Re: [RE-wrenches] Fuse sizing in battery circuits

2013-04-22 Thread Troy Harvey
Ray,

One thing I didn't understand is how you can pair a 400 amp class-T fuse with a 
4/0 cable. The 400 fuse curve looks like the continuous rating is 350A in the 
graph supplied by Allan. Which is well above the 4/0 ampacity of 250A (copper). 
Anyone want to explain?

thanks,

Troy Harvey
-
Principal Engineer
Heliocentric
801-453-9434
tahar...@heliocentric.org



On Apr 5, 2013, at 10:12 PM, Ray Walters r...@solarray.com wrote:

 I just finished a rewire and we kept the Ananda power center, Allan :-) 
 Back when we used class T fuses more they were always over sized relative to 
 Heinemann breakers.
 400 amp class T fuse = 250 amp breaker= 4/0 cable
 200 amp class T fuse = 175 amp breaker= 2/0 cable
 
 I still think class T fuses are superior in some ways to breakers: they have 
 better interrupt capacity and trip faster in a short circuit condition.
 
 However, If you spend too much time thinking about and looking at the trip 
 curves, you'll break your brain and special order some weird fuses and 
 breakers.  (anybody need a 350 amp class T fuse?)
  Just follow the inverter manufacturer's recommendations and all will be well.
 On the other hand, William has brought up a topic I have harped on for years: 
  Having the OCPD in the cabinet doesn't protect the majority of the circuit.  
 Class T fuses at the battery terminals do, but they're not rated for the 
 corrosive environment.  I have thrown a few class T fuses away that had acid 
 eating away at the ends.
 I don't have the solution, but I will continue to point out that this is a 
 real problem. Dropping a wrench across the battery terminals can lead to a 
 spectacular failure that not only can cause a fire, but might even cause a 
 battery explosion, yet NEC offers no protection.  
 We use insulated wrenches from experience, and hope for the best.  
 R.Ray Walters
 CTO, Solarray, Inc
 Nabcep Certified PV Installer, 
 Licensed Master Electrician
 Solar Design Engineer
 303 505-8760
 On 4/5/2013 8:29 PM, William Miller wrote:
 Friends:
 
 Good topic.  Some questions:
 
 1. Most manufacturer's present an installation guide that shows one OCPD in 
 the battery circuit and that is in the BOS cabinet.  This means the battery 
 leads are unprotected.  Do we need an OPCD at the battery terminals?
 
 2. Class T fuses are generally recommended for this application.  The data 
 shows them as fast acting.  Is this a problem?  Will they act too fast and 
 open during normal surge loads?
 
 Thanks in advance!
 
 William Miller
 
 
 
 
 
 Troy,
  
 Overcurrent device size is matched to the conductor size. The inverse time 
 constant nature of an overcurrent device can typically handle the surge 
 currents as long as conductor sizing has truly been done correctly for the 
 conductor. Circuit breakers are preferred to fuses because they can be 
 reset. 
  
 There has been volumes written on this issue. The constant current at 
 lowest battery voltage should be used, plus the ac ripple content on the 
 battery circuit. This is usually a much larger conductor than your average 
 designer will plan for. The best thing is to look at Midnight, Outback, and 
 Schneider and see what size overcurrent devices they require for their 
 products. That will give you a good clue as to how to size the conductor 
 and overcurrent device.
  
 Bill.
  
 From: re-wrenches-boun...@lists.re-wrenches.org 
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Troy Harvey
 Sent: Friday, April 05, 2013 3:38 PM
 To: RE-wrenches
 Subject: [RE-wrenches] Fuse sizing in battery circuits
  
 I've got a question about battery string fusing. Typically we size the wire 
 from the batteries to the inverter based on continuous rating procedures 
 (max power/efficiency)*125%. 
  
 However a 6kW inverter, can peak at 12kW for 5-10 seconds, doubling the 
 source current. That is no big deal for the wire, because it is a short 
 time frame... little heat will be generated. However, in fusing the 
 sub-strings, you need to account for that peak surge current so you don't 
 blow fuses all the time. But if you put a 500-1000 amp fuse on a 4/0 wire, 
 above the max surge draw of the inverter, the wire will be under-protected 
 for its ampacity rating. Any thoughts on the catch-22?
  
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

Re: [RE-wrenches] Fuse sizing in battery circuits

2013-04-22 Thread Ray Walters
:

Good topic.  Some questions:

1. Most manufacturer's present an installation guide that shows one 
OCPD in the battery circuit and that is in the BOS cabinet.  This 
means the battery leads are unprotected.  Do we need an OPCD at the 
battery terminals?


2. Class T fuses are generally recommended for this application.  
The data shows them as fast acting.  Is this a problem?  Will they 
act too fast and open during normal surge loads?


Thanks in advance!

William Miller






Troy,

Overcurrent device size is matched to the conductor size. The 
inverse time constant nature of an overcurrent device can typically 
handle the surge currents as long as conductor sizing has truly 
been done correctly for the conductor. Circuit breakers are 
preferred to fuses because they can be reset.


There has been volumes written on this issue. The constant current 
at lowest battery voltage should be used, plus the ac ripple 
content on the battery circuit. This is usually a much larger 
conductor than your average designer will plan for. The best thing 
is to look at Midnight, Outback, and Schneider and see what size 
overcurrent devices they require for their products. That will give 
you a good clue as to how to size the conductor and overcurrent device.


Bill.

*From:* re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of 
*Troy Harvey

*Sent:* Friday, April 05, 2013 3:38 PM
*To:* RE-wrenches
*Subject:* [RE-wrenches] Fuse sizing in battery circuits

I've got a question about battery string fusing. Typically we size 
the wire from the batteries to the inverter based on continuous 
rating procedures (max power/efficiency)*125%.


However a 6kW inverter, can peak at 12kW for 5-10 seconds, doubling 
the source current. That is no big deal for the wire, because it is 
a short time frame... little heat will be generated. However, in 
fusing the sub-strings, you need to account for that peak surge 
current so you don't blow fuses all the time. But if you put a 
500-1000 amp fuse on a 4/0 wire, above the max surge draw of the 
inverter, the wire will be under-protected for its ampacity rating. 
Any thoughts on the catch-22?



___
List sponsored by Home Power magazine

List Address:RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org 
mailto:RE-wrenches@lists.re-wrenches.org


Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org





___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fuse sizing in battery circuits

2013-04-17 Thread Garrison Riegel
Hi Ray,

Not saying he was right, but it was explained to me by an inspector that the
pipe electrode mentioned in 250.166(C) is different than a water main. The
justification being that 250.52(A)(1) lists requirements for a metal
underground water pipe electrode, while 250.52(A)(5) lists pipe electrode
separately.  I agree a water main fits the description of a pipe, but I
suppose it could depend on the mood of the inspector.  I've managed to avoid
it myself, but have heard horror stories of 4/0 GECs being required by
inspectors.

Good point about 250.53(D)(2) Supplemental Electrode Required.  Although it
does list a pipe again as a possible supplemental electrode to the water
main.  

250.166(C) just seems a little unclear with respect to a water main
electrode.  I have seen a number of sites that do not have a supplemental
electrode in addition to the water main, but I suppose you could simply
install a rod, bond it to the water main, and use #6 copper for the DC GEC.

Thanks,

Garrison



-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ray Walters
Sent: Tuesday, April 16, 2013 2:22 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Fuse sizing in battery circuits

First, a water main is no longer allowed to be used as the primary grounding
electrode by itself, it needs an additional electrode added to it 25053(D)2.
You still are required to bond to it 250.104(A)1,  but it doesn't count as
the electrode.  Also, 250.166 (C) specifically lists pipe as one of the
exceptions.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 4/16/2013 1:06 PM, Garrison Riegel wrote:
 Hi Ray and All,

 250.166 says the GEC must be sized as specified in (A) Not smaller 
 than the neutral conductor, or (B) Not smaller than the largest 
 conductor supplied by the system, except as permitted by (C) through (E).

 A water main [as in 250.52(A)(1)] is not listed as an exception in (C) 
 through (E). So if the GE is a water main wouldn't the GEC need to 
 be 4/0, if the battery cables were 4/0?  Not saying it makes sense, 
 especially if the water main is 3/4, but this has always made me wonder.

 Thoughts?

 Garrison Riegel
 Project Manager | Solar Service Inc
 [p] 847-677-0950 | garri...@solarserviceinc.com

 NABCEP Certified PV Installation ProfessionalT


 -Original Message-
 From: re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ray 
 Walters
 Sent: Tuesday, April 16, 2013 12:52 PM
 To: RE-wrenches
 Subject: Re: [RE-wrenches] Fuse sizing in battery circuits

 Hi Drake;

 Read down a bit more and 250.166(C) and (D) limit the size of the GEC 
 to
 #4 or #6 max., depending on what electrode is used.
 This used to not be the case, and systems in the 90s had 4/0 cable to a
5/8
 electrode: which just like your 1/2 pipe example was absolutely
ridiculous.

 R.Ray Walters
 CTO, Solarray, Inc
 Nabcep Certified PV Installer,
 Licensed Master Electrician
 Solar Design Engineer
 303 505-8760

 On 4/16/2013 9:31 AM, Drake wrote:

 So, in a standard battery system, with a charge control, ground fault 
 protection and an array, the DC system will likely need grounding. If 
 the DC system is grounded, then the battery cables are grounded also.
 In 250.166 (B) it says the grounding electrode conductor (GEC) shall 
 not be smaller than the largest conductor supplied by the system.

 If the battery cables are supplied by the system doesn't this imply 
 that the GEC should be the size of the battery cable?  This is the 
 logic that has led some inspectors to require a 4/0 copper wire to be 
 bonded to a 1/2 water pipe. This is, of course, technically absurd.
 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org

 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org

Re: [RE-wrenches] Fuse sizing in battery circuits

2013-04-17 Thread Ray Walters
A metal underground water pipe is still a pipe in all cases, so I 
think I'm missing your inspector's logic.  A water main is always going 
to be made out of pipe, so I think the exception to 250.166 (C) should 
always apply. (unless some places make them square?;-) ) The difference 
in pipe between 250.52A1 and A5 is that one is a pipe set in the ground 
by an electrician with the sole purpose of being a grounding electrode, 
while the other is used for water and is set by the plumber.  The reason 
I heard that water lines into the house had to have supplementary 
grounding is that they often transition to PVC and so aren't always 
continuous metal.  They also might be cut and changed later by a 
plumber.  That also was a change from earlier code, that used to allow 
the water main to be used as the sole grounding electrode.  EIther way, 
250.166 does not make a distinction, it just says Pipe and would cover 
all GEC connections.


The 4/0 GEC horror stories probably are from earlier editions of the 
code.  BIll Brooks can tell us when that changed.  My guess is that it 
was a pre 2002 code requirement, as I saw that on 90s PV systems.
Your final suggested install should be code compliant with all the 
various NEC sections (IMHO); just use a lay in lug type pipe grounding 
clamp, to keep the GEC continuous to the rod.
Some of this code stuff makes you wonder whether we should have studied 
law to be a Wrench.(ugh)


R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 4/17/2013 7:44 AM, Garrison Riegel wrote:

Hi Ray,

Not saying he was right, but it was explained to me by an inspector that the
pipe electrode mentioned in 250.166(C) is different than a water main. The
justification being that 250.52(A)(1) lists requirements for a metal
underground water pipe electrode, while 250.52(A)(5) lists pipe electrode
separately.  I agree a water main fits the description of a pipe, but I
suppose it could depend on the mood of the inspector.  I've managed to avoid
it myself, but have heard horror stories of 4/0 GECs being required by
inspectors.

Good point about 250.53(D)(2) Supplemental Electrode Required.  Although it
does list a pipe again as a possible supplemental electrode to the water
main.

250.166(C) just seems a little unclear with respect to a water main
electrode.  I have seen a number of sites that do not have a supplemental
electrode in addition to the water main, but I suppose you could simply
install a rod, bond it to the water main, and use #6 copper for the DC GEC.

Thanks,

Garrison



-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ray Walters
Sent: Tuesday, April 16, 2013 2:22 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Fuse sizing in battery circuits

First, a water main is no longer allowed to be used as the primary grounding
electrode by itself, it needs an additional electrode added to it 25053(D)2.
You still are required to bond to it 250.104(A)1,  but it doesn't count as
the electrode.  Also, 250.166 (C) specifically lists pipe as one of the
exceptions.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 4/16/2013 1:06 PM, Garrison Riegel wrote:

Hi Ray and All,

250.166 says the GEC must be sized as specified in (A) Not smaller
than the neutral conductor, or (B) Not smaller than the largest
conductor supplied by the system, except as permitted by (C) through (E).

A water main [as in 250.52(A)(1)] is not listed as an exception in (C)
through (E). So if the GE is a water main wouldn't the GEC need to
be 4/0, if the battery cables were 4/0?  Not saying it makes sense,
especially if the water main is 3/4, but this has always made me wonder.

Thoughts?

Garrison Riegel
Project Manager | Solar Service Inc
[p] 847-677-0950 | garri...@solarserviceinc.com

NABCEP Certified PV Installation ProfessionalT


-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ray
Walters
Sent: Tuesday, April 16, 2013 12:52 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Fuse sizing in battery circuits

Hi Drake;

Read down a bit more and 250.166(C) and (D) limit the size of the GEC
to
#4 or #6 max., depending on what electrode is used.
This used to not be the case, and systems in the 90s had 4/0 cable to a

5/8

electrode: which just like your 1/2 pipe example was absolutely

ridiculous.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 4/16/2013 9:31 AM, Drake wrote:

So, in a standard battery system, with a charge control, ground fault
protection and an array, the DC system will likely need grounding. If
the DC system is grounded, then the battery cables are grounded also.
In 250.166 (B) it says

Re: [RE-wrenches] Fuse sizing in battery circuits

2013-04-16 Thread Drake
This is a fairly complicated issue.  I agree that an ungrounded 
battery system is safer than a grounded one, since the hot wire will 
not arc to the casing of the enclosure.


If a system has a charge control and an array, the negative wire of 
the array usually needs to be grounded (or have a fuse in each 
leg).  If there is an MPPT charge control, the voltage will almost 
certainly be over 50 volts. However, supposedly even a 24 volt system 
with no MPPT can go over 50 V.


So, in a standard battery system, with a charge control, ground fault 
protection and an array, the DC system will likely need 
grounding.  If the DC system is grounded, then the battery cables are 
grounded also.  In 250.166 (B) it says the grounding electrode 
conductor (GEC) shall not be smaller than the largest conductor 
supplied by the system.


If the battery cables are supplied by the system doesn't this imply 
that the GEC should be the size of the battery cable?  This is the 
logic that has led some inspectors to require a 4/0 copper wire to be 
bonded to a 1/2 water pipe. This is, of course, technically absurd.


Are a lot of battery based systems now going in with no DC grounding 
and fuses in both legs?  How does a GFP work in this scenario?


The Sunny Island is a different animal, as the DC system in it does 
not connect to the array.  It is AC coupled instead of DC coupled. 
Therefore, it is connected with AC. The connection to the batteries 
is isolated. So maybe the issue of DC grounding doesn't apply.  The 
DC system in the Sunny Island will, however, normally operate at over 
50 volts, unless the batteries are low.


What is the bottom line here?

At 04:47 PM 4/15/2013, you wrote:

Hi August;

250.162(A) says operating at greater than 50 v, which a 48 v 
nominal system operates most of the time at over 50 v, at least when 
solar charging and/or selling back.
We used to get dinged many years ago for using breakers rated at 50v 
dc on 48 v systems.  John Wiles used to insist we use the highest 
possible voltage (Voc of modules on coldest day)
Personally I prefer ungrounded systems, so I'm not saying there's 
anything wrong from a safety stand point, just that inspectors here 
don't see it the same way.



R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760On 4/15/2013 2:20 PM, August Goers wrote:

Hi Drake,

The Sunny Island System runs at 48 V nominal so I don't believe 
250.162(A) applies. We have some really savvy inspectors in the Bay 
Area and they were happy for us to be ungrounded since we're 
operating at 48 V. Yes, the actual voltage might go above 50 V when 
charging but I believe it is the nominal voltage that the code cares about.


Best,


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fuse sizing in battery circuits

2013-04-16 Thread Ray Walters

Hi Drake;

Read down a bit more and 250.166(C) and (D) limit the size of the GEC to 
#4 or #6 max., depending on what electrode is used.
This used to not be the case, and systems in the 90s had 4/0 cable to a 
5/8 electrode: which just like your 1/2 pipe example was absolutely 
ridiculous.


R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 4/16/2013 9:31 AM, Drake wrote:



So, in a standard battery system, with a charge control, ground fault 
protection and an array, the DC system will likely need grounding. If 
the DC system is grounded, then the battery cables are grounded also.  
In 250.166 (B) it says the grounding electrode conductor (GEC) shall 
not be smaller than the largest conductor supplied by the system.


If the battery cables are supplied by the system doesn't this imply 
that the GEC should be the size of the battery cable?  This is the 
logic that has led some inspectors to require a 4/0 copper wire to be 
bonded to a 1/2 water pipe. This is, of course, technically absurd.


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fuse sizing in battery circuits

2013-04-16 Thread August Goers
Ray,



Thanks for the note and I see your point about operating at greater than
50 v. Does anyone else have an opinion on the operating voltage for
batteries? I know that NEC 480.2 defines the nominal battery voltage as 2
volts per cell for lead-acid and I believe I have a code interpretation
book lying around that states that this is what you apply to 250.162 but I
don't have much info other than that.



Best, August



*From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:
re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Ray Walters
*Sent:* Monday, April 15, 2013 1:48 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Fuse sizing in battery circuits



Hi August;

250.162(A) says operating at greater than 50 v, which a 48 v nominal
system operates most of the time at over 50 v, at least when solar charging
and/or selling back.
We used to get dinged many years ago for using breakers rated at 50v dc on
48 v systems.  John Wiles used to insist we use the highest possible
voltage (Voc of modules on coldest day)
Personally I prefer ungrounded systems, so I'm not saying there's anything
wrong from a safety stand point, just that inspectors here don't see it the
same way.


R.Ray Walters

CTO, Solarray, Inc

Nabcep Certified PV Installer,

Licensed Master Electrician

Solar Design Engineer

303 505-8760

On 4/15/2013 2:20 PM, August Goers wrote:

Hi Drake,



The Sunny Island System runs at 48 V nominal so I don't believe 250.162(A)
applies. We have some really savvy inspectors in the Bay Area and they were
happy for us to be ungrounded since we're operating at 48 V. Yes, the
actual voltage might go above 50 V when charging but I believe it is the
nominal voltage that the code cares about.



Best,
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fuse sizing in battery circuits

2013-04-16 Thread Drake

Hi Ray,

Thanks for that information.  I'm glad they covered that. I never 
install more than a #4.


The question I'm still not sure of is weather or not we need to 
ground the DC.  I always have run a GEC to the DC.  It would be great 
if we didn't need to do so on the Sunny Islands especially, since 
they are not set up for DC grounding.


Drake

At 01:51 PM 4/16/2013, you wrote:

Hi Drake;

Read down a bit more and 250.166(C) and (D) limit the size of the 
GEC to #4 or #6 max., depending on what electrode is used.
This used to not be the case, and systems in the 90s had 4/0 cable 
to a 5/8 electrode: which just like your 1/2 pipe example was 
absolutely ridiculous.


R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 4/16/2013 9:31 AM, Drake wrote:



So, in a standard battery system, with a charge control, ground 
fault protection and an array, the DC system will likely need 
grounding. If the DC system is grounded, then the battery cables 
are grounded also.
In 250.166 (B) it says the grounding electrode conductor (GEC) 
shall not be smaller than the largest conductor supplied by the system.


If the battery cables are supplied by the system doesn't this 
imply that the GEC should be the size of the battery cable?  This 
is the logic that has led some inspectors to require a 4/0 copper 
wire to be bonded to a 1/2 water pipe. This is, of course, technically absurd.


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fuse sizing in battery circuits

2013-04-16 Thread Garrison Riegel
Hi Ray and All,

250.166 says the GEC must be sized as specified in (A) Not smaller than the
neutral conductor, or (B) Not smaller than the largest conductor supplied by
the system, except as permitted by (C) through (E).

A water main [as in 250.52(A)(1)] is not listed as an exception in (C)
through (E). So if the GE is a water main wouldn't the GEC need to be 4/0,
if the battery cables were 4/0?  Not saying it makes sense, especially if
the water main is 3/4, but this has always made me wonder.

Thoughts?

Garrison Riegel
Project Manager | Solar Service Inc
[p] 847-677-0950 | garri...@solarserviceinc.com

NABCEP Certified PV Installation ProfessionalT


-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ray Walters
Sent: Tuesday, April 16, 2013 12:52 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Fuse sizing in battery circuits

Hi Drake;

Read down a bit more and 250.166(C) and (D) limit the size of the GEC to
#4 or #6 max., depending on what electrode is used.
This used to not be the case, and systems in the 90s had 4/0 cable to a 5/8
electrode: which just like your 1/2 pipe example was absolutely ridiculous.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 4/16/2013 9:31 AM, Drake wrote:


 So, in a standard battery system, with a charge control, ground fault 
 protection and an array, the DC system will likely need grounding. If 
 the DC system is grounded, then the battery cables are grounded also.
 In 250.166 (B) it says the grounding electrode conductor (GEC) shall 
 not be smaller than the largest conductor supplied by the system.

 If the battery cables are supplied by the system doesn't this imply 
 that the GEC should be the size of the battery cable?  This is the 
 logic that has led some inspectors to require a 4/0 copper wire to be 
 bonded to a 1/2 water pipe. This is, of course, technically absurd.

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fuse sizing in battery circuits

2013-04-16 Thread Ray Walters
First, a water main is no longer allowed to be used as the primary 
grounding electrode by itself, it needs an additional electrode added to 
it 25053(D)2. You still are required to bond to it 250.104(A)1,  but it 
doesn't count as the electrode.  Also, 250.166 (C) specifically lists 
pipe as one of the exceptions.


R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 4/16/2013 1:06 PM, Garrison Riegel wrote:

Hi Ray and All,

250.166 says the GEC must be sized as specified in (A) Not smaller than the
neutral conductor, or (B) Not smaller than the largest conductor supplied by
the system, except as permitted by (C) through (E).

A water main [as in 250.52(A)(1)] is not listed as an exception in (C)
through (E). So if the GE is a water main wouldn't the GEC need to be 4/0,
if the battery cables were 4/0?  Not saying it makes sense, especially if
the water main is 3/4, but this has always made me wonder.

Thoughts?

Garrison Riegel
Project Manager | Solar Service Inc
[p] 847-677-0950 | garri...@solarserviceinc.com

NABCEP Certified PV Installation ProfessionalT


-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ray Walters
Sent: Tuesday, April 16, 2013 12:52 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Fuse sizing in battery circuits

Hi Drake;

Read down a bit more and 250.166(C) and (D) limit the size of the GEC to
#4 or #6 max., depending on what electrode is used.
This used to not be the case, and systems in the 90s had 4/0 cable to a 5/8
electrode: which just like your 1/2 pipe example was absolutely ridiculous.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 4/16/2013 9:31 AM, Drake wrote:


So, in a standard battery system, with a charge control, ground fault
protection and an array, the DC system will likely need grounding. If
the DC system is grounded, then the battery cables are grounded also.
In 250.166 (B) it says the grounding electrode conductor (GEC) shall
not be smaller than the largest conductor supplied by the system.

If the battery cables are supplied by the system doesn't this imply
that the GEC should be the size of the battery cable?  This is the
logic that has led some inspectors to require a 4/0 copper wire to be
bonded to a 1/2 water pipe. This is, of course, technically absurd.

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fuse sizing in battery circuits

2013-04-15 Thread August Goers
Hi Drake,



The Sunny Island System runs at 48 V nominal so I don't believe 250.162(A)
applies. We have some really savvy inspectors in the Bay Area and they were
happy for us to be ungrounded since we're operating at 48 V. Yes, the
actual voltage might go above 50 V when charging but I believe it is the
nominal voltage that the code cares about.



Best,



August



*From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:
re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Drake
*Sent:* Saturday, April 13, 2013 12:14 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Fuse sizing in battery circuits



Is it possible that not grounding the DC on an inverter could be code
compliant?  In the past, we were always required to install grounding
electrode conductors to the DC negative, as required for grounding Direct
Current systems (250 VIII).

Maybe grounding can be eliminated in a purely AC coupled system due to the
fact that the system is not supplying premise wiring. Maybe the DC can be
considered as an integral part of the system supplying the AC.

The rules for grounding DC are stated below.

250.162 Direct current Circuits and Systems to Be Grounded
(A) Two-Wire, Direct-Current Systems. A 2-wire, dc system supplying
premises wiring and operating at greater than 50 volts but not greater than
300 volts shall be grounded.
Exception No. 1:  A system equipped with a ground detector and supplying
only industrial equipment in limited areas shall not be required to be
grounded.
Exception No. 2:  A rectifier-derived dc system supplied from an ac system
complying with 250.20 shall not be required to be grounded.
Exception No. 3:  Direct-current fire alarm circuits having a maximum
current of 0.030 ampere as specified in Article 760, Part III, shall not be
required to be grounded.

In a Sunny Island system there is no charge control, nothing else in the DC
besides the battery and battery cables.  Does not grounding the negative
really meet code requirements in the US ? Are the inverter cables not
considered to be premise wiring?

Thanks,

Drake


 At 03:56 PM 4/10/2013, you wrote:

Content-Class: urn:content-classes:message
Content-Language: en-US
Content-Type: multipart/alternative;

boundary=_000_B448FC9E37458B469E77EA0BB954AD4702BD99AC6Emailbox01_

August:

The SI can run with an ungrounded battery or a grounded battery.
With the internal breaker it is set up for a negative ground battery.
I believe the manual says ground at the battery terminal.
If you chose to go ungrounded you will need to have an OCPD in both battery
+ and battery – (all ungrounded conductors).

I am pretty sure the SI is not internally bonded to ground.
This is normal in the rest of the world.
Mine are running with an ungrounded battery and there isolation between
battery and ground.

Best Regards,

John Berdner
General Manager, North America

SolarEdge Technologies, Inc.
3347 Gateway Boulevard, Fremont CA 94538 USA  *(*Please note of our new
address.)*
T: 510.498.3200, X 747
M: 530.277.4894

*From:* re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.orgre-wrenches-boun...@lists.re-wrenches.org]
*On Behalf Of *August Goers
*Sent:* Wednesday, April 10, 2013 9:45 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Fuse sizing in battery circuits

Hi All -

As a slightly separate topic, should we fuse both the positive and negative
battery lines with an SMA Sunny Island? I believe that the negative is
grounded so should not be fused but I've heard conflicting stories from
tech support.

Thanks,

August

*From:* re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.orgre-wrenches-boun...@lists.re-wrenches.org]
*On Behalf Of *Drake
*Sent:* Wednesday, April 10, 2013 5:52 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Fuse sizing in battery circuits

boB,

SMA does recommend protecting Sunny Islands with a fuse on the battery,
even though the breakers on the units are rated for 10,000 Amps.  Are the
SI breakers inferior others you have mentioned?

Thanks,

Drake



At 12:14 AM 4/10/2013, you wrote:

After 100's of thousands of  inverters having been shipped in the last many
years
and thousands of inverters broken and shorting the battery terminals, there
has
never been (to our knowledge) one breaker that has not tripped.

The Midnite site lists the AIC rating of all our breakers I believe.

The Carling F series of Magnetic-Hydraulic breakers poop sheet is here...

http://www.carlingtech.com/sites/default/files/documents/F-Series_Details_%26_COS_0.pdf

I guess there isn't a graph of AIC vs. voltage on their F series web page
but we remember
them showing us figures or a graph that says those breakers have an AIC of
more than
100,000 amps at 48 volts.  We'll try to find that info or you may be able
to get that
from Carling.

I have, many times, directly connected these breakers across good L-16
battery strings
to demonstrate the left-hand rule to people where the 4/0

Re: [RE-wrenches] Fuse sizing in battery circuits

2013-04-15 Thread Ray Walters

Hi August;

250.162(A) says operating at greater than 50 v, which a 48 v nominal 
system operates most of the time at over 50 v, at least when solar 
charging and/or selling back.
We used to get dinged many years ago for using breakers rated at 50v dc 
on 48 v systems.  John Wiles used to insist we use the highest possible 
voltage (Voc of modules on coldest day)
Personally I prefer ungrounded systems, so I'm not saying there's 
anything wrong from a safety stand point, just that inspectors here 
don't see it the same way.


R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 4/15/2013 2:20 PM, August Goers wrote:


Hi Drake,

The Sunny Island System runs at 48 V nominal so I don't believe 
250.162(A) applies. We have some really savvy inspectors in the Bay 
Area and they were happy for us to be ungrounded since we're operating 
at 48 V. Yes, the actual voltage might go above 50 V when charging but 
I believe it is the nominal voltage that the code cares about.


Best,




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fuse sizing in battery circuits

2013-04-12 Thread Drake
Are AC coupled systems with no DC loads exempted 
from the grounding rules of DC coupled, battery 
based systems and the rules of DC grounding?





This is from the Sunny Island Manual:
External grounding of the negative pole of the 
batteries is possible, because the batteries

and the grid side are galvanically isolated within the Sunny Island.
• Dimenssion the cross‑section of the 
protective conductor sufficiently. Thus you are
ensuring that in the event of a fault the high 
currents occurring can be discharged with

an external grounding.
• If groounding of the negative pole of the 
battery is necessary, assemble this outside of

the Sunny Island.

As far as I am aware, the NEC code is kind of 
vague on grounding battery banks (please correct 
me if I am wrong), it is more of a AHJ requirement.


There is no reference to ground (DC side) inside the SI.

SMA America, LLC
Steve Jefferson
Supervisor, Service Line
6020 West Oaks Blvd, Suite 300
Rocklin, CA 95765 - 3714
U.S.A.
Tel:  +1 916 625 0870
Fax: +1 916 624-2445
Service Line +1 877 697 6283 (Toll Free)
Email: steve.jeffer...@sma-america.com
http://www.sma-america.com/www.SMA-America.com

This email and any attachments thereto may 
contain SMA America, LLC confidential, 
privileged and private material for the sole use 
of the intended recipient. Any review, copying, 
or distribution of this email (or any 
attachments thereto) by others is strictly 
prohibited. If you are not the intended 
recipient, please contact the sender immediately 
and permanently delete the original and any 
copies of this email and any attachments thereto. Thank you.


From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of August Goers

Sent: Wednesday, April 10, 2013 2:13 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Fuse sizing in battery circuits

Steve,

So if we wanted to ground the negative would we 
literally run a ground wire to one of the 
battery terminals? Is there anything in the NEC 
that governs this? What are the deciding factors 
when deciding to ground the negative or not?


As a separate note, I've noticed that the 
negative battery terminals measure 0 volts to 
ground on a Sunny Island setup once everything 
is connected without any extra grounding added. 
I thought that there must be some reference to 
ground happening in the Sunny Island but apparently I'm wrong.


Thanks, August

From: 
mailto:re-wrenches-boun...@lists.re-wrenches.orgre-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Steve Jefferson

Sent: Wednesday, April 10, 2013 9:56 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Fuse sizing in battery circuits

If the Batt negative is not bonded to ground, 
then yes SMA recommends fusing both Positive and Negative.


Also, the negative is not bonded to ground internally in the Sunny Island.

SMA America, LLC
Steve Jefferson
Supervisor, Service Line
6020 West Oaks Blvd, Suite 300
Rocklin, CA 95765 - 3714
U.S.A.
Tel:  +1 916 625 0870
Fax: +1 916 624-2445
Service Line +1 877 697 6283 (Toll Free)
Email: mailto:steve.jeffer...@sma-america.comsteve.jeffer...@sma-america.com
www.SMA-America.com

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fuse sizing in battery circuits

2013-04-10 Thread Steve Jefferson
If the Batt negative is not bonded to ground, then yes SMA recommends fusing 
both Positive and Negative.

Also, the negative is not bonded to ground internally in the Sunny Island.

SMA America, LLC
Steve Jefferson
Supervisor, Service Line
6020 West Oaks Blvd, Suite 300
Rocklin, CA 95765 - 3714
U.S.A.
Tel:  +1 916 625 0870
Fax: +1 916 624-2445
Service Line +1 877 697 6283 (Toll Free)
Email: steve.jeffer...@sma-america.com
www.SMA-America.comhttp://www.sma-america.com/

This email and any attachments thereto may contain SMA America, LLC 
confidential, privileged and private material for the sole use of the intended 
recipient. Any review, copying, or distribution of this email (or any 
attachments thereto) by others is strictly prohibited. If you are not the 
intended recipient, please contact the sender immediately and permanently 
delete the original and any copies of this email and any attachments thereto. 
Thank you.

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of August Goers
Sent: Wednesday, April 10, 2013 9:45 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Fuse sizing in battery circuits

Hi All -

As a slightly separate topic, should we fuse both the positive and negative 
battery lines with an SMA Sunny Island? I believe that the negative is grounded 
so should not be fused but I've heard conflicting stories from tech support.

Thanks,

August

From: 
re-wrenches-boun...@lists.re-wrenches.orgmailto:re-wrenches-boun...@lists.re-wrenches.org
 
[mailto:re-wrenches-boun...@lists.re-wrenches.orgmailto:re-wrenches-boun...@lists.re-wrenches.org]
 On Behalf Of Drake
Sent: Wednesday, April 10, 2013 5:52 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Fuse sizing in battery circuits

boB,

SMA does recommend protecting Sunny Islands with a fuse on the battery, even 
though the breakers on the units are rated for 10,000 Amps.  Are the  SI 
breakers inferior others you have mentioned?

Thanks,

Drake



At 12:14 AM 4/10/2013, you wrote:

After 100's of thousands of  inverters having been shipped in the last many 
years
and thousands of inverters broken and shorting the battery terminals, there has
never been (to our knowledge) one breaker that has not tripped.

The Midnite site lists the AIC rating of all our breakers I believe.

The Carling F series of Magnetic-Hydraulic breakers poop sheet is here...

http://www.carlingtech.com/sites/default/files/documents/F-Series_Details_%26_COS_0.pdf

I guess there isn't a graph of AIC vs. voltage on their F series web page but 
we remember
them showing us figures or a graph that says those breakers have an AIC of more 
than
100,000 amps at 48 volts.  We'll try to find that info or you may be able to 
get that
from Carling.

I have, many times, directly connected these breakers across good L-16 battery 
strings
to demonstrate the left-hand rule to people where the 4/0 cable jumps apart or 
towards each
other when very high current passes through those wires when they are near each 
other.

It always trips.  Never tried it at anything above a 48V battery banks IIRC.

Robin would like to mention that anyone that wants to use T-Classc fuses 
Welcome back to the 1990's

boB


On 4/9/2013 1:23 PM, Ray Walters wrote:
Hey Bob;

Can you share that AIC vs Voltage chart?

Thanks,

R.Ray Walters

CTO, Solarray, Inc

Nabcep Certified PV Installer,

Licensed Master Electrician

Solar Design Engineer

303 505-8760
On 4/9/2013 1:46 PM, boB wrote:

Those 250 amp and 175 amp breakers we have used for many many years now
have an AIC of 50,000 amps at 125 volts and if you look at the curve, at 48 
volts
they are around 100,000 amps.  I think that this information is on the label
of the breaker.

How many problems have you had with the Carlings or any other type of
those large breakers ?

boB


On 4/9/2013 10:40 AM, Michael Welch wrote:
If anyone would like an Acrobat version of this article, you can find it here:

ftp://ftp.re-wrenches.org/pub/hp27_pg26_freitas.pdf

William Dorsett wrote at 07:00 AM 4/9/2013:

This topic comes up often enough that we ought to mention a yellowed article in 
Home Power, (1992 Issue 27, pg 26). Christopher Freitas wrote Overcurrent 
Protection for Battery-Powered Systems where he describes experiments he did 
back when he was with Ananda. He put a 2000 A Big Switch to initiate a short 
(4/0 cable) between the terminals on a set of four golf cart batteries (2 
strings @ 12V). In series, he put in a 500A Shunt so he could measure current 
passing and various fuses and breakers. For comparison, we decided to directly 
short the battery...the meter read 6960 amps peak current (three seconds) 
...during each test the 4/0 cable lifted off the ground 4 inches into the air 
by the forces generated by the extremely high current.. They videoed the 250 A 
ANN buss fuses arc and smoke; the 200A Heinemann Series AM breakers (paralleled 
ones that maybe Roy mentioned) went 3 seconds without breaking

Re: [RE-wrenches] Fuse sizing in battery circuits

2013-04-10 Thread John Berdner
August:

The SI can run with an ungrounded battery or a grounded battery.
With the internal breaker it is set up for a negative ground battery.
I believe the manual says ground at the battery terminal.
If you chose to go ungrounded you will need to have an OCPD in both battery + 
and battery - (all ungrounded conductors).

I am pretty sure the SI is not internally bonded to ground.
This is normal in the rest of the world.
Mine are running with an ungrounded battery and there isolation between battery 
and ground.

Best Regards,

John Berdner
General Manager, North America

SolarEdge Technologies, Inc.
3347 Gateway Boulevard, Fremont CA 94538 USA  (*Please note of our new address.)
T: 510.498.3200, X 747
M: 530.277.4894

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of August Goers
Sent: Wednesday, April 10, 2013 9:45 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Fuse sizing in battery circuits

Hi All -

As a slightly separate topic, should we fuse both the positive and negative 
battery lines with an SMA Sunny Island? I believe that the negative is grounded 
so should not be fused but I've heard conflicting stories from tech support.

Thanks,

August

From: 
re-wrenches-boun...@lists.re-wrenches.orgmailto:re-wrenches-boun...@lists.re-wrenches.org
 
[mailto:re-wrenches-boun...@lists.re-wrenches.orgmailto:re-wrenches-boun...@lists.re-wrenches.org]
 On Behalf Of Drake
Sent: Wednesday, April 10, 2013 5:52 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Fuse sizing in battery circuits

boB,

SMA does recommend protecting Sunny Islands with a fuse on the battery, even 
though the breakers on the units are rated for 10,000 Amps.  Are the  SI 
breakers inferior others you have mentioned?

Thanks,

Drake



At 12:14 AM 4/10/2013, you wrote:

After 100's of thousands of  inverters having been shipped in the last many 
years
and thousands of inverters broken and shorting the battery terminals, there has
never been (to our knowledge) one breaker that has not tripped.

The Midnite site lists the AIC rating of all our breakers I believe.

The Carling F series of Magnetic-Hydraulic breakers poop sheet is here...

http://www.carlingtech.com/sites/default/files/documents/F-Series_Details_%26_COS_0.pdf

I guess there isn't a graph of AIC vs. voltage on their F series web page but 
we remember
them showing us figures or a graph that says those breakers have an AIC of more 
than
100,000 amps at 48 volts.  We'll try to find that info or you may be able to 
get that
from Carling.

I have, many times, directly connected these breakers across good L-16 battery 
strings
to demonstrate the left-hand rule to people where the 4/0 cable jumps apart or 
towards each
other when very high current passes through those wires when they are near each 
other.

It always trips.  Never tried it at anything above a 48V battery banks IIRC.

Robin would like to mention that anyone that wants to use T-Classc fuses 
Welcome back to the 1990's

boB


On 4/9/2013 1:23 PM, Ray Walters wrote:
Hey Bob;

Can you share that AIC vs Voltage chart?

Thanks,

R.Ray Walters

CTO, Solarray, Inc

Nabcep Certified PV Installer,

Licensed Master Electrician

Solar Design Engineer

303 505-8760
On 4/9/2013 1:46 PM, boB wrote:

Those 250 amp and 175 amp breakers we have used for many many years now
have an AIC of 50,000 amps at 125 volts and if you look at the curve, at 48 
volts
they are around 100,000 amps.  I think that this information is on the label
of the breaker.

How many problems have you had with the Carlings or any other type of
those large breakers ?

boB


On 4/9/2013 10:40 AM, Michael Welch wrote:
If anyone would like an Acrobat version of this article, you can find it here:

ftp://ftp.re-wrenches.org/pub/hp27_pg26_freitas.pdf

William Dorsett wrote at 07:00 AM 4/9/2013:

This topic comes up often enough that we ought to mention a yellowed article in 
Home Power, (1992 Issue 27, pg 26). Christopher Freitas wrote Overcurrent 
Protection for Battery-Powered Systems where he describes experiments he did 
back when he was with Ananda. He put a 2000 A Big Switch to initiate a short 
(4/0 cable) between the terminals on a set of four golf cart batteries (2 
strings @ 12V). In series, he put in a 500A Shunt so he could measure current 
passing and various fuses and breakers. For comparison, we decided to directly 
short the battery...the meter read 6960 amps peak current (three seconds) 
...during each test the 4/0 cable lifted off the ground 4 inches into the air 
by the forces generated by the extremely high current.. They videoed the 250 A 
ANN buss fuses arc and smoke; the 200A Heinemann Series AM breakers (paralleled 
ones that maybe Roy mentioned) went 3 seconds without breaking and the video 
showed a flash and blue smoke.
175A ITE breaker with 42,000 AIC simply tripped...but still allowed a peak 
current of 2960 amps
200A Class T Littlefuse opened promptly with no external signs

Re: [RE-wrenches] Fuse sizing in battery circuits

2013-04-09 Thread Drake
 to that same bus bar.  It has some advantages, as 
individual strings can be monitored and serviced without taking 
the entire system down.


FWIW, OutBack makes a battery rack for AGM batteries with series 
string overcurrent and disconnects on every string.  It's also to 
my knowledge the first UL1741 Listed device available -- the other 
stuff I've seen is either not listed, or is trading on old 508a 
standards.  AGMs might not be for every installation, but for jobs 
where they are appropriate this could be a good, code-compliant solution.



Phil Undercuffler
OutBack Power




On Friday, April 5, 2013, Ray Walters wrote:
I just finished a rewire and we kept the Ananda power center, Allan :-)
Back when we used class T fuses more they were always over sized 
relative to Heinemann breakers.

400 amp class T fuse = 250 amp breaker= 4/0 cable
200 amp class T fuse = 175 amp breaker= 2/0 cable

I still think class T fuses are superior in some ways to breakers: 
they have better interrupt capacity and trip faster in a short 
circuit condition.


However, If you spend too much time thinking about and looking at 
the trip curves, you'll break your brain and special order some 
weird fuses and breakers.  (anybody need a 350 amp class T fuse?)
 Just follow the inverter manufacturer's recommendations and all 
will be well.
On the other hand, William has brought up a topic I have harped on 
for years:  Having the OCPD in the cabinet doesn't protect the 
majority of the circuit.  Class T fuses at the battery terminals 
do, but they're not rated for the corrosive environment.  I have 
thrown a few class T fuses away that had acid eating away at the ends.
I don't have the solution, but I will continue to point out that 
this is a real problem. Dropping a wrench across the battery 
terminals can lead to a spectacular failure that not only can 
cause a fire, but might even cause a battery explosion, yet NEC 
offers no protection.

We use insulated wrenches from experience, and hope for the best.

R.Ray Walters

CTO, Solarray, Inc

Nabcep Certified PV Installer,

Licensed Master Electrician

Solar Design Engineer

303 505-8760
On 4/5/2013 8:29 PM, William Miller wrote:

Friends:

Good topic.  Some questions:

1. Most manufacturer's present an installation guide that shows 
one OCPD in the battery circuit and that is in the BOS 
cabinet.  This means the battery leads are unprotected.  Do we 
need an OPCD at the battery terminals?


2. Class T fuses are generally recommended for this 
application.  The data shows them as fast acting.  Is this a 
problem?  Will they act too fast and open during normal surge loads?


Thanks in advance!

William Miller






Troy,

Overcurrent device size is matched to the conductor size. The 
inverse time constant nature of an overcurrent device can 
typically handle the surge currents as long as conductor sizing 
has truly been done correctly for the conductor. Circuit 
breakers are preferred to fuses because they can be reset.


There has been volumes written on this issue. The constant 
current at lowest battery voltage should be used, plus the ac 
ripple content on the battery circuit. This is usually a much 
larger conductor than your average designer will plan for. The 
best thing is to look at Midnight, Outback, and Schneider and 
see what size overcurrent devices they require for their 
products. That will give you a good clue as to how to size the 
conductor and overcurrent device.


Bill.

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Troy Harvey

Sent: Friday, April 05, 2013 3:38 PM
To: RE-wrenches
Subject: [RE-wrenches] Fuse sizing in battery circuits

I've got a question about battery string fusing. Typically we 
size the wire from the batteries to the inverter based on 
continuous rating procedures (max power/efficiency)*125%.


However a 6kW inverter, can peak at 12kW for 5-10 seconds, 
doubling the source current. That is no big deal for the wire, 
because it is a short time frame... little heat will be 
generated. However, in fusing the sub-strings, you need to 
account for that peak surge current so you don't blow fuses all 
the time. But if you put a 500-1000 amp fuse on a 4/0 wire, 
above the max surge draw of the inverter, the wire will be 
under-protected for its ampacity rating. Any thoughts on the catch-22?







___
List sponsored by Home Power magazine

List Address: 
mailto:RE-wrenches@lists.re-wrenches.orgRE-wrenches@lists.re-wrenches.org


Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orghttp://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orghttp://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules  etiquette:
http://www.re-wrenches.org/etiquette.htmwww.re-wrenches.org/etiquette.htm

Check

Re: [RE-wrenches] Fuse sizing in battery circuits

2013-04-09 Thread Michael Welch


If anyone would like an Acrobat version of this article, you can find it
here:

ftp://ftp.re-wrenches.org/pub/hp27_pg26_freitas.pdf
William Dorsett wrote at 07:00 AM 4/9/2013:

This topic comes up often enough
that we ought to mention a yellowed article in Home Power, (1992 Issue
27, pg 26). Christopher Freitas wrote Overcurrent Protection for
Battery-Powered Systems where he describes experiments he did back
when he was with Ananda. He put a 2000 A Big Switch to initiate a short
(4/0 cable) between the terminals on a set of four golf cart batteries (2
strings @ 12V). In series, he put in a 500A Shunt so he could measure
current passing and various fuses and breakers. “For comparison, we
decided to directly short the battery…the meter read 6960 amps peak
current (three seconds) …during each test the 4/0 cable lifted off the
ground 4 inches into the air by the forces generated by the extremely
high current..” They videoed the 250 A ANN buss fuses arc and smoke; the
200A Heinemann Series AM breakers (paralleled ones that maybe Roy
mentioned) went 3 seconds without breaking and the video showed a flash
and blue smoke. 
175A ITE breaker with 42,000 AIC “simply tripped…but still allowed a peak
current of 2960 amps
200A Class T Littlefuse “opened promptly with no external signs of
stress…1920 amps peak current”
Christopher’s recommendations: 
“Every AE system must have overcurrent protection able to interrupt the
maximum current available from the batteries. For most systems, the main
protection should use current limiting high AIC fuses, such as a Class T
or Class R. A disconnect switch which allows the fuse to be safely
changed should be included. A lower cost alternative is to mount the fuse
in a fuse holder without a disconnect. Although the fuse would always be
electrically hot, it normally would not be changed during the life
of the system. The fuse holder should be mounted outside the battery
enclosure. Fuses should not be bolted directly onto the battery terminal,
as they are not designed to handle the physical stresses that can occur
without the protection of a fuse holder.

Fuses which have exposed elements, such as ANN fuses, should not be used
because they are not current limiting and have only 2500 amps AIC. They
also may be a significant hazard when installed near batteries. 

High AIC breakers, like the Heinemann Series CF (25,000 Amps AIC @ 65VDC)
can provide overcurrent protection for individual items. They cannot be
used to protect lower AIC breakers. This eliminates their use as a main
disconnect in most systems. 

Low AIC breakers, like the Heinemann Series AM (5000A AIC @65 VDC) or the
Square-D QO (5000A @ 125 VDC) can be used in load distribution centers
and components, but must be protected by a current limiting fuse. Using
low-AIC breakers alone will not provide sufficient protection with a
battery system and may be a significant hazard during short circuit
situations.”

It won’t pull up anymore on HP’s article search but probably Michael has
a copy he could post for those interested. 

Bill Dorsett


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fuse sizing in battery circuits

2013-04-09 Thread boB


Those 250 amp and 175 amp breakers we have used for many many years now
have an AIC of 50,000 amps at 125 volts and if you look at the curve, at 
48 volts

they are around 100,000 amps.  I think that this information is on the label
of the breaker.

How many problems have you had with the Carlings or any other type of
those large breakers ?

boB


On 4/9/2013 10:40 AM, Michael Welch wrote:
If anyone would like an Acrobat version of this article, you can find 
it here:


ftp://ftp.re-wrenches.org/pub/hp27_pg26_freitas.pdf

ftp://ftp.re-wrenches.org/pub/hp27_pg26_freitas.pdfWilliam Dorsett 
wrote at 07:00 AM 4/9/2013:


This topic comes up often enough that we ought to mention a yellowed 
article in Home Power, (1992 Issue 27, pg 26). Christopher Freitas 
wrote /Overcurrent Protection for Battery-Powered Systems /where he 
describes experiments he did back when he was with Ananda. He put a 
2000 A Big Switch to initiate a short (4/0 cable) between the 
terminals on a set of four golf cart batteries (2 strings @ 12V). In 
series, he put in a 500A Shunt so he could measure current passing 
and various fuses and breakers. For comparison, we decided to 
directly short the battery...the meter read 6960 amps peak current 
(three seconds) ...during each test the 4/0 cable lifted off the 
ground 4 inches into the air by the forces generated by the extremely 
high current.. They videoed the 250 A ANN buss fuses arc and smoke; 
the 200A Heinemann Series AM breakers (paralleled ones that maybe Roy 
mentioned) went 3 seconds without breaking and the video showed a 
flash and blue smoke.
175A ITE breaker with 42,000 AIC simply tripped...but still allowed 
a peak current of 2960 amps
200A Class T Littlefuse opened promptly with no external signs of 
stress...1920 amps peak current

Christopher's recommendations:
Every AE system must have overcurrent protection able to interrupt 
the maximum current available from the batteries. For most systems, 
the main protection should use current limiting high AIC fuses, such 
as a Class T or Class R. A disconnect switch which allows the fuse to 
be safely changed should be included. A lower cost alternative is to 
mount the fuse in a fuse holder without a disconnect. Although the 
fuse would always be electrically hot,  it normally would not be 
changed during the life of the system. The fuse holder should be 
mounted outside the battery enclosure. Fuses should not be bolted 
directly onto the battery terminal, as they are not designed to 
handle the physical stresses that can occur without the protection of 
a fuse holder.


Fuses which have exposed elements, such as ANN fuses, should not be 
used because they are not current limiting and have only 2500 amps 
AIC. They also may be a significant hazard when installed near 
batteries.


High AIC breakers, like the Heinemann Series CF (25,000 Amps AIC @ 
65VDC) can provide overcurrent protection for individual items. They 
cannot be used to protect lower AIC breakers. This eliminates their 
use as a main disconnect in most systems.


Low AIC breakers, like the Heinemann Series AM (5000A AIC @65 VDC) or 
the Square-D QO (5000A @ 125 VDC) can be used in load distribution 
centers and components, but must be protected by a current limiting 
fuse. Using low-AIC breakers alone will not provide sufficient 
protection with a battery system and may be a significant hazard 
during short circuit situations.


It won't pull up anymore on HP's article search but probably Michael 
has a copy he could post for those interested./

/
Bill  Dorsett





___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fuse sizing in battery circuits

2013-04-07 Thread Troy Harvey
Allan,

that is a good graph. Thanks. The time vs current is way different than whst 
I've seen from fuse charts in the past.

I'd rather use DC-breakers, but I'm having trouble finding 350AMP DC breakers 
for 350MCM cable. Any resources?

thanks,

Troy Harvey
-
Principal Engineer
Heliocentric
801-453-9434
tahar...@heliocentric.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fuse sizing in battery circuits

2013-04-06 Thread Phil Undercuffler
Ray,

690 does offer the protection, it's just that most maufacturers haven't
made it easy.

690.71 Installation

(C) Current Limiting. A listed, current-limiting, overcurrent device shall
be installed in each circuit adjacent to the batteries where the available
short-circuit current from a battery or battery bank exceeds the
interrupting or withstand ratings of other equipment in that circuit. The
installation of current-limiting fuses shall comply with 690.16.

The telcom industry has been doing this for years.  Their norm is to have
each string of batteries on a shelf, and terminate at a breaker.  Each
string then is combined at a bus bar or plate, to help ensure equal current
on each string.  The loads and charging sources all come to that same bus
bar.  It has some advantages, as individual strings can be monitored and
serviced without taking the entire system down.

FWIW, OutBack makes a battery rack for AGM batteries with series string
overcurrent and disconnects on every string.  It's also to my knowledge the
first UL1741 Listed device available -- the other stuff I've seen is either
not listed, or is trading on old 508a standards.  AGMs might not be for
every installation, but for jobs where they are appropriate this could be a
good, code-compliant solution.


Phil Undercuffler
OutBack Power




On Friday, April 5, 2013, Ray Walters wrote:

  I just finished a rewire and we kept the Ananda power center, Allan :-)
 Back when we used class T fuses more they were always over sized relative
 to Heinemann breakers.
 400 amp class T fuse = 250 amp breaker= 4/0 cable
 200 amp class T fuse = 175 amp breaker= 2/0 cable

 I still think class T fuses are superior in some ways to breakers: they
 have better interrupt capacity and trip faster in a short circuit condition.

 However, If you spend too much time thinking about and looking at the trip
 curves, you'll break your brain and special order some weird fuses and
 breakers.  (anybody need a 350 amp class T fuse?)
  Just follow the inverter manufacturer's recommendations and all will be
 well.
 On the other hand, William has brought up a topic I have harped on for
 years:  Having the OCPD in the cabinet doesn't protect the majority of the
 circuit.  Class T fuses at the battery terminals do, but they're not rated
 for the corrosive environment.  I have thrown a few class T fuses away that
 had acid eating away at the ends.
 I don't have the solution, but I will continue to point out that this is a
 real problem. Dropping a wrench across the battery terminals can lead to a
 spectacular failure that not only can cause a fire, but might even cause a
 battery explosion, yet NEC offers no protection.
 We use insulated wrenches from experience, and hope for the best.

 R.Ray Walters
 CTO, Solarray, Inc
 Nabcep Certified PV Installer,
 Licensed Master Electrician
 Solar Design Engineer
 303 505-8760

 On 4/5/2013 8:29 PM, William Miller wrote:

 Friends:

 Good topic.  Some questions:

 1. Most manufacturer's present an installation guide that shows one OCPD
 in the battery circuit and that is in the BOS cabinet.  This means the
 battery leads are unprotected.  Do we need an OPCD at the battery terminals?

 2. Class T fuses are generally recommended for this application.  The data
 shows them as fast acting.  Is this a problem?  Will they act too fast
 and open during normal surge loads?

 Thanks in advance!

 William Miller





 Troy,

 Overcurrent device size is matched to the conductor size. The inverse time
 constant nature of an overcurrent device can typically handle the surge
 currents as long as conductor sizing has truly been done correctly for the
 conductor. Circuit breakers are preferred to fuses because they can be
 reset.

 There has been volumes written on this issue. The constant current at
 lowest battery voltage should be used, plus the ac ripple content on the
 battery circuit. This is usually a much larger conductor than your average
 designer will plan for. The best thing is to look at Midnight, Outback, and
 Schneider and see what size overcurrent devices they require for their
 products. That will give you a good clue as to how to size the conductor
 and overcurrent device.

 Bill.

 *From:* re-wrenches-boun...@lists.re-wrenches.org javascript:_e({},
 'cvml', 're-wrenches-boun...@lists.re-wrenches.org'); [
 mailto:re-wrenches-boun...@lists.re-wrenches.org javascript:_e({},
 'cvml', 're-wrenches-boun...@lists.re-wrenches.org');] *On Behalf Of *Troy
 Harvey
 *Sent:* Friday, April 05, 2013 3:38 PM
 *To:* RE-wrenches
 *Subject:* [RE-wrenches] Fuse sizing in battery circuits

 I've got a question about battery string fusing. Typically we size the
 wire from the batteries to the inverter based on continuous rating
 procedures (max power/efficiency)*125%.

 However a 6kW inverter, can peak at 12kW for 5-10 seconds, doubling the
 source current. That is no big deal for the wire, because it is a short
 time frame... little heat will be generated

Re: [RE-wrenches] Fuse sizing in battery circuits

2013-04-06 Thread Ray Walters
 loads?

Thanks in advance!

William Miller






Troy,

Overcurrent device size is matched to the conductor size. The
inverse time constant nature of an overcurrent device can
typically handle the surge currents as long as conductor sizing
has truly been done correctly for the conductor. Circuit
breakers are preferred to fuses because they can be reset.

There has been volumes written on this issue. The constant
current at lowest battery voltage should be used, plus the ac
ripple content on the battery circuit. This is usually a much
larger conductor than your average designer will plan for. The
best thing is to look at Midnight, Outback, and Schneider and
see what size overcurrent devices they require for their
products. That will give you a good clue as to how to size the
conductor and overcurrent device.

Bill.

*From:* re-wrenches-boun...@lists.re-wrenches.org
javascript:_e({}, 'cvml',
're-wrenches-boun...@lists.re-wrenches.org');
[mailto:re-wrenches-boun...@lists.re-wrenches.org
javascript:_e({}, 'cvml',
're-wrenches-boun...@lists.re-wrenches.org');] *On Behalf Of
*Troy Harvey
*Sent:* Friday, April 05, 2013 3:38 PM
*To:* RE-wrenches
*Subject:* [RE-wrenches] Fuse sizing in battery circuits

I've got a question about battery string fusing. Typically we
size the wire from the batteries to the inverter based on
continuous rating procedures (max power/efficiency)*125%.

However a 6kW inverter, can peak at 12kW for 5-10 seconds,
doubling the source current. That is no big deal for the wire,
because it is a short time frame... little heat will be
generated. However, in fusing the sub-strings, you need to
account for that peak surge current so you don't blow fuses all
the time. But if you put a 500-1000 amp fuse on a 4/0 wire,
above the max surge draw of the inverter, the wire will be
under-protected for its ampacity rating. Any thoughts on the
catch-22?



___
List sponsored by Home Power magazine

List Address:RE-wrenches@lists.re-wrenches.org  javascript:_e({}, 'cvml', 
'RE-wrenches@lists.re-wrenches.org');

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org


List-Archive:http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm  
http://www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org  http://www.members.re-wrenches.org





___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Fuse sizing in battery circuits

2013-04-05 Thread Troy Harvey
I've got a question about battery string fusing. Typically we size the wire 
from the batteries to the inverter based on continuous rating procedures (max 
power/efficiency)*125%. 

However a 6kW inverter, can peak at 12kW for 5-10 seconds, doubling the source 
current. That is no big deal for the wire, because it is a short time frame... 
little heat will be generated. However, in fusing the sub-strings, you need to 
account for that peak surge current so you don't blow fuses all the time. But 
if you put a 500-1000 amp fuse on a 4/0 wire, above the max surge draw of the 
inverter, the wire will be under-protected for its ampacity rating. Any 
thoughts on the catch-22?


thanks,

Troy Harvey
-
Principal Engineer
Heliocentric
801-453-9434
tahar...@heliocentric.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fuse sizing in battery circuits

2013-04-05 Thread William Miller

Friends:

Good topic.  Some questions:

1. Most manufacturer's present an installation guide that shows one OCPD in 
the battery circuit and that is in the BOS cabinet.  This means the battery 
leads are unprotected.  Do we need an OPCD at the battery terminals?


2. Class T fuses are generally recommended for this application.  The data 
shows them as fast acting.  Is this a problem?  Will they act too fast 
and open during normal surge loads?


Thanks in advance!

William Miller






Troy,

Overcurrent device size is matched to the conductor size. The inverse time 
constant nature of an overcurrent device can typically handle the surge 
currents as long as conductor sizing has truly been done correctly for the 
conductor. Circuit breakers are preferred to fuses because they can be reset.


There has been volumes written on this issue. The constant current at 
lowest battery voltage should be used, plus the ac ripple content on the 
battery circuit. This is usually a much larger conductor than your average 
designer will plan for. The best thing is to look at Midnight, Outback, 
and Schneider and see what size overcurrent devices they require for their 
products. That will give you a good clue as to how to size the conductor 
and overcurrent device.


Bill.

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Troy Harvey

Sent: Friday, April 05, 2013 3:38 PM
To: RE-wrenches
Subject: [RE-wrenches] Fuse sizing in battery circuits

I've got a question about battery string fusing. Typically we size the 
wire from the batteries to the inverter based on continuous rating 
procedures (max power/efficiency)*125%.


However a 6kW inverter, can peak at 12kW for 5-10 seconds, doubling the 
source current. That is no big deal for the wire, because it is a short 
time frame... little heat will be generated. However, in fusing the 
sub-strings, you need to account for that peak surge current so you don't 
blow fuses all the time. But if you put a 500-1000 amp fuse on a 4/0 wire, 
above the max surge draw of the inverter, the wire will be under-protected 
for its ampacity rating. Any thoughts on the catch-22?


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fuse sizing in battery circuits

2013-04-05 Thread Ray Walters

I just finished a rewire and we kept the Ananda power center, Allan :-)
Back when we used class T fuses more they were always over sized 
relative to Heinemann breakers.

400 amp class T fuse = 250 amp breaker= 4/0 cable
200 amp class T fuse = 175 amp breaker= 2/0 cable

I still think class T fuses are superior in some ways to breakers: they 
have better interrupt capacity and trip faster in a short circuit condition.


However, If you spend too much time thinking about and looking at the 
trip curves, you'll break your brain and special order some weird fuses 
and breakers.  (anybody need a 350 amp class T fuse?)
 Just follow the inverter manufacturer's recommendations and all will 
be well.
On the other hand, William has brought up a topic I have harped on for 
years:  Having the OCPD in the cabinet doesn't protect the majority of 
the circuit.  Class T fuses at the battery terminals do, but they're not 
rated for the corrosive environment.  I have thrown a few class T fuses 
away that had acid eating away at the ends.
I don't have the solution, but I will continue to point out that this is 
a real problem. Dropping a wrench across the battery terminals can lead 
to a spectacular failure that not only can cause a fire, but might even 
cause a battery explosion, yet NEC offers no protection.

We use insulated wrenches from experience, and hope for the best.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 4/5/2013 8:29 PM, William Miller wrote:

Friends:

Good topic.  Some questions:

1. Most manufacturer's present an installation guide that shows one 
OCPD in the battery circuit and that is in the BOS cabinet.  This 
means the battery leads are unprotected.  Do we need an OPCD at the 
battery terminals?


2. Class T fuses are generally recommended for this application. The 
data shows them as fast acting.  Is this a problem?  Will they act 
too fast and open during normal surge loads?


Thanks in advance!

William Miller






Troy,

Overcurrent device size is matched to the conductor size. The inverse 
time constant nature of an overcurrent device can typically handle 
the surge currents as long as conductor sizing has truly been done 
correctly for the conductor. Circuit breakers are preferred to fuses 
because they can be reset.


There has been volumes written on this issue. The constant current at 
lowest battery voltage should be used, plus the ac ripple content on 
the battery circuit. This is usually a much larger conductor than 
your average designer will plan for. The best thing is to look at 
Midnight, Outback, and Schneider and see what size overcurrent 
devices they require for their products. That will give you a good 
clue as to how to size the conductor and overcurrent device.


Bill.

*From:* re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of 
*Troy Harvey

*Sent:* Friday, April 05, 2013 3:38 PM
*To:* RE-wrenches
*Subject:* [RE-wrenches] Fuse sizing in battery circuits

I've got a question about battery string fusing. Typically we size 
the wire from the batteries to the inverter based on continuous 
rating procedures (max power/efficiency)*125%.


However a 6kW inverter, can peak at 12kW for 5-10 seconds, doubling 
the source current. That is no big deal for the wire, because it is a 
short time frame... little heat will be generated. However, in fusing 
the sub-strings, you need to account for that peak surge current so 
you don't blow fuses all the time. But if you put a 500-1000 amp fuse 
on a 4/0 wire, above the max surge draw of the inverter, the wire 
will be under-protected for its ampacity rating. Any thoughts on the 
catch-22?



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org