I'd like to revisit a thread from early February where we were discussing
Enphase microinverters going off line due to utility power quality issues
when Pinging of smart meters occur.

 

I have a system where I was told by Enphase that they applied their software
fix in late March, but in this case it did work in fixing the problem of the
inverters dropping for anywhere from 5 minutes to an hour a couple of times
per day. The drops are not regular and now it appears that they are not
connected to the pinging of the meters on my customers site as we had the
utility change their schedule to only ping at midnight.

 

We are still seeing AC Frequency Out of Range errors almost daily on our
M-215 inverters. Sometimes it is for only several inverters and other times
up to the whole array of 32 inverters. On my other Enphase systems have no
problems.

 

What other issues besides utility pinging of my customers smart meter could
be causing the problem?

 

Could the pinging of the neighbors meters by the utility off of the same
transformer be affecting the Enphase M-215's? I'm suspicious of something
other than this because the errors occur at random times that appear
unrelated to utility pinging.

 

Thanks,

Dave

 

David Palumbo

Independent Power LLC 

462 Solar Way Drive

Hyde Park, VT 05655

www.independentpowerllc.com 

Vermont Solar Partner

25 Years Experience, (802) 888-7194 

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fuse sizing in battery circuits

2013-04-15 Thread August Goers
Hi Drake,



The Sunny Island System runs at 48 V nominal so I don't believe 250.162(A)
applies. We have some really savvy inspectors in the Bay Area and they were
happy for us to be ungrounded since we're operating at 48 V. Yes, the
actual voltage might go above 50 V when charging but I believe it is the
nominal voltage that the code cares about.



Best,



August



*From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:
re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Drake
*Sent:* Saturday, April 13, 2013 12:14 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Fuse sizing in battery circuits



Is it possible that not grounding the DC on an inverter could be code
compliant?  In the past, we were always required to install grounding
electrode conductors to the DC negative, as required for grounding Direct
Current systems (250 VIII).

Maybe grounding can be eliminated in a purely AC coupled system due to the
fact that the system is not supplying premise wiring. Maybe the DC can be
considered as an integral part of the system supplying the AC.

The rules for grounding DC are stated below.

250.162 Direct current Circuits and Systems to Be Grounded
(A) Two-Wire, Direct-Current Systems. A 2-wire, dc system supplying
premises wiring and operating at greater than 50 volts but not greater than
300 volts shall be grounded.
Exception No. 1:  A system equipped with a ground detector and supplying
only industrial equipment in limited areas shall not be required to be
grounded.
Exception No. 2:  A rectifier-derived dc system supplied from an ac system
complying with 250.20 shall not be required to be grounded.
Exception No. 3:  Direct-current fire alarm circuits having a maximum
current of 0.030 ampere as specified in Article 760, Part III, shall not be
required to be grounded.

In a Sunny Island system there is no charge control, nothing else in the DC
besides the battery and battery cables.  Does not grounding the negative
really meet code requirements in the US ? Are the inverter cables not
considered to be premise wiring?

Thanks,

Drake


 At 03:56 PM 4/10/2013, you wrote:

Content-Class: urn:content-classes:message
Content-Language: en-US
Content-Type: multipart/alternative;

boundary=_000_B448FC9E37458B469E77EA0BB954AD4702BD99AC6Emailbox01_

August:

The SI can run with an ungrounded battery or a grounded battery.
With the internal breaker it is set up for a negative ground battery.
I believe the manual says ground at the battery terminal.
If you chose to go ungrounded you will need to have an OCPD in both battery
+ and battery – (all ungrounded conductors).

I am pretty sure the SI is not internally bonded to ground.
This is normal in the rest of the world.
Mine are running with an ungrounded battery and there isolation between
battery and ground.

Best Regards,

John Berdner
General Manager, North America

SolarEdge Technologies, Inc.
3347 Gateway Boulevard, Fremont CA 94538 USA  *(*Please note of our new
address.)*
T: 510.498.3200, X 747
M: 530.277.4894

*From:* re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.orgre-wrenches-boun...@lists.re-wrenches.org]
*On Behalf Of *August Goers
*Sent:* Wednesday, April 10, 2013 9:45 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Fuse sizing in battery circuits

Hi All -

As a slightly separate topic, should we fuse both the positive and negative
battery lines with an SMA Sunny Island? I believe that the negative is
grounded so should not be fused but I've heard conflicting stories from
tech support.

Thanks,

August

*From:* re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.orgre-wrenches-boun...@lists.re-wrenches.org]
*On Behalf Of *Drake
*Sent:* Wednesday, April 10, 2013 5:52 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Fuse sizing in battery circuits

boB,

SMA does recommend protecting Sunny Islands with a fuse on the battery,
even though the breakers on the units are rated for 10,000 Amps.  Are the
SI breakers inferior others you have mentioned?

Thanks,

Drake



At 12:14 AM 4/10/2013, you wrote:

After 100's of thousands of  inverters having been shipped in the last many
years
and thousands of inverters broken and shorting the battery terminals, there
has
never been (to our knowledge) one breaker that has not tripped.

The Midnite site lists the AIC rating of all our breakers I believe.

The Carling F series of Magnetic-Hydraulic breakers poop sheet is here...

http://www.carlingtech.com/sites/default/files/documents/F-Series_Details_%26_COS_0.pdf

I guess there isn't a graph of AIC vs. voltage on their F series web page
but we remember
them showing us figures or a graph that says those breakers have an AIC of
more than
100,000 amps at 48 volts.  We'll try to find that info or you may be able
to get that
from Carling.

I have, many times, directly connected these breakers across good L-16
battery strings
to demonstrate the left-hand rule to people where the 4/0 

[RE-wrenches] Micro-inverters for 3-phase 220/127 in Mexico

2013-04-15 Thread Larry Crutcher, Starlight Solar Power Systems
Wrenches, 

A customer in Mexico wants to start with about 10kW PV. They have a 225 kva 
transformer supplying 220/127 volt 3-phase to the property. They are adding 
buildings/roof space in several stages over the next 4 years and want to grow 
the installation to 120kW of PV solar power.

Manufacturer data sheets are not real clear. Who makes micro-inverters suitable 
for this? I know Enphase does not.

Thank you,

Larry Crutcher
Starlight Solar Power Systems







___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fuse sizing in battery circuits

2013-04-15 Thread Ray Walters

Hi August;

250.162(A) says operating at greater than 50 v, which a 48 v nominal 
system operates most of the time at over 50 v, at least when solar 
charging and/or selling back.
We used to get dinged many years ago for using breakers rated at 50v dc 
on 48 v systems.  John Wiles used to insist we use the highest possible 
voltage (Voc of modules on coldest day)
Personally I prefer ungrounded systems, so I'm not saying there's 
anything wrong from a safety stand point, just that inspectors here 
don't see it the same way.


R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 4/15/2013 2:20 PM, August Goers wrote:


Hi Drake,

The Sunny Island System runs at 48 V nominal so I don't believe 
250.162(A) applies. We have some really savvy inspectors in the Bay 
Area and they were happy for us to be ungrounded since we're operating 
at 48 V. Yes, the actual voltage might go above 50 V when charging but 
I believe it is the nominal voltage that the code cares about.


Best,




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Enphase AC Frequency Out Of Range

2013-04-15 Thread Kent Osterberg

Dave,

The problem occurs when the kWh meter sends data. I would expect any 
neighbors' meters on the same transformer to cause trouble. And probably 
neighbors that are not on the same transformer too.


Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com
t: 541-568-4882

On 4/15/2013 1:12 PM, Dave Palumbo wrote:


I'd like to revisit a thread from early February where we were 
discussing Enphase microinverters going off line due to utility power 
quality issues when Pinging of smart meters occur.


I have a system where I was told by Enphase that they applied their 
software fix in late March, but in this case it did work in fixing the 
problem of the inverters dropping for anywhere from 5 minutes to an 
hour a couple of times per day. The drops are not regular and now it 
appears that they are not connected to the pinging of the meters on my 
customers site as we had the utility change their schedule to only 
ping at midnight.


We are still seeing AC Frequency Out of Range errors almost daily on 
our M-215 inverters. Sometimes it is for only several inverters and 
other times up to the whole array of 32 inverters. On my other Enphase 
systems have no problems.


What other issues besides utility pinging of my customers smart meter 
could be causing the problem?


Could the pinging of the neighbors meters by the utility off of the 
same transformer be affecting the Enphase M-215's? I'm suspicious of 
something other than this because the errors occur at random times 
that appear unrelated to utility pinging.


Thanks,

Dave

David Palumbo

Independent Power LLC

462 Solar Way Drive

Hyde Park, VT 05655**

*/www.independentpowerllc.com /*

Vermont Solar Partner

25 Years Experience, (802) 888-7194

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Enphase AC Frequency Out Of Range

2013-04-15 Thread penobscotsolar
Dave,
  In multiple conversations about this with both the utility and Enphase
there was concern about high inductive loads, possibly from the paper
mill in the town, that turned out not to be the case. The fix Enphase
developed worked, but I thought it would be worth mentioning.

Daryl


 Dave,

 The problem occurs when the kWh meter sends data. I would expect any
 neighbors' meters on the same transformer to cause trouble. And probably
 neighbors that are not on the same transformer too.

 Kent Osterberg
 Blue Mountain Solar, Inc.
 www.bluemountainsolar.com
 t: 541-568-4882

 On 4/15/2013 1:12 PM, Dave Palumbo wrote:

 I'd like to revisit a thread from early February where we were
 discussing Enphase microinverters going off line due to utility power
 quality issues when Pinging of smart meters occur.

 I have a system where I was told by Enphase that they applied their
 software fix in late March, but in this case it did work in fixing the
 problem of the inverters dropping for anywhere from 5 minutes to an
 hour a couple of times per day. The drops are not regular and now it
 appears that they are not connected to the pinging of the meters on my
 customers site as we had the utility change their schedule to only
 ping at midnight.

 We are still seeing AC Frequency Out of Range errors almost daily on
 our M-215 inverters. Sometimes it is for only several inverters and
 other times up to the whole array of 32 inverters. On my other Enphase
 systems have no problems.

 What other issues besides utility pinging of my customers smart meter
 could be causing the problem?

 Could the pinging of the neighbors meters by the utility off of the
 same transformer be affecting the Enphase M-215's? I'm suspicious of
 something other than this because the errors occur at random times
 that appear unrelated to utility pinging.

 Thanks,

 Dave

 David Palumbo

 Independent Power LLC

 462 Solar Way Drive

 Hyde Park, VT 05655**

 */www.independentpowerllc.com /*

 Vermont Solar Partner

 25 Years Experience, (802) 888-7194

 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Micro-inverters for 3-phase 220/127 in Mexico

2013-04-15 Thread Nick Soleil
Hi Larry,

Enphase is supplying microinverters into Mexico and supporting the 127/220
applications.  We have hundreds of installations installed at this voltage
now.  Feel free to contact me off-line, and I would be happy to discuss the
details.


On Mon, Apr 15, 2013 at 1:25 PM, Larry Crutcher, Starlight Solar Power
Systems la...@starlightsolar.com wrote:

 Wrenches,

A customer in Mexico wants to start with about 10kW PV. They have a
 225 kva transformer supplying 220/127 volt 3-phase to the property. They
 are adding buildings/roof space in several stages over the next 4 years and
 want to grow the installation to 120kW of PV solar power.

 Manufacturer data sheets are not real clear. Who makes micro-inverters
 suitable for this? I know Enphase does not.

 Thank you,

 Larry Crutcher
 Starlight Solar Power Systems








 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org





-- 

Cordially,

*Nick Soleil*

*Field Applications Engineer
*

*Enphase Energy*

Mobile: (707) 321-2937


**

*Enphase Commercial Solar.*
*Limitless.*http://www.enphase.com/commercial?utm_source=emailutm_medium=sigutm_campaign=Comm2012

*
*http://www.enphase.com/commercial?utm_source=emailutm_medium=sigutm_campaign=Comm2012

1420 North McDowell

Petaluma, CA 94954

www.enphase.com http://www.enphaseenergy.com/

P: (707) 763-4784 x7267

F: (707) 763-0784

E: nsol...@enphaseenergy.com

[image: nabcep logo] Certified Solar PV Installer #03262011-300

“Don’t get me wrong: I love nuclear energy! It’s just that I prefer fusion
to fission. And it just so happens that there’s an enormous fusion reactor
safely banked a few million miles from us. It delivers more than we could
ever use in just about 8 minutes. And it’s wireless! .”

- William McDonough



This email message is for the sole use of the intended recipient(s) and may 
contain confidential and/or privileged information. If you are not an intended 
recipient, you may not review, use, copy, disclose or distribute this message. 
If you received this message in error, please contact the sender by reply email 
and destroy all copies of the original message. 

image002.jpg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Micro-inverters for 3-phase 220/127 in Mexico

2013-04-15 Thread Bill Hoffer
Larry

I believe that APS ( Bluefrog http://bluefrogsolar.com/aps-inverters)
micro inverters can be adjusted down to 180 VAC, so they should  work line
to line in your application. I know that their spec sheet and manual do not
indicate that, but I have installed them in adjusted for a 208 VAC and they
have been sending adjusted units to Hawaii.  You will probably have to
contact them directly to see what can be done.

Bill


On Mon, Apr 15, 2013 at 1:25 PM, Larry Crutcher, Starlight Solar Power
Systems la...@starlightsolar.com wrote:

 Wrenches,

 A customer in Mexico wants to start with about 10kW PV. They have a 225
 kva transformer supplying 220/127 volt 3-phase to the property. They are
 adding buildings/roof space in several stages over the next 4 years and
 want to grow the installation to 120kW of PV solar power.

 Manufacturer data sheets are not real clear. Who makes micro-inverters
 suitable for this? I know Enphase does not.

 Thank you,

 Larry Crutcher
 Starlight Solar Power Systems








 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org





-- 
Bill Hoffer
P.O. Box 1823
White Salmon, WA 98672
suneng...@gmail.com bhof...@sunergyengineeringservices.com
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org