2001-08-28 Thread John Woodgate

I read in !emc-pstc that George, David L george.da...@unisys.com wrote
(in 3B10FF0A008FF6458711E6E375E830412C16A6@USTR-
EXCH2.na.uis.unisys.com) about 'CE test suite for computers', on Mon,
27 Aug 2001:
John:
After all your years on the committee and having heard all the technical
arguments, I am surprised the committee is still trying to justify the
additional costs on each product?  If the power system is so bad it can be
fixed cheaply for the consumer once and for 30+ years by changing the
infrastructure.  No electronic product lasts 30 years and the cost is
multiplied each time it is replaced.

Well, of course I am aware of your views and that particular economic
point. No doubt it will be taken into account by IEC SC77A/WG1/TF5a, on
which the ESI experts are in the minority. 
  

The bottom line is data now proves the European power system is very good

I am also aware of that data collection exercise, which indeed is strong
evidence. OTOH, I have the evidence of my own eyes and measurements
here. The mains waveform is very visibly 'flat-topped' and the THD
exceeds 4% on occasions (summer Sunday evenings, when almost all the
load is TV sets and home PCs; we still have very few home air-
conditioners). With regard to voltage changes and flicker, my own
experience is that DIY arc-welders can be a problem, but I don't see
much problem with anything else. This is largely reflected in the
relaxed limits in the still-unpublished (and largely unpublicised)
'other' Millennium Amendment - to IEC/EN61000-3-3.

and these two standards are unnecessary but the standards makers (power
utility people) 

As I wrote above, the ESI people are now in the minority of *attendees*
at the relevant meetings; they also point out that according to the
*membership lists* they have always been in the minority compared to
experts from equipment manufacturing, but not all members attended the
meetings before 1998, when IEC/TC74 realised what was happening, as I
realised in 1991.

still insist in spite of proof, their systems are not so
good.  In their view this is why we need limits on products and the power
distribution system need not be fixed.

There is also a major problem at political level, insofar as all the ESI
companies in European countries where the system has been, or will be,
privatized, are subject to very strict (and somewhat uninformed)
financial control by government Regulators. The ESI is not being allowed
to finance its own harmonic mitigation, except in unusual circumstances.

Information has come to hand that these Regulators are not even in
favour of site-level harmonic mitigation, partly in case it allows some
'polluter' to avoid paying for the 'pollution', and regard equipment-
level control as the Only Solution. Compared with this mantra-oriented
attitude, the ESI people are pussy-cats (now!).
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Eat mink and be dreary!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.



RE: CE test suite for computers

2001-08-27 Thread George, David L

John:
After all your years on the committee and having heard all the technical
arguments, I am surprised the committee is still trying to justify the
additional costs on each product?  If the power system is so bad it can be
fixed cheaply for the consumer once and for 30+ years by changing the
infrastructure.  No electronic product lasts 30 years and the cost is
multiplied each time it is replaced.  

The bottom line is data now proves the European power system is very good
and these two standards are unnecessary but the standards makers (power
utility people) still insist in spite of proof, their systems are not so
good.  In their view this is why we need limits on products and the power
distribution system need not be fixed.

Dave George, Former WG1 member
Unisys Standards Management
Malvern, PA
Net: 385-3653
Fax: 610-695-4700
  

-Original Message-
From: John Woodgate [mailto:j...@jmwa.demon.co.uk]
Sent: Saturday, August 18, 2001 1:55 PM
To: emc-p...@majordomo.ieee.org
Subject: Re: CE test suite for computers



I read in !emc-pstc that Tania Grant taniagr...@msn.com wrote (in
oe127msph2q6dqajy4k4...@hotmail.com) about 'CE test suite for
computers', on Sat, 18 Aug 2001:
Most people will never understand anything unless it is explained 
to them.  Merely stating
that the power distribution in Europe and America is not the same, 
is not an explanation but could even be construed as a lofty 
put-down.

I think one would have to be touchy to regard it as a put-down. I admit
to some exasperation, in that members of IEC SC77A/WG1 and WG2,
especially the US and Canadian experts, have been working hard to
convince their professional colleagues that the European requirements on
harmonic current and voltage-change emissions are *fairly* soundly-
based, not inventions of the Devil. Had the European electricity supply
industry been a little less secretive, and offered more comprehensive
explanations for the need for emission control, much of the controversy
of the last 10 years might have been avoided.
 
If anyone out there can explain the difference between American and 
European power distribution, and why harmonics are not such a big 
problem in the U.S., I am sure that many of us will be extremely 
grateful.

Well, it isn't a big secret but it isn't common knowledge in the
Americas. I feel sure that much more exhaustive explanations than that
offered below can be found by a web search. Several US and Canada-based
academics have written on the subject.

Briefly, in the Americas, power is distributed at Medium Voltage to
points very close to where it is used, and transformers of no more than
a few tens of kVA rating deliver Low Voltage, 220 V centre-grounded, to
residential and light industrial users. The transformer impedances are
lower than is usual in Europe, even allowing for the voltage
differences. The MV network impedances are also lower than in Europe.

Because the supply impedances are lower, a given amount of harmonic
current produces less voltage distortion, and that is what tends to
cause adverse effects, except 'hot neutrals' due to triplen harmonic
addition in the neutral conductors of 3-phase 4-wire systems.

Because the supply impedances are lower, and fewer users are fed from
each transformer, voltage-changes due to rapidly-varying load currents
are smaller and affect fewer users. 120 V lamps have thicker filaments
and flicker less for a given transient voltage change. 

All this is being studied and documented by the above-mentioned IEC WGs,
and improved standards, and other types of publication, will result in
due course.

In Europe, up to typically 500 residential and light industrial users
are supplied from one 500 kVA or larger transformer, so the LV cable
runs are much longer than in the American system, and deliver nominally
230 V single- or 3-phase (230 V phase voltage), with wired neutral. The
way that the neutral is grounded differs between European countries:
France, UK and Norway use systems that are not like the US system,
whereas other countries' systems are more similar. The MV network
impedance is quite high (maybe over 15%), necessitated, AIUI, by fault-
level requirements which I personally have not studied in detail.
 
And can someone explain to me why the European Community is 
adopting the American Energy Star Program?    -- Albeit rendered in 
their own language!
 
No-one knows why the EC does anything. (;-)
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co..uk

Eat mink and be dreary!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael

RE: CE test suite for computers

2001-08-20 Thread Stone, Richard A (Richard)
Don't forget Telco Conducted Emissions is NOT required until
at least 2003'
Richard,

 -Original Message-
From: Frazee, Douglas (Douglas) [mailto:dfra...@lucent.com]
Sent: Friday, August 17, 2001 12:19 PM
To: 'Pettit, Ghery'; 'Stuart Lopata'; emc
Subject: RE: CE test suite for computers



Ghery, I believe 61000-3-2, Class D is also required.
Doug Frazee 
Regulatory Compliance Manager 
Lucent Technologies, Broadband Carrier Networks 
Access Technology Division 
InterNetworking Systems 
(301) 809-4415 
(301) 352-4730 FAX 
dfra...@lucent.com 

-Original Message-
From: Pettit, Ghery [mailto:ghery.pet...@intel.com]
Sent: Thursday, August 16, 2001 4:39 PM
To: 'Stuart Lopata'; emc
Subject: RE: CE test suite for computers


Stuart,
 
For ITE the requirements are EN 55022:1994 (through 1 August 2003) and EN
55024:1998.  If you wish to test to anything else, you need to go through a
Competent Body and convince them that the alternate standards are adequate.
 
Ghery Pettit
Intel
 
-Original Message-
From: Stuart Lopata [mailto:stu...@timcoengr.com]
Sent: Thursday, August 16, 2001 12:14 PM
To: emc
Subject: CE test suite for computers


Any info about the test suite for computers (for commercial  professional
markets in EU) to meet the EMC directive for the CE mark?
 
Also wondering if there is any collection of non-harmonized standards that
are currently accepted for CE mark testing?
 
to my knowledge, EMC testing for computers requires the following. (so
far)
 
EN 55022 for ITE equipment
EN 61000 3-1 through 3-11
 
Sincerely,
 
Stuart Lopata



Re: CE test suite for computers

2001-08-19 Thread John Woodgate

I read in !emc-pstc that Tania Grant taniagr...@msn.com wrote (in
oe67wwnyumtlor31l1g0002c...@hotmail.com) about 'CE test suite for
computers', on Sat, 18 Aug 2001:
Thank you, Mr. Woodgate,
 
I am sure many of the American contingent are grateful for your 
explanation.

I note the tone of your remarks, but I hope, nevertheless that your
second sentence is true.

Rich Nute says 'the problems are the same in USA and Europe' and I say
'they are different'. We are both right: the same harmonic emissions
occur everywhere, but they don't excite most American electricity
suppliers (Hydro Quebec is an exception), whereas in Europe they do
excite, and the excitement is not entirely groundless. 
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co..uk 
Eat mink and be dreary!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.rcic.com/  click on Virtual Conference Hall,




Fw: CE test suite for computers

2001-08-19 Thread Chris Wells

- Original Message - 
From: Chris Wells 
To: Tania Grant 
Sent: Saturday, August 18, 2001 10:54 PM
Subject: Re: CE test suite for computers


Jumping into the middle of this...
In Europe there are a lot of older buildings with half sized neutrals relative 
to the supply phases.
In the USA we tend to have newer designs and tend to have at least neutral 
circuits = to the phase circuits.
In newer buildings we are pushing for 200% neutrals.
This is all due to the effect of single phase loads and the tripplen harmonics 
they create.
The 3, 9 etc do not cancel on the neutral- they tripple up on the neutral 
causing large harmonic loads.
This can cause voltage drops on the phases and over heating of the neutrals - 
even fires.
I assume this is why Europe is pushing for PFC front ends on Power supplies 
above 50 or is it 75W?
The PFC front end does correct Power Factor, but more importantly it pulls 
current closer to a 50 or 60 Hz sinusoide.
It eliminates much of the lower harmonics with distortion only showing up at 
the higher harmonics like the 27th or higher.
At that point the THD levels are very low and insignificant.

Is this related to the Energy STar Program - I have no idea.

Hope this makes some sense relative to the disscussion :-)

Regards

Chris Wells
Senior Design Engineer
Cutler-hammer 
well...@eaton.com






  - Original Message - 
  From: Tania Grant 
  To: John Woodgate ; emc-p...@majordomo.ieee.org 
  Sent: Saturday, August 18, 2001 12:32 PM
  Subject: Re: CE test suite for computers


  Dear Mr. Woodgate,

  Most people will never understand anything unless it is explained to them.  
Merely stating
  that the power distribution in Europe and America is not the same, is not an 
explanation but could even be construed as a lofty put-down.

  If anyone out there can explain the difference between American and European 
power distribution, and why harmonics are not such a big problem in the U.S., I 
am sure that many of us will be extremely grateful.

  And can someone explain to me why the European Community is adopting the 
American Energy Star Program?-- Albeit rendered in their own language!

  taniagr...@msn.com

- Original Message -
From: John Woodgate
Sent: Friday, August 17, 2001 3:37 PM
To: emc-p...@majordomo.ieee.org
Subject: Re: CE test suite for computers


I read in !emc-pstc that Pettit, Ghery ghery.pet...@intel.com wrote
(in d5e932f578ebd111ac3f00a0c96b1e6f09506...@orsmsx31.jf.intel.com)
about 'CE test suite for computers', on Fri, 17 Aug 2001:
Also EN 61000-3-3 needs to be considered.  Useless standards, if you 
ask me.
 

That's because you, like most Americans, do not understand the problems
in Europe. Because the power distribution networks in Europe and the
Americas are very differently configured, you have far fewer problems
with harmonics and voltage changes, and voltage changes seem to be much
more tolerated, in USA anyway.
--
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk
Eat mink and be dreary!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.rcic.com/  click on Virtual Conference Hall,




Re: CE test suite for computers

2001-08-19 Thread Tania Grant
Thank you, Mr. Woodgate,

I am sure many of the American contingent are grateful for your explanation.

taniagr...@msn.com
   
- Original Message -
From: John Woodgate
Sent: Saturday, August 18, 2001 3:25 PM
To: emc-p...@majordomo.ieee.org
Subject: Re: CE test suite for computers
  

I read in !emc-pstc that Tania Grant taniagr...@msn.com wrote (in
oe127msph2q6dqajy4k4...@hotmail.com) about 'CE test suite for
computers', on Sat, 18 Aug 2001:
Most people will never understand anything unless it is explained
to them.  Merely stating
that the power distribution in Europe and America is not the same,
is not an explanation but could even be construed as a lofty
put-down.

I think one would have to be touchy to regard it as a put-down. I admit
to some exasperation, in that members of IEC SC77A/WG1 and WG2,
especially the US and Canadian experts, have been working hard to
convince their professional colleagues that the European requirements on
harmonic current and voltage-change emissions are *fairly* soundly-
based, not inventions of the Devil. Had the European electricity supply
industry been a little less secretive, and offered more comprehensive
explanations for the need for emission control, much of the controversy
of the last 10 years might have been avoided.
  
If anyone out there can explain the difference between American and
European power distribution, and why harmonics are not such a big
problem in the U.S., I am sure that many of us will be extremely
grateful.

Well, it isn't a big secret but it isn't common knowledge in the
Americas. I feel sure that much more exhaustive explanations than that
offered below can be found by a web search. Several US and Canada-based
academics have written on the subject.

Briefly, in the Americas, power is distributed at Medium Voltage to
points very close to where it is used, and transformers of no more than
a few tens of kVA rating deliver Low Voltage, 220 V centre-grounded, to
residential and light industrial users. The transformer impedances are
lower than is usual in Europe, even allowing for the voltage
differences. The MV network impedances are also lower than in Europe.

Because the supply impedances are lower, a given amount of harmonic
current produces less voltage distortion, and that is what tends to
cause adverse effects, except 'hot neutrals' due to triplen harmonic
addition in the neutral conductors of 3-phase 4-wire systems.

Because the supply impedances are lower, and fewer users are fed from
each transformer, voltage-changes due to rapidly-varying load currents
are smaller and affect fewer users. 120 V lamps have thicker filaments
and flicker less for a given transient voltage change.

All this is being studied and documented by the above-mentioned IEC WGs,
and improved standards, and other types of publication, will result in
due course.

In Europe, up to typically 500 residential and light industrial users
are supplied from one 500 kVA or larger transformer, so the LV cable
runs are much longer than in the American system, and deliver nominally
230 V single- or 3-phase (230 V phase voltage), with wired neutral. The
way that the neutral is grounded differs between European countries:
France, UK and Norway use systems that are not like the US system,
whereas other countries' systems are more similar. The MV network
impedance is quite high (maybe over 15%), necessitated, AIUI, by fault-
level requirements which I personally have not studied in detail.
  
And can someone explain to me why the European Community is
adopting the American Energy Star Program?-- Albeit rendered in
their own language!
  
No-one knows why the EC does anything. (;-)
--
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co..uk
Eat mink and be dreary!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.rcic.com/  click on Virtual Conference Hall,


Re: CE test suite for computers

2001-08-19 Thread Tania Grant
Rich,

Thank you very very much.  

taniagr...@msn.com
 
- Original Message -
From: Rich Nute
Sent: Saturday, August 18, 2001 3:02 PM
To: taniagr...@msn.com
Cc: j...@jmwa.demon.co.uk; emc-p...@majordomo.ieee.org
Subject: Re: CE test suite for computers
 




Hi John and Tania:


Actually, the harmonic current problem is no
different between Europe and North America.

The basic problem is that the harmonic currents
generated in the load equipment are dissipated
in the delta primary of a delta-wye distribution
transformer.  If the harmonic content is large,
then the primary winding can overheat, resulting
in transformer failure.

In North America, distribution transformers are
relatively small.  Three-phase is not used in
the home, so the problem only shows up in
commercial and industrial sites.  The distribution
transformers are largely owned by the business,
not by the power company.  North America has
incurred such transformer failures.  The problem
has been publicised, and transformers are now
designed using a K factor which indicates how
much harmonic current the transformer can safely
handle.

In Europe, the distribution transformers are
relatively large.  Three-phase is distributed
to homes.  A single transformer can supply up
to 600 homes and businesses.  (In North America,
the transformer supplies 8 homes maximum.)  It
is relatively rare for the business to own the
distribution transformer.  Failure of such a
transformer can be quite disruptive.

So, in Europe, rather than replace the very large
distribution transformers, the power supply
industry is imposing harmonic current emission
limits on electrical products.

Harmonic currents can cause other problems.  But,
this is my understanding of the reason behind
EN 6100-3-2.


Best regards,
Rich



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.rcic.com/  click on Virtual Conference Hall,

Re: CE test suite for computers

2001-08-19 Thread Ken Javor

The problem I have seen is related to harmonic current, but really is more
easily understood in the time domain.  Electronic power supplies, either
linear or switched, draw large slugs of current when 50/60 Hz filter
capacitor potentials drop two diode drops below line potential, at which
time these diodes switch on to replenish the capacitor.  Without special
circuitry, this happens exclusively at the peak bus potential, meaning that
the current waveform drawn from the bus is a very large spike occurring only
at the time the ac potential crests.  The effect is to flatten the
sinusoidal shape of the bus waveform.  Many years ago I started out working
near the center of one office building relatively near the breaker panel.
Over time my cubicle moved and I was closer to the end of the building.  The
power supply of my desktop was controlled from a soft key on my keyboard.
As I moved from building center, I found that it was harder and harder to
get my computer to turn on.  That's when I measured line potentials with my
scope and found that the further I was from building center the flatter the
line potential was, and the lower the peak.  Of course that is merely an
empirical observation and not a proven cause and effect.

--
From: Rich Nute ri...@sdd.hp.com
To: taniagr...@msn.com
Cc: j...@jmwa.demon.co.uk, emc-p...@majordomo.ieee.org
Subject: Re: CE test suite for computers
Date: Sat, Aug 18, 2001, 4:10 PM






 Hi John and Tania:


 Actually, the harmonic current problem is no
 different between Europe and North America.

 The basic problem is that the harmonic currents
 generated in the load equipment are dissipated
 in the delta primary of a delta-wye distribution
 transformer.  If the harmonic content is large,
 then the primary winding can overheat, resulting
 in transformer failure.

 In North America, distribution transformers are
 relatively small.  Three-phase is not used in
 the home, so the problem only shows up in
 commercial and industrial sites.  The distribution
 transformers are largely owned by the business,
 not by the power company.  North America has
 incurred such transformer failures.  The problem
 has been publicised, and transformers are now
 designed using a K factor which indicates how
 much harmonic current the transformer can safely
 handle.

 In Europe, the distribution transformers are
 relatively large.  Three-phase is distributed
 to homes.  A single transformer can supply up
 to 600 homes and businesses.  (In North America,
 the transformer supplies 8 homes maximum.)  It
 is relatively rare for the business to own the
 distribution transformer.  Failure of such a
 transformer can be quite disruptive.

 So, in Europe, rather than replace the very large
 distribution transformers, the power supply
 industry is imposing harmonic current emission
 limits on electrical products.

 Harmonic currents can cause other problems.  But,
 this is my understanding of the reason behind
 EN 6100-3-2.


 Best regards,
 Rich



 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Michael Garretson:pstc_ad...@garretson.org
  Dave Healddavehe...@mediaone.net

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

 All emc-pstc postings are archived and searchable on the web at:
 http://www.rcic.com/  click on Virtual Conference Hall,
 

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.rcic.com/  click on Virtual Conference Hall,




Re: CE test suite for computers

2001-08-19 Thread John Woodgate

I read in !emc-pstc that Rich Nute ri...@sdd.hp.com wrote (in
200108182110.oaa02...@epgc196.sdd.hp.com) about 'CE test suite for
computers', on Sat, 18 Aug 2001:

The basic problem is that the harmonic currents
generated in the load equipment are dissipated 
in the delta primary of a delta-wye distribution
transformer.  If the harmonic content is large,
then the primary winding can overheat, resulting
in transformer failure.

In Europe, that isn't usually the major problem. System capacitor
overheating due to harmonic currents is more significant. In some cases,
system inductors have failed due to over-voltage. Unfortunately, the
European supply industry only cites extreme cases (like a 1MW motor!),
and then only grudgingly. 
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Eat mink and be dreary!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.rcic.com/  click on Virtual Conference Hall,




Re: CE test suite for computers

2001-08-18 Thread John Woodgate

I read in !emc-pstc that Tania Grant taniagr...@msn.com wrote (in
oe127msph2q6dqajy4k4...@hotmail.com) about 'CE test suite for
computers', on Sat, 18 Aug 2001:
Most people will never understand anything unless it is explained 
to them.  Merely stating
that the power distribution in Europe and America is not the same, 
is not an explanation but could even be construed as a lofty 
put-down.

I think one would have to be touchy to regard it as a put-down. I admit
to some exasperation, in that members of IEC SC77A/WG1 and WG2,
especially the US and Canadian experts, have been working hard to
convince their professional colleagues that the European requirements on
harmonic current and voltage-change emissions are *fairly* soundly-
based, not inventions of the Devil. Had the European electricity supply
industry been a little less secretive, and offered more comprehensive
explanations for the need for emission control, much of the controversy
of the last 10 years might have been avoided.
 
If anyone out there can explain the difference between American and 
European power distribution, and why harmonics are not such a big 
problem in the U.S., I am sure that many of us will be extremely 
grateful.

Well, it isn't a big secret but it isn't common knowledge in the
Americas. I feel sure that much more exhaustive explanations than that
offered below can be found by a web search. Several US and Canada-based
academics have written on the subject.

Briefly, in the Americas, power is distributed at Medium Voltage to
points very close to where it is used, and transformers of no more than
a few tens of kVA rating deliver Low Voltage, 220 V centre-grounded, to
residential and light industrial users. The transformer impedances are
lower than is usual in Europe, even allowing for the voltage
differences. The MV network impedances are also lower than in Europe.

Because the supply impedances are lower, a given amount of harmonic
current produces less voltage distortion, and that is what tends to
cause adverse effects, except 'hot neutrals' due to triplen harmonic
addition in the neutral conductors of 3-phase 4-wire systems.

Because the supply impedances are lower, and fewer users are fed from
each transformer, voltage-changes due to rapidly-varying load currents
are smaller and affect fewer users. 120 V lamps have thicker filaments
and flicker less for a given transient voltage change. 

All this is being studied and documented by the above-mentioned IEC WGs,
and improved standards, and other types of publication, will result in
due course.

In Europe, up to typically 500 residential and light industrial users
are supplied from one 500 kVA or larger transformer, so the LV cable
runs are much longer than in the American system, and deliver nominally
230 V single- or 3-phase (230 V phase voltage), with wired neutral. The
way that the neutral is grounded differs between European countries:
France, UK and Norway use systems that are not like the US system,
whereas other countries' systems are more similar. The MV network
impedance is quite high (maybe over 15%), necessitated, AIUI, by fault-
level requirements which I personally have not studied in detail.
 
And can someone explain to me why the European Community is 
adopting the American Energy Star Program?    -- Albeit rendered in 
their own language!
 
No-one knows why the EC does anything. (;-)
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co..uk 
Eat mink and be dreary!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.rcic.com/  click on Virtual Conference Hall,




Re: CE test suite for computers

2001-08-17 Thread John Woodgate

I read in !emc-pstc that Rich Nute ri...@sdd.hp.com wrote (in
200108171905.maa00...@epgc196.sdd.hp.com) about 'CE test suite for
computers', on Fri, 17 Aug 2001:
Agreed!

Well, see my direct response to G. P.

EN 61000-3-2 is driven by Euro power distributors
who don't want to correct for non-linear loads.
(But who have no quarrel with correcting for 
phase angle.)

That's because it's practicable to correct for phase angle but it is not
practicable (yet) to correct for harmonics at system level. Electricité
de France has one of the first experimental system-level compensators
now under trial.

I don't understand the drive for EN 61000-3-3.

See my comments about voltage change tolerance in my other post.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co..uk 
Eat mink and be dreary!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.rcic.com/  click on Virtual Conference Hall,




Re: CE test suite for computers

2001-08-17 Thread John Woodgate

I read in !emc-pstc that Pettit, Ghery ghery.pet...@intel.com wrote
(in d5e932f578ebd111ac3f00a0c96b1e6f09506...@orsmsx31.jf.intel.com)
about 'CE test suite for computers', on Fri, 17 Aug 2001:
Also EN 61000-3-3 needs to be considered.  Useless standards, if you ask 
 me.
 

That's because you, like most Americans, do not understand the problems
in Europe. Because the power distribution networks in Europe and the
Americas are very differently configured, you have far fewer problems
with harmonics and voltage changes, and voltage changes seem to be much
more tolerated, in USA anyway.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co..uk 
Eat mink and be dreary!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.rcic.com/  click on Virtual Conference Hall,




Re: CE test suite for computers

2001-08-17 Thread Rich Nute




Hi Ghery:


   Also EN 61000-3-3 needs to be considered.  Useless standards, if you ask me.

Agreed!

EN 61000-3-2 is driven by Euro power distributors
who don't want to correct for non-linear loads.
(But who have no quarrel with correcting for 
phase angle.)

I don't understand the drive for EN 61000-3-3.


Best regards,
Rich



---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.rcic.com/  click on Virtual Conference Hall,




RE: CE test suite for computers

2001-08-17 Thread Pettit, Ghery
Also EN 61000-3-3 needs to be considered.  Useless standards, if you ask me.
 
Ghery
 
-Original Message-
From: Frazee, Douglas (Douglas) [mailto:dfra...@lucent.com]
Sent: Friday, August 17, 2001 9:19 AM
To: 'Pettit, Ghery'; 'Stuart Lopata'; emc
Subject: RE: CE test suite for computers


Ghery, I believe 61000-3-2, Class D is also required.
Doug Frazee 
Regulatory Compliance Manager 
Lucent Technologies, Broadband Carrier Networks 
Access Technology Division 
InterNetworking Systems 
(301) 809-4415 
(301) 352-4730 FAX 
dfra...@lucent.com 

-Original Message-
From: Pettit, Ghery [mailto:ghery.pet...@intel.com]
Sent: Thursday, August 16, 2001 4:39 PM
To: 'Stuart Lopata'; emc
Subject: RE: CE test suite for computers


Stuart,
 
For ITE the requirements are EN 55022:1994 (through 1 August 2003) and EN
55024:1998.  If you wish to test to anything else, you need to go through a
Competent Body and convince them that the alternate standards are adequate.
 
Ghery Pettit
Intel
 
-Original Message-
From: Stuart Lopata [mailto:stu...@timcoengr.com]
Sent: Thursday, August 16, 2001 12:14 PM
To: emc
Subject: CE test suite for computers


Any info about the test suite for computers (for commercial  professional
markets in EU) to meet the EMC directive for the CE mark?
 
Also wondering if there is any collection of non-harmonized standards that
are currently accepted for CE mark testing?
 
to my knowledge, EMC testing for computers requires the following. (so
far)
 
EN 55022 for ITE equipment
EN 61000 3-1 through 3-11
 
Sincerely,
 
Stuart Lopata



RE: CE test suite for computers

2001-08-17 Thread Frazee, Douglas (Douglas)
Ghery, I believe 61000-3-2, Class D is also required.
Doug Frazee 
Regulatory Compliance Manager 
Lucent Technologies, Broadband Carrier Networks 
Access Technology Division 
InterNetworking Systems 
(301) 809-4415 
(301) 352-4730 FAX 
dfra...@lucent.com 

-Original Message-
From: Pettit, Ghery [mailto:ghery.pet...@intel.com]
Sent: Thursday, August 16, 2001 4:39 PM
To: 'Stuart Lopata'; emc
Subject: RE: CE test suite for computers


Stuart,
 
For ITE the requirements are EN 55022:1994 (through 1 August 2003) and EN
55024:1998.  If you wish to test to anything else, you need to go through a
Competent Body and convince them that the alternate standards are adequate.
 
Ghery Pettit
Intel
 
-Original Message-
From: Stuart Lopata [mailto:stu...@timcoengr.com]
Sent: Thursday, August 16, 2001 12:14 PM
To: emc
Subject: CE test suite for computers


Any info about the test suite for computers (for commercial  professional
markets in EU) to meet the EMC directive for the CE mark?
 
Also wondering if there is any collection of non-harmonized standards that
are currently accepted for CE mark testing?
 
to my knowledge, EMC testing for computers requires the following. (so
far)
 
EN 55022 for ITE equipment
EN 61000 3-1 through 3-11
 
Sincerely,
 
Stuart Lopata



Re: CE test suite for computers

2001-08-16 Thread John Woodgate

I read in !emc-pstc that Stuart Lopata stu...@timcoengr.com wrote (in
00d301c12687$8b6e8100$1301a8c0@newberry) about 'CE test suite for
computers', on Thu, 16 Aug 2001:
Any info about the test suite for computers (for commercial  professional 
markets in EU) to meet the EMC directive for the CE mark?

Also wondering if there is any collection of non-harmonized standards that are 
currently accepted for CE mark testing?

to my knowledge, EMC testing for computers requires the following. (so far)

EN 55022 for ITE equipment
EN 61000 3-1 through 3-11

Certainly NOT 'EN61000-3-1 through 11'. For desktop computers, you need
to meet EN61000-3-2 (Class D limits) and EN61000-3-3. If your computers
are rated at more than 16A/phase, then EN61000-3-11 and EN61000-3-12
apply INSTEAD, but -12 hasn't been published yet so you don't have to
comply with any limits. -11 and -12 supersede -5 and -4, which are IEC
Reports, not adopted as ENs and could only be applied (if you were
totally insane!) in the context of a Technical Construction File. -11
is, and -12 will be, far more realistic.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Eat mink and be dreary!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://www.rcic.com/  click on Virtual Conference Hall,




RE: CE test suite for computers

2001-08-16 Thread Pettit, Ghery
Stuart,
 
For ITE the requirements are EN 55022:1994 (through 1 August 2003) and EN
55024:1998.  If you wish to test to anything else, you need to go through a
Competent Body and convince them that the alternate standards are adequate.
 
Ghery Pettit
Intel
 
-Original Message-
From: Stuart Lopata [mailto:stu...@timcoengr.com]
Sent: Thursday, August 16, 2001 12:14 PM
To: emc
Subject: CE test suite for computers


Any info about the test suite for computers (for commercial  professional
markets in EU) to meet the EMC directive for the CE mark?
 
Also wondering if there is any collection of non-harmonized standards that
are currently accepted for CE mark testing?
 
to my knowledge, EMC testing for computers requires the following. (so
far)
 
EN 55022 for ITE equipment
EN 61000 3-1 through 3-11
 
Sincerely,
 
Stuart Lopata