RE: CPVC leak

2012-11-15 Thread Tom Binkley
Are you allowed to fill CPVC pipe-work with compressed air? Check it out.

-Original Message-
From: Jim Davidson [mailto:jdavid...@davidsonassociates.net] 
Sent: 14 November 2012 21:09
To: sprinklerforum@firesprinkler.org
Subject: RE: CPVC leak

Be very careful about introduction of a foreign substance into a CPVC pipe 
system, need to check if the odorant is compatible with CPVC piping. You do not 
want to introduce a substance that could cause environmental stress cracking. 
If you do, you have just brought the system.

Regards

Jim

DAVIDSON ASSOCIATES

Fire Protection Engineering P. O. Box 4010
Code ConsultantsGreenville, DE  19807-0010
Medical Gas Systems Engineering (302) 994-9500
Fax (302) 234-1781

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Matt Grise
Sent: Wednesday, November 14, 2012 2:16 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: CPVC leak

Did the owner who drained it note anything about the leak? Is there any 
evidence of water/glycerin staining?

Matt Grisé PE*, LEED AP, NICET II
Sales Engineer
Alliance Fire Protection
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS  MO 

913.888.0647 ph
913.888.0618 f
913.927.0222 cell
www. AFPsprink.com 


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Steve Johnson
Sent: Wednesday, November 14, 2012 1:09 PM
To: sprinklerforum@firesprinkler.org
Subject: CPVC leak

Need some input:  Working on an existing CPVC system which original owner 
drained glycerin out of the system because of a leak.  We have tried to find 
the leak with 40 psi of air pressure, still unable to find a leak.  Has anyone 
introduced a smell into the system with the air pressure to find such a leak.  
If so, what could we use for the smell?

 

Steve Johnson

Office:801.295.1189

  Fax: 801.295.1193

  Cell: 801.301.3950

 

 www.chpfire.com

   

 
http://www.google.com/search?q=chaparral+fire+protection+ie=utf-8oe=u
tf-8aq=trls=org.mozilla:en-US:officialclient=firefox-a
http://www.facebook.com/pages/Chaparral-Fire-Protection/110753688988876
 

 

-- next part --
An HTML attachment was scrubbed...
URL: 
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121114/1383ddee/attachment.html
-- next part --
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 14568 bytes
Desc: image001.png
URL: 
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121114/1383ddee/attachment.png
-- next part --
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 959 bytes
Desc: image002.jpg
URL: 
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121114/1383ddee/attachment.jpg
-- next part --
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 937 bytes
Desc: image003.jpg
URL: 
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121114/1383ddee/attachment-0001.jpg
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum



___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


Re: flow per sprinkler

2012-11-15 Thread Johnson, Duane (NIH/OD/ORS) [C]
Flow and pressure are related, as you stated below. Most of the time you will 
start with a known flow which is based on your density and sprinkler area. 
However, there are portions of code and/or manufacturer's requirements that 
start off with a required pressure. 

Duane

- Original Message -
From: Jeff Garrison [mailto:jeffgarrison1...@gmail.com]
Sent: Wednesday, November 14, 2012 03:02 PM
To: sprinklerforum@firesprinkler.org sprinklerforum@firesprinkler.org
Subject: Re: flow per sprinkler

Flow depends upon pressure, your calculated numbers are corrrect...


On Wed, Nov 14, 2012 at 2:40 PM, Rubén Miranda Idrovo
seus...@hotmail.comwrote:



 Hi evreybody:
 I¨m new in the sprinklers world so I have a question every sprinkler
 (ESFR, CMDA, CMSA) have a fixed flow value (GPM) no matter the pressure???
 or the flow is up to the pressure value???
 for example an ESFR k 16.8 according to the k formula k=Q/ P^(1/2)
 with 64 PSI flow will be 134.4 GPM
 with 50 PSI flow will be 118.7 GPM
 Is this right???
 -- next part --
 An HTML attachment was scrubbed...
 URL: 
 http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121114/d1c5ed0c/attachment.html
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-- next part --
An HTML attachment was scrubbed...
URL: 
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121114/da227ed4/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


AFSA Storage Webinar

2012-11-15 Thread Bill Brooks
A little AFSA cheerleading today.

Yesterday the AFSA sponsored a webinar on storage applications.  James
Golinveaux from Tyco was the presenter. Two hours in length and worth every
penny of my membership dues. First seminar where I had outstanding
evaluation marks in every category and actually meant it. He had tables and
flow charts and detailed comparisons of NFPA 13 and FM storage rules, along
with videos. He covered the new EC applications, the 6-head designs,
cautions in making sure your open racks don't turn into solid shelving
because of slip ups in flue space allocation, etc.

Just like George Church says, membership is a great idea.  I'm in.

Bill Brooks


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


Re: AFSA Storage Webinar

2012-11-15 Thread Todd - FPDC
Ditto. It also answered the question for a concurrent thread

Sent from my iPhone

On Nov 15, 2012, at 9:10 AM, Bill Brooks bill.bro...@brooksfpe.com wrote:

 A little AFSA cheerleading today.
 
 Yesterday the AFSA sponsored a webinar on storage applications.  James
 Golinveaux from Tyco was the presenter. Two hours in length and worth every
 penny of my membership dues. First seminar where I had outstanding
 evaluation marks in every category and actually meant it. He had tables and
 flow charts and detailed comparisons of NFPA 13 and FM storage rules, along
 with videos. He covered the new EC applications, the 6-head designs,
 cautions in making sure your open racks don't turn into solid shelving
 because of slip ups in flue space allocation, etc.
 
 Just like George Church says, membership is a great idea.  I'm in.
 
 Bill Brooks
 
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


Re: AFSA Storage Webinar

2012-11-15 Thread Ron Greenman
Give me an A! Give me an F! Give me an S! Give me an A! What's THAT
SPELL? AFSA! What's THAT SPELL? AFSA! What's THAT SPELL? AFSA! American
Fire Sprinkler Association! YAY

AFSA. A better valure for your dollar than cable and ESPN.

On Thu, Nov 15, 2012 at 6:58 AM, Todd - FPDC t...@fpdc.com wrote:

 Ditto. It also answered the question for a concurrent thread

 Sent from my iPhone

 On Nov 15, 2012, at 9:10 AM, Bill Brooks bill.bro...@brooksfpe.com
 wrote:

  A little AFSA cheerleading today.
 
  Yesterday the AFSA sponsored a webinar on storage applications.  James
  Golinveaux from Tyco was the presenter. Two hours in length and worth
 every
  penny of my membership dues. First seminar where I had outstanding
  evaluation marks in every category and actually meant it. He had tables
 and
  flow charts and detailed comparisons of NFPA 13 and FM storage rules,
 along
  with videos. He covered the new EC applications, the 6-head designs,
  cautions in making sure your open racks don't turn into solid shelving
  because of slip ups in flue space allocation, etc.
 
  Just like George Church says, membership is a great idea.  I'm in.
 
  Bill Brooks
 
 
  ___
  Sprinklerforum mailing list
  Sprinklerforum@firesprinkler.org
  http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum




-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

rgreen...@bates.ctc.edu

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-- next part --
An HTML attachment was scrubbed...
URL: 
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121115/99d464cf/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


Re: AFSA Storage Webinar

2012-11-15 Thread Richard Lindner
I was fortunate enough to see the same presentation last week at the ASCET
meeting in King of Prussia and even though the AFSA one was a repeat for
me, I still found info that I missed and I also got the slides too!

Richard
-- next part --
An HTML attachment was scrubbed...
URL: 
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121115/5c1c8ffa/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


Re: AFSA Storage Webinar

2012-11-15 Thread Ben Young
Seeing the videos again was also a kicker.  I had everyone in the office
around for the exposed expanded plastics fire.

Benjamin Young



On Thu, Nov 15, 2012 at 11:25 AM, Richard Lindner
rklindner.w...@gmail.comwrote:

 I was fortunate enough to see the same presentation last week at the ASCET
 meeting in King of Prussia and even though the AFSA one was a repeat for
 me, I still found info that I missed and I also got the slides too!

 Richard
 -- next part --
 An HTML attachment was scrubbed...
 URL: 
 http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121115/5c1c8ffa/attachment.html
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-- next part --
An HTML attachment was scrubbed...
URL: 
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121115/a2914051/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


Re: AFSA Storage Webinar

2012-11-15 Thread Todd Williams
The sprinkler fish cheer?

At 11:21 AM 11/15/2012, you wrote:
Give me an A! Give me an F! Give me an S! Give me an A! What's THAT
SPELL? AFSA! What's THAT SPELL? AFSA! What's THAT SPELL? AFSA! American
Fire Sprinkler Association! YAY






Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


Standpipe Calc

2012-11-15 Thread RFletcher
Existing hospital with 5 standpipes. New addition will have two SP's with 
standalone pump and underground supply. The new addition SP is not connected to 
the existing SP system. The addition is only 30k sqft but the entire hospital 
is over 80K sqft. Can the new addition be calc'd for 500  250 or must it be 
500 + 500?

Ron Fletcher
Aero Phoenix

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


Re: Standpipe Calc

2012-11-15 Thread Johnson, Duane (NIH/OD/ORS) [C]
Why aren't they connected? 

- Original Message -
From: rfletc...@aerofire.com [mailto:rfletc...@aerofire.com]
Sent: Thursday, November 15, 2012 05:07 PM
To: sprinklerforum@firesprinkler.org sprinklerforum@firesprinkler.org
Subject: Standpipe Calc

Existing hospital with 5 standpipes. New addition will have two SP's with 
standalone pump and underground supply. The new addition SP is not connected to 
the existing SP system. The addition is only 30k sqft but the entire hospital 
is over 80K sqft. Can the new addition be calc'd for 500  250 or must it be 
500 + 500?

Ron Fletcher
Aero Phoenix

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: New Jersey

2012-11-15 Thread John Drucker
Hi Bruce, Had the pleasure of working with electricians from Seattle doing 
electrical service assessments the other night. Although we had all been 
working since 7am they and the rest of the crew, new jersey, illinois, florida, 
mississipi, massachusetts, ohio and alabama stayed on until 10:30pm restoring 
service to hundreds of residents in the borough of little silver. 

John 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bruce Verhei
Sent: Saturday, November 10, 2012 3:52 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: New Jersey

John
Power crews and their vehicles have come from as far as Seattle City Light and 
California via the 62nd Air Wing and their handy C-17's.
Bv

Sent from my Motorola ATRIX™ 4G on ATT

-Original message-
From: John Drucker jdruc...@redbanknj.org
To: sprinklerforum@firesprinkler.org
Sent: Sat, Nov 10, 2012 08:07:59 GMT+00:00
Subject: Re: New Jersey

Power is back on in most of the state. People are being let back into coastal 
areas including the barrier islands but finding their homes severly damaged or 
destroyed. Tens of thousands displaced. Fema reps working to assist w aid and 
grants. Warm weather is forecast for this weekend which will give everyone a 
break. Red cross and Salvation army are on the ground, financial donations to 
these is appreciated. More utility crews being brought in from southern states 
as well as state police from as far as mississipi. Damage assessments may run 
as high as 50 billion. Lots of rebuilding work and contractors needed. State 
DCA has hired  inspectors to assist local jurisdictions. Fuel is still a 
problem with odd/even rationing in effect. Unfortunately problems have occurred 
, fuel hoarding, storing large quantitys in vehicles and homes, generators 
being hooked directly to pumps in violation of NEC. With power restored tripped 
dry systems are being drained and restored in advance of c
 old weather.   Thanks to all who helped out !   
John Drucker - Mobile Email

- Original Message -
From: sprinklerforum-boun...@firesprinkler.org 
sprinklerforum-boun...@firesprinkler.org
To: sprinklerforum@firesprinkler.org sprinklerforum@firesprinkler.org
Sent: Fri Nov 02 11:14:08 2012
Subject: RE: New Jersey

Thanks John,

Cold weather is forecast this weekend and 1.5 million homes are without power. 
The situation is dire, if anyone has family or friends in the northeast please 
reach out and contact them, help in any way you can. People are running out of 
fuel, only 35% of the gas stations are open and lines miles long for cars and 
hundreds of feet long for generators. Anyone you can help is important.

John Drucker
New Jersey

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of 321
Sent: Thursday, November 01, 2012 6:21 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: New Jersey

John,

We here in South Florida know all too well what you are experiencing. Our 
hearts and prayers are with you all. Know that it will get better and that the 
Calvary is coming.
 John W. Farabee, Vice President


Bass United Fire and Security




561-707-5150





From: John Drucker jdruc...@redbanknj.org
To: sprinklerforum@firesprinkler.org
Sent: Thu, November 1, 2012 4:08:40 AM
Subject: New Jersey

Thursday widespread power still out . Major roads cleared of debris and trees. 
Fuel is precious commodity, lines for gas were two miles long on garden state 
parkway. Food was starting to be a problem but some stores reopened on 
generators brought in or partial power restored.  Our beautiful coastline and 
historic locations are mere memories. Sadly people have died as a result. Gov 
and Pres toured yesterday, send money. Flooding has destroyed or damaged 
buildings and electrical equipment. On the tech side lots of tripped dry valves 
and unpowered fire pumps. All in all were lucky. 

John Drucker - Mobile Email

- Original Message -
From: sprinklerforum-boun...@firesprinkler.org
sprinklerforum-boun...@firesprinkler.org
To: sprinklerforum@firesprinkler.org sprinklerforum@firesprinkler.org
Sent: Wed Oct 31 15:47:20 2012
Subject: Re: Sodium Silicate

Several reasons

Sodium silicate is a white powder that is readily soluble in water, producing 
an alkaline http://en.wikipedia.org/wiki/Alkaline solution. It is one of a 
number of related compounds which include sodium 
orthosilicatehttp://en.wikipedia.org/wiki/Orthosilicate,
Na4SiO4, sodium
pyrosilicatehttp://en.wikipedia.org/w/index.php?title=Pyrosilicateaction=e
ditredlink=1,

Na6Si2O7, and others. All are glassy http://en.wikipedia.org/wiki/Glassy,
colourless and dissolve in water.

Sodium silicate is stable in neutral http://en.wikipedia.org/wiki/PH and 
alkaline http://en.wikipedia.org/wiki/Alkaline
solutionshttp://en.wikipedia.org/wiki/Solution.
In acidic 

RE: Standpipe Calc

2012-11-15 Thread Brad Casterline
If not separate fire areas, it looks like 500+500 (instead of +250). But
then what about the existing building; Wouldn't you have to prove 500+500
for that arrangement now also? 

-Original Message-
From: rfletc...@aerofire.com [mailto:rfletc...@aerofire.com] 
Sent: Thursday, November 15, 2012 4:07 PM
To: sprinklerforum@firesprinkler.org
Subject: Standpipe Calc

Existing hospital with 5 standpipes. New addition will have two SP's with
standalone pump and underground supply. The new addition SP is not connected
to the existing SP system. The addition is only 30k sqft but the entire
hospital is over 80K sqft. Can the new addition be calc'd for 500  250 or
must it be 500 + 500?

Ron Fletcher
Aero Phoenix

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: New Jersey

2012-11-15 Thread Bruce Verhei
/sprinklerforum
-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20121101/cb9c15f4/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity to 
which it is addressed and may contain information that is privileged and 
confidential, nor is it, unless specifically stated, intended to be relied upon 
by any person or persons other than the individual or entity named above and no 
warranties or representations are made or intended to persons or entities not 
named above.  If the reader is not the intended recipient, you are hereby 
notified that any dissemination, distribution or copying of this communication 
is strictly prohibited.  If you have received this communication in error, 
please notify us immediately by telephone, return this message to the address 
above and delete all copies.  Thank you.

-- next part --
An HTML attachment was scrubbed...
URL: 
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121110/9437b836/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
-- next part --
An HTML attachment was scrubbed...
URL: 
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121110/0f323859/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
-- next part --
An HTML attachment was scrubbed...
URL: 
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121115/ef969dc6/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: New Jersey

2012-11-15 Thread Bruce Verhei
: 
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20121101/088e2c26/attachment.html

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20121101/cb9c15f4/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity to 
which it is addressed and may contain information that is privileged and 
confidential, nor is it, unless specifically stated, intended to be relied upon 
by any person or persons other than the individual or entity named above and no 
warranties or representations are made or intended to persons or entities not 
named above.  If the reader is not the intended recipient, you are hereby 
notified that any dissemination, distribution or copying of this communication 
is strictly prohibited.  If you have received this communication in error, 
please notify us immediately by telephone, return this message to the address 
above and delete all copies.  Thank you.

-- next part --
An HTML attachment was scrubbed...
URL: 
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121110/9437b836/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
-- next part --
An HTML attachment was scrubbed...
URL: 
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121110/0f323859/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
-- next part --
An HTML attachment was scrubbed...
URL: 
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121115/ef969dc6/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
-- next part --
An HTML attachment was scrubbed...
URL: 
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20121115/0b66d1e9/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


ISO

2012-11-15 Thread Tom Duross
Are there any forum members here ISO certified?

TD

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


water storage tank: 300,000 gallon size: failure

2012-11-15 Thread å . . . . . . .
Does anyone know and care to share, whether the ~ 300,000 gallon tank that
failed about the 7th of April in Lake Placid, NY in 2011 was a welded, or a
bolted tank?  I am doing no litigation work, nor I am being paid by any
party relative to this incident.

http://www.wtsp.com/news/topstories/article/185855/250/Massive-water-tank-bursts-kills-two-following-tsunami-like-wave

Scot Deal
Excelsior Fire Engineering