJ
Someone from our UK office is asking if ULC is the same as CUL.  Does anyone 
know the difference between these two marks?
Your help is always appreciated.

Thanks,
Joe

Josiah P. Burch
Compliance Engineer II
Andover Controls Corporation
300 Brickstone Square
Andover,Ma 01810
(978)-470-0555  x335
(978)-470-3615  Fax



Re: Define Continuous DC Voltage

2001-11-13 Thread Rich Nute




Hi Gregg:


   There was also a very good (but short) article by Tektronix in the 70's
   called The Lethal Current.
   
   It concluded that currents between 100 mA and 3 Amps were more lethal that
   currents of more than 3 Amps because those high currents tended to 'restart'
   the heart.

Hmm.  Having been the manager of product safety at Tektronix in 
the '70's, I don't recall such an article.  At least not by that
name.

Electric energy causes various injuries to the body depending 
on the magnitude of the energy.  Only two of the injuries can 
lead to a fatality.

The two injuries are fibrillation of the heart, and overheating 
of internal organs, especially the liver.

Fibrillation is caused by ac current in the range of 50 mA to
500 mA (external connections) where the current pathway through 
the body includes the chest (and the heart).  Above 500 mA, 
fibrillation is not a likely consequence.  (And, I believe I
am correct in asserting that dc cannot cause fibrillation.)

Overheating of internal organs is a function of power dissipated
in the body, where the body impedance can be taken as 1000 ohms.
The power required depends on the time of contact.  Electric
utility linemen are subject to such injury.  Consider 1 ampere
through 1000 ohms is 1000 watts!  (The electric chair kills by
over-heating the internal organs, not by fibrillation.)

So, Gregg's statement that there is both a lower and upper limit 
for fibrillation is correct (although I do not agree with Gregg's 
values).


Best regards,
Rich






---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: RF Immunity Testing to 50V

2001-11-13 Thread Lfresearch

Hi Kevin,

we too can achieve high fields, currently about 80 v/m is our limit. Again, 
you may want to talk more offline

Best regards,

Derek.

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: Define Continuous DC Voltage

2001-11-13 Thread Rich Nute




Hi Chris:


I'll attempt to answer the question as to the effect of
ac and dc current on the body (the hazard).

The discussion is in regard to three waveforms:

1)  ac sinusoidal -- 50-60 Hz.
2)  dc
3)  dc interrupted (equal on and off times) up to 200 Hz.

Each has a different effect on the body. 

For each waveform, the magnitudes of voltage and current 
at which the effect takes place are different.

The body is most sensitive to ac, where the current
reverses through the body.  Such currents can cause both
tetanus of various muscles, and fibrillation of the heart.

Dc does not cause either tetanus or fibrillation.  Dc 
with ripple or superimposed ac is still dc because the
current does not reverse direction.  From my reading of
research papers, there is no significant effect on the
body due to ac riding on a dc bias provided the current
does not change direction.

Interrupted dc (50% duty cycle, 0 mA off, up to 200 Hz) 
is surmised to have similar effect to that of ac.  I 
believe that UL modeled this, and came to the conclusion 
that such interruption could cause fibrillation.  (I 
don't believe any tests on animals or people were 
actually performed.)  Hence, the limitation on voltage 
for such waveforms.

Most of the research on live humans (grad students) was 
performed by Charles Dalziel, UC Berkeley, during the 
late 40's and early 50's.  Dalziel published numerous 
papers on his tests, most in IRE and AIEE journals.

Dalziel gave us the tetanus values for ac, and determined
there was no tetanus for dc.  Dalziel also gave us the
effect of frequency on humans.

During the 30's, 40's and 50's, UL also did some 
measurements on live humans (UL employees) to determine 
body impedance.

Most recently, Beigelmeier (Vienna) has measured himself.
His research is the basis for much of the data in IEC
60479, effects of current on the human body.

Almost all other research was either on live (anesthesized)
animals or on cadavers.

When discussing waveforms that are beyond the research,
we must identify the injury we wish to prevent.  If we
are considering 40 V dc which has an on/off period of 1
second, then the person can disconnect himself from the
source during the 0.5-second off period.  So, this would
be the same as a steady-state 40 V dc source which is
deemed non-hazardous.


Best regards,
Rich


ps:  Charles Dalziel is the inventor of the GFCI.



   Subject: RE: Define Continuous DC Voltage
   Date: Fri, 9 Nov 2001 16:10:29 -0500
   From: Chris Maxwell chris.maxw...@nettest.com
   To: Ken Javor ken.ja...@emccompliance.com,
   Tania Grant taniagr...@msn.com,
   Doug McKean dmck...@corp.auspex.com,
   EMC-PSTC Discussion Group emc-p...@majordomo.ieee.org
   
   
   Sadly, I can't give that frequency; but I think I know the reasoning
   behind Eric's question...
   
   AC signals under 200Hz are especially dangerous to humans because AC
   currents really screw up our nervous system and cause death by heart
   attack at very low currents.  It only takes milliamps of 60Hz AC current
   to kill a human being.
   
   On the other hand, people can withstand far more current from a DC
   source because it doesn't have the same effect on our nervous system.
   (Come on, who hasn't put a 9V battery on their tongue to test it out?)
   
   I think that this is the reasoning that the referenced standard uses to
   give two limits for AC and DC.  My GUESS is that someone (who loved
   to torture living organisms) must have performed tests to figure out how
   DC current affected people (or monkeys, or rats... something).  They
   then must have performed tests with different AC frequencies.  Perhaps
   they even plotted a graph of hazardous voltage/current versus
   frequency.  I would imagine that this is the type of data used by the
   IEC or any other safety organizationn to set hazardous voltage levels.
   Problem is...the standards don't give a graph or table of hazardous
   voltage vs. frequency, it just says DC and AC.   Since we don't have
   access to the graph we really don't know what happens at ultra low
   frequencies.   (Although I have a few rodents in my basement who are
   just asking to be test samples.)
   
   Of course, now there is the gray area of interpretation. (which keeps us
   all employed)
   
   For example, how would a safety engineer classify a 40V thermostat
   control signal (non current limited) with a five second hysteresis that
   prevents it from switching any faster than once every five seconds (0.2
   Hz).   Under normal conditions, this signal would switch once every
   couple of hours (0.00014Hz).  Is this hazardous AC (after all it is
   40V, and it does vary with time)?  Or is it non-hazardous DC.  
   
   Anybody want to tackle that question?  It may help us to figure out
   Eric's initial problem.  Remember to show your work...partial credit
   will be given :-)
   
   Just to show that I'm game... I'll take a stab.  My opinion