[RE-wrenches] UPS disturbance with SMA Inverters

2014-08-04 Thread Carl Adams
Hello Wrenches,

I have a site which is experiencing nuisance disturbance of the computer
UPS systems at the site.  The site owner suspects this is due to the PV
system which is a 50 kW system using 6 SMA SunnyBoy inverters.  The
nuisance disturbance is a clicking noise in the UPS units.  The disturbance
is not enough to cause the UPS to engage, so it seems to be a small
disturbance on the AC power.   The site owner suspects the inverters are
the source of this disturbance since 1) It seems to only occur when we have
a good solar day.  2) If the inverters are shut down the problem goes away,
and if you start up the inverters the problem exhibits again.

The site was commissioned in March of 2012 and has had no problems till
this issue last month.  In reviewing the event log on Sunny Portal there
are no inverter anomalies.  SMA tech support had not run into this issue
and had no ideas, they too agree the inverters are not reporting any
anomalies.

The problem is not persistent but rather intermittent making this harder to
troubleshoot.

So my questions are
1) Has anyone else seen this sort of issue before, related to SMA SunnyBoy
inverters.
2) Can you recommend an AC power monitoring tool which would support
 frequency and voltage monitoring on the AC line.  Perhaps one data set on
the circuit feeding the computers and another on the inverter output
circuit.

For clarity the six SunnyBoys feed into an AC Combiner panel which backfeeds
into the building main distribution panel.  The service is 240V single
phase.

With Regards
Carl Adams, SunRock Solar
NABCEP Certified PV Installer
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] UPS disturbance with SMA Inverters

2014-08-04 Thread RE Ellison
How about disabling one inverter at a time when the disturbances are happening?

That might narrow it down to it being a single inverter.

Through the process of elimination you may be able to find out if it is a 
single inverter or a combination of inverters that makes it do it.

It might be a specific inverter or it might be a specific combination of 
inverters

I have seen APC UPS units click but not activate, in that case it was one 
inverter off grid and one UPS.

Somewhat irritating, I put it where I couldn't hear it to make the problem go 
away so to speak !

Later,
Bob ellison




Bob Ellison

 On Aug 4, 2014, at 10:29 AM, Carl Adams swingjun...@gmail.com wrote:
 
 Hello Wrenches,
 
 I have a site which is experiencing nuisance disturbance of the computer UPS 
 systems at the site.  The site owner suspects this is due to the PV system 
 which is a 50 kW system using 6 SMA SunnyBoy inverters.  The nuisance 
 disturbance is a clicking noise in the UPS units.  The disturbance is not 
 enough to cause the UPS to engage, so it seems to be a small disturbance on 
 the AC power.   The site owner suspects the inverters are the source of 
 this disturbance since 1) It seems to only occur when we have a good solar 
 day.  2) If the inverters are shut down the problem goes away, and if you 
 start up the inverters the problem exhibits again.
 
 The site was commissioned in March of 2012 and has had no problems till this 
 issue last month.  In reviewing the event log on Sunny Portal there are no 
 inverter anomalies.  SMA tech support had not run into this issue and had no 
 ideas, they too agree the inverters are not reporting any anomalies.
 
 The problem is not persistent but rather intermittent making this harder to 
 troubleshoot.
 
 So my questions are
 1) Has anyone else seen this sort of issue before, related to SMA SunnyBoy 
 inverters.
 2) Can you recommend an AC power monitoring tool which would support  
 frequency and voltage monitoring on the AC line.  Perhaps one data set on the 
 circuit feeding the computers and another on the inverter output circuit.
 
 For clarity the six SunnyBoys feed into an AC Combiner panel which backfeeds 
 into the building main distribution panel.  The service is 240V single phase.
 
 With Regards
 Carl Adams, SunRock Solar
 NABCEP Certified PV Installer
 ___
 List sponsored by Redwood Alliance
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out or update participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] UPS disturbance with SMA Inverters

2014-08-04 Thread Ray Walters
Is it possible that the inverters are raising line voltage high enough 
to make the UPS respond by clicking, but not high enough to have them 
actually trip?  I'm not familiar enough with UPS control structure, but 
it might run a quick test (the click) when the voltage gets close to its 
high voltage trip off.

Just a crazed monday morning idea.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 8/4/2014 8:50 AM, RE Ellison wrote:

How about disabling one inverter at a time when the disturbances are happening?

That might narrow it down to it being a single inverter.

Through the process of elimination you may be able to find out if it is a 
single inverter or a combination of inverters that makes it do it.

It might be a specific inverter or it might be a specific combination of 
inverters

I have seen APC UPS units click but not activate, in that case it was one 
inverter off grid and one UPS.

Somewhat irritating, I put it where I couldn't hear it to make the problem go 
away so to speak !

Later,
Bob ellison




Bob Ellison


On Aug 4, 2014, at 10:29 AM, Carl Adams swingjun...@gmail.com wrote:

Hello Wrenches,

I have a site which is experiencing nuisance disturbance of the computer UPS systems at the site.  
The site owner suspects this is due to the PV system which is a 50 kW system using 6 
SMA SunnyBoy inverters.  The nuisance disturbance is a clicking noise in the UPS units.  The 
disturbance is not enough to cause the UPS to engage, so it seems to be a small disturbance on the 
AC power.   The site owner suspects the inverters are the source of this disturbance 
since 1) It seems to only occur when we have a good solar day.  2) If the inverters are shut down 
the problem goes away, and if you start up the inverters the problem exhibits again.

The site was commissioned in March of 2012 and has had no problems till this 
issue last month.  In reviewing the event log on Sunny Portal there are no 
inverter anomalies.  SMA tech support had not run into this issue and had no 
ideas, they too agree the inverters are not reporting any anomalies.

The problem is not persistent but rather intermittent making this harder to 
troubleshoot.

So my questions are
1) Has anyone else seen this sort of issue before, related to SMA SunnyBoy 
inverters.
2) Can you recommend an AC power monitoring tool which would support  frequency 
and voltage monitoring on the AC line.  Perhaps one data set on the circuit 
feeding the computers and another on the inverter output circuit.

For clarity the six SunnyBoys feed into an AC Combiner panel which backfeeds 
into the building main distribution panel.  The service is 240V single phase.

With Regards
Carl Adams, SunRock Solar
NABCEP Certified PV Installer
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org




___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] UPS disturbance with SMA Inverters

2014-08-04 Thread Glenn Burt
I wonder if the UPS is grumbling about high voltage as the inverters push back 
current...

Glenn 

-Original Message-
From: Carl Adams swingjun...@gmail.com
Sent: ‎8/‎4/‎2014 10:29
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] UPS disturbance with SMA Inverters

Hello Wrenches,

I have a site which is experiencing nuisance disturbance of the computer
UPS systems at the site.  The site owner suspects this is due to the PV
system which is a 50 kW system using 6 SMA SunnyBoy inverters.  The
nuisance disturbance is a clicking noise in the UPS units.  The disturbance
is not enough to cause the UPS to engage, so it seems to be a small
disturbance on the AC power.   The site owner suspects the inverters are
the source of this disturbance since 1) It seems to only occur when we have
a good solar day.  2) If the inverters are shut down the problem goes away,
and if you start up the inverters the problem exhibits again.

The site was commissioned in March of 2012 and has had no problems till
this issue last month.  In reviewing the event log on Sunny Portal there
are no inverter anomalies.  SMA tech support had not run into this issue
and had no ideas, they too agree the inverters are not reporting any
anomalies.

The problem is not persistent but rather intermittent making this harder to
troubleshoot.

So my questions are
1) Has anyone else seen this sort of issue before, related to SMA SunnyBoy
inverters.
2) Can you recommend an AC power monitoring tool which would support
 frequency and voltage monitoring on the AC line.  Perhaps one data set on
the circuit feeding the computers and another on the inverter output
circuit.

For clarity the six SunnyBoys feed into an AC Combiner panel which backfeeds
into the building main distribution panel.  The service is 240V single
phase.

With Regards
Carl Adams, SunRock Solar
NABCEP Certified PV Installer
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] Ct Utility test requirement?

2014-08-04 Thread Allen Frishman
Wrenchers,
The Ct Utility company CLP requires the following as part of the verification 
test.
Because this is a three-phase service, the witness test must also demonstrate 
that the inverter shuts down upon loss of each individual phase

Any recommendations on how to do this test safely?
Al Frishman
AeonSolar

(917) 699-6641 - cell
(888) 460-2867
www.aeonsolar.com


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Ct Utility test requirement?

2014-08-04 Thread Rebekah Hren
Al,
I have witnessed this test in NC several times, but with medium voltage
connected systems, not systems connected to a building service.  A medium
voltage subcontractor used a disconnect stick to open one phase at a time
at the fused cutout point of delivery to the distribution network (on the
high side of the transformers) . We learned to do the test early in the
morning with the array divided in subsections to keep the current as low as
possible at the POD because there is an arc pulled when one phase is
opened.

The phase current was being monitored during the test to insure that the
inverters stopped exporting current to the other two phases when one phase
was lost.
It's been awhile, so there may be a better/safer way to do this test for MV
connected systems now that I'm not aware of...would be happy to hear about
it if so.

If this is a PV system connected to a building service this wouldn't be the
way to do this test.
Cheers,
Rebekah Hren



On Mon, Aug 4, 2014 at 11:24 AM, Allen Frishman amfr...@aeonsolar.com
wrote:

 Wrenchers,
 The Ct Utility company CLP requires the following as part of the
 verification test.
 Because this is a three-phase service, the witness test must also
 demonstrate that the inverter shuts down upon loss of each individual phase

 Any recommendations on how to do this test safely?

 *Al Frishman*
 AeonSolar

 *(917) 699-6641 %28917%29%20699-6641 - cell*
 *(888) 460-2867 %2%29%20460-2867*
 *www.aeonsolar.com http://www.aeonsolar.com/*


 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org





-- 
Tel: 336.266.8800
NABCEP Certified Solar PV Installation Professional™ 091209-85
NC Licensed Electrical Contractor
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] UPS disturbance with SMA Inverters

2014-08-04 Thread Carl Adams
Bob, Ray, Glenn,

Thanks for the responses.  We could cycle through the inverters and see if
it is one, or some combinations of inverters, which is causing the problem.
 This results in a minimum of 6 trials.  If it is a combination of
inverters  many more.

Any feedback on the idea of monitoring the AC circuits; computer feed and
combined inverter output?  Seems to me this might provide a one step
correlation between the event and the cause.  Just not sure what equipment
to suggest for this.

Could be there is some other cause, unrelated to the inverters.  AC unit
kicking on, etc.  Though they do not see any lights dimiming/brightening,
or any other notable change in electrical equipment at the sight.



On Mon, Aug 4, 2014 at 1:03 PM, Glenn Burt glenn.b...@glbcc.com wrote:

  I wonder if the UPS is grumbling about high voltage as the inverters
 push back current...

 Glenn
  --
 From: Carl Adams swingjun...@gmail.com
 Sent: ‎8/‎4/‎2014 10:29
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Subject: [RE-wrenches] UPS disturbance with SMA Inverters

 Hello Wrenches,

 I have a site which is experiencing nuisance disturbance of the computer
 UPS systems at the site.  The site owner suspects this is due to the PV
 system which is a 50 kW system using 6 SMA SunnyBoy inverters.  The
 nuisance disturbance is a clicking noise in the UPS units.  The disturbance
 is not enough to cause the UPS to engage, so it seems to be a small
 disturbance on the AC power.   The site owner suspects the inverters are
 the source of this disturbance since 1) It seems to only occur when we have
 a good solar day.  2) If the inverters are shut down the problem goes away,
 and if you start up the inverters the problem exhibits again.

 The site was commissioned in March of 2012 and has had no problems till
 this issue last month.  In reviewing the event log on Sunny Portal there
 are no inverter anomalies.  SMA tech support had not run into this issue
 and had no ideas, they too agree the inverters are not reporting any
 anomalies.

 The problem is not persistent but rather intermittent making this harder
 to troubleshoot.

 So my questions are
 1) Has anyone else seen this sort of issue before, related to SMA SunnyBoy
 inverters.
 2) Can you recommend an AC power monitoring tool which would support
  frequency and voltage monitoring on the AC line.  Perhaps one data set on
 the circuit feeding the computers and another on the inverter output
 circuit.

 For clarity the six SunnyBoys feed into an AC Combiner panel which
 backfeeds into the building main distribution panel.  The service is 240V
 single phase.

 With Regards
 Carl Adams, SunRock Solar
 NABCEP Certified PV Installer

 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org



___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] UPS disturbance with SMA Inverters

2014-08-04 Thread Mac Lewis
Hello Carl,

The egauge may be a good monitoring unit for this application.  You can
monitor 12 CT's at a time, and everything is time-stamped.  The egauge is
actually its own server, so it can be monitored remotely or on a site
computer on the same network.  It can give you power factor, phase voltage,
line voltage among other parameters.  It does require that all of the
monitored lines are relatively close spatially (or you can get more
egauges).
I am curious, does the clicking that they hear from the UPS indicate the
UPS is taking the load momentarily, or is it something else?

Good luck




On Mon, Aug 4, 2014 at 3:11 PM, Carl Adams swingjun...@gmail.com wrote:

 Bob, Ray, Glenn,

 Thanks for the responses.  We could cycle through the inverters and see if
 it is one, or some combinations of inverters, which is causing the problem.
  This results in a minimum of 6 trials.  If it is a combination of
 inverters  many more.

 Any feedback on the idea of monitoring the AC circuits; computer feed and
 combined inverter output?  Seems to me this might provide a one step
 correlation between the event and the cause.  Just not sure what equipment
 to suggest for this.

 Could be there is some other cause, unrelated to the inverters.  AC unit
 kicking on, etc.  Though they do not see any lights dimiming/brightening,
 or any other notable change in electrical equipment at the sight.



 On Mon, Aug 4, 2014 at 1:03 PM, Glenn Burt glenn.b...@glbcc.com wrote:

  I wonder if the UPS is grumbling about high voltage as the inverters
 push back current...

 Glenn
  --
 From: Carl Adams swingjun...@gmail.com
 Sent: ‎8/‎4/‎2014 10:29
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Subject: [RE-wrenches] UPS disturbance with SMA Inverters

  Hello Wrenches,

 I have a site which is experiencing nuisance disturbance of the computer
 UPS systems at the site.  The site owner suspects this is due to the PV
 system which is a 50 kW system using 6 SMA SunnyBoy inverters.  The
 nuisance disturbance is a clicking noise in the UPS units.  The disturbance
 is not enough to cause the UPS to engage, so it seems to be a small
 disturbance on the AC power.   The site owner suspects the inverters are
 the source of this disturbance since 1) It seems to only occur when we have
 a good solar day.  2) If the inverters are shut down the problem goes away,
 and if you start up the inverters the problem exhibits again.

 The site was commissioned in March of 2012 and has had no problems till
 this issue last month.  In reviewing the event log on Sunny Portal there
 are no inverter anomalies.  SMA tech support had not run into this issue
 and had no ideas, they too agree the inverters are not reporting any
 anomalies.

 The problem is not persistent but rather intermittent making this harder
 to troubleshoot.

 So my questions are
 1) Has anyone else seen this sort of issue before, related to SMA
 SunnyBoy inverters.
 2) Can you recommend an AC power monitoring tool which would support
  frequency and voltage monitoring on the AC line.  Perhaps one data set on
 the circuit feeding the computers and another on the inverter output
 circuit.

 For clarity the six SunnyBoys feed into an AC Combiner panel which
 backfeeds into the building main distribution panel.  The service is
 240V single phase.

 With Regards
 Carl Adams, SunRock Solar
 NABCEP Certified PV Installer

 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org




 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org





-- 



Mac Lewis

*Yo solo sé que no sé nada. -Sócrates*
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] UPS disturbance with SMA Inverters

2014-08-04 Thread Chris Mason
Is it possible that the UPS issue is raised voltage, causing the UPS
voltage regulator to switch settings? A large amount of solar on a circuit
can raise the voltage in the system at full sun. I would rent a Fluke
Energy Analyzer and leave it in place for a number of days to see how the
voltage, current and power factor varies with the inverter output.


On Mon, Aug 4, 2014 at 5:11 PM, Carl Adams swingjun...@gmail.com wrote:

 Bob, Ray, Glenn,

 Thanks for the responses.  We could cycle through the inverters and see if
 it is one, or some combinations of inverters, which is causing the problem.
  This results in a minimum of 6 trials.  If it is a combination of
 inverters  many more.

 Any feedback on the idea of monitoring the AC circuits; computer feed and
 combined inverter output?  Seems to me this might provide a one step
 correlation between the event and the cause.  Just not sure what equipment
 to suggest for this.

 Could be there is some other cause, unrelated to the inverters.  AC unit
 kicking on, etc.  Though they do not see any lights dimiming/brightening,
 or any other notable change in electrical equipment at the sight.



 On Mon, Aug 4, 2014 at 1:03 PM, Glenn Burt glenn.b...@glbcc.com wrote:

  I wonder if the UPS is grumbling about high voltage as the inverters
 push back current...

 Glenn
  --
 From: Carl Adams swingjun...@gmail.com
 Sent: ‎8/‎4/‎2014 10:29
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Subject: [RE-wrenches] UPS disturbance with SMA Inverters

  Hello Wrenches,

 I have a site which is experiencing nuisance disturbance of the computer
 UPS systems at the site.  The site owner suspects this is due to the PV
 system which is a 50 kW system using 6 SMA SunnyBoy inverters.  The
 nuisance disturbance is a clicking noise in the UPS units.  The disturbance
 is not enough to cause the UPS to engage, so it seems to be a small
 disturbance on the AC power.   The site owner suspects the inverters are
 the source of this disturbance since 1) It seems to only occur when we have
 a good solar day.  2) If the inverters are shut down the problem goes away,
 and if you start up the inverters the problem exhibits again.

 The site was commissioned in March of 2012 and has had no problems till
 this issue last month.  In reviewing the event log on Sunny Portal there
 are no inverter anomalies.  SMA tech support had not run into this issue
 and had no ideas, they too agree the inverters are not reporting any
 anomalies.

 The problem is not persistent but rather intermittent making this harder
 to troubleshoot.

 So my questions are
 1) Has anyone else seen this sort of issue before, related to SMA
 SunnyBoy inverters.
 2) Can you recommend an AC power monitoring tool which would support
  frequency and voltage monitoring on the AC line.  Perhaps one data set on
 the circuit feeding the computers and another on the inverter output
 circuit.

 For clarity the six SunnyBoys feed into an AC Combiner panel which
 backfeeds into the building main distribution panel.  The service is
 240V single phase.

 With Regards
 Carl Adams, SunRock Solar
 NABCEP Certified PV Installer

 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org




 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org





-- 
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com http://www.cometenergysystems.com
264.235.5670
869.662.5670
Skype: netconcepts
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] UPS disturbance with SMA Inverters

2014-08-04 Thread Jerry Shafer
It would be good to put a volt meter at the input to the UPS confirm input
voltage is within range at the time there is an issue. If volts are high
there is a problem between that location and as far as the transformer. A
scope would help to see noise on the AC side but an old AM radio may do the
same to detect noise on the line.
On Aug 4, 2014 1:30 PM, Chris Mason cometenergysyst...@gmail.com wrote:

 Is it possible that the UPS issue is raised voltage, causing the UPS
 voltage regulator to switch settings? A large amount of solar on a circuit
 can raise the voltage in the system at full sun. I would rent a Fluke
 Energy Analyzer and leave it in place for a number of days to see how the
 voltage, current and power factor varies with the inverter output.


 On Mon, Aug 4, 2014 at 5:11 PM, Carl Adams swingjun...@gmail.com wrote:

 Bob, Ray, Glenn,

 Thanks for the responses.  We could cycle through the inverters and see
 if it is one, or some combinations of inverters, which is causing the
 problem.  This results in a minimum of 6 trials.  If it is a combination of
 inverters  many more.

 Any feedback on the idea of monitoring the AC circuits; computer feed and
 combined inverter output?  Seems to me this might provide a one step
 correlation between the event and the cause.  Just not sure what equipment
 to suggest for this.

 Could be there is some other cause, unrelated to the inverters.  AC unit
 kicking on, etc.  Though they do not see any lights dimiming/brightening,
 or any other notable change in electrical equipment at the sight.



 On Mon, Aug 4, 2014 at 1:03 PM, Glenn Burt glenn.b...@glbcc.com wrote:

  I wonder if the UPS is grumbling about high voltage as the inverters
 push back current...

 Glenn
  --
 From: Carl Adams swingjun...@gmail.com
 Sent: ‎8/‎4/‎2014 10:29
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Subject: [RE-wrenches] UPS disturbance with SMA Inverters

  Hello Wrenches,

 I have a site which is experiencing nuisance disturbance of the computer
 UPS systems at the site.  The site owner suspects this is due to the
 PV system which is a 50 kW system using 6 SMA SunnyBoy inverters.  The
 nuisance disturbance is a clicking noise in the UPS units.  The disturbance
 is not enough to cause the UPS to engage, so it seems to be a small
 disturbance on the AC power.   The site owner suspects the inverters are
 the source of this disturbance since 1) It seems to only occur when we have
 a good solar day.  2) If the inverters are shut down the problem goes away,
 and if you start up the inverters the problem exhibits again.

 The site was commissioned in March of 2012 and has had no problems till
 this issue last month.  In reviewing the event log on Sunny Portal there
 are no inverter anomalies.  SMA tech support had not run into this
 issue and had no ideas, they too agree the inverters are not reporting any
 anomalies.

 The problem is not persistent but rather intermittent making this harder
 to troubleshoot.

 So my questions are
 1) Has anyone else seen this sort of issue before, related to SMA
 SunnyBoy inverters.
 2) Can you recommend an AC power monitoring tool which would support
  frequency and voltage monitoring on the AC line.  Perhaps one data set on
 the circuit feeding the computers and another on the inverter output
 circuit.

 For clarity the six SunnyBoys feed into an AC Combiner panel which
 backfeeds into the building main distribution panel.  The service is
 240V single phase.

 With Regards
 Carl Adams, SunRock Solar
 NABCEP Certified PV Installer

 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org




 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org





 --
 Chris Mason
 NABCEP Certified Solar PV Installer™
 Solar Design Engineer
 Generac Generators Industrial technician

 www.cometsolar.com http://www.cometenergysystems.com
 264.235.5670
 869.662.5670
 Skype: netconcepts

 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 

Re: [RE-wrenches] Ct Utility test requirement?

2014-08-04 Thread Jerry Shafer
If you using a AC disconnect shut off power to it install a jumper on two
of the legs just testing once inverter is back on line pull the switch and
see what happens. Swap jumper location and tetest, once you tesy all legs
remove jumper wires.
On Aug 4, 2014 7:43 AM, Rebekah Hren rebekah.h...@gmail.com wrote:

 Al,
 I have witnessed this test in NC several times, but with medium voltage
 connected systems, not systems connected to a building service.  A medium
 voltage subcontractor used a disconnect stick to open one phase at a time
 at the fused cutout point of delivery to the distribution network (on the
 high side of the transformers) . We learned to do the test early in the
 morning with the array divided in subsections to keep the current as low as
 possible at the POD because there is an arc pulled when one phase is
 opened.

 The phase current was being monitored during the test to insure that the
 inverters stopped exporting current to the other two phases when one phase
 was lost.
 It's been awhile, so there may be a better/safer way to do this test for
 MV connected systems now that I'm not aware of...would be happy to hear
 about it if so.

 If this is a PV system connected to a building service this wouldn't be
 the way to do this test.
 Cheers,
 Rebekah Hren



 On Mon, Aug 4, 2014 at 11:24 AM, Allen Frishman amfr...@aeonsolar.com
 wrote:

 Wrenchers,
 The Ct Utility company CLP requires the following as part of the
 verification test.
 Because this is a three-phase service, the witness test must also
 demonstrate that the inverter shuts down upon loss of each individual phase

 Any recommendations on how to do this test safely?

 *Al Frishman*
 AeonSolar

 *(917) 699-6641 %28917%29%20699-6641 - cell*
 *(888) 460-2867 %2%29%20460-2867*
 *www.aeonsolar.com http://www.aeonsolar.com/*


 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org





 --
 Tel: 336.266.8800
 NABCEP Certified Solar PV Installation Professional™ 091209-85
 NC Licensed Electrical Contractor

 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org



___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Ct Utility test requirement?

2014-08-04 Thread Chris Mason
If you are using a load center to aggregate the inverter outputs, swap the
3 pole breaker for three single poles. Hopefully you can demonstrate only
one inverter works.
If the UL listing tests and certifies for this, why do they need to do it
in the field? Next they will want you to set up a full lab test suite.


On Mon, Aug 4, 2014 at 8:56 PM, Jerry Shafer jerrysgarag...@gmail.com
wrote:

 If you using a AC disconnect shut off power to it install a jumper on two
 of the legs just testing once inverter is back on line pull the switch and
 see what happens. Swap jumper location and tetest, once you tesy all legs
 remove jumper wires.
 On Aug 4, 2014 7:43 AM, Rebekah Hren rebekah.h...@gmail.com wrote:

 Al,
 I have witnessed this test in NC several times, but with medium voltage
 connected systems, not systems connected to a building service.  A medium
 voltage subcontractor used a disconnect stick to open one phase at a time
 at the fused cutout point of delivery to the distribution network (on the
 high side of the transformers) . We learned to do the test early in the
 morning with the array divided in subsections to keep the current as low as
 possible at the POD because there is an arc pulled when one phase is
 opened.

 The phase current was being monitored during the test to insure that the
 inverters stopped exporting current to the other two phases when one phase
 was lost.
 It's been awhile, so there may be a better/safer way to do this test for
 MV connected systems now that I'm not aware of...would be happy to hear
 about it if so.

 If this is a PV system connected to a building service this wouldn't be
 the way to do this test.
 Cheers,
 Rebekah Hren



 On Mon, Aug 4, 2014 at 11:24 AM, Allen Frishman amfr...@aeonsolar.com
 wrote:

 Wrenchers,
 The Ct Utility company CLP requires the following as part of the
 verification test.
 Because this is a three-phase service, the witness test must also
 demonstrate that the inverter shuts down upon loss of each individual phase

 Any recommendations on how to do this test safely?

 *Al Frishman*
 AeonSolar

 *(917) 699-6641 %28917%29%20699-6641 - cell*
 *(888) 460-2867 %2%29%20460-2867*
 *www.aeonsolar.com http://www.aeonsolar.com/*


 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org





 --
 Tel: 336.266.8800
 NABCEP Certified Solar PV Installation Professional™ 091209-85
 NC Licensed Electrical Contractor

 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org



 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org





-- 
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com http://www.cometenergysystems.com
264.235.5670
869.662.5670
Skype: netconcepts
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org