Re: Another anti-freeze question or teo

2014-09-19 Thread Tom Wellen
I spoke with UL last week regarding another issue.

The testing standard for UL is complete and ready for companies to get it and 
develop their product.  A UL rep told me there was only one company that had an 
interest in the testing standard.

I believe it's going to be some time before listed anti-freeze solutions are 
available.


Tom Wellen - AFSA




On Sep 18, 2014, at 10:15 PM, Forest Wilson forestwilso...@gmail.com wrote:

 I think that UL would be the listing lab.
 
 On Thu, Sep 18, 2014 at 2:59 PM, Todd - Work t...@fpdc.com wrote:
 
 Is there any progress on developing a listed anti-freeze solution? Who
 would be the listing agency?
 
 Todd G Williams, PE
 Fire Protection Design/Consulting
 Stonington, CT
 www.fpdc.com
 860-535-2080 (ofc)
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


13D multiple tank system

2014-09-19 Thread Todd - Work
When using multiple tanks for a 13D (or 13R) system, is there any special 
arrangement for the suction piping?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Cloud Ceiling Article in Sprinkler Age

2014-09-19 Thread Brad Casterline
Good Article by Tom Wellen in current Sprinkler Age.

Tom did the original modeling in 2000, and came up with max gap width 8 (to
not need heads above).

The recent tests and modeling confirmed that, but showed it was reasonable
to extend it to allow 1 gap width per foot of ceiling height, so at 12'-0
ceiling height the gap between clouds could be 12 and not need heads above.

There are other rules that apply. 

I found it disturbing that the TC decided to go conservative after all
that and say 8 max gap width PERIOD. That really gives the Architects a lot
of leeway in the design phase... (frigging) NOT!

Design by Committee. That is something to NITMAM if I ever did see one, and
I will if I get a chance. 

 

Is there somewhere I can see whom voted for what on this issue, a link or
something? I've been stewing over this for a few days now, and it doesn't
help to 'talk it out'.

Brad Casterline, NICET IV

Fire Protection Division

 

FSC, Inc.

P: 913-722-3473

bcasterl...@fsc-inc.com

www.fsc-inc.com

 

Engineering Solutions for the Built Environment

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Cloud Ceiling Article in Sprinkler Age (Get Involved)

2014-09-19 Thread Bill Brooks
Brad, you need to 1) start submitting proposals and comments during the NFPA
Standards cycle, and/or 2) apply for a seat on one of the Technical
Committees.  It is an awakening process to see the way a typical committee
operates.  In my experience there is a handful of opinion leaders on each
committee who drive the process forward.  It's best to figure out who these
individuals are and attempt to understand their motivations.  The process is
set up to make it difficult to overturn committee actions.  This is good or
bad depending on your point of view.  All this said, it is actually possible
to affect a change if you are persistent.

The NFPA website has all the proposals and comments for each Standard, along
with the committee action.

Bill Brooks

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Brad Casterline
Sent: Friday, September 19, 2014 9:39 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Cloud Ceiling Article in Sprinkler Age

Good Article by Tom Wellen in current Sprinkler Age.

Tom did the original modeling in 2000, and came up with max gap width 8 (to
not need heads above).

The recent tests and modeling confirmed that, but showed it was reasonable
to extend it to allow 1 gap width per foot of ceiling height, so at 12'-0
ceiling height the gap between clouds could be 12 and not need heads above.

There are other rules that apply. 

I found it disturbing that the TC decided to go conservative after all
that and say 8 max gap width PERIOD. That really gives the Architects a lot
of leeway in the design phase... (frigging) NOT!

Design by Committee. That is something to NITMAM if I ever did see one, and
I will if I get a chance. 

 

Is there somewhere I can see whom voted for what on this issue, a link or
something? I've been stewing over this for a few days now, and it doesn't
help to 'talk it out'.

Brad Casterline, NICET IV

Fire Protection Division

 

FSC, Inc.

P: 913-722-3473

bcasterl...@fsc-inc.com

www.fsc-inc.com

 

Engineering Solutions for the Built Environment

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Cloud Ceiling Article in Sprinkler Age (Get Involved)

2014-09-19 Thread Brad Casterline
Thanks Bill.
 
I would like to sit in on TC meetings, in the corner perhaps, napping on and
off, and I would feel qualified enough to be the person who went out for
coffee and sandwiches in the wee hours of the debate. It takes me too long
to figure things out though to catch anything early in the process.
This issue is different-- 14 years ago Tom's results were not accepted
because there was not enough data, tests, calculations, etc., to back them
up. Now his results ARE accepted-- why? Is it because they are backed-up
now? No. It is because 1 max gap width per foot of ceiling height has been
shown to be conservative in itself, so the only hammer SOMBODY had left was
to 'virtually limit the ceiling height'. Ridiculous.

Thanks again Mr. Brooks,

Brad

-Original Message-
From: Bill Brooks [mailto:bill.bro...@brooksfpe.com] 
Sent: Friday, September 19, 2014 9:10 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Cloud Ceiling Article in Sprinkler Age (Get Involved)

Brad, you need to 1) start submitting proposals and comments during the NFPA
Standards cycle, and/or 2) apply for a seat on one of the Technical
Committees.  It is an awakening process to see the way a typical committee
operates.  In my experience there is a handful of opinion leaders on each
committee who drive the process forward.  It's best to figure out who these
individuals are and attempt to understand their motivations.  The process is
set up to make it difficult to overturn committee actions.  This is good or
bad depending on your point of view.  All this said, it is actually possible
to affect a change if you are persistent.

The NFPA website has all the proposals and comments for each Standard, along
with the committee action.

Bill Brooks

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Brad Casterline
Sent: Friday, September 19, 2014 9:39 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Cloud Ceiling Article in Sprinkler Age

Good Article by Tom Wellen in current Sprinkler Age.

Tom did the original modeling in 2000, and came up with max gap width 8 (to
not need heads above).

The recent tests and modeling confirmed that, but showed it was reasonable
to extend it to allow 1 gap width per foot of ceiling height, so at 12'-0
ceiling height the gap between clouds could be 12 and not need heads above.

There are other rules that apply. 

I found it disturbing that the TC decided to go conservative after all
that and say 8 max gap width PERIOD. That really gives the Architects a lot
of leeway in the design phase... (frigging) NOT!

Design by Committee. That is something to NITMAM if I ever did see one, and
I will if I get a chance. 

 

Is there somewhere I can see whom voted for what on this issue, a link or
something? I've been stewing over this for a few days now, and it doesn't
help to 'talk it out'.

Brad Casterline, NICET IV

Fire Protection Division

 

FSC, Inc.

P: 913-722-3473

bcasterl...@fsc-inc.com

www.fsc-inc.com

 

Engineering Solutions for the Built Environment

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: 13D multiple tank system

2014-09-19 Thread Ed Kramer
I'm probably stating the obvious:  connect tanks at the bottom (parallel or
series), each tank to be vented at the top.

Ed Kramer
Lawrence, KS

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Todd - Work
Sent: Friday, September 19, 2014 7:56 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: 13D multiple tank system

When using multiple tanks for a 13D (or 13R) system, is there any special
arrangement for the suction piping?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Sprinkler statistics

2014-09-19 Thread å . . . . . . .
Franz:

The pp. 8 table you graciously referred,  indicates these fires were
extinguished not controlled.

Do the Dutch parse these words per NFPA definitions, or could this
difference be a result of translation?  In the big scheme, the difference
is trifling when comparing losses from sprinklered vs non-sprinklered
fires.  I am simply curious on your take on this angle.

Many firefighters will confirm, at least for commercial and residential
fires, one could virtually extinguish with a few buckets of water, any
remaining fire not extinguished by a well designed, installed and
maintained sprinkler system.

Scot Deal
Excelsior Risk/Fire Engineering

On Thu, Sep 18, 2014 at 1:28 AM, Frans Stoop f.st...@fo.nl wrote:

 This is what I found on the Dutch CIBV site:

 http://cibv.nl/wp-content/uploads/2014/04/Sprinkler_
 Statistics_2011-2012a.pdf

 The table is on page 8.
 The last column is the most significant, but the figures are about fires
 controlled by sprinklers in the Netherlands only.
 Apparently we have 10 million sprinklers installed.

 Met vriendelijke groet / Best regards,

 Frans Stoop
 ​

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


No Longitudinal Bracing

2014-09-19 Thread Owen Evans
So I enter a new underground parking area and look up at the fire sprinkler 
piping hanging from a concrete deck. As I look I notice there is no bracing 
other than a 4X at the top of the riser. From the top of the riser it travels 
out about 4' feet and makes a 90 degree turn and travels about 15'. At that 
point it makes a 90 degree turn at a T and makes it's longest run of 
approximately 70'. From there it makes a 90 degree turn for a run of 
approximately 40'. All the hangers are less than 6 so that explains the no 
lateral bracing. My question is, what about longitudinal bracing? I looked in 
13 chapter 9 and it appears that longitudinal bracing would be required. Am I 
missing something? I work exclusively with 13D systems, I don't do commercial 
but I am interested in this situation.


Owen Evans
First-In Residential Design
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: No Longitudinal Bracing

2014-09-19 Thread Steve Leyton
There isn't an exception for longitudinal bracing.  The exception for
lateral bracing is where the distance from the point of anchorage
(concrete deck, in this case) to the top of pipe is 6 or less.   The
standard used to say where rods were 6 or less, but now it's the
distance from the anchor to top of pipe, which means rods measurably
less than 6.   The scenario you describe requires at least longitudinal
bracing.

SML

 




-Original Message-
From: Sprinklerforum
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
Owen Evans
Sent: Friday, September 19, 2014 10:35 AM
To: sprinklerfo...@firesprinkler.org
Subject: No Longitudinal Bracing

So I enter a new underground parking area and look up at the fire
sprinkler piping hanging from a concrete deck. As I look I notice there
is no bracing other than a 4X at the top of the riser. From the top of
the riser it travels out about 4' feet and makes a 90 degree turn and
travels about 15'. At that point it makes a 90 degree turn at a T and
makes it's longest run of approximately 70'. From there it makes a 90
degree turn for a run of approximately 40'. All the hangers are less
than 6 so that explains the no lateral bracing. My question is, what
about longitudinal bracing? I looked in 13 chapter 9 and it appears that
longitudinal bracing would be required. Am I missing something? I work
exclusively with 13D systems, I don't do commercial but I am interested
in this situation.


Owen Evans
First-In Residential Design
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: No Longitudinal Bracing

2014-09-19 Thread RFletcher
If it is in a seismic zone. We do 4 ways at the top of risers only even though 
Phoenix is not in a seismic zone. Maybe that is what he saw.
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Steve Leyton
Sent: Friday, September 19, 2014 10:43 AM
To: sprinklerforum@lists.firesprinkler.org; sprinklerfo...@firesprinkler.org
Subject: RE: No Longitudinal Bracing

There isn't an exception for longitudinal bracing.  The exception for lateral 
bracing is where the distance from the point of anchorage
(concrete deck, in this case) to the top of pipe is 6 or less.   The
standard used to say where rods were 6 or less, but now it's the distance from 
the anchor to top of pipe, which means rods measurably
less than 6.   The scenario you describe requires at least longitudinal
bracing.

SML

 




-Original Message-
From: Sprinklerforum
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Owen Evans
Sent: Friday, September 19, 2014 10:35 AM
To: sprinklerfo...@firesprinkler.org
Subject: No Longitudinal Bracing

So I enter a new underground parking area and look up at the fire sprinkler 
piping hanging from a concrete deck. As I look I notice there is no bracing 
other than a 4X at the top of the riser. From the top of the riser it travels 
out about 4' feet and makes a 90 degree turn and travels about 15'. At that 
point it makes a 90 degree turn at a T and makes it's longest run of 
approximately 70'. From there it makes a 90 degree turn for a run of 
approximately 40'. All the hangers are less than 6 so that explains the no 
lateral bracing. My question is, what about longitudinal bracing? I looked in 
13 chapter 9 and it appears that longitudinal bracing would be required. Am I 
missing something? I work exclusively with 13D systems, I don't do commercial 
but I am interested in this situation.


Owen Evans
First-In Residential Design
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Pipe Schedule velocity limitations

2014-09-19 Thread å . . . . . . .
*​ and I will question everything else the specifier has to say!*

It is realized this statement was made tongue-in-cheek.
Point is though,  instead of judging the person, judge the decision or
action.

To question EVERYthing a person has to say after they make a mistake,
is perhaps on par with expecting a politician to continue malfeasance after
being caught once, with their hand in the cookie jar.

Velocity limitations are still used in oil  gas specifications, today.  I
have yet to hear of a good reason for them.   Some claim water hammer,
which is a matter with 24-inch diameters, but soft-start pumps can jump
that hurdle, and most of the lines are looped which dampens other concerns
coming and going.

We don't question the motivations of oil and gas corporations, just because
they still use velocity limitations.

​Scot Deal
Excelsior Risk/Fire Engineering​
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Pipe Schedule velocity limitations

2014-09-19 Thread Brad Casterline

So the next time I see a spec that limits the velocity I'll know that is
from the old days- when the pipe size was the same whether the water supply
was very poor or very good ;), and I will question everything else the
specifier has to 
say!

Brad Casterline
AFSA Designer Member
***


How you doing Scott!
yes tongue tongue-in-cheek because I question everything everybody has to
say. If they are quoting code I question the code :)
I have no idea whether they will go up or down when they die however.
(i hope up)

Brad

-Original Message-
From: å...  [mailto:eurekaig...@gmail.com] 
Sent: Friday, September 19, 2014 12:59 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Pipe Schedule  velocity limitations

*? and I will question everything else the specifier has to say!*

It is realized this statement was made tongue-in-cheek.
Point is though,  instead of judging the person, judge the decision or
action.

To question EVERYthing a person has to say after they make a mistake,
is perhaps on par with expecting a politician to continue malfeasance after
being caught once, with their hand in the cookie jar.

Velocity limitations are still used in oil  gas specifications, today.  I
have yet to hear of a good reason for them.   Some claim water hammer,
which is a matter with 24-inch diameters, but soft-start pumps can jump
that hurdle, and most of the lines are looped which dampens other concerns
coming and going.

We don't question the motivations of oil and gas corporations, just because
they still use velocity limitations.

?Scot Deal
Excelsior Risk/Fire Engineering?
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Sprinklers on 3 Pipe

2014-09-19 Thread Jay Stough
I have a customer that is moving into a warehouse that was renovated in
2013, using NFPA 13 (2007).  They have Victaulic 3403 upright sprinklers
directly on 3 pipe.  Unless I am missing something, I am pretty sure this
sprinkler is listed as a standard upright sprinkler and cannot be installed
this way.  I have checked the spec sheet and appears to be a large orifice
standard spray sprinkler.  Am I correct or am I missing a listing for this
sprinkler?


-- 
*Jay Stough*
NICET IV LAYOUT
NICET III ITM
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Pipe Schedule velocity limitations

2014-09-19 Thread Mark A. Sornsin, P.E.
I have no way of knowing for sure, but I suspect most engineers calling for 
velocity restrictions are doing it because it was what they were taught and/or 
it was in their company's specs. WHY it is in the specs is most likely due to 
plumbing standards being intermingled with sprinkler standards, which makes 
some sense when you consider all mechanical was lumped together in Div. 15 
(until CSI changed their format and put sprinklers into Div. 13, then Div. 21). 
 The plumbing standards want lower velocities to reduce noise as well as to 
eliminate pitting from high velocity flow. We all know these are bogus reasons 
for sprinkler systems that almost never flow, and have an even lower chance of 
flowing at the design flow rates.

Has anyone else heard different reasons (regardless validity) for velocity 
restrictions?

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Brad Casterline
Sent: Friday, September 19, 2014 1:24 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Pipe Schedule  velocity limitations


So the next time I see a spec that limits the velocity I'll know that is from 
the old days- when the pipe size was the same whether the water supply was very 
poor or very good ;), and I will question everything else the specifier has to 
say!

Brad Casterline
AFSA Designer Member
***



__
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
__
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Sprinklers on 3 Pipe

2014-09-19 Thread Parsley Consulting
I'm not sure Jay.  The tech sheet I looked at just now seems to suggest 
that in either the upright or pendent V3403 are listed for storage, when 
using density/area.  I looked at Victaulic sheet 40.20.


Did you come across something else?
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*Phone 760-745-6181*
Visit our website http://www.parsleyconsulting.com/ ***
On 9/19/2014 11:36 AM, Jay Stough wrote:

I have a customer that is moving into a warehouse that was renovated in
2013, using NFPA 13 (2007).  They have Victaulic 3403 upright sprinklers
directly on 3 pipe.  Unless I am missing something, I am pretty sure this
sprinkler is listed as a standard upright sprinkler and cannot be installed
this way.  I have checked the spec sheet and appears to be a large orifice
standard spray sprinkler.  Am I correct or am I missing a listing for this
sprinkler?




___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Sprinklers on 3 Pipe

2014-09-19 Thread Cliff Whitfield
Ken,

I assumed Jay was talking about having 3 lines without sprigs to the
sprinklers.  I haven’t been where I could confirm in the book but I believe
if this is what he's talking about, the heads would be required to be on
sprigs.

Cliff Whitfield, SET
President
Fire Design, Inc.
Ph: 719-488-3479
 
 

cl...@fire-design.com
www.fire-design.com

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Parsley Consulting
Sent: Friday, September 19, 2014 1:47 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Sprinklers on 3 Pipe

I'm not sure Jay.  The tech sheet I looked at just now seems to suggest 
that in either the upright or pendent V3403 are listed for storage, when 
using density/area.  I looked at Victaulic sheet 40.20.

Did you come across something else?
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*Phone 760-745-6181*
Visit our website http://www.parsleyconsulting.com/ ***
On 9/19/2014 11:36 AM, Jay Stough wrote:
 I have a customer that is moving into a warehouse that was renovated in
 2013, using NFPA 13 (2007).  They have Victaulic 3403 upright sprinklers
 directly on 3 pipe.  Unless I am missing something, I am pretty sure this
 sprinkler is listed as a standard upright sprinkler and cannot be
installed
 this way.  I have checked the spec sheet and appears to be a large orifice
 standard spray sprinkler.  Am I correct or am I missing a listing for this
 sprinkler?



___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Sprinklers on 3 Pipe

2014-09-19 Thread Parsley Consulting

Cliff,
I thought about that, however the only place I could find language 
like that in the '07 was in the section on Large Drop sprinklers, which 
does not apply to that model. Or maybe it does, it's just that I've been 
stuck on the '13 edition for so long I'm a bit confused going 
backwards.  Could the V3404 be regarded as a CMSA/Large Drop?  The large 
drop tables I'm looking at in my '07 edition show the CMSA as having 
specific pressure requirements, while the V3404 clearly notes it can be 
used for storage in an area/density method.

Lots to think about.
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*Phone 760-745-6181*
Visit our website http://www.parsleyconsulting.com/ ***
On 9/19/2014 1:02 PM, Cliff Whitfield wrote:

Ken,

I assumed Jay was talking about having 3 lines without sprigs to the
sprinklers.  I haven’t been where I could confirm in the book but I believe
if this is what he's talking about, the heads would be required to be on
sprigs.

Cliff Whitfield, SET
President
Fire Design, Inc.
Ph: 719-488-3479
  
  


cl...@fire-design.com
www.fire-design.com

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Parsley Consulting
Sent: Friday, September 19, 2014 1:47 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Sprinklers on 3 Pipe

I'm not sure Jay.  The tech sheet I looked at just now seems to suggest
that in either the upright or pendent V3403 are listed for storage, when
using density/area.  I looked at Victaulic sheet 40.20.

Did you come across something else?
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*Phone 760-745-6181*
Visit our website http://www.parsleyconsulting.com/ ***
On 9/19/2014 11:36 AM, Jay Stough wrote:

I have a customer that is moving into a warehouse that was renovated in
2013, using NFPA 13 (2007).  They have Victaulic 3403 upright sprinklers
directly on 3 pipe.  Unless I am missing something, I am pretty sure this
sprinkler is listed as a standard upright sprinkler and cannot be

installed

this way.  I have checked the spec sheet and appears to be a large orifice
standard spray sprinkler.  Am I correct or am I missing a listing for this
sprinkler?



___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org




___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Sprinklers on 3 Pipe

2014-09-19 Thread Cliff Whitfield
This was bugging me so I had to stop and look it up.

NFPA 13 - 2010

8.6.5.2.1.8  The requirements of 8.6.5.2.1.3 shall not apply to sprinkler
system piping less than 3 in. in diameter.

The commentary goes on to say that sprigs or riser nipples (or offsetting
the heads) are required on 3 and larger pipe.  This is for SSU heads.  Not
only Large Drop.

Cliff Whitfield, SET
President
Fire Design, Inc.
Ph: 719-488-3479
 
 

cl...@fire-design.com
www.fire-design.com


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Parsley Consulting
Sent: Friday, September 19, 2014 2:18 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Sprinklers on 3 Pipe

Cliff,
 I thought about that, however the only place I could find language like
that in the '07 was in the section on Large Drop sprinklers, which does not
apply to that model. Or maybe it does, it's just that I've been stuck on the
'13 edition for so long I'm a bit confused going backwards.  Could the V3404
be regarded as a CMSA/Large Drop?  The large drop tables I'm looking at in
my '07 edition show the CMSA as having specific pressure requirements, while
the V3404 clearly notes it can be used for storage in an area/density
method.
 Lots to think about.
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*Phone 760-745-6181*
Visit our website http://www.parsleyconsulting.com/ *** On 9/19/2014 1:02
PM, Cliff Whitfield wrote:
 Ken,

 I assumed Jay was talking about having 3 lines without sprigs to the 
 sprinklers.  I haven’t been where I could confirm in the book but I 
 believe if this is what he's talking about, the heads would be 
 required to be on sprigs.

 Cliff Whitfield, SET
 President
 Fire Design, Inc.
 Ph: 719-488-3479
   
   

 cl...@fire-design.com
 www.fire-design.com

 -Original Message-
 From: Sprinklerforum 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
 On Behalf Of Parsley Consulting
 Sent: Friday, September 19, 2014 1:47 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Sprinklers on 3 Pipe

 I'm not sure Jay.  The tech sheet I looked at just now seems to 
 suggest that in either the upright or pendent V3403 are listed for 
 storage, when using density/area.  I looked at Victaulic sheet 40.20.

 Did you come across something else?
 *Ken Wagoner, SET
 *Parsley Consulting***
 *350 West 9th Avenue, Suite 206
 *Escondido, California 92025
 *Phone 760-745-6181*
 Visit our website http://www.parsleyconsulting.com/ *** On 9/19/2014 
 11:36 AM, Jay Stough wrote:
 I have a customer that is moving into a warehouse that was renovated 
 in 2013, using NFPA 13 (2007).  They have Victaulic 3403 upright 
 sprinklers directly on 3 pipe.  Unless I am missing something, I am 
 pretty sure this sprinkler is listed as a standard upright sprinkler 
 and cannot be
 installed
 this way.  I have checked the spec sheet and appears to be a large 
 orifice standard spray sprinkler.  Am I correct or am I missing a 
 listing for this sprinkler?


 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org

 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org



___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Sprinklers on 3 Pipe

2014-09-19 Thread Pete Schwab
Cliff
I recall we changed this in the 2013 edition. I do not have in front of me but 
check that edition as well.
Pete

Wayne Automatic Fire Sprinklers Inc.
222 Capitol Court
Ocoee, FL 34761

Mobile: (407) 468-8248
Direct: (407) 877-5570
Fax: (407) 656-8026

www.waynefire.com



We’re hiring great people at all of our locations!  Please check out our 
website for the details!


From: Sprinklerforum [sprinklerforum-boun...@lists.firesprinkler.org] on behalf 
of Cliff Whitfield [cl...@fire-design.com]
Sent: Friday, September 19, 2014 4:32 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Sprinklers on 3 Pipe

This was bugging me so I had to stop and look it up.

NFPA 13 - 2010

8.6.5.2.1.8  The requirements of 8.6.5.2.1.3 shall not apply to sprinkler
system piping less than 3 in. in diameter.

The commentary goes on to say that sprigs or riser nipples (or offsetting
the heads) are required on 3 and larger pipe.  This is for SSU heads.  Not
only Large Drop.

Cliff Whitfield, SET
President
Fire Design, Inc.
Ph: 719-488-3479



cl...@fire-design.com
www.fire-design.com


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Parsley Consulting
Sent: Friday, September 19, 2014 2:18 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Sprinklers on 3 Pipe

Cliff,
 I thought about that, however the only place I could find language like
that in the '07 was in the section on Large Drop sprinklers, which does not
apply to that model. Or maybe it does, it's just that I've been stuck on the
'13 edition for so long I'm a bit confused going backwards.  Could the V3404
be regarded as a CMSA/Large Drop?  The large drop tables I'm looking at in
my '07 edition show the CMSA as having specific pressure requirements, while
the V3404 clearly notes it can be used for storage in an area/density
method.
 Lots to think about.
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*Phone 760-745-6181*
Visit our website http://www.parsleyconsulting.com/ *** On 9/19/2014 1:02
PM, Cliff Whitfield wrote:
 Ken,

 I assumed Jay was talking about having 3 lines without sprigs to the
 sprinklers.  I haven’t been where I could confirm in the book but I
 believe if this is what he's talking about, the heads would be
 required to be on sprigs.

 Cliff Whitfield, SET
 President
 Fire Design, Inc.
 Ph: 719-488-3479



 cl...@fire-design.com
 www.fire-design.com

 -Original Message-
 From: Sprinklerforum
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
 On Behalf Of Parsley Consulting
 Sent: Friday, September 19, 2014 1:47 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Sprinklers on 3 Pipe

 I'm not sure Jay.  The tech sheet I looked at just now seems to
 suggest that in either the upright or pendent V3403 are listed for
 storage, when using density/area.  I looked at Victaulic sheet 40.20.

 Did you come across something else?
 *Ken Wagoner, SET
 *Parsley Consulting***
 *350 West 9th Avenue, Suite 206
 *Escondido, California 92025
 *Phone 760-745-6181*
 Visit our website http://www.parsleyconsulting.com/ *** On 9/19/2014
 11:36 AM, Jay Stough wrote:
 I have a customer that is moving into a warehouse that was renovated
 in 2013, using NFPA 13 (2007).  They have Victaulic 3403 upright
 sprinklers directly on 3 pipe.  Unless I am missing something, I am
 pretty sure this sprinkler is listed as a standard upright sprinkler
 and cannot be
 installed
 this way.  I have checked the spec sheet and appears to be a large
 orifice standard spray sprinkler.  Am I correct or am I missing a
 listing for this sprinkler?


 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org

 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org



___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Sprinklers on 3 Pipe

2014-09-19 Thread Cliff Whitfield
Pete,

I did check it there before I posted.  It reads the same.  Maybe you guys
are changing it in the next edition?

Cliff Whitfield, SET
President
Fire Design, Inc.
Ph: 719-488-3479
 
 

cl...@fire-design.com
www.fire-design.com


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Pete Schwab
Sent: Friday, September 19, 2014 2:35 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Sprinklers on 3 Pipe

Cliff
I recall we changed this in the 2013 edition. I do not have in front of me
but check that edition as well.
Pete

Wayne Automatic Fire Sprinklers Inc.
222 Capitol Court
Ocoee, FL 34761

Mobile: (407) 468-8248
Direct: (407) 877-5570
Fax: (407) 656-8026

www.waynefire.com



We’re hiring great people at all of our locations!  Please check out our
website for the details!


From: Sprinklerforum [sprinklerforum-boun...@lists.firesprinkler.org] on
behalf of Cliff Whitfield [cl...@fire-design.com]
Sent: Friday, September 19, 2014 4:32 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Sprinklers on 3 Pipe

This was bugging me so I had to stop and look it up.

NFPA 13 - 2010

8.6.5.2.1.8  The requirements of 8.6.5.2.1.3 shall not apply to sprinkler
system piping less than 3 in. in diameter.

The commentary goes on to say that sprigs or riser nipples (or offsetting
the heads) are required on 3 and larger pipe.  This is for SSU heads.  Not
only Large Drop.

Cliff Whitfield, SET
President
Fire Design, Inc.
Ph: 719-488-3479



cl...@fire-design.com
www.fire-design.com


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Parsley Consulting
Sent: Friday, September 19, 2014 2:18 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Sprinklers on 3 Pipe

Cliff,
 I thought about that, however the only place I could find language like
that in the '07 was in the section on Large Drop sprinklers, which does not
apply to that model. Or maybe it does, it's just that I've been stuck on the
'13 edition for so long I'm a bit confused going backwards.  Could the V3404
be regarded as a CMSA/Large Drop?  The large drop tables I'm looking at in
my '07 edition show the CMSA as having specific pressure requirements, while
the V3404 clearly notes it can be used for storage in an area/density
method.
 Lots to think about.
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*Phone 760-745-6181*
Visit our website http://www.parsleyconsulting.com/ *** On 9/19/2014 1:02
PM, Cliff Whitfield wrote:
 Ken,

 I assumed Jay was talking about having 3 lines without sprigs to the 
 sprinklers.  I haven’t been where I could confirm in the book but I 
 believe if this is what he's talking about, the heads would be 
 required to be on sprigs.

 Cliff Whitfield, SET
 President
 Fire Design, Inc.
 Ph: 719-488-3479



 cl...@fire-design.com
 www.fire-design.com

 -Original Message-
 From: Sprinklerforum
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
 On Behalf Of Parsley Consulting
 Sent: Friday, September 19, 2014 1:47 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Sprinklers on 3 Pipe

 I'm not sure Jay.  The tech sheet I looked at just now seems to 
 suggest that in either the upright or pendent V3403 are listed for 
 storage, when using density/area.  I looked at Victaulic sheet 40.20.

 Did you come across something else?
 *Ken Wagoner, SET
 *Parsley Consulting***
 *350 West 9th Avenue, Suite 206
 *Escondido, California 92025
 *Phone 760-745-6181*
 Visit our website http://www.parsleyconsulting.com/ *** On 9/19/2014
 11:36 AM, Jay Stough wrote:
 I have a customer that is moving into a warehouse that was renovated 
 in 2013, using NFPA 13 (2007).  They have Victaulic 3403 upright 
 sprinklers directly on 3 pipe.  Unless I am missing something, I am 
 pretty sure this sprinkler is listed as a standard upright sprinkler 
 and cannot be
 installed
 this way.  I have checked the spec sheet and appears to be a large 
 orifice standard spray sprinkler.  Am I correct or am I missing a 
 listing for this sprinkler?


 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org

 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org



___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org

Re: Sprinkler statistics

2014-09-19 Thread John Powell
To Russell and others.
I do have a copy of Marryatt's later book and the tabulated results 
corresponding to Russell's are :- 1 head 64.55 %
2. 15.86
3.  6.13
4.  3.21
5.  2.09

This is up to 1986.
It is a very long table recording fire up to 113 heads 
Fires controlled   99.46 % Australia and New Zealand statistics

John Powell NZ

Sent from my iPad

 On 19/09/2014, at 1:19 pm, Frans Stoop f.st...@fo.nl wrote:
 
 Russell,
 
 Thanks!
 That's an interesting source of figures indeed.
 
 Met vriendelijke groet / Best regards,
 
 Frans Stoop
 TOS architecture  fire protection
 Netherlands f.st...@tosfire.com
 Tel. +31-24-324 0112
 
 
 At 15:35 18-9-2014 +1200, you wrote:
 When I joined Wormald in New Zealand 50 years ago they used this type of
 table in the promotion of Fire Sprinkler systems.
 The figures came from the records that Wormald kept on all sprinkler fires
 in Australia and New Zealand. I also think that Mather and Platt did a
 similar record in the UK.
 
 In the book Fire - Automatic Sprinklers in Australia and New Zealand 1886 -
 1968 by Harry Marryatt there is very good analysis of that time period. It
 was updated his 1986 edition which I think was called A Century of Fire
 Sprinklers( I don't have a copy of the later book).
 The figures in 1968 were;
 66.6%   1 head
 15.6%   2 heads
 5.9%3 heads
 3.2%  4 heads
 1.6%5 heads
 So 93% of sprinklered fires were 5 heads or less.
 There were 5720 recorded fires in this study.
 Satisfactory operation was 99.76% with 0.24% unsatisfactory incidents (14)
 
 Wormald still keep a record of sprinkler saves on our systems, but the NZ
 and Australian Fire Protection Associations and the NZ Fire Service try to
 keep a full list, but it lacks the Technical Detail that was recorded for
 over 100 years in the Wormald record.
 
 Trust this is of interest.
 Russell Gregory
 Christchurch, New Zealand
 
 -Original Message-
 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
 On Behalf Of Frans Stoop
 Sent: Thursday, 18 September 2014 4:53 a.m.
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Sprinkler statistics
 
 Gentlemen,
 
 Once I saw a sprinkler statistic table saying something like this (I don't
 remember the exact percentages):
 
 Regarding fires that are succesfully controlled by sprinklers
 50 % of the fires by 1 sprinkler
 66 % of the fires by 1 or 2 sprinklers
 75 % of the fires by upto 3 sprinklers
 80 % of the fires by upto 4 sprinklers
 83 % of the fires by upto 5 sprinklers
 etcetera...
 
 Does anyone recognize this table?
 If so, any idea where I can find it?
 
 I already found some statistics on the NFPA, AFSA, FM, SFPE and CIBV
 websites, but couldn't find this simple table.
 
 Met vriendelijke groet / Best regards,
 
 Frans Stoop
 TOS architecture  fire protection
 Netherlands f.st...@tosfire.com
 Tel. +31-24-324 0112
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Sprinklers on 3 Pipe

2014-09-19 Thread Jay Stough
I am talking about uprights without sprigs.  I don't have NFPA 13 in front
of me, but I found under obstructions where you can put sprinklers directly
on the pipe up to 2-1/2.  This was also found in the section for extended
coverage and Large Drop.  Also, the V3403 can be used for storage, but it
is listed as a  standard spray sprinkler.  I was going to advise the
customer that he should have these changed before signing a lease.

On Fri, Sep 19, 2014 at 4:02 PM, Cliff Whitfield cl...@fire-design.com
wrote:

 Ken,

 I assumed Jay was talking about having 3 lines without sprigs to the
 sprinklers.  I haven’t been where I could confirm in the book but I believe
 if this is what he's talking about, the heads would be required to be on
 sprigs.

 Cliff Whitfield, SET
 President
 Fire Design, Inc.
 Ph: 719-488-3479



 cl...@fire-design.com
 www.fire-design.com

 -Original Message-
 From: Sprinklerforum [mailto:
 sprinklerforum-boun...@lists.firesprinkler.org]
 On Behalf Of Parsley Consulting
 Sent: Friday, September 19, 2014 1:47 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Sprinklers on 3 Pipe

 I'm not sure Jay.  The tech sheet I looked at just now seems to suggest
 that in either the upright or pendent V3403 are listed for storage, when
 using density/area.  I looked at Victaulic sheet 40.20.

 Did you come across something else?
 *Ken Wagoner, SET
 *Parsley Consulting***
 *350 West 9th Avenue, Suite 206
 *Escondido, California 92025
 *Phone 760-745-6181*
 Visit our website http://www.parsleyconsulting.com/ ***
 On 9/19/2014 11:36 AM, Jay Stough wrote:
  I have a customer that is moving into a warehouse that was renovated in
  2013, using NFPA 13 (2007).  They have Victaulic 3403 upright sprinklers
  directly on 3 pipe.  Unless I am missing something, I am pretty sure
 this
  sprinkler is listed as a standard upright sprinkler and cannot be
 installed
  this way.  I have checked the spec sheet and appears to be a large
 orifice
  standard spray sprinkler.  Am I correct or am I missing a listing for
 this
  sprinkler?
 
 

 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org

 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org

 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org




-- 
*Jay Stough*
NICET IV LAYOUT
NICET III ITM
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Sprinklers on 3 Pipe

2014-09-19 Thread Ron Greenman
That was my on your first post without looking up the head and just going with 
your ssu determination.

Sent from my iPhone

 On Sep 19, 2014, at 4:47 PM, Jay Stough jaycs7...@gmail.com wrote:
 
 I am talking about uprights without sprigs.  I don't have NFPA 13 in front
 of me, but I found under obstructions where you can put sprinklers directly
 on the pipe up to 2-1/2.  This was also found in the section for extended
 coverage and Large Drop.  Also, the V3403 can be used for storage, but it
 is listed as a  standard spray sprinkler.  I was going to advise the
 customer that he should have these changed before signing a lease.
 
 On Fri, Sep 19, 2014 at 4:02 PM, Cliff Whitfield cl...@fire-design.com
 wrote:
 
 Ken,
 
 I assumed Jay was talking about having 3 lines without sprigs to the
 sprinklers.  I haven’t been where I could confirm in the book but I believe
 if this is what he's talking about, the heads would be required to be on
 sprigs.
 
 Cliff Whitfield, SET
 President
 Fire Design, Inc.
 Ph: 719-488-3479
 
 
 
 cl...@fire-design.com
 www.fire-design.com
 
 -Original Message-
 From: Sprinklerforum [mailto:
 sprinklerforum-boun...@lists.firesprinkler.org]
 On Behalf Of Parsley Consulting
 Sent: Friday, September 19, 2014 1:47 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Sprinklers on 3 Pipe
 
 I'm not sure Jay.  The tech sheet I looked at just now seems to suggest
 that in either the upright or pendent V3403 are listed for storage, when
 using density/area.  I looked at Victaulic sheet 40.20.
 
 Did you come across something else?
 *Ken Wagoner, SET
 *Parsley Consulting***
 *350 West 9th Avenue, Suite 206
 *Escondido, California 92025
 *Phone 760-745-6181*
 Visit our website http://www.parsleyconsulting.com/ ***
 On 9/19/2014 11:36 AM, Jay Stough wrote:
 I have a customer that is moving into a warehouse that was renovated in
 2013, using NFPA 13 (2007).  They have Victaulic 3403 upright sprinklers
 directly on 3 pipe.  Unless I am missing something, I am pretty sure
 this
 sprinkler is listed as a standard upright sprinkler and cannot be
 installed
 this way.  I have checked the spec sheet and appears to be a large
 orifice
 standard spray sprinkler.  Am I correct or am I missing a listing for
 this
 sprinkler?
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 
 
 
 -- 
 *Jay Stough*
 NICET IV LAYOUT
 NICET III ITM
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Formality question

2014-09-19 Thread Brad Casterline
Why do Technical Committee Members submit Public Input?

Thanks,

Brad Casterline
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Formality question

2014-09-19 Thread Steve Leyton
Because most of us drink so much after the meetings we lose track of what's 
already on the docket.

Steve 

div Original message /divdivFrom: Brad Casterline 
bcasterl...@fsc-inc.com /divdivDate:09/19/2014  8:35 PM  (GMT-08:00) 
/divdivTo: sprinklerforum@lists.firesprinkler.org /divdivSubject: 
Formality question /divdiv
/divWhy do Technical Committee Members submit Public Input?

Thanks,

Brad Casterline
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Formality question

2014-09-19 Thread Brad Casterline
And you forget you are one of the heavy lifters and think you can spot with one 
hand and drink wid the other?

 On Sep 19, 2014, at 10:48 PM, Steve Leyton st...@protectiondesign.com 
 wrote:
 
 Because most of us drink so much after the meetings we lose track of what's 
 already on the docket.
 
 Steve 
 
 div Original message /divdivFrom: Brad Casterline 
 bcasterl...@fsc-inc.com /divdivDate:09/19/2014  8:35 PM  (GMT-08:00) 
 /divdivTo: sprinklerforum@lists.firesprinkler.org /divdivSubject: 
 Formality question /divdiv
 /divWhy do Technical Committee Members submit Public Input?
 
 Thanks,
 
 Brad Casterline
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Formality question

2014-09-19 Thread Brad Casterline
It just seems like a conflict of interest,  which is fine for my government, I 
just wouldn't want it in my 13, 14, 20, or 24 

 On Sep 19, 2014, at 11:03 PM, Brad Casterline bcasterl...@fsc-inc.com wrote:
 
 And you forget you are one of the heavy lifters and think you can spot with 
 one hand and drink wid the other?
 
 On Sep 19, 2014, at 10:48 PM, Steve Leyton st...@protectiondesign.com 
 wrote:
 
 Because most of us drink so much after the meetings we lose track of what's 
 already on the docket.
 
 Steve 
 
 div Original message /divdivFrom: Brad Casterline 
 bcasterl...@fsc-inc.com /divdivDate:09/19/2014  8:35 PM  (GMT-08:00) 
 /divdivTo: sprinklerforum@lists.firesprinkler.org /divdivSubject: 
 Formality question /divdiv
 /divWhy do Technical Committee Members submit Public Input?
 
 Thanks,
 
 Brad Casterline
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Formality question

2014-09-19 Thread Steve Leyton
Kidding aside, committee members are most familiar with phasing and contextual 
issues - for most standards, in any given cycle at least half and sometimes 2/3 
of the proposals are what we refer to as editorial or clean-up.   NFPA 14 was a 
formatting mess when I got on and we've completely overhauled it in 4 cycles, 
intentionally drawing out the reorganization so we could get stuff into the 
sections where they belonged.   This extended to the definitions, 
chapterization ... the whole standard was considered new in 2007.   

You have to also remember that most committees include members who serve that 
committee because they are especially expert and/or interested in that topic.  
Who better to propose to that standard?   There's no conflict of interest in 
that the proposals and committee actions are available for public review and 
comment - the process is pretty transparent and as Roland explained, there's a 
Spanish Inquisition at the end for those who don't think the consensus process 
was truly served.

I have said this hundreds of times over the last few years:  Don't like it?  
Change it!  Make a proposal, make a comment, get involved in the process.   
How many people reading this have been to the annual NFPA Life Safety 
Conference?   How many stayed for the code hearing?   You know what they say 
about government, right?   People generally get the government they deserve.


-Original Message-
From: Sprinklerforum on behalf of Brad Casterline
Sent: Fri 9/19/2014 9:15 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Formality question
 
It just seems like a conflict of interest,  which is fine for my government, I 
just wouldn't want it in my 13, 14, 20, or 24 

 On Sep 19, 2014, at 11:03 PM, Brad Casterline bcasterl...@fsc-inc.com wrote:
 
 And you forget you are one of the heavy lifters and think you can spot with 
 one hand and drink wid the other?
 
 On Sep 19, 2014, at 10:48 PM, Steve Leyton st...@protectiondesign.com 
 wrote:
 
 Because most of us drink so much after the meetings we lose track of what's 
 already on the docket.
 
 Steve 
 
 div Original message /divdivFrom: Brad Casterline 
 bcasterl...@fsc-inc.com /divdivDate:09/19/2014  8:35 PM  (GMT-08:00) 
 /divdivTo: sprinklerforum@lists.firesprinkler.org /divdivSubject: 
 Formality question /divdiv
 /divWhy do Technical Committee Members submit Public Input?
 
 Thanks,
 
 Brad Casterline
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Formality question

2014-09-19 Thread Steve Leyton
I meant that first sentence to say phrasing.


-Original Message-
From: Sprinklerforum on behalf of Steve Leyton
Sent: Fri 9/19/2014 9:24 PM
To: sprinklerforum@lists.firesprinkler.org; 
sprinklerforum@lists.firesprinkler.org
Subject: RE: Formality question
 
Kidding aside, committee members are most familiar with phasing and contextual 
issues - for most standards, in any given cycle at least half and sometimes 2/3 
of the proposals are what we refer to as editorial or clean-up.   NFPA 14 was a 
formatting mess when I got on and we've completely overhauled it in 4 cycles, 
intentionally drawing out the reorganization so we could get stuff into the 
sections where they belonged.   This extended to the definitions, 
chapterization ... the whole standard was considered new in 2007.   

You have to also remember that most committees include members who serve that 
committee because they are especially expert and/or interested in that topic.  
Who better to propose to that standard?   There's no conflict of interest in 
that the proposals and committee actions are available for public review and 
comment - the process is pretty transparent and as Roland explained, there's a 
Spanish Inquisition at the end for those who don't think the consensus process 
was truly served.

I have said this hundreds of times over the last few years:  Don't like it?  
Change it!  Make a proposal, make a comment, get involved in the process.   
How many people reading this have been to the annual NFPA Life Safety 
Conference?   How many stayed for the code hearing?   You know what they say 
about government, right?   People generally get the government they deserve.


-Original Message-
From: Sprinklerforum on behalf of Brad Casterline
Sent: Fri 9/19/2014 9:15 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Formality question
 
It just seems like a conflict of interest,  which is fine for my government, I 
just wouldn't want it in my 13, 14, 20, or 24 

 On Sep 19, 2014, at 11:03 PM, Brad Casterline bcasterl...@fsc-inc.com wrote:
 
 And you forget you are one of the heavy lifters and think you can spot with 
 one hand and drink wid the other?
 
 On Sep 19, 2014, at 10:48 PM, Steve Leyton st...@protectiondesign.com 
 wrote:
 
 Because most of us drink so much after the meetings we lose track of what's 
 already on the docket.
 
 Steve 
 
 div Original message /divdivFrom: Brad Casterline 
 bcasterl...@fsc-inc.com /divdivDate:09/19/2014  8:35 PM  (GMT-08:00) 
 /divdivTo: sprinklerforum@lists.firesprinkler.org /divdivSubject: 
 Formality question /divdiv
 /divWhy do Technical Committee Members submit Public Input?
 
 Thanks,
 
 Brad Casterline
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Formality question

2014-09-19 Thread John Denhardt
Very we'll said Steve.  Could not  agree more.  Get involved is the bottom 
line. It makes you stay current and you see what is the intent of the standard. 

Sent from my iPhone

 On Sep 20, 2014, at 12:20 AM, Steve Leyton st...@protectiondesign.com 
 wrote:
 
 Kidding aside, committee members are most familiar with phasing and 
 contextual issues - for most standards, in any given cycle at least half and 
 sometimes 2/3 of the proposals are what we refer to as editorial or clean-up. 
   NFPA 14 was a formatting mess when I got on and we've completely overhauled 
 it in 4 cycles, intentionally drawing out the reorganization so we could get 
 stuff into the sections where they belonged.   This extended to the 
 definitions, chapterization ... the whole standard was considered new in 
 2007.   
 
 You have to also remember that most committees include members who serve that 
 committee because they are especially expert and/or interested in that topic. 
  Who better to propose to that standard?   There's no conflict of interest in 
 that the proposals and committee actions are available for public review and 
 comment - the process is pretty transparent and as Roland explained, there's 
 a Spanish Inquisition at the end for those who don't think the consensus 
 process was truly served.
 
 I have said this hundreds of times over the last few years:  Don't like it?  
 Change it!  Make a proposal, make a comment, get involved in the process.   
 How many people reading this have been to the annual NFPA Life Safety 
 Conference?   How many stayed for the code hearing?   You know what they say 
 about government, right?   People generally get the government they deserve.
 
 
 -Original Message-
 From: Sprinklerforum on behalf of Brad Casterline
 Sent: Fri 9/19/2014 9:15 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Formality question
 
 It just seems like a conflict of interest,  which is fine for my government, 
 I just wouldn't want it in my 13, 14, 20, or 24 
 
 On Sep 19, 2014, at 11:03 PM, Brad Casterline bcasterl...@fsc-inc.com 
 wrote:
 
 And you forget you are one of the heavy lifters and think you can spot with 
 one hand and drink wid the other?
 
 On Sep 19, 2014, at 10:48 PM, Steve Leyton st...@protectiondesign.com 
 wrote:
 
 Because most of us drink so much after the meetings we lose track of what's 
 already on the docket.
 
 Steve 
 
 div Original message /divdivFrom: Brad Casterline 
 bcasterl...@fsc-inc.com /divdivDate:09/19/2014  8:35 PM  (GMT-08:00) 
 /divdivTo: sprinklerforum@lists.firesprinkler.org /divdivSubject: 
 Formality question /divdiv
 /divWhy do Technical Committee Members submit Public Input?
 
 Thanks,
 
 Brad Casterline
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Formality question

2014-09-19 Thread Brad Casterline
Well thanks guys. I thought I was down for the count but hell, I might be just 
getting started. I did get an NFPA 2015 C  E (get outta here Chicago in June 
shut up ) Education Session proposal in under the wire.

 On Sep 19, 2014, at 11:23 PM, John Denhardt jdenha...@stricklandfire.com 
 wrote:
 
 Very we'll said Steve.  Could not  agree more.  Get involved is the bottom 
 line. It makes you stay current and you see what is the intent of the 
 standard. 
 
 Sent from my iPhone
 
 On Sep 20, 2014, at 12:20 AM, Steve Leyton st...@protectiondesign.com 
 wrote:
 
 Kidding aside, committee members are most familiar with phasing and 
 contextual issues - for most standards, in any given cycle at least half and 
 sometimes 2/3 of the proposals are what we refer to as editorial or 
 clean-up.   NFPA 14 was a formatting mess when I got on and we've completely 
 overhauled it in 4 cycles, intentionally drawing out the reorganization so 
 we could get stuff into the sections where they belonged.   This extended to 
 the definitions, chapterization ... the whole standard was considered new in 
 2007.   
 
 You have to also remember that most committees include members who serve 
 that committee because they are especially expert and/or interested in that 
 topic.  Who better to propose to that standard?   There's no conflict of 
 interest in that the proposals and committee actions are available for 
 public review and comment - the process is pretty transparent and as Roland 
 explained, there's a Spanish Inquisition at the end for those who don't 
 think the consensus process was truly served.
 
 I have said this hundreds of times over the last few years:  Don't like it? 
  Change it!  Make a proposal, make a comment, get involved in the process.  
  How many people reading this have been to the annual NFPA Life Safety 
 Conference?   How many stayed for the code hearing?   You know what they say 
 about government, right?   People generally get the government they deserve.
 
 
 -Original Message-
 From: Sprinklerforum on behalf of Brad Casterline
 Sent: Fri 9/19/2014 9:15 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Formality question
 
 It just seems like a conflict of interest,  which is fine for my government, 
 I just wouldn't want it in my 13, 14, 20, or 24 
 
 On Sep 19, 2014, at 11:03 PM, Brad Casterline bcasterl...@fsc-inc.com 
 wrote:
 
 And you forget you are one of the heavy lifters and think you can spot with 
 one hand and drink wid the other?
 
 On Sep 19, 2014, at 10:48 PM, Steve Leyton st...@protectiondesign.com 
 wrote:
 
 Because most of us drink so much after the meetings we lose track of 
 what's already on the docket.
 
 Steve 
 
 div Original message /divdivFrom: Brad Casterline 
 bcasterl...@fsc-inc.com /divdivDate:09/19/2014  8:35 PM  (GMT-08:00) 
 /divdivTo: sprinklerforum@lists.firesprinkler.org /divdivSubject: 
 Formality question /divdiv
 /divWhy do Technical Committee Members submit Public Input?
 
 Thanks,
 
 Brad Casterline
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Formality question

2014-09-19 Thread Brad Casterline
All I can do now is keep my fingers crossed til about mid Nov to see if it is 
accepted or not

 On Sep 19, 2014, at 11:37 PM, Brad Casterline bcasterl...@fsc-inc.com wrote:
 
 Well thanks guys. I thought I was down for the count but hell, I might be 
 just getting started. I did get an NFPA 2015 C  E (get outta here Chicago in 
 June shut up ) Education Session proposal in under the wire.
 
 On Sep 19, 2014, at 11:23 PM, John Denhardt jdenha...@stricklandfire.com 
 wrote:
 
 Very we'll said Steve.  Could not  agree more.  Get involved is the bottom 
 line. It makes you stay current and you see what is the intent of the 
 standard. 
 
 Sent from my iPhone
 
 On Sep 20, 2014, at 12:20 AM, Steve Leyton st...@protectiondesign.com 
 wrote:
 
 Kidding aside, committee members are most familiar with phasing and 
 contextual issues - for most standards, in any given cycle at least half 
 and sometimes 2/3 of the proposals are what we refer to as editorial or 
 clean-up.   NFPA 14 was a formatting mess when I got on and we've 
 completely overhauled it in 4 cycles, intentionally drawing out the 
 reorganization so we could get stuff into the sections where they belonged. 
   This extended to the definitions, chapterization ... the whole standard 
 was considered new in 2007.   
 
 You have to also remember that most committees include members who serve 
 that committee because they are especially expert and/or interested in that 
 topic.  Who better to propose to that standard?   There's no conflict of 
 interest in that the proposals and committee actions are available for 
 public review and comment - the process is pretty transparent and as Roland 
 explained, there's a Spanish Inquisition at the end for those who don't 
 think the consensus process was truly served.
 
 I have said this hundreds of times over the last few years:  Don't like 
 it?  Change it!  Make a proposal, make a comment, get involved in the 
 process.   How many people reading this have been to the annual NFPA Life 
 Safety Conference?   How many stayed for the code hearing?   You know what 
 they say about government, right?   People generally get the government 
 they deserve.
 
 
 -Original Message-
 From: Sprinklerforum on behalf of Brad Casterline
 Sent: Fri 9/19/2014 9:15 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Formality question
 
 It just seems like a conflict of interest,  which is fine for my 
 government, I just wouldn't want it in my 13, 14, 20, or 24 
 
 On Sep 19, 2014, at 11:03 PM, Brad Casterline bcasterl...@fsc-inc.com 
 wrote:
 
 And you forget you are one of the heavy lifters and think you can spot 
 with one hand and drink wid the other?
 
 On Sep 19, 2014, at 10:48 PM, Steve Leyton st...@protectiondesign.com 
 wrote:
 
 Because most of us drink so much after the meetings we lose track of 
 what's already on the docket.
 
 Steve 
 
 div Original message /divdivFrom: Brad Casterline 
 bcasterl...@fsc-inc.com /divdivDate:09/19/2014  8:35 PM  
 (GMT-08:00) /divdivTo: sprinklerforum@lists.firesprinkler.org 
 /divdivSubject: Formality question /divdiv
 /divWhy do Technical Committee Members submit Public Input?
 
 Thanks,
 
 Brad Casterline
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Formality question

2014-09-19 Thread Brad Casterline
If I make it, I will be a co-presenter again- but try harder to speak this 
time. It will be my 2nd convention in my 40 year career, and be the 2nd in a 
row, and I will be dragging the Presenter to the podium, and in his hands will 
be HIS original Printouts of The Very First Density/Area Curves and supporting 
calculations.

 On Sep 19, 2014, at 11:51 PM, Brad Casterline bcasterl...@fsc-inc.com wrote:
 
 All I can do now is keep my fingers crossed til about mid Nov to see if it is 
 accepted or not
 
 On Sep 19, 2014, at 11:37 PM, Brad Casterline bcasterl...@fsc-inc.com 
 wrote:
 
 Well thanks guys. I thought I was down for the count but hell, I might be 
 just getting started. I did get an NFPA 2015 C  E (get outta here Chicago 
 in June shut up ) Education Session proposal in under the wire.
 
 On Sep 19, 2014, at 11:23 PM, John Denhardt jdenha...@stricklandfire.com 
 wrote:
 
 Very we'll said Steve.  Could not  agree more.  Get involved is the bottom 
 line. It makes you stay current and you see what is the intent of the 
 standard. 
 
 Sent from my iPhone
 
 On Sep 20, 2014, at 12:20 AM, Steve Leyton st...@protectiondesign.com 
 wrote:
 
 Kidding aside, committee members are most familiar with phasing and 
 contextual issues - for most standards, in any given cycle at least half 
 and sometimes 2/3 of the proposals are what we refer to as editorial or 
 clean-up.   NFPA 14 was a formatting mess when I got on and we've 
 completely overhauled it in 4 cycles, intentionally drawing out the 
 reorganization so we could get stuff into the sections where they 
 belonged.   This extended to the definitions, chapterization ... the whole 
 standard was considered new in 2007.   
 
 You have to also remember that most committees include members who serve 
 that committee because they are especially expert and/or interested in 
 that topic.  Who better to propose to that standard?   There's no conflict 
 of interest in that the proposals and committee actions are available for 
 public review and comment - the process is pretty transparent and as 
 Roland explained, there's a Spanish Inquisition at the end for those who 
 don't think the consensus process was truly served.
 
 I have said this hundreds of times over the last few years:  Don't like 
 it?  Change it!  Make a proposal, make a comment, get involved in the 
 process.   How many people reading this have been to the annual NFPA Life 
 Safety Conference?   How many stayed for the code hearing?   You know what 
 they say about government, right?   People generally get the government 
 they deserve.
 
 
 -Original Message-
 From: Sprinklerforum on behalf of Brad Casterline
 Sent: Fri 9/19/2014 9:15 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Formality question
 
 It just seems like a conflict of interest,  which is fine for my 
 government, I just wouldn't want it in my 13, 14, 20, or 24 
 
 On Sep 19, 2014, at 11:03 PM, Brad Casterline bcasterl...@fsc-inc.com 
 wrote:
 
 And you forget you are one of the heavy lifters and think you can spot 
 with one hand and drink wid the other?
 
 On Sep 19, 2014, at 10:48 PM, Steve Leyton 
 st...@protectiondesign.com wrote:
 
 Because most of us drink so much after the meetings we lose track of 
 what's already on the docket.
 
 Steve 
 
 div Original message /divdivFrom: Brad Casterline 
 bcasterl...@fsc-inc.com /divdivDate:09/19/2014  8:35 PM  
 (GMT-08:00) /divdivTo: sprinklerforum@lists.firesprinkler.org 
 /divdivSubject: Formality question /divdiv
 /divWhy do Technical Committee Members submit Public Input?
 
 Thanks,
 
 Brad Casterline
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org