RE: Rack System Safety (UL1950/EN 60950) Questions

1999-03-11 Thread Peter Merguerian
Richard,

Adding Approved disks, tapes and similar devices and adding 
model designation usually involves paperwork. However, 
adding/changing Approved , datacom and other similar equipment 
usually requires a repeat of some of the tests, including but not 
limited to Input, Leakage and Capacitance Discharge Tests.

Regards, 


 
 
 On Wednesday, March 10, 1999 5:00 AM, WOODS, RICHARD 
 [SMTP:wo...@sensormatic.com] wrote:
  As I think about this situation, there is a way of obtaining UL Listing 
 on
  the rack and have other certification marks on the internal equipment. 
 Have
  UL List just the rack without the equipment. Now you can mix and match 
 the
  internal certified equipment as you see fit keeping in mind not to exceed
  the cooling and electrical capacity of the rack. This is what we use to 
 do a
  decade ago at a mini-computer company. We would configure systems from
  Listed racks, cpus, disks, tapes, etc.
 
 RRR. So after we obtained the UL listed for rack (model ABC-001), then we 
 configure, add recognized disks, recognized tapes ...etc. etc.. now it 
 become new model (DEF-001). Do we have to submit this new model for 
 certification again ???.
 
 
  Now to Jim's point. There is no law that requires one agency to accept the
  certification marks of another agency. For example, UL will not accept 
 ETL
  marks on components and both are NRTLS. The only way one agency will 
 accept
  the marks of another is if there is an agreement between them. The CB 
 scheme
  is one good example. CSA and UL have an agreement to accept each others 
 test
  data I believe, but I don't believe that they will accept each others 
 marks.
 
 RRR. They don't accept each others mark, but would they review and accept 
 test data???
 
 Tac Pham
 HC Power
 
  --
  From:  Jim Eichner [SMTP:jeich...@statpower.com]
  Sent:  Tuesday, March 09, 1999 3:23 PM
  To:  'EMC-PSTC - forum'
  Subject:  RE: Rack System Safety (UL1950/EN 60950) Questions
 
  Re Richard's item 5)...
 
   5.UL requires that all internal equipment be UL Listed or
   Recognized.
  
  If that is true, then the value of the CSA/NRTL mark, and conversely
  the
  cUL mark if CSA plays this way too, is highly questionable.  Do you
  have
  a direct-from-UL interpretation saying that they are not accepting
  the
  CSA/NRTL mark?  If so, I would expect CSA to take action to defend
  its
  mark, and UL to have no firm ground to stand on!
 
  Comments?
 
  Jim Eichner
  Statpower Technologies Corporation
  jeich...@statpower.com
  http://www.statpower.com
  Any opinions expressed are those of my invisible friend, who really
  exists.  Honest.
 
 
 
 
 -
 This message is coming from the emc-pstc discussion list.
 To cancel your subscription, send mail to majord...@ieee.org
 with the single line: unsubscribe emc-pstc (without the
 quotes).  For help, send mail to ed.pr...@cubic.com,
 j...@gwmail.monarch.com, ri...@sdd.hp.com, or
 roger.volgst...@compaq.com (the list administrators).
 


PETER S. MERGUERIAN
MANAGING DIRECTOR
PRODUCT TESTING DIVISION
I.T.L. (PRODUCT TESTING) LTD.
HACHAROSHET 26, P.O.B. 211
OR YEHUDA 60251, ISRAEL

TEL: 972-3-5339022
FAX: 972-3-5339019
E-MAIL: pe...@itl.co.il
Visit our Website: http://www.itl.co.il

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


RE: Rack System Safety (UL1950/EN 60950) Questions

1999-03-11 Thread WOODS, RICHARD
That's what I love about this mailing list. I learn something new most every
day. Thanks Tania!

--
From:  Grant, Tania (Tania) [SMTP:tgr...@lucent.com]
Sent:  Wednesday, March 10, 1999 4:27 PM
To:  'EMC-PSTC - forum'; 'WOODS, RICHARD'
Subject:  RE: Rack System Safety (UL1950/EN 60950) Questions

Richard,

Regarding your last statement   I don't believe that they [CSA
 UL]
will accept each others marks.

Certain UL and CSA component standards have been harmonized and, I
believe, this effort is continuing.  If you look at Appendix  P.2
[be sure
it is P.2 and not P.1]  of UL 1950, 3rd edition, you will find a
matrix of
UL and CSA component standards where meeting one or the other is
considered
acceptable for meeting the requirements of UL1950, 3rd edition.
Additionally, if you are working with an astute UL engineer, very
often they
will inform you of additional components that fall under that
category but
have not yet been published in this Appendix. 

Tania Grant, Lucent Technologies, Octel Messaging Division
tgr...@lucent.com


--
From:  WOODS, RICHARD[SMTP:wo...@sensormatic.com]
Sent:  Wednesday, March 10, 1999 5:00 AM
To:  'EMC-PSTC - forum'
Subject:  RE: Rack System Safety (UL1950/EN 60950) Questions

As I think about this situation, there is a way of obtaining UL
Listing on
the rack and have other certification marks on the internal
equipment. Have
UL List just the rack without the equipment. Now you can mix and
match the
internal certified equipment as you see fit keeping in mind not to
exceed
the cooling and electrical capacity of the rack. This is what we use
to do a
decade ago at a mini-computer company. We would configure systems
from
Listed racks, cpus, disks, tapes, etc.

Now to Jim's point. There is no law that requires one agency to
accept the
certification marks of another agency. For example, UL will not
accept ETL
marks on components and both are NRTLS. The only way one agency will
accept
the marks of another is if there is an agreement between them. The
CB scheme
is one good example. CSA and UL have an agreement to accept each
others test
data I believe, but I don't believe that they will accept each
others marks.

--
From:  Jim Eichner [SMTP:jeich...@statpower.com]
Sent:  Tuesday, March 09, 1999 3:23 PM
To:  'EMC-PSTC - forum'
Subject:  RE: Rack System Safety (UL1950/EN 60950) Questions

Re Richard's item 5)...

 5.UL requires that all internal equipment be UL Listed
or
 Recognized.
 
If that is true, then the value of the CSA/NRTL mark, and
conversely
the
cUL mark if CSA plays this way too, is highly questionable.
Do you
have
a direct-from-UL interpretation saying that they are not
accepting
the
CSA/NRTL mark?  If so, I would expect CSA to take action to
defend
its
mark, and UL to have no firm ground to stand on!  

Comments?

Jim Eichner
Statpower Technologies Corporation
jeich...@statpower.com
http://www.statpower.com
Any opinions expressed are those of my invisible friend, who
really
exists.  Honest.  


 -Original Message-
 From: WOODS, RICHARD [SMTP:wo...@sensormatic.com]
 Sent: Tuesday, March 09, 1999 11:15 AM
 To:   emc-p...@majordomo.ieee.org; t...@world.std.com
 Subject:  RE: Rack System Safety (UL1950/EN 60950)
Questions
 
 1.Peter, equipment with the standard NEMA plug is
considered
to be
 Class A.. 
 2.Equipment using the heavy duty Industrial plugs
complying
with
 IEC
 are considered to be Class B. I have never seen those used
inside
rack
 mounted equipment.
 3.If the power supply is UL Listed, then temperature
 measurements
 are not required. However, most power supplies are
categorized as
 Recognized and are therefore incomplete in construction
- that
is,
 they
 cannot pass the safety requirements for a stand alone
power
supply.
 Temperature measurements will be required.
 4.Stability is performed in a worst case situation,
but reason
is
 also
 taken

RE: Rack System Safety (UL1950/EN 60950) Questions

1999-03-10 Thread Grant, Tania (Tania)
Richard,

Regarding your last statement   I don't believe that they [CSA  UL]
will accept each others marks.

Certain UL and CSA component standards have been harmonized and, I
believe, this effort is continuing.  If you look at Appendix  P.2  [be sure
it is P.2 and not P.1]  of UL 1950, 3rd edition, you will find a matrix of
UL and CSA component standards where meeting one or the other is considered
acceptable for meeting the requirements of UL1950, 3rd edition.
Additionally, if you are working with an astute UL engineer, very often they
will inform you of additional components that fall under that category but
have not yet been published in this Appendix. 

Tania Grant, Lucent Technologies, Octel Messaging Division
tgr...@lucent.com


--
From:  WOODS, RICHARD[SMTP:wo...@sensormatic.com]
Sent:  Wednesday, March 10, 1999 5:00 AM
To:  'EMC-PSTC - forum'
Subject:  RE: Rack System Safety (UL1950/EN 60950) Questions

As I think about this situation, there is a way of obtaining UL Listing on
the rack and have other certification marks on the internal equipment. Have
UL List just the rack without the equipment. Now you can mix and match the
internal certified equipment as you see fit keeping in mind not to exceed
the cooling and electrical capacity of the rack. This is what we use to do a
decade ago at a mini-computer company. We would configure systems from
Listed racks, cpus, disks, tapes, etc.

Now to Jim's point. There is no law that requires one agency to accept the
certification marks of another agency. For example, UL will not accept ETL
marks on components and both are NRTLS. The only way one agency will accept
the marks of another is if there is an agreement between them. The CB scheme
is one good example. CSA and UL have an agreement to accept each others test
data I believe, but I don't believe that they will accept each others marks.

--
From:  Jim Eichner [SMTP:jeich...@statpower.com]
Sent:  Tuesday, March 09, 1999 3:23 PM
To:  'EMC-PSTC - forum'
Subject:  RE: Rack System Safety (UL1950/EN 60950) Questions

Re Richard's item 5)...

 5.UL requires that all internal equipment be UL Listed or
 Recognized.
 
If that is true, then the value of the CSA/NRTL mark, and conversely
the
cUL mark if CSA plays this way too, is highly questionable.  Do you
have
a direct-from-UL interpretation saying that they are not accepting
the
CSA/NRTL mark?  If so, I would expect CSA to take action to defend
its
mark, and UL to have no firm ground to stand on!  

Comments?

Jim Eichner
Statpower Technologies Corporation
jeich...@statpower.com
http://www.statpower.com
Any opinions expressed are those of my invisible friend, who really
exists.  Honest.  


 -Original Message-
 From: WOODS, RICHARD [SMTP:wo...@sensormatic.com]
 Sent: Tuesday, March 09, 1999 11:15 AM
 To:   emc-p...@majordomo.ieee.org; t...@world.std.com
 Subject:  RE: Rack System Safety (UL1950/EN 60950) Questions
 
 1.Peter, equipment with the standard NEMA plug is considered
to be
 Class A.. 
 2.Equipment using the heavy duty Industrial plugs complying
with
 IEC
 are considered to be Class B. I have never seen those used inside
rack
 mounted equipment.
 3.If the power supply is UL Listed, then temperature
 measurements
 are not required. However, most power supplies are categorized as
 Recognized and are therefore incomplete in construction - that
is,
 they
 cannot pass the safety requirements for a stand alone power
supply.
 Temperature measurements will be required.
 4.Stability is performed in a worst case situation, but reason
is
 also
 taken into account. Most likely, you will determine that it is
 possible and
 reasonable to assume that more than one assembly can be extending
at
 the
 same time.
 5.UL requires that all internal equipment be UL Listed or
 Recognized.
 
 ---
   From:  pe...@itl.co.il [SMTP:pe...@itl.co.il]
   Sent:  Tuesday, March 09, 1999 11:26 AM
   To:  emc-p...@majordomo.ieee.org; t...@world.std.com
   Subject:  Rack System Safety (UL1950/EN 60950) Questions
 
   Dear All,
 
   I would like to know some of your professional advice on
some 
   issues reagrding rack systems to be evaluated to UL1950/EN
60 
   950.
 
   1. For the North America, does a NEMA 125 V, 20 A plug meet
the 
   pluggable B definition?
 
   2. What are some plug configurations which will meet the 
   pluggable B

RE: Rack System Safety (UL1950/EN 60950) Questions

1999-03-10 Thread Tac Pham


On Wednesday, March 10, 1999 5:00 AM, WOODS, RICHARD 
[SMTP:wo...@sensormatic.com] wrote:
 As I think about this situation, there is a way of obtaining UL Listing 
on
 the rack and have other certification marks on the internal equipment. 
Have
 UL List just the rack without the equipment. Now you can mix and match 
the
 internal certified equipment as you see fit keeping in mind not to exceed
 the cooling and electrical capacity of the rack. This is what we use to 
do a
 decade ago at a mini-computer company. We would configure systems from
 Listed racks, cpus, disks, tapes, etc.

RRR. So after we obtained the UL listed for rack (model ABC-001), then we 
configure, add recognized disks, recognized tapes ...etc. etc.. now it 
become new model (DEF-001). Do we have to submit this new model for 
certification again ???.


 Now to Jim's point. There is no law that requires one agency to accept the
 certification marks of another agency. For example, UL will not accept 
ETL
 marks on components and both are NRTLS. The only way one agency will 
accept
 the marks of another is if there is an agreement between them. The CB 
scheme
 is one good example. CSA and UL have an agreement to accept each others 
test
 data I believe, but I don't believe that they will accept each others 
marks.

RRR. They don't accept each others mark, but would they review and accept 
test data???

Tac Pham
HC Power

   --
   From:  Jim Eichner [SMTP:jeich...@statpower.com]
   Sent:  Tuesday, March 09, 1999 3:23 PM
   To:  'EMC-PSTC - forum'
   Subject:  RE: Rack System Safety (UL1950/EN 60950) Questions

   Re Richard's item 5)...

5.UL requires that all internal equipment be UL Listed or
Recognized.
   
   If that is true, then the value of the CSA/NRTL mark, and conversely
 the
   cUL mark if CSA plays this way too, is highly questionable.  Do you
 have
   a direct-from-UL interpretation saying that they are not accepting
 the
   CSA/NRTL mark?  If so, I would expect CSA to take action to defend
 its
   mark, and UL to have no firm ground to stand on!

   Comments?

   Jim Eichner
   Statpower Technologies Corporation
   jeich...@statpower.com
   http://www.statpower.com
   Any opinions expressed are those of my invisible friend, who really
   exists.  Honest.




-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


Re: Rack System Safety (UL1950/EN 60950) Questions

1999-03-10 Thread Rich Nute



Hello from San Diego:


I said:

  1. For the North America, does a NEMA 125 V, 20 A plug meet the 
  pluggable B definition?
   
   No.  The objective of the Pluggable Type B connection is that
   of a reliable, non-defeatable earth connection.  The NEMA 20 A 
   plug uses the same earthing connection as the NEMA 15 A plug.  
   The 15 A plug is notorious for having the earthing connection
   destroyed or removed in use.

A colleague has pointed out that the NEMA 20 A plug is indeed
accepted by some North American certification houses as meeting 
the Pluggable Type B definition.

The thinking is twofold:  1) the 20 A receptacle is ALWAYS a 
grounding type, and 2) the 20 A plug is not subject to the same
abuse as the 15 A plug.


Best regards,
Rich



-
 Richard Nute  Product Safety Engineer
 Hewlett-Packard Company   Product Regulations Group 
 AiO Division  Tel   :   +1 619 655 3329 
 16399 West Bernardo Drive FAX   :   +1 619 655 4979 
 San Diego, California 92127   e-mail:  ri...@sdd.hp.com 
-






-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


Re: Rack System Safety (UL1950/EN 60950) Questions

1999-03-09 Thread ron_pickard
 Peter,
 
 Some experiences I have had in past lives follow each of your questions. My 
 responses are brief due to lack of time. I hope this helps.
 
 Anyone else, please feel free to comment.
 
 Best regards,
 Ron Pickard
 ron_pick...@hypercom.com


__ Reply Separator _
Subject: Rack System Safety (UL1950/EN 60950) Questions 
Author:  pe...@itl.co.il (Peter Merguerian) at INTERNET
List-Post: emc-pstc@listserv.ieee.org
Date:3/9/99 6:26 PM


Dear All,
 
I would like to know some of your professional advice on some 
issues reagrding rack systems to be evaluated to UL1950/EN 60 
950.
 
1. For the North America, does a NEMA 125 V, 20 A plug meet the 
pluggable B definition?

 R. I must say no. A pluggable type B plug is of the industrial 
 grade (e.g., NEMA twist lock, IEC309, etc.). Anyone correct me if 
 I'm off base here, but an industrial plug (type B) is not normally 
 found in a residential or light commercial (office) environment.
 
2. What are some plug configurations which will meet the 
pluggable B equipment requirements for North America and 
Europe?

 R. See above.
 
3.  Does anyone have experience with UL and/or CSA and/or TUV when 
testing a unit employing a Recognized/Certified/Approved computer 
type totally enclosed power supply? I am interested to know if 
temperatures should be monitored within such a power supply. So 
far, I have been asked to thermocouple various points within the 
power supply and as you all know, it could get very crowded in 
there. I am interested to know if someone out there knows if such 
a waiver exists for totally enclosed Approved power supplies.

 R. Its a pain, I know, but I see no way for you to avoid having 
 to theromcouple points in the power supply as part of your system 
 safety tests. How else are you to verify that the power supply is 
 still within the temperature limits required by the safety 
 standard of your product.
 
4. When conducting stability tests for rack systems, should all the 
serviceable card cages be extended out or is it enough to do it one 
at a time.

 R. 4.1.1 of UL1950 deals with the subject of stability. If the rack 
 system does become unstable with more than 1 cage extended, then a 
 stabilizing means must be employed or a warning must be 
 conspicuously placed to prevent that.
 
5. For a CSA NRTLC unit employed in the rack system, does 
anyone know if the CSA NRTLC Mark is automatically accepted by 
UL or does UL require that the unit must be re-investigated and 
placed under their Follow-Up Program?

 R. I have no experience with this, but UL will likely need 
 detailed information in the form of the equipment's CSA 
 certification report to include test data. After all, if UL 
 allows you to put their mark on your product, I would think 
 that they should want make sure all is ok first. I would 
 suggest that you contact your friendly UL engineer for more 
 details.
 
6. Has the US Robotics Listed Sporster card modem been 
evaluated to UL1950 Third Edition?

 R. I have no idea. I would suggest contacting US Robotics 
 and/or look into UL's Recognized Component Directory or 
 yellow book.
 
7. Can I List/Certify a rack system to UL1950 Third Edition if the 
units within it have been Listed/Certified to UL1950 First and/or 
Second Editions? I do not think so, but am interested to hear your 
opinions.

 R. In my experience, I would have to say no. UL1950 1st/2nd 
 Editions are significantly different from the 3rd Edition and even 
 the 3/1/98 revision made significant changes to the 3rd Edition. 
 Doing what you suggest may be mixing apples and oranges. UL should 
 be able to tell you what they need. BTW, see page 11 of UL1950 3rd 
 Edition for effectivity dates.
 
8. How is a CB test report done for a rack system which consists 
of previously Listed/Certified/Approved units? Does the CB scheme 
Recognize the Approvals of the various test agencies 
(UL/CSA/TUV)?
 
 R. In my experience, it's most important that the individual 
 components/sub-systems meet the requirements that would be acceptable to the 
 applicable standard of your product as it relates to the CB Scheme. This can 
be 
 done as a collection of documents from reputable authorities* such as 
licenses, 
 approval certificates, test reports, etc., each of which connect the 
respective 
 components/sub-systems to the requirements. These documents should then be 
made 
 a part of the greater CB test report.
 
 * CB Scheme member NCBs preferred.
 
Thanks in advance.
 
 
PETER S. MERGUERIAN
MANAGING DIRECTOR
PRODUCT TESTING DIVISION
I.T.L. (PRODUCT TESTING) LTD.
HACHAROSHET 26, P.O.B. 211
OR YEHUDA 60251, ISRAEL
 
TEL: 972-3-5339022
FAX: 972-3-5339019
E-MAIL: pe...@itl.co.il
Visit our Website: http://www.itl.co.il
 


-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes). 

RE: Rack System Safety (UL1950/EN 60950) Questions

1999-03-09 Thread Jim Eichner
Re Richard's item 5)...

 5.UL requires that all internal equipment be UL Listed or
 Recognized.
 
If that is true, then the value of the CSA/NRTL mark, and conversely the
cUL mark if CSA plays this way too, is highly questionable.  Do you have
a direct-from-UL interpretation saying that they are not accepting the
CSA/NRTL mark?  If so, I would expect CSA to take action to defend its
mark, and UL to have no firm ground to stand on!  

Comments?

Jim Eichner
Statpower Technologies Corporation
jeich...@statpower.com
http://www.statpower.com
Any opinions expressed are those of my invisible friend, who really
exists.  Honest.  


 -Original Message-
 From: WOODS, RICHARD [SMTP:wo...@sensormatic.com]
 Sent: Tuesday, March 09, 1999 11:15 AM
 To:   emc-p...@majordomo.ieee.org; t...@world.std.com
 Subject:  RE: Rack System Safety (UL1950/EN 60950) Questions
 
 1.Peter, equipment with the standard NEMA plug is considered to be
 Class A.. 
 2.Equipment using the heavy duty Industrial plugs complying with
 IEC
 are considered to be Class B. I have never seen those used inside rack
 mounted equipment.
 3.If the power supply is UL Listed, then temperature
 measurements
 are not required. However, most power supplies are categorized as
 Recognized and are therefore incomplete in construction - that is,
 they
 cannot pass the safety requirements for a stand alone power supply.
 Temperature measurements will be required.
 4.Stability is performed in a worst case situation, but reason is
 also
 taken into account. Most likely, you will determine that it is
 possible and
 reasonable to assume that more than one assembly can be extending at
 the
 same time.
 5.UL requires that all internal equipment be UL Listed or
 Recognized.
 
 ---
   From:  pe...@itl.co.il [SMTP:pe...@itl.co.il]
   Sent:  Tuesday, March 09, 1999 11:26 AM
   To:  emc-p...@majordomo.ieee.org; t...@world.std.com
   Subject:  Rack System Safety (UL1950/EN 60950) Questions
 
   Dear All,
 
   I would like to know some of your professional advice on some 
   issues reagrding rack systems to be evaluated to UL1950/EN 60 
   950.
 
   1. For the North America, does a NEMA 125 V, 20 A plug meet the 
   pluggable B definition?
 
   2. What are some plug configurations which will meet the 
   pluggable B equipment requirements for North America and 
   Europe?
 
   3.  Does anyone have experience with UL and/or CSA and/or TUV 
   when testing a unit employing a Recognized/Certified/Approved 
   computer type totally enclosed power supply? I am interested
 to 
   know if temperatures should be monitored within such a power 
   supply. So far, I have been asked to thermocouple various points
 
   within the power supply and as you all know, it could get very 
   crowded in there. I am interested to know if someone out there 
   knows if such a waiver exists for totally enclosed Approved
 power 
   supplies.
 
   4. When conducting stability tests for rack systems, should all
 the 
   serviceable card cages be extended out or is it enough to do it
 one 
   at a time.
 
   5. For a CSA NRTLC unit employed in the rack system, does 
   anyone know if the CSA NRTLC Mark is automatically accepted by 
   UL or does UL require that the unit must be re-investigated and 
   placed under their Follow-Up Program?
 
   6. Has the US Robotics Listed Sporster card modem been 
   evaluated to UL1950 Third Edition?
 
   7. Can I List/Certify a rack system to UL1950 Third Edition if
 the 
   units within it have been Listed/Certified to UL1950 First
 and/or 
   Second Editions? I do not think so, but am interested to hear
 your 
   opinions.
 
   8. How is a CB test report done for a rack system which consists
 
   of previously Listed/Certified/Approved units? Does the CB
 scheme 
   Recognize the Approvals of the various test agencies 
   (UL/CSA/TUV)?
 
   Thanks in advance.
 
 
   PETER S. MERGUERIAN
   MANAGING DIRECTOR
   PRODUCT TESTING DIVISION
   I.T.L. (PRODUCT TESTING) LTD.
   HACHAROSHET 26, P.O.B. 211
   OR YEHUDA 60251, ISRAEL
 
   TEL: 972-3-5339022
   FAX: 972-3-5339019
   E-MAIL: pe...@itl.co.il
   Visit our Website: http://www.itl.co.il
 
   -
   This message is coming from the emc-pstc discussion list.
   To cancel your subscription, send mail to majord...@ieee.org
   with the single line: unsubscribe emc-pstc (without the
   quotes).  For help, send mail to ed.pr...@cubic.com,
   j...@gwmail.monarch.com, ri...@sdd.hp.com, or
   roger.volgst...@compaq.com (the list administrators).
 
 -
 This message is coming from the emc-pstc discussion list.
 To cancel your subscription, send mail to majord...@ieee.org
 with the single line: unsubscribe emc-pstc (without the
 quotes).  For help, send

Re: Rack System Safety (UL1950/EN 60950) Questions

1999-03-09 Thread Rich Nute


Hello Peter:


   1. For the North America, does a NEMA 125 V, 20 A plug meet the 
   pluggable B definition?

No.  The objective of the Pluggable Type B connection is that
of a reliable, non-defeatable earth connection.  The NEMA 20 A 
plug uses the same earthing connection as the NEMA 15 A plug.  
The 15 A plug is notorious for having the earthing connection
destroyed or removed in use.

   2. What are some plug configurations which will meet the 
   pluggable B equipment requirements for North America and 
   Europe?

I'm afraid I can't answer this question.  I suggest you ask UL
or CSA.

   3.  Does anyone have experience with UL and/or CSA and/or TUV 
   when testing a unit employing a Recognized/Certified/Approved 
   computer type totally enclosed power supply? I am interested to 
   know if temperatures should be monitored within such a power 
   supply. So far, I have been asked to thermocouple various points 
   within the power supply and as you all know, it could get very 
   crowded in there. I am interested to know if someone out there 
   knows if such a waiver exists for totally enclosed Approved power 
   supplies.

Any component, including component power supplies, must be tested
for temperature rise in the end-product configuration.  It is not
necessary to measure all of the same points as was done for the
power supply safety qualification.  I choose a sub-set of those,
especially the highest temperatures.  If the highest temperatures
are okay in the end-product, then it is a good assumption that the
lower temperatures are also okay.  I would expect that you would
only need to test 20% of the total test points.

   4. When conducting stability tests for rack systems, should all the 
   serviceable card cages be extended out or is it enough to do it one 
   at a time.

Testing is almost always the worst-case condition, regardless whether
such condition is not expected in normal service.  Doors, drawers,
etc., which may be moved for servicing by the operator or by service 
personnel are placed in their most infavourable position, consistent
with the manufacturer's instructions.

   5. For a CSA NRTLC unit employed in the rack system, does 
   anyone know if the CSA NRTLC Mark is automatically accepted by 
   UL or does UL require that the unit must be re-investigated and 
   placed under their Follow-Up Program?

The CSA NRTL mark means the unit is acceptable for use in any USA
workplace.  The unit need not be also certified by UL.

If CSA certifies the unit to the bi-national standard, then the
certification is accepted by UL if you should submit the unit to
UL as part of another equipment.  Otherwise, it does not make much
sense to also submit the unit to UL.

Both CSA and UL and all other NRTLs have follow-up programs.  This 
is a NRTL requirement.

   6. Has the US Robotics Listed Sporster card modem been 
   evaluated to UL1950 Third Edition?

If so, such certification would be marked on the unit or on the
packaging accompanying the unit.  In addition, it would appear in
the UL Listed Products book.

   7. Can I List/Certify a rack system to UL1950 Third Edition if the 
   units within it have been Listed/Certified to UL1950 First and/or 
   Second Editions? I do not think so, but am interested to hear your 
   opinions.

No.  All certifications of components and sub-systems must be to the
same or newer edition of the standard as for the entire equipment.  
(In most cases, certification to newer editions also means compliance 
to former editions.)

By the way, the differences between editions rarely mean the hardware
does not comply with newer requirements.  Re-evaluating the hardware 
to the newer editions rarely results in a need to change the hardware.  
Its an exercise which costs the submittor money, and benefits the 
certifier, but has no effect on the safety of the equipment, and has 
no benefit to the customer.  I have several products certified to IEC
60950 Amd 1, 2, and 3.  We're adding some new models to these families.
All new models must now be evaluated to Amds 1, 2, 3, and 4.  No
hardware changes, but I must go through a complete new evaluation
because Amd 4 is now in effect.  Since safety is realized in the 
hardware, and since there is no hardware change, what is the value of
Amd 4?

   8. How is a CB test report done for a rack system which consists 
   of previously Listed/Certified/Approved units? Does the CB scheme 
   Recognize the Approvals of the various test agencies 
   (UL/CSA/TUV)?

A CB for a rack system must include CBs for each of the individual
parts of the system.  Or, each individual part must be evaluated in
accordance with the standard.  The NCB can use the listing/certification/
approval reports from other NCBs to reduce the amount of evaluation of
those parts.  But, the CB Report it issues must cover everything in the 
rack, either directly included in the CB Report or included as attachment 
CB Reports.


Best regards,
Rich




RE: Rack System Safety (UL1950/EN 60950) Questions

1999-03-09 Thread John Juhasz
Peter,

Responses are below each question. (NOTE: The answers to these questions are
easily found in the UL 1950 3rd ed. standard).

-Original Message-
From: pe...@itl.co.il [mailto:pe...@itl.co.il]
Sent: Tuesday, March 09, 1999 11:26 AM
To: emc-p...@majordomo.ieee.org; t...@world.std.com
Subject: Rack System Safety (UL1950/EN 60950) Questions


Dear All,

I would like to know some of your professional advice on some 
issues reagrding rack systems to be evaluated to UL1950/EN 60 
950.

1. For the North America, does a NEMA 125 V, 20 A plug meet the 
pluggable B definition?

Answer: As per UL1950 3rd Ed/CAN CSA C22.2 No.950 the answer is maybe.
If you are just talking a NEMA 5-20P then it is pluggable equipment A.
That is - non-industrial. If you use a NEMA L5-20P ('L' for locking or more
commonly refered to as 'Twist-Lock') then the answer is Yes. Pluggable
equipment Type B 
requires an 'industrial type plug or appliance coupler.

2. What are some plug configurations which will meet the 
pluggable B equipment requirements for North America and 
Europe?

Answer: Quote from UL1950 Equipment iwhich is intended for connection to
the building power supply wiring via an industrial plug and socket-outlet or
an appliance coupler, or both, complying with IEC 309 or with national
standards for similar applications.

3.  Does anyone have experience with UL and/or CSA and/or TUV 
when testing a unit employing a Recognized/Certified/Approved 
computer type totally enclosed power supply? I am interested to 
know if temperatures should be monitored within such a power 
supply. So far, I have been asked to thermocouple various points 
within the power supply and as you all know, it could get very 
crowded in there. I am interested to know if someone out there 
knows if such a waiver exists for totally enclosed Approved power 
supplies.

Answer: If said unit is located WITHIN YOUR enclosed product, you still need
to take temperature measurements. This is because since it is enclosed in
your product, you could increase the ambient temperature of the power
supply. Your product will be tested with all openings closed to determine if
the internal temperatures of the pwoer supply exceed that allowed
temperature rises. You are affecting the power supply's environment.
The power supply was originally tested in free air, now you are enclosing it
in your unit. 

4. When conducting stability tests for rack systems, should all the 
serviceable card cages be extended out or is it enough to do it one 
at a time.

Answer: All the drawers could be extended out. They check the unit in its 
most unfavorable condition.

5. For a CSA NRTLC unit employed in the rack system, does 
anyone know if the CSA NRTLC Mark is automatically accepted by 
UL or does UL require that the unit must be re-investigated and 
placed under their Follow-Up Program?

Answer: The unit will not typically have to be re-investigated. If there is
cause for concern, they may require a temperature evaluation.

6. Has the US Robotics Listed Sporster card modem been 
evaluated to UL1950 Third Edition?

Answer: Call US Robotics.

7. Can I List/Certify a rack system to UL1950 Third Edition if the 
units within it have been Listed/Certified to UL1950 First and/or 
Second Editions? I do not think so, but am interested to hear your 
opinions.

Answer: I believe you can do this. After April 1, 2000 products that were
previously evaluated by UL to the requirements in other existing standards
(like 1st/second ed.) may continue to be approved until April 1, 2005
without further investigation, provided no significant changes or revisions
are made to such products.

8. How is a CB test report done for a rack system which consists 
of previously Listed/Certified/Approved units? Does the CB scheme 
Recognize the Approvals of the various test agencies 
(UL/CSA/TUV)?

Answer: I can't answer this one. Anyone else??


John A. Juhasz
Product Qualification 
Compliance Engr.

Fiber Options, Inc.
80 Orville Dr. Suite 102
Bohemia, NY 11716 USA

Tel: 516-567-8320 ext. 24
Fax: 516-567-8322 

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).


RE: Rack System Safety (UL1950/EN 60950) Questions

1999-03-09 Thread WOODS, RICHARD
1.  Peter, equipment with the standard NEMA plug is considered to be
Class A.. 
2.  Equipment using the heavy duty Industrial plugs complying with IEC
are considered to be Class B. I have never seen those used inside rack
mounted equipment.
3.  If the power supply is UL Listed, then temperature measurements
are not required. However, most power supplies are categorized as
Recognized and are therefore incomplete in construction - that is, they
cannot pass the safety requirements for a stand alone power supply.
Temperature measurements will be required.
4.  Stability is performed in a worst case situation, but reason is also
taken into account. Most likely, you will determine that it is possible and
reasonable to assume that more than one assembly can be extending at the
same time.
5.  UL requires that all internal equipment be UL Listed or Recognized.

---
From:  pe...@itl.co.il [SMTP:pe...@itl.co.il]
Sent:  Tuesday, March 09, 1999 11:26 AM
To:  emc-p...@majordomo.ieee.org; t...@world.std.com
Subject:  Rack System Safety (UL1950/EN 60950) Questions

Dear All,

I would like to know some of your professional advice on some 
issues reagrding rack systems to be evaluated to UL1950/EN 60 
950.

1. For the North America, does a NEMA 125 V, 20 A plug meet the 
pluggable B definition?

2. What are some plug configurations which will meet the 
pluggable B equipment requirements for North America and 
Europe?

3.  Does anyone have experience with UL and/or CSA and/or TUV 
when testing a unit employing a Recognized/Certified/Approved 
computer type totally enclosed power supply? I am interested to 
know if temperatures should be monitored within such a power 
supply. So far, I have been asked to thermocouple various points 
within the power supply and as you all know, it could get very 
crowded in there. I am interested to know if someone out there 
knows if such a waiver exists for totally enclosed Approved power 
supplies.

4. When conducting stability tests for rack systems, should all the 
serviceable card cages be extended out or is it enough to do it one 
at a time.

5. For a CSA NRTLC unit employed in the rack system, does 
anyone know if the CSA NRTLC Mark is automatically accepted by 
UL or does UL require that the unit must be re-investigated and 
placed under their Follow-Up Program?

6. Has the US Robotics Listed Sporster card modem been 
evaluated to UL1950 Third Edition?

7. Can I List/Certify a rack system to UL1950 Third Edition if the 
units within it have been Listed/Certified to UL1950 First and/or 
Second Editions? I do not think so, but am interested to hear your 
opinions.

8. How is a CB test report done for a rack system which consists 
of previously Listed/Certified/Approved units? Does the CB scheme 
Recognize the Approvals of the various test agencies 
(UL/CSA/TUV)?

Thanks in advance.


PETER S. MERGUERIAN
MANAGING DIRECTOR
PRODUCT TESTING DIVISION
I.T.L. (PRODUCT TESTING) LTD.
HACHAROSHET 26, P.O.B. 211
OR YEHUDA 60251, ISRAEL

TEL: 972-3-5339022
FAX: 972-3-5339019
E-MAIL: pe...@itl.co.il
Visit our Website: http://www.itl.co.il

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).