Re: [RE-wrenches] Tech Support Issues with Sensata
We had one Magnum PAE 4048 have the frequency go high. It would not AC couple. When checking the frequency, it was out of range for the on grid inverters. So far, my tech support experience with Sensata has been good. The equipment I've installed has been problematic. I like the PAE system, but the inverters keep coming back off the wall. Drake Athens Electric --- On 2023-05-31 13:50, Ray Walters via RE-wrenches wrote: What were the issues? I've not seen a Magnum have power quality troubles, but they are not the "grid" either. My experience is that they are similar or a bit better than Outback, but certainly have measurable THD in the 4 to 5% range. Its almost always finicky loads, and the inverter has always been within its tolerances, so I doubt you have an actual warranty issue. However, I have seen inverter output get strange after lightning damage, which is not covered under warranty either. You need a decent meter that can measure THD, and can capture the peak voltage of the waveform. A good oscilloscope is even better, so you can see the waveform. Stuff like clocks not keeping time, or certain digital controls on certain appliances not functioning, is not a warranty claim. Lights dimming, or LEDs flickering is not a warranty claim. These are normal living off grid, and the only thing better than a Magnum for power quality is Exeltech in my experience. Ray Walters Remote Solar On 5/31/2023 11:37 AM, Chris Sparadeo via RE-wrenches wrote: Hi all, I have a client with a Magnum MS 4024- PAE inverter. There are some serious issues with power output quality and according to the client, another installer had started the RMA process while the inverter was still under warranty, however Sensata has not been responsive and has lost track of the case. They are asking for a new case to be initiated, but the inverter is now out of warranty. Has anyone out there had similar lack luster support issues with Sensata? Best, Chris -- Chris Sparadeo C_802-369-4458 H_802-728-3059 ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org
Re: [RE-wrenches] Tech Support Issues with Sensata
Those voltage and frequency variations are way out. No need for THD readings. You can't reliably run a household with that much variation, it will start letting the magic smoke out of many of the appliances. I'm not sure about a bad relay, I don't see how that would cause that variation. That sounds more like a cooked control board. I had lightning damage cause an inverter to put out 140 vac, while its onboard electronics read 120 vac. If it helps, I have a used MS 4024 PAE (very low hours) that I could send to you. Contact me off list if you want. Ray Walters Remote Solar On 5/31/2023 4:15 PM, Chris Sparadeo via RE-wrenches wrote: Ray, I don’t have too much time into troubleshooting, but I have confirmed that inverter AC output readings on the RC are suggesting steady voltage and frequency but my meter readings are showing voltage from 108-135VAC per leg and 60-95 Hz with or without loads. It sounds like a bad AC relay, but I haven’t put in the head banging against the wall effort to track down tech support that the previous installer had. I agree, a THD would be a good next step. Kindly, Chris On Wed, May 31, 2023 at 5:06 PM Bradley Bassett via RE-wrenches wrote: Just so you know, AEE Solar still has a bunch of Magnum panels and controls, no inverters, no support though. At least until they find someone to take it all. Keep an eye out for other close out stuff too. But, yes they are still going and working on getting better. Brad Bassett Retired--- 1985 Solar Engineering Services->Applied Power->Schott Applied Power->AEE Solar->AEE Solar (Mainstream Energy)->AEE Solar (Sunrun) 2023 On Wed, May 31, 2023 at 12:29 PM Rich Nicol via RE-wrenches wrote: Magnum has been difficult that last 3 years – we currently multiple inverters that are down needing boards for repair that can’t be obtained. It appears stock of new inverters is just starting to trickle back into suppliers so we hope to see parts soon. It seemed Magnum quality took also took a hit when purchased by Sensata and I think operations were moved to a new location? – we found MMP’s shipped with missing parts etc. The best tech support engineer they had went to Outback, but then was lost tragically to complications from Covid. *From:*RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Ray Walters via RE-wrenches *Sent:* Wednesday, May 31, 2023 1:51 PM *To:* re-wrenches@lists.re-wrenches.org *Cc:* Ray Walters *Subject:* Re: [RE-wrenches] Tech Support Issues with Sensata What were the issues? I've not seen a Magnum have power quality troubles, but they are not the "grid" either. My experience is that they are similar or a bit better than Outback, but certainly have measurable THD in the 4 to 5% range. Its almost always finicky loads, and the inverter has always been within its tolerances, so I doubt you have an actual warranty issue. However, I have seen inverter output get strange after lightning damage, which is not covered under warranty either. You need a decent meter that can measure THD, and can capture the peak voltage of the waveform. A good oscilloscope is even better, so you can see the waveform. Stuff like clocks not keeping time, or certain digital controls on certain appliances not functioning, is not a warranty claim. Lights dimming, or LEDs flickering is not a warranty claim. These are normal living off grid, and the only thing better than a Magnum for power quality is Exeltech in my experience. Ray Walters Remote Solar On 5/31/2023 11:37 AM, Chris Sparadeo via RE-wrenches wrote: Hi all, I have a client with a Magnum MS 4024- PAE inverter. There are some serious issues with power output quality and according to the client, another installer had started the RMA process while the inverter was still under warranty, however Sensata has not been responsive and has lost track of the case. They are asking for a new case to be initiated, but the inverter is now out of warranty. Has anyone out there had similar lack luster support issues with Sensata? Best, Chris -- Chris Sparadeo C_802-369-4458 H_802-728-3059 ___ List sponsored by Redwood Alliance Pay optional member dues here:http://re-wrenches.org List Address:RE-wrenches@lists.re-wrenches.org
Re: [RE-wrenches] Tech Support Issues with Sensata
Ray, I don’t have too much time into troubleshooting, but I have confirmed that inverter AC output readings on the RC are suggesting steady voltage and frequency but my meter readings are showing voltage from 108-135VAC per leg and 60-95 Hz with or without loads. It sounds like a bad AC relay, but I haven’t put in the head banging against the wall effort to track down tech support that the previous installer had. I agree, a THD would be a good next step. Kindly, Chris On Wed, May 31, 2023 at 5:06 PM Bradley Bassett via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Just so you know, AEE Solar still has a bunch of Magnum panels and > controls, no inverters, no support though. At least until they find someone > to take it all. Keep an eye out for other close out stuff too. But, yes > they are still going and working on getting better. > > Brad Bassett > Retired--- > 1985 Solar Engineering Services->Applied Power->Schott Applied Power->AEE > Solar->AEE Solar (Mainstream Energy)->AEE Solar (Sunrun) 2023 > > On Wed, May 31, 2023 at 12:29 PM Rich Nicol via RE-wrenches < > re-wrenches@lists.re-wrenches.org> wrote: > >> Magnum has been difficult that last 3 years – we currently multiple >> inverters that are down needing boards for repair that can’t be obtained. >> It appears stock of new inverters is just starting to trickle back into >> suppliers so we hope to see parts soon. >> >> It seemed Magnum quality took also took a hit when purchased by Sensata >> and I think operations were moved to a new location? – we found MMP’s >> shipped with missing parts etc. The best tech support engineer they had >> went to Outback, but then was lost tragically to complications from Covid. >> >> >> >> >> >> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On >> Behalf Of *Ray Walters via RE-wrenches >> *Sent:* Wednesday, May 31, 2023 1:51 PM >> *To:* re-wrenches@lists.re-wrenches.org >> *Cc:* Ray Walters >> *Subject:* Re: [RE-wrenches] Tech Support Issues with Sensata >> >> >> >> What were the issues? I've not seen a Magnum have power quality >> troubles, but they are not the "grid" either. My experience is that they >> are similar or a bit better than Outback, but certainly have measurable THD >> in the 4 to 5% range. Its almost always finicky loads, and the inverter >> has always been within its tolerances, so I doubt you have an actual >> warranty issue. However, I have seen inverter output get strange after >> lightning damage, which is not covered under warranty either. >> >> You need a decent meter that can measure THD, and can capture the peak >> voltage of the waveform. A good oscilloscope is even better, so you can >> see the waveform. >> >> Stuff like clocks not keeping time, or certain digital controls on >> certain appliances not functioning, is not a warranty claim. Lights >> dimming, or LEDs flickering is not a warranty claim. These are normal >> living off grid, and the only thing better than a Magnum for power quality >> is Exeltech in my experience. >> >> Ray Walters >> Remote Solar >> >> On 5/31/2023 11:37 AM, Chris Sparadeo via RE-wrenches wrote: >> >> Hi all, >> >> >> >> I have a client with a Magnum MS 4024- PAE inverter. There are some >> serious issues with power output quality and according to the client, >> another installer had started the RMA process while the inverter was still >> under warranty, however Sensata has not been responsive and has lost track >> of the case. They are asking for a new case to be initiated, but the >> inverter is now out of warranty. Has anyone out there had similar lack >> luster support issues with Sensata? >> >> >> >> Best, >> >> >> >> Chris >> >> -- >> >> Chris Sparadeo >> >> >> >> >> >> C_802-369-4458 >> >> H_802-728-3059 >> >> >> >> ___ >> >> List sponsored by Redwood Alliance >> >> >> >> Pay optional member dues here: http://re-wrenches.org >> >> >> >> List Address: RE-wrenches@lists.re-wrenches.org >> >> >> >> Change listserver email address & settings: >> >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> >> >> >> There are two list archives for searching. When one doesn't work, try the >> other: >> >> https://www.mail-archive.com/re-wrenches@lists.re-
Re: [RE-wrenches] Tech Support Issues with Sensata
Just so you know, AEE Solar still has a bunch of Magnum panels and controls, no inverters, no support though. At least until they find someone to take it all. Keep an eye out for other close out stuff too. But, yes they are still going and working on getting better. Brad Bassett Retired--- 1985 Solar Engineering Services->Applied Power->Schott Applied Power->AEE Solar->AEE Solar (Mainstream Energy)->AEE Solar (Sunrun) 2023 On Wed, May 31, 2023 at 12:29 PM Rich Nicol via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Magnum has been difficult that last 3 years – we currently multiple > inverters that are down needing boards for repair that can’t be obtained. > It appears stock of new inverters is just starting to trickle back into > suppliers so we hope to see parts soon. > > It seemed Magnum quality took also took a hit when purchased by Sensata > and I think operations were moved to a new location? – we found MMP’s > shipped with missing parts etc. The best tech support engineer they had > went to Outback, but then was lost tragically to complications from Covid. > > > > > > *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On > Behalf Of *Ray Walters via RE-wrenches > *Sent:* Wednesday, May 31, 2023 1:51 PM > *To:* re-wrenches@lists.re-wrenches.org > *Cc:* Ray Walters > *Subject:* Re: [RE-wrenches] Tech Support Issues with Sensata > > > > What were the issues? I've not seen a Magnum have power quality troubles, > but they are not the "grid" either. My experience is that they are similar > or a bit better than Outback, but certainly have measurable THD in the 4 to > 5% range. Its almost always finicky loads, and the inverter has always > been within its tolerances, so I doubt you have an actual warranty issue. > However, I have seen inverter output get strange after lightning damage, > which is not covered under warranty either. > > You need a decent meter that can measure THD, and can capture the peak > voltage of the waveform. A good oscilloscope is even better, so you can > see the waveform. > > Stuff like clocks not keeping time, or certain digital controls on certain > appliances not functioning, is not a warranty claim. Lights dimming, or > LEDs flickering is not a warranty claim. These are normal living off grid, > and the only thing better than a Magnum for power quality is Exeltech in my > experience. > > Ray Walters > Remote Solar > > On 5/31/2023 11:37 AM, Chris Sparadeo via RE-wrenches wrote: > > Hi all, > > > > I have a client with a Magnum MS 4024- PAE inverter. There are some > serious issues with power output quality and according to the client, > another installer had started the RMA process while the inverter was still > under warranty, however Sensata has not been responsive and has lost track > of the case. They are asking for a new case to be initiated, but the > inverter is now out of warranty. Has anyone out there had similar lack > luster support issues with Sensata? > > > > Best, > > > > Chris > > -- > > Chris Sparadeo > > > > > > C_802-369-4458 > > H_802-728-3059 > > > > ___ > > List sponsored by Redwood Alliance > > > > Pay optional member dues here: http://re-wrenches.org > > > > List Address: RE-wrenches@lists.re-wrenches.org > > > > Change listserver email address & settings: > > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > > > There are two list archives for searching. When one doesn't work, try the > other: > > https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ > > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > > > List rules & etiquette: > > http://www.re-wrenches.org/etiquette.htm > > > > Check out or update participant bios: > > http://www.members.re-wrenches.org > > > > ___ > List sponsored by Redwood Alliance > > Pay optional member dues here: http://re-wrenches.org > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > There are two list archives for searching. When one doesn't work, try the > other: > https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > http://www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > http://www.members.re-wrenches.org > >
Re: [RE-wrenches] Tech Support Issues with Sensata
MMPs – Many Missing Parts? Dana Orzel - E - d...@solarwork.com - C - 208.721.7003 From: RE-wrenches On Behalf Of Rich Nicol via RE-wrenches Sent: Wednesday, May 31, 2023 1:28 PM To: 'RE-wrenches' Cc: r...@solartechvt.com Subject: Re: [RE-wrenches] Tech Support Issues with Sensata Magnum has been difficult that last 3 years – we currently multiple inverters that are down needing boards for repair that can’t be obtained. It appears stock of new inverters is just starting to trickle back into suppliers so we hope to see parts soon. It seemed Magnum quality took also took a hit when purchased by Sensata and I think operations were moved to a new location? – we found MMP’s shipped with missing parts etc. The best tech support engineer they had went to Outback, but then was lost tragically to complications from Covid. From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ray Walters via RE-wrenches Sent: Wednesday, May 31, 2023 1:51 PM To: re-wrenches@lists.re-wrenches.org <mailto:re-wrenches@lists.re-wrenches.org> Cc: Ray Walters Subject: Re: [RE-wrenches] Tech Support Issues with Sensata What were the issues? I've not seen a Magnum have power quality troubles, but they are not the "grid" either. My experience is that they are similar or a bit better than Outback, but certainly have measurable THD in the 4 to 5% range. Its almost always finicky loads, and the inverter has always been within its tolerances, so I doubt you have an actual warranty issue. However, I have seen inverter output get strange after lightning damage, which is not covered under warranty either. You need a decent meter that can measure THD, and can capture the peak voltage of the waveform. A good oscilloscope is even better, so you can see the waveform. Stuff like clocks not keeping time, or certain digital controls on certain appliances not functioning, is not a warranty claim. Lights dimming, or LEDs flickering is not a warranty claim. These are normal living off grid, and the only thing better than a Magnum for power quality is Exeltech in my experience. Ray Walters Remote Solar On 5/31/2023 11:37 AM, Chris Sparadeo via RE-wrenches wrote: Hi all, I have a client with a Magnum MS 4024- PAE inverter. There are some serious issues with power output quality and according to the client, another installer had started the RMA process while the inverter was still under warranty, however Sensata has not been responsive and has lost track of the case. They are asking for a new case to be initiated, but the inverter is now out of warranty. Has anyone out there had similar lack luster support issues with Sensata? Best, Chris -- Chris Sparadeo C_802-369-4458 H_802-728-3059 ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org <mailto:RE-wrenches@lists.re-wrenches.org> Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org
Re: [RE-wrenches] Tech Support Issues with Sensata
Magnum has been difficult that last 3 years – we currently multiple inverters that are down needing boards for repair that can’t be obtained. It appears stock of new inverters is just starting to trickle back into suppliers so we hope to see parts soon. It seemed Magnum quality took also took a hit when purchased by Sensata and I think operations were moved to a new location? – we found MMP’s shipped with missing parts etc. The best tech support engineer they had went to Outback, but then was lost tragically to complications from Covid. From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ray Walters via RE-wrenches Sent: Wednesday, May 31, 2023 1:51 PM To: re-wrenches@lists.re-wrenches.org Cc: Ray Walters Subject: Re: [RE-wrenches] Tech Support Issues with Sensata What were the issues? I've not seen a Magnum have power quality troubles, but they are not the "grid" either. My experience is that they are similar or a bit better than Outback, but certainly have measurable THD in the 4 to 5% range. Its almost always finicky loads, and the inverter has always been within its tolerances, so I doubt you have an actual warranty issue. However, I have seen inverter output get strange after lightning damage, which is not covered under warranty either. You need a decent meter that can measure THD, and can capture the peak voltage of the waveform. A good oscilloscope is even better, so you can see the waveform. Stuff like clocks not keeping time, or certain digital controls on certain appliances not functioning, is not a warranty claim. Lights dimming, or LEDs flickering is not a warranty claim. These are normal living off grid, and the only thing better than a Magnum for power quality is Exeltech in my experience. Ray Walters Remote Solar On 5/31/2023 11:37 AM, Chris Sparadeo via RE-wrenches wrote: Hi all, I have a client with a Magnum MS 4024- PAE inverter. There are some serious issues with power output quality and according to the client, another installer had started the RMA process while the inverter was still under warranty, however Sensata has not been responsive and has lost track of the case. They are asking for a new case to be initiated, but the inverter is now out of warranty. Has anyone out there had similar lack luster support issues with Sensata? Best, Chris -- Chris Sparadeo C_802-369-4458 H_802-728-3059 ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org
Re: [RE-wrenches] Tech Support Issues with Sensata
What were the issues? I've not seen a Magnum have power quality troubles, but they are not the "grid" either. My experience is that they are similar or a bit better than Outback, but certainly have measurable THD in the 4 to 5% range. Its almost always finicky loads, and the inverter has always been within its tolerances, so I doubt you have an actual warranty issue. However, I have seen inverter output get strange after lightning damage, which is not covered under warranty either. You need a decent meter that can measure THD, and can capture the peak voltage of the waveform. A good oscilloscope is even better, so you can see the waveform. Stuff like clocks not keeping time, or certain digital controls on certain appliances not functioning, is not a warranty claim. Lights dimming, or LEDs flickering is not a warranty claim. These are normal living off grid, and the only thing better than a Magnum for power quality is Exeltech in my experience. Ray Walters Remote Solar On 5/31/2023 11:37 AM, Chris Sparadeo via RE-wrenches wrote: Hi all, I have a client with a Magnum MS 4024- PAE inverter. There are some serious issues with power output quality and according to the client, another installer had started the RMA process while the inverter was still under warranty, however Sensata has not been responsive and has lost track of the case. They are asking for a new case to be initiated, but the inverter is now out of warranty. Has anyone out there had similar lack luster support issues with Sensata? Best, Chris -- Chris Sparadeo C_802-369-4458 H_802-728-3059 ___ List sponsored by Redwood Alliance Pay optional member dues here:http://re-wrenches.org List Address:RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org